Donya,
   Because the 3d model contains the geometry information needed to 
determine the solar radiation falling on each surface, Type56 
automatically gets solar radiation from the same data file as is being 
used to provide the ambient temperature. You should be able to use 
Type99 directly and Type56 should be able to pick up the radiation 
itself. If you want to be more transparent about it all (and provide the 
radiation yourself via individual links to the building model the way we 
used to do) then you can open the *.b17 in TRNBuild and double click on 
each of the orientations shown in the project info window. Set any of 
the orientations you want from "internal calculation" to "external by 
another component." When you return to the Studio and update the 
building variable list you will have three new inputs for each 
orientation in your building description.
Kind regards,
  David
On 3/27/2015 7:38 AM, Donya Sheikh Khan wrote:
> Hi,
>
> When one generates a 3D model with the TRNSYS wizard, there is no 
> connection made between the amount of radiation from type15 and 
> TRNBuild type56. How does TRNBuild than receive information about the 
> amount of radiation from the sun?
>
> The reason for asking is, that I would like to use my own weather data 
> file (so I have to use type99 or similar), but if type56 doesn't need 
> a link between weather file telling it the amount of radiation (from 
> what I see), how can I use my own weather file?
>
> -- 
> Regards
> Donya
>
>
>
> _______________________________________________
> TRNSYS-users mailing list
> TRNSYS-users at lists.onebuilding.org
> http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org
-- 
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI  53703 USA
P:+1.608.274.2577
F:+1.608.278.1475
d.bradley at tess-inc.com
http://www.tess-inc.com
http://www.trnsys.com
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20150327/c37aeaa0/attachment.htm>
    
    
More information about the TRNSYS-users
mailing list