The Type2 Powell's Method mode is not appropriate for what you are
trying to do. If you are getting more chatter in your collector control
than you want or if you are running at times when the collector cannot
sustain an outlet temperature higher than the tank temperature then you
need to modify the temperature deadbands in the differential controller
that turns on and off the collector pump. A "turn on" temperature
difference of 10C and a "turn off" temperature difference of 2C would be
good starting places.
regards,
David
On 08/25/2015 09:05, Manrique Delgado Benjamin wrote:
>
> Hi,
>
> I am getting poor results by using Type2b to control a solar
> collector, since it operates at some time-steps when it shouldn’t (for
> example, when the temperature coming out from the tank is higher than
> the SC output temperature, effectively cooling the tank). I tried to
> switch to Type 2a, and changed to Powell’s method, but the model won’t
> run since I am using an Aquastat in a different part of the model, and
> that one requires the Successive substitution method.
>
> Has anyone faced this problem before?
>
> I am using a 0.25 hour resolution.
>
> In advance, thanks for your help.
>
> Best regards,
>
> Benjamin Manrique D.
>
>
>
> _______________________________________________
> TRNSYS-users mailing list
> TRNSYS-users at lists.onebuilding.org
> http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org
--
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI 53703 USA
P:+1.608.274.2577
F:+1.608.278.1475
d.bradley at tess-inc.com
http://www.tess-inc.com
http://www.trnsys.com
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20150825/d1825fa7/attachment.htm>
More information about the TRNSYS-users
mailing list