[TRNSYS-users] FW: FW: want to design an array of hybrid pv panels or combination of hybrid pv panels and transparant pv panels

David BRADLEY d.bradley at tess-inc.com
Thu Jul 23 07:55:39 PDT 2015


Benjamin,
   If you have access to the TESS Storage Library then you can use 
Type534, which can have quite a few inlets and outlets. If you are using 
only the standard component library then you will need to use some 
instances of Type11 to mix all the returns from your solar collectors 
before they go into the tank. You will also need to then use some 
instances of Type11 at the outlet of the tank to split the mixed flow so 
that it goes back to the appropriate collector.
kind regards,
  David


On 07/23/2015 00:30, benjamin stobbe wrote:
> Sorry to be more clear i am talking about a Stratified Storage Tank, 
> because i saw by some other tanks there is the option for 2 inlets i 
> want 4 inlets if possible from every facade, if you use water from 
> other solar panels the water is warmer and less heat exchange and less 
> cooling for the solar panels so this option is not feasable.
>
> Best regards,
>
> Benjamin
>
> ------------------------------------------------------------------------
> From: benjamin_stobbe at hotmail.com
> To: trnsys-users at lists.onebuilding.org
> Date: Thu, 23 Jul 2015 06:57:02 +0200
> Subject: [TRNSYS-users] FW: want to design an array of hybrid pv 
> panels or combination of hybrid pv panels and transparant pv panels
>
> Dear everyone,
>
> I had a followup on this question. I have that building and a building 
> has four different facades with four different direction but if i want 
> to model this with one tank is this possible. So a tank with more 
> inputs or must i then connect the solar panels with eachother and then 
> to the tank.
>
> Best regards,
>
> Benjamin Stobbe
>
> ------------------------------------------------------------------------
> From: benjamin_stobbe at hotmail.com
> To: trnsys-users at lists.onebuilding.org
> Date: Wed, 22 Jul 2015 10:37:28 +0800
> Subject: [TRNSYS-users] want to design an array of hybrid pv panels or 
> combination of hybrid pv panels and transparant pv panels
>
> Dear people,
>
> I am busy with designing a solar system on a facade of a building and 
> i want this to be a combination of transparent solar cells and hybrid 
> pv panels. Now the last weeks I already figured the hybrid pv(PV-t) 
> panels and I thought about how can I do an array. There is a possible 
> to do an array of pv-panels but this is not hybrid and I thought I can 
> make the surface of the hybrid pv panel bigger but this also is not 
> what you want because then you also have to increase the amount of 
> pipes and this does not seem to work that good. For the problem 
> transparent pv panels I can just use array of solar panels and make 
> the yield times the factor of transparent or make the panels smaller.
>
> But I hope someone can help me with the hybrid pv-t panels.
>
> Best regards,
>
> Benjamin Stobbe
>
>
> _______________________________________________ TRNSYS-users mailing 
> list TRNSYS-users at lists.onebuilding.org 
> http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org
>
> _______________________________________________ TRNSYS-users mailing 
> list TRNSYS-users at lists.onebuilding.org 
> http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org
> _______________________________________________ TRNSYS-users mailing 
> list TRNSYS-users at lists.onebuilding.org 
> http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org
>
>
> _______________________________________________
> TRNSYS-users mailing list
> TRNSYS-users at lists.onebuilding.org
> http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org

-- 
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI  53703 USA

P:+1.608.274.2577
F:+1.608.278.1475
d.bradley at tess-inc.com

http://www.tess-inc.com
http://www.trnsys.com

-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20150723/0110984a/attachment.htm>


More information about the TRNSYS-users mailing list