[TRNSYS-users] Generating Shading/insolation matrix - Success and fail with two different TRNSYS versions

Roberto Ruiz doppler83 at gmail.com
Tue May 12 07:25:43 PDT 2015


Dear all,

I'm experiencing a problem when try to generate the shading/insolation 
matrices for the detailed model of /Beam/diffused distribution/ (TRNBUILD).
I have the TRNSYS version 17.02.0004 (in my computer).

The error is the following:
/TRNSHD Message     14 : The internal solar distribution did not sum up 
1. Make sure that the zones with detailed beam radiation mode are CONVEX 
and CLOSED!!//"/
The file (shd) indicates the surface and thermal zone (external wall - 
surface 237 - zone B6_F2_OF) that is failing.
After verifying again the idf file I could not find any error in the 
geometrical model (.idf).

I have also the TRNSYS version 17.01.0025 (in the server of the lab) and 
when I do the same exercise: importing the same idf to TRNSYS, selecting 
detailed radiation model for all the zones and generating 
shading/insolation matrices. Everything goes well!

In order to understand better the problem, I modified the .bui model 
used in the version 17.02.0004 by setting the standard radiation model 
only for problematic zone (B6_F2_OF) and the remaining zones were kept 
as detailed. Then I could get the shading/insolation matrices.

Then looking at the matrix files (_vfm) provided by the 2 versions 
(below), I realized that version 17.02.0004 doesn't calculate the matrix 
for the zone in question (what was supposed to happen) but at the same 
time, it means that the version 17.01.0025  does not see any problem 
with this zone (B6_F2_OF). /*

Version 17.02.0004*/



/*Version 17.01.0025*/


Since the idf file used is exactly the same in both cases, the problem 
must come from the TRNSYS version.

Any of you have experience something similar? Any clue?
I attach the idf file used and the shd file providing the error.

Best Regards,
Roberto Ruiz
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20150512/8ea66d31/attachment-0001.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/png
Size: 44997 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20150512/8ea66d31/attachment-0002.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/png
Size: 79458 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20150512/8ea66d31/attachment-0003.png>
-------------- next part --------------
!-   ===========  BUI-Template for TRNSYS 17 ==========
!-T17_Template_Start
!-*********************************************************************************************************************************************************************************************************
!-*  TRNBuild   1.0.142
!-*********************************************************************************************************************************************************************************************************
!-*   BUILDING DESCRIPTIONS FILE TRNSYS
!-*   FOR BUILDING:   
!-*   GET BY WORKING WITH TRNBuild 1.0 for Windows
!-*********************************************************************************************************************************************************************************************************
!-*
!-*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
!-*  C o m m e n t s
!-*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
!-*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
!-*  P r o j e c t
!-*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
!-*+++ PROJECT
!-*+++ TITLE=BELGIAN DEMO - ISIL BUILDING
!-*+++ DESCRIPTION=EDUCATIONAL BUILDING (HEPL)
!-*+++ CREATED=ROBERTO RUIZ
!-*+++ ADDRESS=UNIVERSITÉ DE LIÈGE (ULG)
!-*+++ CITY=LIEGE
!-*+++ SWITCH=UNDEFINED
!-*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
!-*  P r o p e r t i e s
!-*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
!-PROPERTIES
!- DENSITY=1.204 : CAPACITY=1.012 : PRESSURE=101325.000 : HVAPOR=2454.0 : SIGMA=2.041e-007 : RTEMP=293.15
!-*--- alpha calculation -------------------
!- KFLOORUP=7.2 : EFLOORUP=0.31 : KFLOORDOWN=3.888 : EFLOORDOWN=0.31
!- KCEILUP=7.2 : ECEILUP=0.31 : KCEILDOWN=3.888 : ECEILDOWN=0.31
!- KVERTICAL=5.76 : EVERTICAL=0.3
!-*
!-*++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++
!-TYPES
!-*++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++
!-*
!-*--------------------------------------------------------------------------------------
!-*  L a y e r s
!-*--------------------------------------------------------------------------------------
!-LAYER PLASTERBOA
!- CONDUCTIVITY=  0.576 : CAPACITY=   0.84 : DENSITY=    950
!-LAYER FBRGLS_ASHRAE
!- CONDUCTIVITY=  0.144 : CAPACITY=   0.84 : DENSITY=     12
!-LAYER WD_SIDN_ASHRA
!- CONDUCTIVITY=  0.504 : CAPACITY=    0.9 : DENSITY=    530
!-LAYER TMBR_FLR_ASHR
!- CONDUCTIVITY=  0.504 : CAPACITY=    1.2 : DENSITY=    650
!-LAYER INS_FLR_ASH
!- RESISTANCE=    6.965
!-LAYER RFDCK_ASHRAE
!- CONDUCTIVITY=  0.504 : CAPACITY=    0.9 : DENSITY=    530
!-LAYER CONC_SLAB
!- CONDUCTIVITY=  4.068 : CAPACITY=      1 : DENSITY=   1400
!-LAYER INS_FLR_ASH_900
!- RESISTANCE=    6.993
!-LAYER CONCRETE
!- CONDUCTIVITY=  4.068 : CAPACITY=      1 : DENSITY=   1400
!-LAYER WATERPROOFING
!- CONDUCTIVITY=   0.61 : CAPACITY=      1 : DENSITY=   1200
!-LAYER MINERAL_WOOL
!- CONDUCTIVITY=   0.16 : CAPACITY=    0.9 : DENSITY=     80
!-LAYER MORTAR
!- CONDUCTIVITY=   5.04 : CAPACITY=      1 : DENSITY=   2000
!-LAYER STEELPROFILED
!- CONDUCTIVITY=407.942 : CAPACITY=  0.418 : DENSITY=   6600
!-LAYER BRICK_SOLID
!- CONDUCTIVITY=  3.132 : CAPACITY=    1.4 : DENSITY=   1800
!-LAYER BRICK_PERFORATED
!- CONDUCTIVITY=  2.736 : CAPACITY=      1 : DENSITY=   1600
!-LAYER VERTICAL_AIR_LAYER
!- RESISTANCE=    0.047
!-LAYER HORIZONTAL_AIR_LAYER
!- RESISTANCE=    0.047
!-LAYER LIMESTONE
!- CONDUCTIVITY=   3.56 : CAPACITY=      1 : DENSITY=   1800
!-LAYER TILE
!- CONDUCTIVITY=    3.6 : CAPACITY=      1 : DENSITY=   2000
!-*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
!-*  I n p u t s
!-*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
!-INPUTS TGROUND TBOUNDARY BRIGHT
!-*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
!-*  S c h e d u l e s
!-*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
!-SCHEDULE WORKDAY
!- HOURS =0.000 8.000 18.000 24.0
!- VALUES=0 1. 0 0 
!-SCHEDULE WEEKEND
!- HOURS =0.000 1.000 24.0
!- VALUES=0 0 0 
!-SCHEDULE WORKLIGHT
!- HOURS =0.000 8.000 18.000 24.0
!- VALUES=0 1. 0 0 
!-SCHEDULE DAYNIGHT
!- HOURS =0.000 6.000 18.000 24.0
!- VALUES=0 1. 0 0 
!-SCHEDULE USE
!- DAYS=1 2 3 4 5 6 7
!- HOURLY=WORKDAY WORKDAY WORKDAY WORKDAY WORKDAY WEEKEND WEEKEND
!-SCHEDULE LIGHT
!- DAYS=1 2 3 4 5 6 7
!- HOURLY=WORKLIGHT WORKLIGHT WORKLIGHT WORKLIGHT WORKLIGHT WEEKEND WEEKEND
!-SCHEDULE SETOFF
!- DAYS=1 2 3 4 5 6 7
!- HOURLY=DAYNIGHT DAYNIGHT DAYNIGHT DAYNIGHT DAYNIGHT WEEKEND WEEKEND
!-*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
!-*  W a l l s
!-*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
!-WALL BND_WALL
!- LAYERS   = CONCRETE MORTAR 
!- THICKNESS= 0.2      0.08   
!- ABS-FRONT= 0.6   : ABS-BACK= 0.6  
!- EPS-FRONT= 0.9   : EPS-BACK= 0.9  
!- HFRONT   = 27.7 : HBACK= 27.7
!-WALL EXT_WALL_NE_EF_AL
!- LAYERS   = CONCRETE BRICK_SOLID 
!- THICKNESS= 0.3      0.12        
!- ABS-FRONT= 0.6   : ABS-BACK= 0.6  
!- EPS-FRONT= 0.9   : EPS-BACK= 0.9  
!- HFRONT   = 27.7 : HBACK= 90
!-WALL EXT_ROOF_SR
!- LAYERS   = CONCRETE HORIZONTAL_AIR_LAYER 
!- THICKNESS= 0.2      0                    
!- ABS-FRONT= 0.6   : ABS-BACK= 0.6  
!- EPS-FRONT= 0.9   : EPS-BACK= 0.9  
!- HFRONT   = 36 : HBACK= 90
!-WALL EXT_FLOOR
!- LAYERS   = TMBR_FLR_ASHR INS_FLR_ASH 
!- THICKNESS= 0.03          0           
!- ABS-FRONT= 0.6   : ABS-BACK= 0.6  
!- EPS-FRONT= 0.9   : EPS-BACK= 0.9  
!- HFRONT   = 11 : HBACK= 11
!-WALL BND_CEILING
!- LAYERS   = CONC_SLAB 
!- THICKNESS= 0.08      
!- ABS-FRONT= 0.6   : ABS-BACK= 0.6  
!- EPS-FRONT= 0.9   : EPS-BACK= 0.9  
!- HFRONT   = 11 : HBACK= 11
!-WALL BND_FLOOR
!- LAYERS   = TMBR_FLR_ASHR INS_FLR_ASH 
!- THICKNESS= 0.03          0           
!- ABS-FRONT= 0.6   : ABS-BACK= 0.6  
!- EPS-FRONT= 0.9   : EPS-BACK= 0.9  
!- HFRONT   = 11 : HBACK= 11
!-WALL GROUND_FLOOR
!- LAYERS   = CONCRETE MORTAR TILE  
!- THICKNESS= 0.2      0.08   0.02  
!- ABS-FRONT= 0.6   : ABS-BACK= 0.6  
!- EPS-FRONT= 0.9   : EPS-BACK= 0.9  
!- HFRONT   = 21.2 : HBACK= 0.001
!-WALL ADJ_WALL
!- LAYERS   = CONCRETE MORTAR 
!- THICKNESS= 0.2      0.08   
!- ABS-FRONT= 0.6   : ABS-BACK= 0.6  
!- EPS-FRONT= 0.9   : EPS-BACK= 0.9  
!- HFRONT   = 27.7 : HBACK= 27.7
!-WALL ADJ_CEILING
!- LAYERS   = CONCRETE MORTAR TILE  
!- THICKNESS= 0.2      0.08   0.02  
!- ABS-FRONT= 0.6   : ABS-BACK= 0.6  
!- EPS-FRONT= 0.9   : EPS-BACK= 0.9  
!- HFRONT   = 21.2 : HBACK= 21.2
!-WALL EXT_WALL_SW_EF_L0
!- LAYERS   = CONCRETE LIMESTONE 
!- THICKNESS= 0.38     0.1       
!- ABS-FRONT= 0.6   : ABS-BACK= 0.6  
!- EPS-FRONT= 0.9   : EPS-BACK= 0.9  
!- HFRONT   = 27.7 : HBACK= 90
!-WALL EXT_WALL_SW_EF_RL
!- LAYERS   = CONCRETE LIMESTONE 
!- THICKNESS= 0.3      0.1       
!- ABS-FRONT= 0.6   : ABS-BACK= 0.6  
!- EPS-FRONT= 0.9   : EPS-BACK= 0.9  
!- HFRONT   = 27.7 : HBACK= 90
!-WALL EXT_WALL_SW_EF_GL
!- LAYERS   = CONCRETE MINERAL_WOOL HORIZONTAL_AIR_LAYER 
!- THICKNESS= 0.2      0.02         0                    
!- ABS-FRONT= 0.6   : ABS-BACK= 0.6  
!- EPS-FRONT= 0.9   : EPS-BACK= 0.9  
!- HFRONT   = 27.7 : HBACK= 90
!-WALL EXT_WALL_IF_S0
!- LAYERS   = CONCRETE LIMESTONE 
!- THICKNESS= 0.38     0.1       
!- ABS-FRONT= 0.6   : ABS-BACK= 0.6  
!- EPS-FRONT= 0.9   : EPS-BACK= 0.9  
!- HFRONT   = 27.7 : HBACK= 90
!-WALL EXT_WALL_IF_RL
!- LAYERS   = CONCRETE BRICK_PERFORATED 
!- THICKNESS= 0.38     0.12             
!- ABS-FRONT= 0.6   : ABS-BACK= 0.6  
!- EPS-FRONT= 0.9   : EPS-BACK= 0.9  
!- HFRONT   = 27.7 : HBACK= 90
!-WALL EXT_ROOF_FR
!- LAYERS   = CONCRETE WATERPROOFING 
!- THICKNESS= 0.2      0.08          
!- ABS-FRONT= 0.6   : ABS-BACK= 0.6  
!- EPS-FRONT= 0.9   : EPS-BACK= 0.9  
!- HFRONT   = 36 : HBACK= 90
!-*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
!-*  W i n d o w s
!-*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
!-WINDOW EXT_WINDOW_SG
!- WINID=6001 : HINSIDE=11 : HOUTSIDE=64 : SLOPE=90 : SPACID=0 : WWID=0 : WHEIG=0 : FFRAME=0.3 : UFRAME=10.9091 : ABSFRAME=0.6 : RISHADE=0 : RESHADE=0 : REFLISHADE=0.5 : REFLOSHADE=0.5 : ;
!- CCISHADE=0.5 : EPSFRAME=0.9 : EPSISHADE=0.9
!-WINDOW EXT_WINDOW_DG
!- WINID=6001 : HINSIDE=11 : HOUTSIDE=64 : SLOPE=90 : SPACID=0 : WWID=0 : WHEIG=0 : FFRAME=0.3 : UFRAME=10.9091 : ABSFRAME=0.6 : RISHADE=0 : RESHADE=0 : REFLISHADE=0.5 : REFLOSHADE=0.5 : ;
!- CCISHADE=0.5 : EPSFRAME=0.9 : EPSISHADE=0.9
!-WINDOW ADJ_WINDOW
!- WINID=6001 : HINSIDE=11 : HOUTSIDE=64 : SLOPE=90 : SPACID=0 : WWID=0 : WHEIG=0 : FFRAME=0.3 : UFRAME=10.9091 : ABSFRAME=0.6 : RISHADE=0 : RESHADE=0 : REFLISHADE=0.5 : REFLOSHADE=0.5 : ;
!- CCISHADE=0.5 : EPSFRAME=0.9 : EPSISHADE=0.9
!-*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
!-*  D e f a u l t  G a i n s
!-*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
!-*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
!-*  O t h e r  G a i n s
!-*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
!-*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
!-*  C o m f o r t
!-*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
!-*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
!-*  I n f i l t r a t i o n
!-*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
!-*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
!-*  V e n t i l a t i o n
!-*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
!-*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
!-*  C o o l i n g
!-*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
!-*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
!-*  H e a t i n g
!-*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
!-*
!-*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
!-*  Z o n e s
!-*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
!-ZONES 
!-*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
!-*  O r i e n t a t i o n s
!-*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
!-ORIENTATIONS H_0_0 
!-*
!-*++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++
!-BUILDING
!-*++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++
!-
!-*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
!-*  O u t p u t s
!-*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
!-OUTPUTS
!- TRANSFER : TIMEBASE=1.000
!- DEFAULT
!-*
!-*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
!-*  E n d
!-*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
!-END
!-
!-_EXTENSION_WINPOOL_START_
!-Window 5.2  v5.2.17  DOE-2 Data File : Multi Band Calculation
!-Unit System : SI
!-Name        : DOE-2 WINDOW LIB
!-Desc        : ASH140 DBLE - MOD
!-Window ID   : 6001
!-Tilt        : 90.0
!-Glazings    : 2
!-Frame       :  2 Al w/break            5.680
!-Spacer      :  1 Class1                2.330  -0.010   0.138
!-Total Height: 1500.0 mm
!-Total Width : 1200.0 mm
!-Glass Height: 1385.7 mm
!-Glass Width : 1085.7 mm
!-Mullion     : None
!-Gap        Thick    Cond  dCond    Vis   dVis   Dens   dDens     Pr     dPr
!-1 Air       13.0 0.02407  7.760  1.722  4.940  1.292 -0.0046  0.720 -0.0002
!-2              0       0      0      0      0      0       0      0       0
!-3              0       0      0      0      0      0       0      0       0
!-4              0       0      0      0      0      0       0      0       0
!-5              0       0      0      0      0      0       0      0       0
!-Angle     0    10    20    30    40    50    60    70    80    90 Hemis
!-Tsol  0.747 0.747 0.745 0.740 0.730 0.707 0.652 0.517 0.263 0.000 0.652
!-Abs1  0.064 0.065 0.066 0.068 0.071 0.075 0.080 0.086 0.094 0.000 0.080
!-Abs2  0.052 0.053 0.053 0.055 0.057 0.058 0.059 0.054 0.041 0.000 0.059
!-Abs3      0     0     0     0     0     0     0     0     0     0     0
!-Abs4      0     0     0     0     0     0     0     0     0     0     0
!-Abs5      0     0     0     0     0     0     0     0     0     0     0
!-Abs6      0     0     0     0     0     0     0     0     0     0     0
!-Rfsol 0.136 0.136 0.136 0.137 0.143 0.160 0.210 0.343 0.602 1.000 0.210
!-Rbsol 0.136 0.136 0.136 0.137 0.143 0.160 0.210 0.343 0.602 1.000 0.210
!-Tvis  0.747 0.747 0.745 0.740 0.730 0.707 0.652 0.517 0.263 0.000 0.652
!-Rfvis 0.136 0.136 0.136 0.137 0.143 0.160 0.210 0.343 0.602 1.000 0.210
!-Rbvis 0.136 0.136 0.136 0.137 0.143 0.160 0.210 0.343 0.602 1.000 0.210
!-SHGC  0.789 0.789 0.787 0.782 0.769 0.739 0.668 0.519 0.267 0.000 0.688
!-SC: 0.81
!-Layer ID#         9991     9991        0        0        0        0
!-Tir              0.000    0.000        0        0        0        0
!-Emis F           0.840    0.840        0        0        0        0
!-Emis B           0.840    0.840        0        0        0        0
!-Thickness(mm)      3.2      3.2        0        0        0        0
!-Cond(W/m2-K     ) 333.9    333.9        0        0        0        0
!-Spectral File         None         None         None         None         None         None
!-Overall and Center of Glass Ig U-values (W/m2-K)
!-Outdoor Temperature                 -17.8 C      15.6 C      26.7 C      37.8 C
!-Solar      WdSpd  hcout hrout  hin
!-(W/m2)     (m/s)     (W/m2-K)
!-0        0.00   4.00  3.39  2.43  2.12 2.12  2.24 2.24  2.32 2.32  2.49 2.49
!-0        6.71  30.84  3.23  2.58  2.72 2.72  2.80 2.80  2.89 2.89  3.13 3.13
!-783        0.00   4.00  3.52  2.03  2.12 2.12  2.24 2.24  2.32 2.32  2.49 2.49
!-783        6.71  30.84  3.27  2.39  2.72 2.72  2.80 2.80  2.89 2.89  3.13 3.13
!-*** END OF LIBRARY ***
!-***************************************************************************************************
!-*WinID   Description                              Design         U-Value g-value T-sol Rf-sol T-vis
!-***************************************************************************************************
!-  6001   ASH140 DBLE - MOD                        3.2/13/3.2       2.89  0.789  0.747  0.136  0.747
!-_EXTENSION_WINPOOL_END_
!-
!-_EXTENSION_BuildingGeometry_START_
!-
!-_EXTENSION_BuildingGeometry_END_
!-
!-
!-_EXTENSION_ExternalShadingGeometry_START_
!-
!-_EXTENSION_ExternalShadingGeometry_END_
!-
!-
!-_EXTENSION_GeoPositionGeometry_START_
!-_EXTENSION_GeoPositionGeometry_END_
!-
!-T17_Template_Stop


!-   ===========  ALL OBJECTS IN CLASS: VERSION ===========
Version,4;

!-   ===========  ALL OBJECTS IN CLASS: BUILDING ===========
Building,
    ISIL BUILDING,                !- Name
    0.0,                     !- North Axis {deg}
    City,                    !- Terrain
    0,                    !- Loads Convergence Tolerance Value
    0,                     !- Temperature Convergence Tolerance Value {deltaC}
    FullInteriorAndExterior, !- Solar Distribution
    0;                      !- Maximum Number of Warmup Days

!-   ===========  ALL OBJECTS IN CLASS: LOCATION ===========
Site:Location,
    not used,          !- LocationName
    0.0,                 !- Latitude {deg}
    0.0,                 !- Longitude {deg}
    0.0,                 !- TimeZone {hr}
    0;                 !- Elevation {m}

GlobalGeometryRules,
    UpperLeftCorner,         !- Starting Vertex Position
    Counterclockwise,        !- Vertex Entry Direction
    Absolute;                !- Coordinate System

!-   ===========  ALL OBJECTS IN CLASS: CONSTRUCTION ===========
Construction,
    GROUND_FLOOR;      !- Name
Construction,         
    EXT_WALL_NE_EF_AL;         !- Name
Construction,         
    EXT_WALL_SW_EF_L0;         !- Name
Construction,         
    EXT_WALL_SW_EF_RL;         !- Name
Construction,         
    EXT_WALL_SW_EF_GL;         !- Name
Construction,         
    EXT_WALL_IF_S0;         !- Name
Construction,         
    EXT_WALL_IF_RL;         !- Name
Construction,    
    EXT_FLOOR;        !- Name
Construction,
    EXT_ROOF_SR;         !- Name
Construction,
    EXT_ROOF_FR;         !- Name
Construction,
    BND_WALL;         !- Name
Construction,    
    BND_FLOOR;        !- Name
Construction,
    BND_CEILING;      !- Name
Construction,
    ADJ_WALL;         !- Name
Construction,
    ADJ_CEILING;      !- Name
Construction,
    VirtualSurface;   !- Name
Construction,
    EXT_WINDOW_SG;         !- Name
Construction,
    EXT_WINDOW_DG;         !- Name
Construction,
    ADJ_WINDOW;          !- Name

!-   ===========  ALL OBJECTS IN CLASS: SurfaceProperty:OtherSideCoefficients ===========
SurfaceProperty:OtherSideCoefficients,
    BOUNDARY=IDENTICAL;
SurfaceProperty:OtherSideCoefficients,
    BOUNDARY=INPUT 1*TBOUNDARY;
SurfaceProperty:OtherSideCoefficients,   
    BOUNDARY=INPUT 1*TGROUND;
SurfaceProperty:OtherSideCoefficients,
    BOUNDARY=20; 
SurfaceProperty:OtherSideCoefficients,
    BOUNDARY=15; 
    
!-   ===========  ALL OBJECTS IN CLASS: OUPUT ===========
Output:VariableDictionary,Regular;  

!-   ===========  ALL OBJECTS IN CLASS: Zone, Surface ===========




  Zone,
    B2_S1_UN,  !- Name
    0.0,  !- Direction of Relative North {deg}
    39.326026,  !- X Origin {m}
    0.0,  !- Y Origin {m}
    0.0,  !- Z Origin {m}
    ,  !- Type
    1;  !- Multiplier

  BuildingSurface:Detailed,
    23C717,  !- Name
    Floor,  !- Surface Type
    GROUND_FLOOR,  !- Construction Name
    B2_S1_UN,  !- Zone Name
    Ground,  !- Outside Boundary Condition
    BOUNDARY=INPUT 1*TGROUND,  !- Outside Boundary Condition Object
    NoSun,  !- Sun Exposure
    NoWind,  !- Wind Exposure
    ,  !- TRNSYS 17 - additional surface data
    4,  !- Number of Vertices
    2.593766518227,  !- Vertex 1 X-coordinate {m}
    67.937044189933,  !- Vertex 1 Y-coordinate {m}
    0.000000000000,  !- Vertex 1 Z-coordinate {m}
    4.070095347853,  !- Vertex 2 X-coordinate {m}
    51.062528451241,  !- Vertex 2 Y-coordinate {m}
    0.000000000000,  !- Vertex 2 Z-coordinate {m}
    -5.353906496095,  !- Vertex 3 X-coordinate {m}
    50.238035124848,  !- Vertex 3 Y-coordinate {m}
    0.000000000000,  !- Vertex 3 Z-coordinate {m}
    -6.830235325721,  !- Vertex 4 X-coordinate {m}
    67.112550863540,  !- Vertex 4 Y-coordinate {m}
    0.000000000000;  !- Vertex 4 Z-coordinate {m}

  BuildingSurface:Detailed,
    80EE45,  !- Name
    Wall,  !- Surface Type
    EXT_WALL_NE_EF_AL,  !- Construction Name
    B2_S1_UN,  !- Zone Name
    Ground,  !- Outside Boundary Condition
    BOUNDARY=INPUT 1*TGROUND,  !- Outside Boundary Condition Object
    NoSun,  !- Sun Exposure
    NoWind,  !- Wind Exposure
    0.0,  !- TRNSYS 17 - additional surface data
    4,  !- Number of Vertices
    2.593766518227,  !- Vertex 1 X-coordinate {m}
    67.937044189933,  !- Vertex 1 Y-coordinate {m}
    3.910000000000,  !- Vertex 1 Z-coordinate {m}
    2.593766518227,  !- Vertex 2 X-coordinate {m}
    67.937044189933,  !- Vertex 2 Y-coordinate {m}
    0.000000000000,  !- Vertex 2 Z-coordinate {m}
    -6.830235325721,  !- Vertex 3 X-coordinate {m}
    67.112550863540,  !- Vertex 3 Y-coordinate {m}
    0.000000000000,  !- Vertex 3 Z-coordinate {m}
    -6.830235325721,  !- Vertex 4 X-coordinate {m}
    67.112550863540,  !- Vertex 4 Y-coordinate {m}
    3.910000000000;  !- Vertex 4 Z-coordinate {m}

  BuildingSurface:Detailed,
    D25484,  !- Name
    Ceiling,  !- Surface Type
    ADJ_CEILING,  !- Construction Name
    B2_S1_UN,  !- Zone Name
    Zone,  !- Outside Boundary Condition
    B2_F0_OF,  !- Outside Boundary Condition Object
    NoSun,  !- Sun Exposure
    NoWind,  !- Wind Exposure
    ,  !- TRNSYS 17 - additional surface data
    4,  !- Number of Vertices
    -6.830235325721,  !- Vertex 1 X-coordinate {m}
    67.112550863540,  !- Vertex 1 Y-coordinate {m}
    3.910000000000,  !- Vertex 1 Z-coordinate {m}
    -5.353906496095,  !- Vertex 2 X-coordinate {m}
    50.238035124848,  !- Vertex 2 Y-coordinate {m}
    3.910000000000,  !- Vertex 2 Z-coordinate {m}
    4.070095347853,  !- Vertex 3 X-coordinate {m}
    51.062528451241,  !- Vertex 3 Y-coordinate {m}
    3.910000000000,  !- Vertex 3 Z-coordinate {m}
    2.593766518227,  !- Vertex 4 X-coordinate {m}
    67.937044189933,  !- Vertex 4 Y-coordinate {m}
    3.910000000000;  !- Vertex 4 Z-coordinate {m}

  BuildingSurface:Detailed,
    C83B57,  !- Name
    Wall,  !- Surface Type
    EXT_WALL_SW_EF_L0,  !- Construction Name
    B2_S1_UN,  !- Zone Name
    Ground,  !- Outside Boundary Condition
    BOUNDARY=INPUT 1*TGROUND,  !- Outside Boundary Condition Object
    NoSun,  !- Sun Exposure
    NoWind,  !- Wind Exposure
    0.0,  !- TRNSYS 17 - additional surface data
    4,  !- Number of Vertices
    -6.830235325721,  !- Vertex 1 X-coordinate {m}
    67.112550863540,  !- Vertex 1 Y-coordinate {m}
    3.910000000000,  !- Vertex 1 Z-coordinate {m}
    -6.830235325721,  !- Vertex 2 X-coordinate {m}
    67.112550863540,  !- Vertex 2 Y-coordinate {m}
    0.000000000000,  !- Vertex 2 Z-coordinate {m}
    -5.353906496095,  !- Vertex 3 X-coordinate {m}
    50.238035124848,  !- Vertex 3 Y-coordinate {m}
    0.000000000000,  !- Vertex 3 Z-coordinate {m}
    -5.353906496095,  !- Vertex 4 X-coordinate {m}
    50.238035124848,  !- Vertex 4 Y-coordinate {m}
    3.910000000000;  !- Vertex 4 Z-coordinate {m}

  BuildingSurface:Detailed,
    A54EC0,  !- Name
    Wall,  !- Surface Type
    EXT_WALL_SW_EF_L0,  !- Construction Name
    B2_S1_UN,  !- Zone Name
    Ground,  !- Outside Boundary Condition
    BOUNDARY=INPUT 1*TGROUND,  !- Outside Boundary Condition Object
    NoSun,  !- Sun Exposure
    NoWind,  !- Wind Exposure
    0.0,  !- TRNSYS 17 - additional surface data
    4,  !- Number of Vertices
    -5.353906496095,  !- Vertex 1 X-coordinate {m}
    50.238035124848,  !- Vertex 1 Y-coordinate {m}
    3.910000000000,  !- Vertex 1 Z-coordinate {m}
    -5.353906496095,  !- Vertex 2 X-coordinate {m}
    50.238035124848,  !- Vertex 2 Y-coordinate {m}
    0.000000000000,  !- Vertex 2 Z-coordinate {m}
    -4.402540559418,  !- Vertex 3 X-coordinate {m}
    50.321268859172,  !- Vertex 3 Y-coordinate {m}
    0.000000000000,  !- Vertex 3 Z-coordinate {m}
    -4.402540559418,  !- Vertex 4 X-coordinate {m}
    50.321268859172,  !- Vertex 4 Y-coordinate {m}
    3.910000000000;  !- Vertex 4 Z-coordinate {m}

  BuildingSurface:Detailed,
    4C3C38,  !- Name
    Wall,  !- Surface Type
    ADJ_WALL,  !- Construction Name
    B2_S1_UN,  !- Zone Name
    Zone,  !- Outside Boundary Condition
    B1_S1_CL,  !- Outside Boundary Condition Object
    NoSun,  !- Sun Exposure
    NoWind,  !- Wind Exposure
    ,  !- TRNSYS 17 - additional surface data
    4,  !- Number of Vertices
    -4.402540559418,  !- Vertex 1 X-coordinate {m}
    50.321268859172,  !- Vertex 1 Y-coordinate {m}
    3.910000000000,  !- Vertex 1 Z-coordinate {m}
    -4.402540559418,  !- Vertex 2 X-coordinate {m}
    50.321268859172,  !- Vertex 2 Y-coordinate {m}
    0.000000000000,  !- Vertex 2 Z-coordinate {m}
    4.070095347853,  !- Vertex 3 X-coordinate {m}
    51.062528451241,  !- Vertex 3 Y-coordinate {m}
    0.000000000000,  !- Vertex 3 Z-coordinate {m}
    4.070095347853,  !- Vertex 4 X-coordinate {m}
    51.062528451241,  !- Vertex 4 Y-coordinate {m}
    3.910000000000;  !- Vertex 4 Z-coordinate {m}

  BuildingSurface:Detailed,
    3E54D6,  !- Name
    Wall,  !- Surface Type
    ADJ_WALL,  !- Construction Name
    B2_S1_UN,  !- Zone Name
    Zone,  !- Outside Boundary Condition
    B2_S1_SC,  !- Outside Boundary Condition Object
    NoSun,  !- Sun Exposure
    NoWind,  !- Wind Exposure
    ,  !- TRNSYS 17 - additional surface data
    4,  !- Number of Vertices
    4.070095347853,  !- Vertex 1 X-coordinate {m}
    51.062528451241,  !- Vertex 1 Y-coordinate {m}
    3.910000000000,  !- Vertex 1 Z-coordinate {m}
    4.070095347853,  !- Vertex 2 X-coordinate {m}
    51.062528451241,  !- Vertex 2 Y-coordinate {m}
    0.000000000000,  !- Vertex 2 Z-coordinate {m}
    2.593766518227,  !- Vertex 3 X-coordinate {m}
    67.937044189933,  !- Vertex 3 Y-coordinate {m}
    0.000000000000,  !- Vertex 3 Z-coordinate {m}
    2.593766518227,  !- Vertex 4 X-coordinate {m}
    67.937044189933,  !- Vertex 4 Y-coordinate {m}
    3.910000000000;  !- Vertex 4 Z-coordinate {m}

  Zone,
    B2_S1_SC,  !- Name
    0.0,  !- Direction of Relative North {deg}
    39.326026,  !- X Origin {m}
    9.46,  !- Y Origin {m}
    0.0,  !- Z Origin {m}
    ,  !- Type
    1;  !- Multiplier

  BuildingSurface:Detailed,
    B32CE0,  !- Name
    Floor,  !- Surface Type
    GROUND_FLOOR,  !- Construction Name
    B2_S1_SC,  !- Zone Name
    Ground,  !- Outside Boundary Condition
    BOUNDARY=INPUT 1*TGROUND,  !- Outside Boundary Condition Object
    NoSun,  !- Sun Exposure
    NoWind,  !- Wind Exposure
    ,  !- TRNSYS 17 - additional surface data
    4,  !- Number of Vertices
    12.187071739319,  !- Vertex 1 X-coordinate {m}
    68.776349642523,  !- Vertex 1 Y-coordinate {m}
    0.000000000000,  !- Vertex 1 Z-coordinate {m}
    13.663400568944,  !- Vertex 2 X-coordinate {m}
    51.901833903830,  !- Vertex 2 Y-coordinate {m}
    0.000000000000,  !- Vertex 2 Z-coordinate {m}
    4.070095347853,  !- Vertex 3 X-coordinate {m}
    51.062528451241,  !- Vertex 3 Y-coordinate {m}
    0.000000000000,  !- Vertex 3 Z-coordinate {m}
    2.593766518227,  !- Vertex 4 X-coordinate {m}
    67.937044189933,  !- Vertex 4 Y-coordinate {m}
    0.000000000000;  !- Vertex 4 Z-coordinate {m}

  BuildingSurface:Detailed,
    20FD6C,  !- Name
    Wall,  !- Surface Type
    ADJ_WALL,  !- Construction Name
    B2_S1_SC,  !- Zone Name
    OtherSideCoefficients,  !- Outside Boundary Condition
    BOUNDARY=IDENTICAL,  !- Outside Boundary Condition Object
    NoSun,  !- Sun Exposure
    NoWind,  !- Wind Exposure
    0.0,  !- TRNSYS 17 - additional surface data
    4,  !- Number of Vertices
    13.663400568944,  !- Vertex 1 X-coordinate {m}
    51.901833903830,  !- Vertex 1 Y-coordinate {m}
    3.910000000000,  !- Vertex 1 Z-coordinate {m}
    13.663400568944,  !- Vertex 2 X-coordinate {m}
    51.901833903830,  !- Vertex 2 Y-coordinate {m}
    0.000000000000,  !- Vertex 2 Z-coordinate {m}
    12.187071739319,  !- Vertex 3 X-coordinate {m}
    68.776349642523,  !- Vertex 3 Y-coordinate {m}
    0.000000000000,  !- Vertex 3 Z-coordinate {m}
    12.187071739319,  !- Vertex 4 X-coordinate {m}
    68.776349642523,  !- Vertex 4 Y-coordinate {m}
    3.910000000000;  !- Vertex 4 Z-coordinate {m}

  BuildingSurface:Detailed,
    3BE9A4,  !- Name
    Ceiling,  !- Surface Type
    ADJ_CEILING,  !- Construction Name
    B2_S1_SC,  !- Zone Name
    Zone,  !- Outside Boundary Condition
    B2_F0_SC,  !- Outside Boundary Condition Object
    NoSun,  !- Sun Exposure
    NoWind,  !- Wind Exposure
    ,  !- TRNSYS 17 - additional surface data
    4,  !- Number of Vertices
    2.593766518227,  !- Vertex 1 X-coordinate {m}
    67.937044189933,  !- Vertex 1 Y-coordinate {m}
    3.910000000000,  !- Vertex 1 Z-coordinate {m}
    4.070095347853,  !- Vertex 2 X-coordinate {m}
    51.062528451241,  !- Vertex 2 Y-coordinate {m}
    3.910000000000,  !- Vertex 2 Z-coordinate {m}
    13.663400568944,  !- Vertex 3 X-coordinate {m}
    51.901833903830,  !- Vertex 3 Y-coordinate {m}
    3.910000000000,  !- Vertex 3 Z-coordinate {m}
    12.187071739319,  !- Vertex 4 X-coordinate {m}
    68.776349642523,  !- Vertex 4 Y-coordinate {m}
    3.910000000000;  !- Vertex 4 Z-coordinate {m}

  BuildingSurface:Detailed,
    BDED90,  !- Name
    Wall,  !- Surface Type
    ADJ_WALL,  !- Construction Name
    B2_S1_SC,  !- Zone Name
    Zone,  !- Outside Boundary Condition
    B2_S1_UN,  !- Outside Boundary Condition Object
    NoSun,  !- Sun Exposure
    NoWind,  !- Wind Exposure
    ,  !- TRNSYS 17 - additional surface data
    4,  !- Number of Vertices
    2.593766518227,  !- Vertex 1 X-coordinate {m}
    67.937044189933,  !- Vertex 1 Y-coordinate {m}
    3.910000000000,  !- Vertex 1 Z-coordinate {m}
    2.593766518227,  !- Vertex 2 X-coordinate {m}
    67.937044189933,  !- Vertex 2 Y-coordinate {m}
    0.000000000000,  !- Vertex 2 Z-coordinate {m}
    4.070095347853,  !- Vertex 3 X-coordinate {m}
    51.062528451241,  !- Vertex 3 Y-coordinate {m}
    0.000000000000,  !- Vertex 3 Z-coordinate {m}
    4.070095347853,  !- Vertex 4 X-coordinate {m}
    51.062528451241,  !- Vertex 4 Y-coordinate {m}
    3.910000000000;  !- Vertex 4 Z-coordinate {m}

  BuildingSurface:Detailed,
    EFFF39,  !- Name
    Wall,  !- Surface Type
    EXT_WALL_IF_S0,  !- Construction Name
    B2_S1_SC,  !- Zone Name
    Outdoors,  !- Outside Boundary Condition
    ,  !- Outside Boundary Condition Object
    SunExposed,  !- Sun Exposure
    WindExposed,  !- Wind Exposure
    ,  !- TRNSYS 17 - additional surface data
    4,  !- Number of Vertices
    12.707103380308,  !- Vertex 1 X-coordinate {m}
    51.818168740863,  !- Vertex 1 Y-coordinate {m}
    3.910000000000,  !- Vertex 1 Z-coordinate {m}
    12.707103380308,  !- Vertex 2 X-coordinate {m}
    51.818168740863,  !- Vertex 2 Y-coordinate {m}
    0.000000000000,  !- Vertex 2 Z-coordinate {m}
    13.663400568944,  !- Vertex 3 X-coordinate {m}
    51.901833903830,  !- Vertex 3 Y-coordinate {m}
    0.000000000000,  !- Vertex 3 Z-coordinate {m}
    13.663400568944,  !- Vertex 4 X-coordinate {m}
    51.901833903830,  !- Vertex 4 Y-coordinate {m}
    3.910000000000;  !- Vertex 4 Z-coordinate {m}

  BuildingSurface:Detailed,
    BA0E45,  !- Name
    Wall,  !- Surface Type
    EXT_WALL_NE_EF_AL,  !- Construction Name
    B2_S1_SC,  !- Zone Name
    Ground,  !- Outside Boundary Condition
    BOUNDARY=INPUT 1*TGROUND,  !- Outside Boundary Condition Object
    NoSun,  !- Sun Exposure
    NoWind,  !- Wind Exposure
    0.0,  !- TRNSYS 17 - additional surface data
    4,  !- Number of Vertices
    12.187071739319,  !- Vertex 1 X-coordinate {m}
    68.776349642523,  !- Vertex 1 Y-coordinate {m}
    3.910000000000,  !- Vertex 1 Z-coordinate {m}
    12.187071739319,  !- Vertex 2 X-coordinate {m}
    68.776349642523,  !- Vertex 2 Y-coordinate {m}
    0.000000000000,  !- Vertex 2 Z-coordinate {m}
    2.593766518227,  !- Vertex 3 X-coordinate {m}
    67.937044189933,  !- Vertex 3 Y-coordinate {m}
    0.000000000000,  !- Vertex 3 Z-coordinate {m}
    2.593766518227,  !- Vertex 4 X-coordinate {m}
    67.937044189933,  !- Vertex 4 Y-coordinate {m}
    3.910000000000;  !- Vertex 4 Z-coordinate {m}

  BuildingSurface:Detailed,
    B26397,  !- Name
    Wall,  !- Surface Type
    ADJ_WALL,  !- Construction Name
    B2_S1_SC,  !- Zone Name
    Zone,  !- Outside Boundary Condition
    B1_S1_CL,  !- Outside Boundary Condition Object
    NoSun,  !- Sun Exposure
    NoWind,  !- Wind Exposure
    ,  !- TRNSYS 17 - additional surface data
    4,  !- Number of Vertices
    4.070095347853,  !- Vertex 1 X-coordinate {m}
    51.062528451241,  !- Vertex 1 Y-coordinate {m}
    3.910000000000,  !- Vertex 1 Z-coordinate {m}
    4.070095347853,  !- Vertex 2 X-coordinate {m}
    51.062528451241,  !- Vertex 2 Y-coordinate {m}
    0.000000000000,  !- Vertex 2 Z-coordinate {m}
    12.707103380308,  !- Vertex 3 X-coordinate {m}
    51.818168740863,  !- Vertex 3 Y-coordinate {m}
    0.000000000000,  !- Vertex 3 Z-coordinate {m}
    12.707103380308,  !- Vertex 4 X-coordinate {m}
    51.818168740863,  !- Vertex 4 Y-coordinate {m}
    3.910000000000;  !- Vertex 4 Z-coordinate {m}

  Zone,
    B6_S1_CL1,  !- Name
    0.0,  !- Direction of Relative North {deg}
    56.729463,  !- X Origin {m}
    67.860144,  !- Y Origin {m}
    0.0,  !- Z Origin {m}
    ,  !- Type
    1;  !- Multiplier

  BuildingSurface:Detailed,
    C2F74F,  !- Name
    Floor,  !- Surface Type
    GROUND_FLOOR,  !- Construction Name
    B6_S1_CL1,  !- Zone Name
    Ground,  !- Outside Boundary Condition
    BOUNDARY=INPUT 1*TGROUND,  !- Outside Boundary Condition Object
    NoSun,  !- Sun Exposure
    NoWind,  !- Wind Exposure
    ,  !- TRNSYS 17 - additional surface data
    4,  !- Number of Vertices
    73.517257553134,  !- Vertex 1 X-coordinate {m}
    50.190783041650,  !- Vertex 1 Y-coordinate {m}
    0.000000000000,  !- Vertex 1 Z-coordinate {m}
    56.911828519733,  !- Vertex 2 X-coordinate {m}
    16.357320878178,  !- Vertex 2 Y-coordinate {m}
    0.000000000000,  !- Vertex 2 Z-coordinate {m}
    45.689599808048,  !- Vertex 3 X-coordinate {m}
    21.864319033099,  !- Vertex 3 Y-coordinate {m}
    0.000000000000,  !- Vertex 3 Z-coordinate {m}
    62.288489505666,  !- Vertex 4 X-coordinate {m}
    55.689741033696,  !- Vertex 4 Y-coordinate {m}
    0.000000000000;  !- Vertex 4 Z-coordinate {m}

  BuildingSurface:Detailed,
    FD4A8F,  !- Name
    Ceiling,  !- Surface Type
    ADJ_CEILING,  !- Construction Name
    B6_S1_CL1,  !- Zone Name
    Zone,  !- Outside Boundary Condition
    B6_F1_LB,  !- Outside Boundary Condition Object
    NoSun,  !- Sun Exposure
    NoWind,  !- Wind Exposure
    ,  !- TRNSYS 17 - additional surface data
    4,  !- Number of Vertices
    62.288489505666,  !- Vertex 1 X-coordinate {m}
    55.689741033696,  !- Vertex 1 Y-coordinate {m}
    7.990000000000,  !- Vertex 1 Z-coordinate {m}
    45.689599808048,  !- Vertex 2 X-coordinate {m}
    21.864319033099,  !- Vertex 2 Y-coordinate {m}
    7.990000000000,  !- Vertex 2 Z-coordinate {m}
    56.911828519733,  !- Vertex 3 X-coordinate {m}
    16.357320878178,  !- Vertex 3 Y-coordinate {m}
    7.990000000000,  !- Vertex 3 Z-coordinate {m}
    73.517257553134,  !- Vertex 4 X-coordinate {m}
    50.190783041650,  !- Vertex 4 Y-coordinate {m}
    7.990000000000;  !- Vertex 4 Z-coordinate {m}

  BuildingSurface:Detailed,
    9AFB19,  !- Name
    Wall,  !- Surface Type
    ADJ_WALL,  !- Construction Name
    B6_S1_CL1,  !- Zone Name
    Zone,  !- Outside Boundary Condition
    B6_F0_CL,  !- Outside Boundary Condition Object
    NoSun,  !- Sun Exposure
    NoWind,  !- Wind Exposure
    ,  !- TRNSYS 17 - additional surface data
    4,  !- Number of Vertices
    45.689599808048,  !- Vertex 1 X-coordinate {m}
    21.864319033099,  !- Vertex 1 Y-coordinate {m}
    7.990000000000,  !- Vertex 1 Z-coordinate {m}
    45.689599808048,  !- Vertex 2 X-coordinate {m}
    21.864319033099,  !- Vertex 2 Y-coordinate {m}
    3.910000000000,  !- Vertex 2 Z-coordinate {m}
    56.911828519733,  !- Vertex 3 X-coordinate {m}
    16.357320878178,  !- Vertex 3 Y-coordinate {m}
    3.910000000000,  !- Vertex 3 Z-coordinate {m}
    56.911828519733,  !- Vertex 4 X-coordinate {m}
    16.357320878178,  !- Vertex 4 Y-coordinate {m}
    7.990000000000;  !- Vertex 4 Z-coordinate {m}

  BuildingSurface:Detailed,
    199120,  !- Name
    Wall,  !- Surface Type
    EXT_WALL_IF_S0,  !- Construction Name
    B6_S1_CL1,  !- Zone Name
    Outdoors,  !- Outside Boundary Condition
    ,  !- Outside Boundary Condition Object
    SunExposed,  !- Sun Exposure
    WindExposed,  !- Wind Exposure
    ,  !- TRNSYS 17 - additional surface data
    4,  !- Number of Vertices
    62.288489505666,  !- Vertex 1 X-coordinate {m}
    55.689741033696,  !- Vertex 1 Y-coordinate {m}
    7.990000000000,  !- Vertex 1 Z-coordinate {m}
    62.288489505666,  !- Vertex 2 X-coordinate {m}
    55.689741033696,  !- Vertex 2 Y-coordinate {m}
    0.000000000000,  !- Vertex 2 Z-coordinate {m}
    45.689599808048,  !- Vertex 3 X-coordinate {m}
    21.864319033099,  !- Vertex 3 Y-coordinate {m}
    0.000000000000,  !- Vertex 3 Z-coordinate {m}
    45.689599808048,  !- Vertex 4 X-coordinate {m}
    21.864319033099,  !- Vertex 4 Y-coordinate {m}
    7.990000000000;  !- Vertex 4 Z-coordinate {m}

  BuildingSurface:Detailed,
    EE5EC2,  !- Name
    Wall,  !- Surface Type
    ADJ_WALL,  !- Construction Name
    B6_S1_CL1,  !- Zone Name
    OtherSideCoefficients,  !- Outside Boundary Condition
    BOUNDARY=IDENTICAL,  !- Outside Boundary Condition Object
    NoSun,  !- Sun Exposure
    NoWind,  !- Wind Exposure
    0.0,  !- TRNSYS 17 - additional surface data
    4,  !- Number of Vertices
    73.517257553134,  !- Vertex 1 X-coordinate {m}
    50.190783041650,  !- Vertex 1 Y-coordinate {m}
    7.990000000000,  !- Vertex 1 Z-coordinate {m}
    73.517257553134,  !- Vertex 2 X-coordinate {m}
    50.190783041650,  !- Vertex 2 Y-coordinate {m}
    0.000000000000,  !- Vertex 2 Z-coordinate {m}
    62.288489505666,  !- Vertex 3 X-coordinate {m}
    55.689741033696,  !- Vertex 3 Y-coordinate {m}
    0.000000000000,  !- Vertex 3 Z-coordinate {m}
    62.288489505666,  !- Vertex 4 X-coordinate {m}
    55.689741033696,  !- Vertex 4 Y-coordinate {m}
    7.990000000000;  !- Vertex 4 Z-coordinate {m}

  BuildingSurface:Detailed,
    7C3219,  !- Name
    Wall,  !- Surface Type
    EXT_WALL_NE_EF_AL,  !- Construction Name
    B6_S1_CL1,  !- Zone Name
    Outdoors,  !- Outside Boundary Condition
    ,  !- Outside Boundary Condition Object
    SunExposed,  !- Sun Exposure
    WindExposed,  !- Wind Exposure
    ,  !- TRNSYS 17 - additional surface data
    4,  !- Number of Vertices
    56.911828519733,  !- Vertex 1 X-coordinate {m}
    16.357320878178,  !- Vertex 1 Y-coordinate {m}
    7.990000000000,  !- Vertex 1 Z-coordinate {m}
    56.911828519733,  !- Vertex 2 X-coordinate {m}
    16.357320878178,  !- Vertex 2 Y-coordinate {m}
    0.000000000000,  !- Vertex 2 Z-coordinate {m}
    73.517257553134,  !- Vertex 3 X-coordinate {m}
    50.190783041650,  !- Vertex 3 Y-coordinate {m}
    0.000000000000,  !- Vertex 3 Z-coordinate {m}
    73.517257553134,  !- Vertex 4 X-coordinate {m}
    50.190783041650,  !- Vertex 4 Y-coordinate {m}
    7.990000000000;  !- Vertex 4 Z-coordinate {m}

  Zone,
    B6_S1_CL2,  !- Name
    0.0,  !- Direction of Relative North {deg}
    88.97948,  !- X Origin {m}
    48.376338,  !- Y Origin {m}
    0.0,  !- Z Origin {m}
    ,  !- Type
    1;  !- Multiplier

  BuildingSurface:Detailed,
    2D0686,  !- Name
    Floor,  !- Surface Type
    GROUND_FLOOR,  !- Construction Name
    B6_S1_CL2,  !- Zone Name
    Ground,  !- Outside Boundary Condition
    BOUNDARY=INPUT 1*TGROUND,  !- Outside Boundary Condition Object
    NoSun,  !- Sun Exposure
    NoWind,  !- Wind Exposure
    ,  !- TRNSYS 17 - additional surface data
    4,  !- Number of Vertices
    56.911828519733,  !- Vertex 1 X-coordinate {m}
    16.357320878178,  !- Vertex 1 Y-coordinate {m}
    0.000000000000,  !- Vertex 1 Z-coordinate {m}
    52.505893082225,  !- Vertex 2 X-coordinate {m}
    7.380253822592,  !- Vertex 2 Y-coordinate {m}
    0.000000000000,  !- Vertex 2 Z-coordinate {m}
    41.284559262741,  !- Vertex 3 X-coordinate {m}
    12.887673119476,  !- Vertex 3 Y-coordinate {m}
    0.000000000000,  !- Vertex 3 Z-coordinate {m}
    45.689599808048,  !- Vertex 4 X-coordinate {m}
    21.864319033099,  !- Vertex 4 Y-coordinate {m}
    0.000000000000;  !- Vertex 4 Z-coordinate {m}

  BuildingSurface:Detailed,
    70E33E,  !- Name
    Wall,  !- Surface Type
    ADJ_WALL,  !- Construction Name
    B6_S1_CL2,  !- Zone Name
    OtherSideCoefficients,  !- Outside Boundary Condition
    BOUNDARY=IDENTICAL,  !- Outside Boundary Condition Object
    NoSun,  !- Sun Exposure
    NoWind,  !- Wind Exposure
    0.0,  !- TRNSYS 17 - additional surface data
    4,  !- Number of Vertices
    41.284559262741,  !- Vertex 1 X-coordinate {m}
    12.887673119476,  !- Vertex 1 Y-coordinate {m}
    3.910000000000,  !- Vertex 1 Z-coordinate {m}
    41.284559262741,  !- Vertex 2 X-coordinate {m}
    12.887673119476,  !- Vertex 2 Y-coordinate {m}
    0.000000000000,  !- Vertex 2 Z-coordinate {m}
    52.505893082225,  !- Vertex 3 X-coordinate {m}
    7.380253822592,  !- Vertex 3 Y-coordinate {m}
    0.000000000000,  !- Vertex 3 Z-coordinate {m}
    52.505893082225,  !- Vertex 4 X-coordinate {m}
    7.380253822592,  !- Vertex 4 Y-coordinate {m}
    3.910000000000;  !- Vertex 4 Z-coordinate {m}

  BuildingSurface:Detailed,
    D7C7B0,  !- Name
    Wall,  !- Surface Type
    EXT_WALL_NE_EF_AL,  !- Construction Name
    B6_S1_CL2,  !- Zone Name
    Outdoors,  !- Outside Boundary Condition
    ,  !- Outside Boundary Condition Object
    SunExposed,  !- Sun Exposure
    WindExposed,  !- Wind Exposure
    ,  !- TRNSYS 17 - additional surface data
    4,  !- Number of Vertices
    52.505893082225,  !- Vertex 1 X-coordinate {m}
    7.380253822592,  !- Vertex 1 Y-coordinate {m}
    3.910000000000,  !- Vertex 1 Z-coordinate {m}
    52.505893082225,  !- Vertex 2 X-coordinate {m}
    7.380253822592,  !- Vertex 2 Y-coordinate {m}
    0.000000000000,  !- Vertex 2 Z-coordinate {m}
    56.911828519733,  !- Vertex 3 X-coordinate {m}
    16.357320878178,  !- Vertex 3 Y-coordinate {m}
    0.000000000000,  !- Vertex 3 Z-coordinate {m}
    56.911828519733,  !- Vertex 4 X-coordinate {m}
    16.357320878178,  !- Vertex 4 Y-coordinate {m}
    3.910000000000;  !- Vertex 4 Z-coordinate {m}

  BuildingSurface:Detailed,
    F2B258,  !- Name
    Ceiling,  !- Surface Type
    ADJ_CEILING,  !- Construction Name
    B6_S1_CL2,  !- Zone Name
    Zone,  !- Outside Boundary Condition
    B6_F0_CL,  !- Outside Boundary Condition Object
    NoSun,  !- Sun Exposure
    NoWind,  !- Wind Exposure
    ,  !- TRNSYS 17 - additional surface data
    4,  !- Number of Vertices
    45.689599808048,  !- Vertex 1 X-coordinate {m}
    21.864319033099,  !- Vertex 1 Y-coordinate {m}
    3.910000000000,  !- Vertex 1 Z-coordinate {m}
    41.284559262741,  !- Vertex 2 X-coordinate {m}
    12.887673119476,  !- Vertex 2 Y-coordinate {m}
    3.910000000000,  !- Vertex 2 Z-coordinate {m}
    52.505893082225,  !- Vertex 3 X-coordinate {m}
    7.380253822592,  !- Vertex 3 Y-coordinate {m}
    3.910000000000,  !- Vertex 3 Z-coordinate {m}
    56.911828519733,  !- Vertex 4 X-coordinate {m}
    16.357320878178,  !- Vertex 4 Y-coordinate {m}
    3.910000000000;  !- Vertex 4 Z-coordinate {m}

  BuildingSurface:Detailed,
    12F867,  !- Name
    Wall,  !- Surface Type
    EXT_WALL_IF_S0,  !- Construction Name
    B6_S1_CL2,  !- Zone Name
    Outdoors,  !- Outside Boundary Condition
    ,  !- Outside Boundary Condition Object
    SunExposed,  !- Sun Exposure
    WindExposed,  !- Wind Exposure
    ,  !- TRNSYS 17 - additional surface data
    4,  !- Number of Vertices
    45.689599808048,  !- Vertex 1 X-coordinate {m}
    21.864319033099,  !- Vertex 1 Y-coordinate {m}
    3.910000000000,  !- Vertex 1 Z-coordinate {m}
    45.689599808048,  !- Vertex 2 X-coordinate {m}
    21.864319033099,  !- Vertex 2 Y-coordinate {m}
    0.000000000000,  !- Vertex 2 Z-coordinate {m}
    41.284559262741,  !- Vertex 3 X-coordinate {m}
    12.887673119476,  !- Vertex 3 Y-coordinate {m}
    0.000000000000,  !- Vertex 3 Z-coordinate {m}
    41.284559262741,  !- Vertex 4 X-coordinate {m}
    12.887673119476,  !- Vertex 4 Y-coordinate {m}
    3.910000000000;  !- Vertex 4 Z-coordinate {m}

  BuildingSurface:Detailed,
    478C64,  !- Name
    Wall,  !- Surface Type
    ADJ_WALL,  !- Construction Name
    B6_S1_CL2,  !- Zone Name
    Zone,  !- Outside Boundary Condition
    B6_S1_CL1,  !- Outside Boundary Condition Object
    NoSun,  !- Sun Exposure
    NoWind,  !- Wind Exposure
    ,  !- TRNSYS 17 - additional surface data
    4,  !- Number of Vertices
    56.911828519733,  !- Vertex 1 X-coordinate {m}
    16.357320878178,  !- Vertex 1 Y-coordinate {m}
    3.910000000000,  !- Vertex 1 Z-coordinate {m}
    56.911828519733,  !- Vertex 2 X-coordinate {m}
    16.357320878178,  !- Vertex 2 Y-coordinate {m}
    0.000000000000,  !- Vertex 2 Z-coordinate {m}
    45.689599808048,  !- Vertex 3 X-coordinate {m}
    21.864319033099,  !- Vertex 3 Y-coordinate {m}
    0.000000000000,  !- Vertex 3 Z-coordinate {m}
    45.689599808048,  !- Vertex 4 X-coordinate {m}
    21.864319033099,  !- Vertex 4 Y-coordinate {m}
    3.910000000000;  !- Vertex 4 Z-coordinate {m}

  BuildingSurface:Detailed,
    45717D,  !- Name
    Wall,  !- Surface Type
    ADJ_WALL,  !- Construction Name
    B6_S1_CL1,  !- Zone Name
    Zone,  !- Outside Boundary Condition
    B6_S1_CL2,  !- Outside Boundary Condition Object
    NoSun,  !- Sun Exposure
    NoWind,  !- Wind Exposure
    ,  !- TRNSYS 17 - additional surface data
    4,  !- Number of Vertices
    45.689599808048,  !- Vertex 1 X-coordinate {m}
    21.864319033099,  !- Vertex 1 Y-coordinate {m}
    3.910000000000,  !- Vertex 1 Z-coordinate {m}
    45.689599808048,  !- Vertex 2 X-coordinate {m}
    21.864319033099,  !- Vertex 2 Y-coordinate {m}
    0.000000000000,  !- Vertex 2 Z-coordinate {m}
    56.911828519733,  !- Vertex 3 X-coordinate {m}
    16.357320878178,  !- Vertex 3 Y-coordinate {m}
    0.000000000000,  !- Vertex 3 Z-coordinate {m}
    56.911828519733,  !- Vertex 4 X-coordinate {m}
    16.357320878178,  !- Vertex 4 Y-coordinate {m}
    3.910000000000;  !- Vertex 4 Z-coordinate {m}

  Zone,
    B1_S1_CL,  !- Name
    0.0,  !- Direction of Relative North {deg}
    56.265,  !- X Origin {m}
    0.955,  !- Y Origin {m}
    0.0,  !- Z Origin {m}
    ,  !- Type
    1;  !- Multiplier

  BuildingSurface:Detailed,
    EEE41B,  !- Name
    Floor,  !- Surface Type
    GROUND_FLOOR,  !- Construction Name
    B1_S1_CL,  !- Zone Name
    Ground,  !- Outside Boundary Condition
    BOUNDARY=INPUT 1*TGROUND,  !- Outside Boundary Condition Object
    NoSun,  !- Sun Exposure
    NoWind,  !- Wind Exposure
    ,  !- TRNSYS 17 - additional surface data
    4,  !- Number of Vertices
    12.707103380308,  !- Vertex 1 X-coordinate {m}
    51.818168740863,  !- Vertex 1 Y-coordinate {m}
    0.000000000000,  !- Vertex 1 Z-coordinate {m}
    16.201612885775,  !- Vertex 2 X-coordinate {m}
    11.875742320874,  !- Vertex 2 Y-coordinate {m}
    0.000000000000,  !- Vertex 2 Z-coordinate {m}
    -0.908031053950,  !- Vertex 3 X-coordinate {m}
    10.378842439183,  !- Vertex 3 Y-coordinate {m}
    0.000000000000,  !- Vertex 3 Z-coordinate {m}
    -4.402540559418,  !- Vertex 4 X-coordinate {m}
    50.321268859172,  !- Vertex 4 Y-coordinate {m}
    0.000000000000;  !- Vertex 4 Z-coordinate {m}

  BuildingSurface:Detailed,
    A1B870,  !- Name
    Ceiling,  !- Surface Type
    ADJ_CEILING,  !- Construction Name
    B1_S1_CL,  !- Zone Name
    Zone,  !- Outside Boundary Condition
    B1_F0_OF,  !- Outside Boundary Condition Object
    NoSun,  !- Sun Exposure
    NoWind,  !- Wind Exposure
    ,  !- TRNSYS 17 - additional surface data
    4,  !- Number of Vertices
    -4.402540559418,  !- Vertex 1 X-coordinate {m}
    50.321268859172,  !- Vertex 1 Y-coordinate {m}
    3.910000000000,  !- Vertex 1 Z-coordinate {m}
    -0.908031053950,  !- Vertex 2 X-coordinate {m}
    10.378842439183,  !- Vertex 2 Y-coordinate {m}
    3.910000000000,  !- Vertex 2 Z-coordinate {m}
    16.201612885775,  !- Vertex 3 X-coordinate {m}
    11.875742320874,  !- Vertex 3 Y-coordinate {m}
    3.910000000000,  !- Vertex 3 Z-coordinate {m}
    12.707103380308,  !- Vertex 4 X-coordinate {m}
    51.818168740863,  !- Vertex 4 Y-coordinate {m}
    3.910000000000;  !- Vertex 4 Z-coordinate {m}

  BuildingSurface:Detailed,
    6EE34E,  !- Name
    Wall,  !- Surface Type
    EXT_WALL_SW_EF_L0,  !- Construction Name
    B1_S1_CL,  !- Zone Name
    Outdoors,  !- Outside Boundary Condition
    ,  !- Outside Boundary Condition Object
    SunExposed,  !- Sun Exposure
    WindExposed,  !- Wind Exposure
    0.0,  !- TRNSYS 17 - additional surface data
    4,  !- Number of Vertices
    -4.402540559418,  !- Vertex 1 X-coordinate {m}
    50.321268859172,  !- Vertex 1 Y-coordinate {m}
    3.910000000000,  !- Vertex 1 Z-coordinate {m}
    -4.402540559418,  !- Vertex 2 X-coordinate {m}
    50.321268859172,  !- Vertex 2 Y-coordinate {m}
    0.000000000000,  !- Vertex 2 Z-coordinate {m}
    -0.908031053950,  !- Vertex 3 X-coordinate {m}
    10.378842439183,  !- Vertex 3 Y-coordinate {m}
    0.000000000000,  !- Vertex 3 Z-coordinate {m}
    -0.908031053950,  !- Vertex 4 X-coordinate {m}
    10.378842439183,  !- Vertex 4 Y-coordinate {m}
    3.910000000000;  !- Vertex 4 Z-coordinate {m}

  BuildingSurface:Detailed,
    45F5C3,  !- Name
    Wall,  !- Surface Type
    ADJ_WALL,  !- Construction Name
    B1_S1_CL,  !- Zone Name
    Zone,  !- Outside Boundary Condition
    B2_S1_UN,  !- Outside Boundary Condition Object
    NoSun,  !- Sun Exposure
    NoWind,  !- Wind Exposure
    ,  !- TRNSYS 17 - additional surface data
    4,  !- Number of Vertices
    4.070095347853,  !- Vertex 1 X-coordinate {m}
    51.062528451241,  !- Vertex 1 Y-coordinate {m}
    3.910000000000,  !- Vertex 1 Z-coordinate {m}
    4.070095347853,  !- Vertex 2 X-coordinate {m}
    51.062528451241,  !- Vertex 2 Y-coordinate {m}
    0.000000000000,  !- Vertex 2 Z-coordinate {m}
    -4.402540559418,  !- Vertex 3 X-coordinate {m}
    50.321268859172,  !- Vertex 3 Y-coordinate {m}
    0.000000000000,  !- Vertex 3 Z-coordinate {m}
    -4.402540559418,  !- Vertex 4 X-coordinate {m}
    50.321268859172,  !- Vertex 4 Y-coordinate {m}
    3.910000000000;  !- Vertex 4 Z-coordinate {m}

  BuildingSurface:Detailed,
    14EE47,  !- Name
    Wall,  !- Surface Type
    EXT_WALL_IF_S0,  !- Construction Name
    B1_S1_CL,  !- Zone Name
    Outdoors,  !- Outside Boundary Condition
    ,  !- Outside Boundary Condition Object
    SunExposed,  !- Sun Exposure
    WindExposed,  !- Wind Exposure
    ,  !- TRNSYS 17 - additional surface data
    4,  !- Number of Vertices
    16.201612885775,  !- Vertex 1 X-coordinate {m}
    11.875742320874,  !- Vertex 1 Y-coordinate {m}
    3.910000000000,  !- Vertex 1 Z-coordinate {m}
    16.201612885775,  !- Vertex 2 X-coordinate {m}
    11.875742320874,  !- Vertex 2 Y-coordinate {m}
    0.000000000000,  !- Vertex 2 Z-coordinate {m}
    12.707103380308,  !- Vertex 3 X-coordinate {m}
    51.818168740863,  !- Vertex 3 Y-coordinate {m}
    0.000000000000,  !- Vertex 3 Z-coordinate {m}
    12.707103380308,  !- Vertex 4 X-coordinate {m}
    51.818168740863,  !- Vertex 4 Y-coordinate {m}
    3.910000000000;  !- Vertex 4 Z-coordinate {m}

  BuildingSurface:Detailed,
    413510,  !- Name
    Wall,  !- Surface Type
    ADJ_WALL,  !- Construction Name
    B1_S1_CL,  !- Zone Name
    Zone,  !- Outside Boundary Condition
    B2_S1_SC,  !- Outside Boundary Condition Object
    NoSun,  !- Sun Exposure
    NoWind,  !- Wind Exposure
    ,  !- TRNSYS 17 - additional surface data
    4,  !- Number of Vertices
    12.707103380308,  !- Vertex 1 X-coordinate {m}
    51.818168740863,  !- Vertex 1 Y-coordinate {m}
    3.910000000000,  !- Vertex 1 Z-coordinate {m}
    12.707103380308,  !- Vertex 2 X-coordinate {m}
    51.818168740863,  !- Vertex 2 Y-coordinate {m}
    0.000000000000,  !- Vertex 2 Z-coordinate {m}
    4.070095347853,  !- Vertex 3 X-coordinate {m}
    51.062528451241,  !- Vertex 3 Y-coordinate {m}
    0.000000000000,  !- Vertex 3 Z-coordinate {m}
    4.070095347853,  !- Vertex 4 X-coordinate {m}
    51.062528451241,  !- Vertex 4 Y-coordinate {m}
    3.910000000000;  !- Vertex 4 Z-coordinate {m}

  BuildingSurface:Detailed,
    F91CA1,  !- Name
    Wall,  !- Surface Type
    EXT_WALL_IF_S0,  !- Construction Name
    B1_S1_CL,  !- Zone Name
    Outdoors,  !- Outside Boundary Condition
    ,  !- Outside Boundary Condition Object
    SunExposed,  !- Sun Exposure
    WindExposed,  !- Wind Exposure
    ,  !- TRNSYS 17 - additional surface data
    4,  !- Number of Vertices
    13.893796264487,  !- Vertex 1 X-coordinate {m}
    11.673834529015,  !- Vertex 1 Y-coordinate {m}
    3.910000000000,  !- Vertex 1 Z-coordinate {m}
    13.893796264487,  !- Vertex 2 X-coordinate {m}
    11.673834529015,  !- Vertex 2 Y-coordinate {m}
    0.000000000000,  !- Vertex 2 Z-coordinate {m}
    16.201612885775,  !- Vertex 3 X-coordinate {m}
    11.875742320874,  !- Vertex 3 Y-coordinate {m}
    0.000000000000,  !- Vertex 3 Z-coordinate {m}
    16.201612885775,  !- Vertex 4 X-coordinate {m}
    11.875742320874,  !- Vertex 4 Y-coordinate {m}
    3.910000000000;  !- Vertex 4 Z-coordinate {m}

  BuildingSurface:Detailed,
    FE6CD6,  !- Name
    Wall,  !- Surface Type
    ADJ_WALL,  !- Construction Name
    B1_S1_CL,  !- Zone Name
    Zone,  !- Outside Boundary Condition
    B1_S1_SC,  !- Outside Boundary Condition Object
    NoSun,  !- Sun Exposure
    NoWind,  !- Wind Exposure
    ,  !- TRNSYS 17 - additional surface data
    4,  !- Number of Vertices
    -0.908031053950,  !- Vertex 1 X-coordinate {m}
    10.378842439183,  !- Vertex 1 Y-coordinate {m}
    3.910000000000,  !- Vertex 1 Z-coordinate {m}
    -0.908031053950,  !- Vertex 2 X-coordinate {m}
    10.378842439183,  !- Vertex 2 Y-coordinate {m}
    0.000000000000,  !- Vertex 2 Z-coordinate {m}
    13.893796264487,  !- Vertex 3 X-coordinate {m}
    11.673834529015,  !- Vertex 3 Y-coordinate {m}
    0.000000000000,  !- Vertex 3 Z-coordinate {m}
    13.893796264487,  !- Vertex 4 X-coordinate {m}
    11.673834529015,  !- Vertex 4 Y-coordinate {m}
    3.910000000000;  !- Vertex 4 Z-coordinate {m}

  Zone,
    B2_F0_OF,  !- Name
    0.0,  !- Direction of Relative North {deg}
    39.326026,  !- X Origin {m}
    0.0,  !- Y Origin {m}
    3.91,  !- Z Origin {m}
    ,  !- Type
    1;  !- Multiplier

  BuildingSurface:Detailed,
    84742A,  !- Name
    Floor,  !- Surface Type
    ADJ_CEILING,  !- Construction Name
    B2_F0_OF,  !- Zone Name
    Zone,  !- Outside Boundary Condition
    B2_S1_UN,  !- Outside Boundary Condition Object
    NoSun,  !- Sun Exposure
    NoWind,  !- Wind Exposure
    ,  !- TRNSYS 17 - additional surface data
    4,  !- Number of Vertices
    2.593766518227,  !- Vertex 1 X-coordinate {m}
    67.937044189933,  !- Vertex 1 Y-coordinate {m}
    3.910000000000,  !- Vertex 1 Z-coordinate {m}
    4.070095347853,  !- Vertex 2 X-coordinate {m}
    51.062528451241,  !- Vertex 2 Y-coordinate {m}
    3.910000000000,  !- Vertex 2 Z-coordinate {m}
    -5.353906496095,  !- Vertex 3 X-coordinate {m}
    50.238035124848,  !- Vertex 3 Y-coordinate {m}
    3.910000000000,  !- Vertex 3 Z-coordinate {m}
    -6.830235325721,  !- Vertex 4 X-coordinate {m}
    67.112550863540,  !- Vertex 4 Y-coordinate {m}
    3.910000000000;  !- Vertex 4 Z-coordinate {m}

  BuildingSurface:Detailed,
    55CA96,  !- Name
    Wall,  !- Surface Type
    ADJ_WALL,  !- Construction Name
    B2_F0_OF,  !- Zone Name
    Zone,  !- Outside Boundary Condition
    B1_F0_OF,  !- Outside Boundary Condition Object
    NoSun,  !- Sun Exposure
    NoWind,  !- Wind Exposure
    ,  !- TRNSYS 17 - additional surface data
    4,  !- Number of Vertices
    -4.402540559418,  !- Vertex 1 X-coordinate {m}
    50.321268859172,  !- Vertex 1 Y-coordinate {m}
    7.990000000000,  !- Vertex 1 Z-coordinate {m}
    -4.402540559418,  !- Vertex 2 X-coordinate {m}
    50.321268859172,  !- Vertex 2 Y-coordinate {m}
    3.910000000000,  !- Vertex 2 Z-coordinate {m}
    4.070095347853,  !- Vertex 3 X-coordinate {m}
    51.062528451241,  !- Vertex 3 Y-coordinate {m}
    3.910000000000,  !- Vertex 3 Z-coordinate {m}
    4.070095347853,  !- Vertex 4 X-coordinate {m}
    51.062528451241,  !- Vertex 4 Y-coordinate {m}
    7.990000000000;  !- Vertex 4 Z-coordinate {m}

  BuildingSurface:Detailed,
    3CEA5C,  !- Name
    Ceiling,  !- Surface Type
    ADJ_CEILING,  !- Construction Name
    B2_F0_OF,  !- Zone Name
    Zone,  !- Outside Boundary Condition
    B2_F1_OF,  !- Outside Boundary Condition Object
    NoSun,  !- Sun Exposure
    NoWind,  !- Wind Exposure
    ,  !- TRNSYS 17 - additional surface data
    4,  !- Number of Vertices
    -6.830235325721,  !- Vertex 1 X-coordinate {m}
    67.112550863540,  !- Vertex 1 Y-coordinate {m}
    7.990000000000,  !- Vertex 1 Z-coordinate {m}
    -5.353906496095,  !- Vertex 2 X-coordinate {m}
    50.238035124848,  !- Vertex 2 Y-coordinate {m}
    7.990000000000,  !- Vertex 2 Z-coordinate {m}
    4.070095347853,  !- Vertex 3 X-coordinate {m}
    51.062528451241,  !- Vertex 3 Y-coordinate {m}
    7.990000000000,  !- Vertex 3 Z-coordinate {m}
    2.593766518227,  !- Vertex 4 X-coordinate {m}
    67.937044189933,  !- Vertex 4 Y-coordinate {m}
    7.990000000000;  !- Vertex 4 Z-coordinate {m}

  BuildingSurface:Detailed,
    40DD51,  !- Name
    Wall,  !- Surface Type
    EXT_WALL_SW_EF_L0,  !- Construction Name
    B2_F0_OF,  !- Zone Name
    Outdoors,  !- Outside Boundary Condition
    ,  !- Outside Boundary Condition Object
    SunExposed,  !- Sun Exposure
    WindExposed,  !- Wind Exposure
    ,  !- TRNSYS 17 - additional surface data
    4,  !- Number of Vertices
    -6.830235325721,  !- Vertex 1 X-coordinate {m}
    67.112550863540,  !- Vertex 1 Y-coordinate {m}
    7.990000000000,  !- Vertex 1 Z-coordinate {m}
    -6.830235325721,  !- Vertex 2 X-coordinate {m}
    67.112550863540,  !- Vertex 2 Y-coordinate {m}
    3.910000000000,  !- Vertex 2 Z-coordinate {m}
    -5.353906496095,  !- Vertex 3 X-coordinate {m}
    50.238035124848,  !- Vertex 3 Y-coordinate {m}
    3.910000000000,  !- Vertex 3 Z-coordinate {m}
    -5.353906496095,  !- Vertex 4 X-coordinate {m}
    50.238035124848,  !- Vertex 4 Y-coordinate {m}
    7.990000000000;  !- Vertex 4 Z-coordinate {m}

  BuildingSurface:Detailed,
    F2A5E9,  !- Name
    Wall,  !- Surface Type
    EXT_WALL_SW_EF_L0,  !- Construction Name
    B2_F0_OF,  !- Zone Name
    Outdoors,  !- Outside Boundary Condition
    ,  !- Outside Boundary Condition Object
    SunExposed,  !- Sun Exposure
    WindExposed,  !- Wind Exposure
    ,  !- TRNSYS 17 - additional surface data
    4,  !- Number of Vertices
    -5.353906496095,  !- Vertex 1 X-coordinate {m}
    50.238035124848,  !- Vertex 1 Y-coordinate {m}
    7.990000000000,  !- Vertex 1 Z-coordinate {m}
    -5.353906496095,  !- Vertex 2 X-coordinate {m}
    50.238035124848,  !- Vertex 2 Y-coordinate {m}
    3.910000000000,  !- Vertex 2 Z-coordinate {m}
    -4.402540559418,  !- Vertex 3 X-coordinate {m}
    50.321268859172,  !- Vertex 3 Y-coordinate {m}
    3.910000000000,  !- Vertex 3 Z-coordinate {m}
    -4.402540559418,  !- Vertex 4 X-coordinate {m}
    50.321268859172,  !- Vertex 4 Y-coordinate {m}
    7.990000000000;  !- Vertex 4 Z-coordinate {m}

  BuildingSurface:Detailed,
    617641,  !- Name
    Wall,  !- Surface Type
    EXT_WALL_NE_EF_AL,  !- Construction Name
    B2_F0_OF,  !- Zone Name
    Outdoors,  !- Outside Boundary Condition
    ,  !- Outside Boundary Condition Object
    SunExposed,  !- Sun Exposure
    WindExposed,  !- Wind Exposure
    ,  !- TRNSYS 17 - additional surface data
    4,  !- Number of Vertices
    2.593766518227,  !- Vertex 1 X-coordinate {m}
    67.937044189933,  !- Vertex 1 Y-coordinate {m}
    7.990000000000,  !- Vertex 1 Z-coordinate {m}
    2.593766518227,  !- Vertex 2 X-coordinate {m}
    67.937044189933,  !- Vertex 2 Y-coordinate {m}
    3.910000000000,  !- Vertex 2 Z-coordinate {m}
    -6.830235325721,  !- Vertex 3 X-coordinate {m}
    67.112550863540,  !- Vertex 3 Y-coordinate {m}
    3.910000000000,  !- Vertex 3 Z-coordinate {m}
    -6.830235325721,  !- Vertex 4 X-coordinate {m}
    67.112550863540,  !- Vertex 4 Y-coordinate {m}
    7.990000000000;  !- Vertex 4 Z-coordinate {m}

  BuildingSurface:Detailed,
    127407,  !- Name
    Wall,  !- Surface Type
    ADJ_WALL,  !- Construction Name
    B2_F0_OF,  !- Zone Name
    Zone,  !- Outside Boundary Condition
    B2_F0_SC,  !- Outside Boundary Condition Object
    NoSun,  !- Sun Exposure
    NoWind,  !- Wind Exposure
    ,  !- TRNSYS 17 - additional surface data
    4,  !- Number of Vertices
    4.070095347853,  !- Vertex 1 X-coordinate {m}
    51.062528451241,  !- Vertex 1 Y-coordinate {m}
    7.990000000000,  !- Vertex 1 Z-coordinate {m}
    4.070095347853,  !- Vertex 2 X-coordinate {m}
    51.062528451241,  !- Vertex 2 Y-coordinate {m}
    3.910000000000,  !- Vertex 2 Z-coordinate {m}
    2.593766518227,  !- Vertex 3 X-coordinate {m}
    67.937044189933,  !- Vertex 3 Y-coordinate {m}
    3.910000000000,  !- Vertex 3 Z-coordinate {m}
    2.593766518227,  !- Vertex 4 X-coordinate {m}
    67.937044189933,  !- Vertex 4 Y-coordinate {m}
    7.990000000000;  !- Vertex 4 Z-coordinate {m}

  Zone,
    B2_F0_SC,  !- Name
    0.0,  !- Direction of Relative North {deg}
    39.326026,  !- X Origin {m}
    9.46,  !- Y Origin {m}
    3.91,  !- Z Origin {m}
    ,  !- Type
    1;  !- Multiplier

  BuildingSurface:Detailed,
    7423F1,  !- Name
    Floor,  !- Surface Type
    ADJ_CEILING,  !- Construction Name
    B2_F0_SC,  !- Zone Name
    Zone,  !- Outside Boundary Condition
    B2_S1_SC,  !- Outside Boundary Condition Object
    NoSun,  !- Sun Exposure
    NoWind,  !- Wind Exposure
    ,  !- TRNSYS 17 - additional surface data
    4,  !- Number of Vertices
    12.187071708591,  !- Vertex 1 X-coordinate {m}
    68.776349993744,  !- Vertex 1 Y-coordinate {m}
    3.910000000000,  !- Vertex 1 Z-coordinate {m}
    13.663400568944,  !- Vertex 2 X-coordinate {m}
    51.901833903830,  !- Vertex 2 Y-coordinate {m}
    3.910000000000,  !- Vertex 2 Z-coordinate {m}
    4.070095347853,  !- Vertex 3 X-coordinate {m}
    51.062528451241,  !- Vertex 3 Y-coordinate {m}
    3.910000000000,  !- Vertex 3 Z-coordinate {m}
    2.593766487499,  !- Vertex 4 X-coordinate {m}
    67.937044541155,  !- Vertex 4 Y-coordinate {m}
    3.910000000000;  !- Vertex 4 Z-coordinate {m}

  BuildingSurface:Detailed,
    D31381,  !- Name
    Ceiling,  !- Surface Type
    ADJ_CEILING,  !- Construction Name
    B2_F0_SC,  !- Zone Name
    Zone,  !- Outside Boundary Condition
    B2_F1_SC,  !- Outside Boundary Condition Object
    NoSun,  !- Sun Exposure
    NoWind,  !- Wind Exposure
    ,  !- TRNSYS 17 - additional surface data
    4,  !- Number of Vertices
    2.988928359068,  !- Vertex 1 X-coordinate {m}
    63.420323681069,  !- Vertex 1 Y-coordinate {m}
    7.990000000000,  !- Vertex 1 Z-coordinate {m}
    4.070095347853,  !- Vertex 2 X-coordinate {m}
    51.062528451241,  !- Vertex 2 Y-coordinate {m}
    7.990000000000,  !- Vertex 2 Z-coordinate {m}
    13.663400568944,  !- Vertex 3 X-coordinate {m}
    51.901833903830,  !- Vertex 3 Y-coordinate {m}
    7.990000000000,  !- Vertex 3 Z-coordinate {m}
    12.582233580160,  !- Vertex 4 X-coordinate {m}
    64.259629133658,  !- Vertex 4 Y-coordinate {m}
    7.990000000000;  !- Vertex 4 Z-coordinate {m}

  BuildingSurface:Detailed,
    6554B6,  !- Name
    Wall,  !- Surface Type
    ADJ_WALL,  !- Construction Name
    B2_F0_SC,  !- Zone Name
    Zone,  !- Outside Boundary Condition
    B2_F0_OF,  !- Outside Boundary Condition Object
    NoSun,  !- Sun Exposure
    NoWind,  !- Wind Exposure
    ,  !- TRNSYS 17 - additional surface data
    4,  !- Number of Vertices
    2.593766487499,  !- Vertex 1 X-coordinate {m}
    67.937044541155,  !- Vertex 1 Y-coordinate {m}
    7.990000000000,  !- Vertex 1 Z-coordinate {m}
    2.593766487499,  !- Vertex 2 X-coordinate {m}
    67.937044541155,  !- Vertex 2 Y-coordinate {m}
    3.910000000000,  !- Vertex 2 Z-coordinate {m}
    4.070095347853,  !- Vertex 3 X-coordinate {m}
    51.062528451241,  !- Vertex 3 Y-coordinate {m}
    3.910000000000,  !- Vertex 3 Z-coordinate {m}
    4.070095347853,  !- Vertex 4 X-coordinate {m}
    51.062528451241,  !- Vertex 4 Y-coordinate {m}
    7.990000000000;  !- Vertex 4 Z-coordinate {m}

  BuildingSurface:Detailed,
    63C225,  !- Name
    Wall,  !- Surface Type
    EXT_WALL_NE_EF_AL,  !- Construction Name
    B2_F0_SC,  !- Zone Name
    Outdoors,  !- Outside Boundary Condition
    ,  !- Outside Boundary Condition Object
    SunExposed,  !- Sun Exposure
    WindExposed,  !- Wind Exposure
    ,  !- TRNSYS 17 - additional surface data
    4,  !- Number of Vertices
    12.187071708591,  !- Vertex 1 X-coordinate {m}
    68.776349993744,  !- Vertex 1 Y-coordinate {m}
    7.990000000000,  !- Vertex 1 Z-coordinate {m}
    12.187071708591,  !- Vertex 2 X-coordinate {m}
    68.776349993744,  !- Vertex 2 Y-coordinate {m}
    3.910000000000,  !- Vertex 2 Z-coordinate {m}
    2.593766487499,  !- Vertex 3 X-coordinate {m}
    67.937044541155,  !- Vertex 3 Y-coordinate {m}
    3.910000000000,  !- Vertex 3 Z-coordinate {m}
    2.593766487499,  !- Vertex 4 X-coordinate {m}
    67.937044541155,  !- Vertex 4 Y-coordinate {m}
    7.990000000000;  !- Vertex 4 Z-coordinate {m}

  BuildingSurface:Detailed,
    5BB221,  !- Name
    Wall,  !- Surface Type
    ADJ_WALL,  !- Construction Name
    B2_F0_SC,  !- Zone Name
    Zone,  !- Outside Boundary Condition
    B1_F0_OF,  !- Outside Boundary Condition Object
    NoSun,  !- Sun Exposure
    NoWind,  !- Wind Exposure
    ,  !- TRNSYS 17 - additional surface data
    4,  !- Number of Vertices
    4.070095347853,  !- Vertex 1 X-coordinate {m}
    51.062528451241,  !- Vertex 1 Y-coordinate {m}
    7.990000000000,  !- Vertex 1 Z-coordinate {m}
    4.070095347853,  !- Vertex 2 X-coordinate {m}
    51.062528451241,  !- Vertex 2 Y-coordinate {m}
    3.910000000000,  !- Vertex 2 Z-coordinate {m}
    12.707103380308,  !- Vertex 3 X-coordinate {m}
    51.818168740863,  !- Vertex 3 Y-coordinate {m}
    3.910000000000,  !- Vertex 3 Z-coordinate {m}
    12.707103380308,  !- Vertex 4 X-coordinate {m}
    51.818168740863,  !- Vertex 4 Y-coordinate {m}
    7.990000000000;  !- Vertex 4 Z-coordinate {m}

  BuildingSurface:Detailed,
    7CFF97,  !- Name
    Wall,  !- Surface Type
    EXT_WALL_IF_S0,  !- Construction Name
    B2_F0_SC,  !- Zone Name
    Outdoors,  !- Outside Boundary Condition
    ,  !- Outside Boundary Condition Object
    SunExposed,  !- Sun Exposure
    WindExposed,  !- Wind Exposure
    ,  !- TRNSYS 17 - additional surface data
    4,  !- Number of Vertices
    12.707103380308,  !- Vertex 1 X-coordinate {m}
    51.818168740863,  !- Vertex 1 Y-coordinate {m}
    7.990000000000,  !- Vertex 1 Z-coordinate {m}
    12.707103380308,  !- Vertex 2 X-coordinate {m}
    51.818168740863,  !- Vertex 2 Y-coordinate {m}
    3.910000000000,  !- Vertex 2 Z-coordinate {m}
    13.663400568944,  !- Vertex 3 X-coordinate {m}
    51.901833903830,  !- Vertex 3 Y-coordinate {m}
    3.910000000000,  !- Vertex 3 Z-coordinate {m}
    13.663400568944,  !- Vertex 4 X-coordinate {m}
    51.901833903830,  !- Vertex 4 Y-coordinate {m}
    7.990000000000;  !- Vertex 4 Z-coordinate {m}

  BuildingSurface:Detailed,
    B9A925,  !- Name
    Wall,  !- Surface Type
    ADJ_WALL,  !- Construction Name
    B2_F0_SC,  !- Zone Name
    OtherSideCoefficients,  !- Outside Boundary Condition
    BOUNDARY=IDENTICAL,  !- Outside Boundary Condition Object
    NoSun,  !- Sun Exposure
    NoWind,  !- Wind Exposure
    0.0,  !- TRNSYS 17 - additional surface data
    4,  !- Number of Vertices
    13.663400568944,  !- Vertex 1 X-coordinate {m}
    51.901833903830,  !- Vertex 1 Y-coordinate {m}
    7.990000000000,  !- Vertex 1 Z-coordinate {m}
    13.663400568944,  !- Vertex 2 X-coordinate {m}
    51.901833903830,  !- Vertex 2 Y-coordinate {m}
    3.910000000000,  !- Vertex 2 Z-coordinate {m}
    12.187071708591,  !- Vertex 3 X-coordinate {m}
    68.776349993744,  !- Vertex 3 Y-coordinate {m}
    3.910000000000,  !- Vertex 3 Z-coordinate {m}
    12.187071708591,  !- Vertex 4 X-coordinate {m}
    68.776349993744,  !- Vertex 4 Y-coordinate {m}
    7.990000000000;  !- Vertex 4 Z-coordinate {m}

  Zone,
    B6_F0_CL,  !- Name
    0.0,  !- Direction of Relative North {deg}
    88.97948,  !- X Origin {m}
    48.376338,  !- Y Origin {m}
    3.91,  !- Z Origin {m}
    ,  !- Type
    1;  !- Multiplier

  BuildingSurface:Detailed,
    C16D0F,  !- Name
    Floor,  !- Surface Type
    ADJ_CEILING,  !- Construction Name
    B6_F0_CL,  !- Zone Name
    Zone,  !- Outside Boundary Condition
    B6_S1_CL2,  !- Outside Boundary Condition Object
    NoSun,  !- Sun Exposure
    NoWind,  !- Wind Exposure
    ,  !- TRNSYS 17 - additional surface data
    4,  !- Number of Vertices
    56.911828519733,  !- Vertex 1 X-coordinate {m}
    16.357320878178,  !- Vertex 1 Y-coordinate {m}
    3.910000000000,  !- Vertex 1 Z-coordinate {m}
    52.505893082225,  !- Vertex 2 X-coordinate {m}
    7.380253822592,  !- Vertex 2 Y-coordinate {m}
    3.910000000000,  !- Vertex 2 Z-coordinate {m}
    41.284559262741,  !- Vertex 3 X-coordinate {m}
    12.887673119476,  !- Vertex 3 Y-coordinate {m}
    3.910000000000,  !- Vertex 3 Z-coordinate {m}
    45.689599808048,  !- Vertex 4 X-coordinate {m}
    21.864319033099,  !- Vertex 4 Y-coordinate {m}
    3.910000000000;  !- Vertex 4 Z-coordinate {m}

  BuildingSurface:Detailed,
    626131,  !- Name
    Wall,  !- Surface Type
    ADJ_WALL,  !- Construction Name
    B6_F0_CL,  !- Zone Name
    Zone,  !- Outside Boundary Condition
    B6_S1_CL1,  !- Outside Boundary Condition Object
    NoSun,  !- Sun Exposure
    NoWind,  !- Wind Exposure
    ,  !- TRNSYS 17 - additional surface data
    4,  !- Number of Vertices
    56.911828519733,  !- Vertex 1 X-coordinate {m}
    16.357320878178,  !- Vertex 1 Y-coordinate {m}
    7.990000000000,  !- Vertex 1 Z-coordinate {m}
    56.911828519733,  !- Vertex 2 X-coordinate {m}
    16.357320878178,  !- Vertex 2 Y-coordinate {m}
    3.910000000000,  !- Vertex 2 Z-coordinate {m}
    45.689599808048,  !- Vertex 3 X-coordinate {m}
    21.864319033099,  !- Vertex 3 Y-coordinate {m}
    3.910000000000,  !- Vertex 3 Z-coordinate {m}
    45.689599808048,  !- Vertex 4 X-coordinate {m}
    21.864319033099,  !- Vertex 4 Y-coordinate {m}
    7.990000000000;  !- Vertex 4 Z-coordinate {m}

  BuildingSurface:Detailed,
    732C9E,  !- Name
    Ceiling,  !- Surface Type
    ADJ_CEILING,  !- Construction Name
    B6_F0_CL,  !- Zone Name
    Zone,  !- Outside Boundary Condition
    B6_F1_LB,  !- Outside Boundary Condition Object
    NoSun,  !- Sun Exposure
    NoWind,  !- Wind Exposure
    ,  !- TRNSYS 17 - additional surface data
    4,  !- Number of Vertices
    45.689599808048,  !- Vertex 1 X-coordinate {m}
    21.864319033099,  !- Vertex 1 Y-coordinate {m}
    7.990000000000,  !- Vertex 1 Z-coordinate {m}
    41.284559262741,  !- Vertex 2 X-coordinate {m}
    12.887673119476,  !- Vertex 2 Y-coordinate {m}
    7.990000000000,  !- Vertex 2 Z-coordinate {m}
    52.505893082225,  !- Vertex 3 X-coordinate {m}
    7.380253822592,  !- Vertex 3 Y-coordinate {m}
    7.990000000000,  !- Vertex 3 Z-coordinate {m}
    56.911828519733,  !- Vertex 4 X-coordinate {m}
    16.357320878178,  !- Vertex 4 Y-coordinate {m}
    7.990000000000;  !- Vertex 4 Z-coordinate {m}

  BuildingSurface:Detailed,
    EBDC5E,  !- Name
    Wall,  !- Surface Type
    EXT_WALL_IF_S0,  !- Construction Name
    B6_F0_CL,  !- Zone Name
    Outdoors,  !- Outside Boundary Condition
    ,  !- Outside Boundary Condition Object
    SunExposed,  !- Sun Exposure
    WindExposed,  !- Wind Exposure
    ,  !- TRNSYS 17 - additional surface data
    4,  !- Number of Vertices
    45.689599808048,  !- Vertex 1 X-coordinate {m}
    21.864319033099,  !- Vertex 1 Y-coordinate {m}
    7.990000000000,  !- Vertex 1 Z-coordinate {m}
    45.689599808048,  !- Vertex 2 X-coordinate {m}
    21.864319033099,  !- Vertex 2 Y-coordinate {m}
    3.910000000000,  !- Vertex 2 Z-coordinate {m}
    41.284559262741,  !- Vertex 3 X-coordinate {m}
    12.887673119476,  !- Vertex 3 Y-coordinate {m}
    3.910000000000,  !- Vertex 3 Z-coordinate {m}
    41.284559262741,  !- Vertex 4 X-coordinate {m}
    12.887673119476,  !- Vertex 4 Y-coordinate {m}
    7.990000000000;  !- Vertex 4 Z-coordinate {m}

  BuildingSurface:Detailed,
    EB9389,  !- Name
    Wall,  !- Surface Type
    EXT_WALL_NE_EF_AL,  !- Construction Name
    B6_F0_CL,  !- Zone Name
    Outdoors,  !- Outside Boundary Condition
    ,  !- Outside Boundary Condition Object
    SunExposed,  !- Sun Exposure
    WindExposed,  !- Wind Exposure
    ,  !- TRNSYS 17 - additional surface data
    4,  !- Number of Vertices
    52.505893082225,  !- Vertex 1 X-coordinate {m}
    7.380253822592,  !- Vertex 1 Y-coordinate {m}
    7.990000000000,  !- Vertex 1 Z-coordinate {m}
    52.505893082225,  !- Vertex 2 X-coordinate {m}
    7.380253822592,  !- Vertex 2 Y-coordinate {m}
    3.910000000000,  !- Vertex 2 Z-coordinate {m}
    56.911828519733,  !- Vertex 3 X-coordinate {m}
    16.357320878178,  !- Vertex 3 Y-coordinate {m}
    3.910000000000,  !- Vertex 3 Z-coordinate {m}
    56.911828519733,  !- Vertex 4 X-coordinate {m}
    16.357320878178,  !- Vertex 4 Y-coordinate {m}
    7.990000000000;  !- Vertex 4 Z-coordinate {m}

  BuildingSurface:Detailed,
    FD0BE5,  !- Name
    Wall,  !- Surface Type
    ADJ_WALL,  !- Construction Name
    B6_F0_CL,  !- Zone Name
    OtherSideCoefficients,  !- Outside Boundary Condition
    BOUNDARY=IDENTICAL,  !- Outside Boundary Condition Object
    NoSun,  !- Sun Exposure
    NoWind,  !- Wind Exposure
    0.0,  !- TRNSYS 17 - additional surface data
    4,  !- Number of Vertices
    41.284559262741,  !- Vertex 1 X-coordinate {m}
    12.887673119476,  !- Vertex 1 Y-coordinate {m}
    7.990000000000,  !- Vertex 1 Z-coordinate {m}
    41.284559262741,  !- Vertex 2 X-coordinate {m}
    12.887673119476,  !- Vertex 2 Y-coordinate {m}
    3.910000000000,  !- Vertex 2 Z-coordinate {m}
    52.505893082225,  !- Vertex 3 X-coordinate {m}
    7.380253822592,  !- Vertex 3 Y-coordinate {m}
    3.910000000000,  !- Vertex 3 Z-coordinate {m}
    52.505893082225,  !- Vertex 4 X-coordinate {m}
    7.380253822592,  !- Vertex 4 Y-coordinate {m}
    7.990000000000;  !- Vertex 4 Z-coordinate {m}

  Zone,
    B1_S1_SC,  !- Name
    0.0,  !- Direction of Relative North {deg}
    96.36,  !- X Origin {m}
    0.955,  !- Y Origin {m}
    0.0,  !- Z Origin {m}
    ,  !- Type
    1;  !- Multiplier

  BuildingSurface:Detailed,
    FC0E6F,  !- Name
    Floor,  !- Surface Type
    GROUND_FLOOR,  !- Construction Name
    B1_S1_SC,  !- Zone Name
    Ground,  !- Outside Boundary Condition
    BOUNDARY=INPUT 1*TGROUND,  !- Outside Boundary Condition Object
    NoSun,  !- Sun Exposure
    NoWind,  !- Wind Exposure
    ,  !- TRNSYS 17 - additional surface data
    4,  !- Number of Vertices
    13.893796264487,  !- Vertex 1 X-coordinate {m}
    11.673834529015,  !- Vertex 1 Y-coordinate {m}
    0.000000000000,  !- Vertex 1 Z-coordinate {m}
    11.024619423024,  !- Vertex 2 X-coordinate {m}
    -2.268709539582,  !- Vertex 2 Y-coordinate {m}
    0.000000000000,  !- Vertex 2 Z-coordinate {m}
    0.000000000000,  !- Vertex 3 X-coordinate {m}
    0.000000000000,  !- Vertex 3 Y-coordinate {m}
    0.000000000000,  !- Vertex 3 Z-coordinate {m}
    -0.908031053950,  !- Vertex 4 X-coordinate {m}
    10.378842439183,  !- Vertex 4 Y-coordinate {m}
    0.000000000000;  !- Vertex 4 Z-coordinate {m}

  BuildingSurface:Detailed,
    CDB830,  !- Name
    Wall,  !- Surface Type
    ADJ_WALL,  !- Construction Name
    B1_S1_SC,  !- Zone Name
    OtherSideCoefficients,  !- Outside Boundary Condition
    BOUNDARY=IDENTICAL,  !- Outside Boundary Condition Object
    NoSun,  !- Sun Exposure
    NoWind,  !- Wind Exposure
    0.0,  !- TRNSYS 17 - additional surface data
    4,  !- Number of Vertices
    11.024619423024,  !- Vertex 1 X-coordinate {m}
    -2.268709539582,  !- Vertex 1 Y-coordinate {m}
    3.910000000000,  !- Vertex 1 Z-coordinate {m}
    11.024619423024,  !- Vertex 2 X-coordinate {m}
    -2.268709539582,  !- Vertex 2 Y-coordinate {m}
    0.000000000000,  !- Vertex 2 Z-coordinate {m}
    13.313760665876,  !- Vertex 3 X-coordinate {m}
    8.855196326266,  !- Vertex 3 Y-coordinate {m}
    0.000000000000,  !- Vertex 3 Z-coordinate {m}
    13.313760665876,  !- Vertex 4 X-coordinate {m}
    8.855196326266,  !- Vertex 4 Y-coordinate {m}
    3.910000000000;  !- Vertex 4 Z-coordinate {m}

  BuildingSurface:Detailed,
    89A01B,  !- Name
    Ceiling,  !- Surface Type
    ADJ_CEILING,  !- Construction Name
    B1_S1_SC,  !- Zone Name
    Zone,  !- Outside Boundary Condition
    B1_F0_SC,  !- Outside Boundary Condition Object
    NoSun,  !- Sun Exposure
    NoWind,  !- Wind Exposure
    ,  !- TRNSYS 17 - additional surface data
    4,  !- Number of Vertices
    -0.908031053950,  !- Vertex 1 X-coordinate {m}
    10.378842439183,  !- Vertex 1 Y-coordinate {m}
    3.910000000000,  !- Vertex 1 Z-coordinate {m}
    0.000000000000,  !- Vertex 2 X-coordinate {m}
    0.000000000000,  !- Vertex 2 Y-coordinate {m}
    3.910000000000,  !- Vertex 2 Z-coordinate {m}
    11.024619423024,  !- Vertex 3 X-coordinate {m}
    -2.268709539582,  !- Vertex 3 Y-coordinate {m}
    3.910000000000,  !- Vertex 3 Z-coordinate {m}
    13.893796264487,  !- Vertex 4 X-coordinate {m}
    11.673834529015,  !- Vertex 4 Y-coordinate {m}
    3.910000000000;  !- Vertex 4 Z-coordinate {m}

  BuildingSurface:Detailed,
    376070,  !- Name
    Wall,  !- Surface Type
    EXT_WALL_IF_S0,  !- Construction Name
    B1_S1_SC,  !- Zone Name
    Outdoors,  !- Outside Boundary Condition
    ,  !- Outside Boundary Condition Object
    SunExposed,  !- Sun Exposure
    WindExposed,  !- Wind Exposure
    ,  !- TRNSYS 17 - additional surface data
    4,  !- Number of Vertices
    13.313760665876,  !- Vertex 1 X-coordinate {m}
    8.855196326266,  !- Vertex 1 Y-coordinate {m}
    3.910000000000,  !- Vertex 1 Z-coordinate {m}
    13.313760665876,  !- Vertex 2 X-coordinate {m}
    8.855196326266,  !- Vertex 2 Y-coordinate {m}
    0.000000000000,  !- Vertex 2 Z-coordinate {m}
    13.893796264487,  !- Vertex 3 X-coordinate {m}
    11.673834529015,  !- Vertex 3 Y-coordinate {m}
    0.000000000000,  !- Vertex 3 Z-coordinate {m}
    13.893796264487,  !- Vertex 4 X-coordinate {m}
    11.673834529015,  !- Vertex 4 Y-coordinate {m}
    3.910000000000;  !- Vertex 4 Z-coordinate {m}

  BuildingSurface:Detailed,
    7D4F97,  !- Name
    Wall,  !- Surface Type
    ADJ_WALL,  !- Construction Name
    B1_S1_SC,  !- Zone Name
    Zone,  !- Outside Boundary Condition
    B1_S1_CL,  !- Outside Boundary Condition Object
    NoSun,  !- Sun Exposure
    NoWind,  !- Wind Exposure
    ,  !- TRNSYS 17 - additional surface data
    4,  !- Number of Vertices
    13.893796264487,  !- Vertex 1 X-coordinate {m}
    11.673834529015,  !- Vertex 1 Y-coordinate {m}
    3.910000000000,  !- Vertex 1 Z-coordinate {m}
    13.893796264487,  !- Vertex 2 X-coordinate {m}
    11.673834529015,  !- Vertex 2 Y-coordinate {m}
    0.000000000000,  !- Vertex 2 Z-coordinate {m}
    -0.908031053950,  !- Vertex 3 X-coordinate {m}
    10.378842439183,  !- Vertex 3 Y-coordinate {m}
    0.000000000000,  !- Vertex 3 Z-coordinate {m}
    -0.908031053950,  !- Vertex 4 X-coordinate {m}
    10.378842439183,  !- Vertex 4 Y-coordinate {m}
    3.910000000000;  !- Vertex 4 Z-coordinate {m}

  BuildingSurface:Detailed,
    840AA7,  !- Name
    Wall,  !- Surface Type
    EXT_WALL_SW_EF_L0,  !- Construction Name
    B1_S1_SC,  !- Zone Name
    Outdoors,  !- Outside Boundary Condition
    ,  !- Outside Boundary Condition Object
    SunExposed,  !- Sun Exposure
    WindExposed,  !- Wind Exposure
    0.0,  !- TRNSYS 17 - additional surface data
    4,  !- Number of Vertices
    -0.908031053950,  !- Vertex 1 X-coordinate {m}
    10.378842439183,  !- Vertex 1 Y-coordinate {m}
    3.910000000000,  !- Vertex 1 Z-coordinate {m}
    -0.908031053950,  !- Vertex 2 X-coordinate {m}
    10.378842439183,  !- Vertex 2 Y-coordinate {m}
    0.000000000000,  !- Vertex 2 Z-coordinate {m}
    0.000000000000,  !- Vertex 3 X-coordinate {m}
    0.000000000000,  !- Vertex 3 Y-coordinate {m}
    0.000000000000,  !- Vertex 3 Z-coordinate {m}
    0.000000000000,  !- Vertex 4 X-coordinate {m}
    0.000000000000,  !- Vertex 4 Y-coordinate {m}
    3.910000000000;  !- Vertex 4 Z-coordinate {m}

  BuildingSurface:Detailed,
    CE3450,  !- Name
    Wall,  !- Surface Type
    EXT_WALL_SW_EF_L0,  !- Construction Name
    B1_S1_SC,  !- Zone Name
    Outdoors,  !- Outside Boundary Condition
    ,  !- Outside Boundary Condition Object
    SunExposed,  !- Sun Exposure
    WindExposed,  !- Wind Exposure
    ,  !- TRNSYS 17 - additional surface data
    4,  !- Number of Vertices
    0.000000000000,  !- Vertex 1 X-coordinate {m}
    0.000000000000,  !- Vertex 1 Y-coordinate {m}
    3.910000000000,  !- Vertex 1 Z-coordinate {m}
    0.000000000000,  !- Vertex 2 X-coordinate {m}
    0.000000000000,  !- Vertex 2 Y-coordinate {m}
    0.000000000000,  !- Vertex 2 Z-coordinate {m}
    11.024619423024,  !- Vertex 3 X-coordinate {m}
    -2.268709539582,  !- Vertex 3 Y-coordinate {m}
    0.000000000000,  !- Vertex 3 Z-coordinate {m}
    11.024619423024,  !- Vertex 4 X-coordinate {m}
    -2.268709539582,  !- Vertex 4 Y-coordinate {m}
    3.910000000000;  !- Vertex 4 Z-coordinate {m}

  Zone,
    B1_F0_SC,  !- Name
    0.0,  !- Direction of Relative North {deg}
    96.36,  !- X Origin {m}
    0.955,  !- Y Origin {m}
    3.91,  !- Z Origin {m}
    ,  !- Type
    1;  !- Multiplier

  BuildingSurface:Detailed,
    4E001F,  !- Name
    Floor,  !- Surface Type
    ADJ_CEILING,  !- Construction Name
    B1_F0_SC,  !- Zone Name
    Zone,  !- Outside Boundary Condition
    B1_S1_SC,  !- Outside Boundary Condition Object
    NoSun,  !- Sun Exposure
    NoWind,  !- Wind Exposure
    ,  !- TRNSYS 17 - additional surface data
    4,  !- Number of Vertices
    13.893796264487,  !- Vertex 1 X-coordinate {m}
    11.673834529015,  !- Vertex 1 Y-coordinate {m}
    3.910000000000,  !- Vertex 1 Z-coordinate {m}
    11.024619423024,  !- Vertex 2 X-coordinate {m}
    -2.268709539582,  !- Vertex 2 Y-coordinate {m}
    3.910000000000,  !- Vertex 2 Z-coordinate {m}
    0.000000000000,  !- Vertex 3 X-coordinate {m}
    0.000000000000,  !- Vertex 3 Y-coordinate {m}
    3.910000000000,  !- Vertex 3 Z-coordinate {m}
    -0.908031053950,  !- Vertex 4 X-coordinate {m}
    10.378842439183,  !- Vertex 4 Y-coordinate {m}
    3.910000000000;  !- Vertex 4 Z-coordinate {m}

  BuildingSurface:Detailed,
    F227CB,  !- Name
    Ceiling,  !- Surface Type
    ADJ_CEILING,  !- Construction Name
    B1_F0_SC,  !- Zone Name
    Zone,  !- Outside Boundary Condition
    B1_F2_SC,  !- Outside Boundary Condition Object
    NoSun,  !- Sun Exposure
    NoWind,  !- Wind Exposure
    ,  !- TRNSYS 17 - additional surface data
    4,  !- Number of Vertices
    -0.908031053950,  !- Vertex 1 X-coordinate {m}
    10.378842439183,  !- Vertex 1 Y-coordinate {m}
    12.580000000000,  !- Vertex 1 Z-coordinate {m}
    0.000000000000,  !- Vertex 2 X-coordinate {m}
    0.000000000000,  !- Vertex 2 Y-coordinate {m}
    12.580000000000,  !- Vertex 2 Z-coordinate {m}
    11.024619423024,  !- Vertex 3 X-coordinate {m}
    -2.268709539582,  !- Vertex 3 Y-coordinate {m}
    12.580000000000,  !- Vertex 3 Z-coordinate {m}
    13.893796264487,  !- Vertex 4 X-coordinate {m}
    11.673834529015,  !- Vertex 4 Y-coordinate {m}
    12.580000000000;  !- Vertex 4 Z-coordinate {m}

  BuildingSurface:Detailed,
    C8D5D3,  !- Name
    Wall,  !- Surface Type
    ADJ_WALL,  !- Construction Name
    B1_F0_SC,  !- Zone Name
    Zone,  !- Outside Boundary Condition
    B1_F1_KT,  !- Outside Boundary Condition Object
    NoSun,  !- Sun Exposure
    NoWind,  !- Wind Exposure
    ,  !- TRNSYS 17 - additional surface data
    4,  !- Number of Vertices
    13.893796264487,  !- Vertex 1 X-coordinate {m}
    11.673834529015,  !- Vertex 1 Y-coordinate {m}
    12.580000000000,  !- Vertex 1 Z-coordinate {m}
    13.893796264487,  !- Vertex 2 X-coordinate {m}
    11.673834529015,  !- Vertex 2 Y-coordinate {m}
    7.990000000000,  !- Vertex 2 Z-coordinate {m}
    7.564604853320,  !- Vertex 3 X-coordinate {m}
    11.120102031252,  !- Vertex 3 Y-coordinate {m}
    7.990000000000,  !- Vertex 3 Z-coordinate {m}
    7.564604853320,  !- Vertex 4 X-coordinate {m}
    11.120102031252,  !- Vertex 4 Y-coordinate {m}
    12.580000000000;  !- Vertex 4 Z-coordinate {m}

  BuildingSurface:Detailed,
    D5890F,  !- Name
    Wall,  !- Surface Type
    EXT_WALL_SW_EF_GL,  !- Construction Name
    B1_F0_SC,  !- Zone Name
    Outdoors,  !- Outside Boundary Condition
    ,  !- Outside Boundary Condition Object
    SunExposed,  !- Sun Exposure
    WindExposed,  !- Wind Exposure
    ,  !- TRNSYS 17 - additional surface data
    4,  !- Number of Vertices
    -0.908031053950,  !- Vertex 1 X-coordinate {m}
    10.378842439183,  !- Vertex 1 Y-coordinate {m}
    12.580000000000,  !- Vertex 1 Z-coordinate {m}
    -0.908031053950,  !- Vertex 2 X-coordinate {m}
    10.378842439183,  !- Vertex 2 Y-coordinate {m}
    7.990000000000,  !- Vertex 2 Z-coordinate {m}
    -0.592963043918,  !- Vertex 3 X-coordinate {m}
    6.777598605582,  !- Vertex 3 Y-coordinate {m}
    7.990000000000,  !- Vertex 3 Z-coordinate {m}
    -0.592963043918,  !- Vertex 4 X-coordinate {m}
    6.777598605582,  !- Vertex 4 Y-coordinate {m}
    12.580000000000;  !- Vertex 4 Z-coordinate {m}

  BuildingSurface:Detailed,
    60CF3B,  !- Name
    Wall,  !- Surface Type
    ADJ_WALL,  !- Construction Name
    B1_F0_SC,  !- Zone Name
    OtherSideCoefficients,  !- Outside Boundary Condition
    BOUNDARY=IDENTICAL,  !- Outside Boundary Condition Object
    NoSun,  !- Sun Exposure
    NoWind,  !- Wind Exposure
    0.0,  !- TRNSYS 17 - additional surface data
    4,  !- Number of Vertices
    11.024619423024,  !- Vertex 1 X-coordinate {m}
    -2.268709539582,  !- Vertex 1 Y-coordinate {m}
    12.580000000000,  !- Vertex 1 Z-coordinate {m}
    11.024619423024,  !- Vertex 2 X-coordinate {m}
    -2.268709539582,  !- Vertex 2 Y-coordinate {m}
    3.910000000000,  !- Vertex 2 Z-coordinate {m}
    13.313760665876,  !- Vertex 3 X-coordinate {m}
    8.855196326266,  !- Vertex 3 Y-coordinate {m}
    3.910000000000,  !- Vertex 3 Z-coordinate {m}
    13.313760665876,  !- Vertex 4 X-coordinate {m}
    8.855196326266,  !- Vertex 4 Y-coordinate {m}
    12.580000000000;  !- Vertex 4 Z-coordinate {m}

  BuildingSurface:Detailed,
    5C186E,  !- Name
    Wall,  !- Surface Type
    EXT_WALL_SW_EF_L0,  !- Construction Name
    B1_F0_SC,  !- Zone Name
    Outdoors,  !- Outside Boundary Condition
    ,  !- Outside Boundary Condition Object
    SunExposed,  !- Sun Exposure
    WindExposed,  !- Wind Exposure
    ,  !- TRNSYS 17 - additional surface data
    4,  !- Number of Vertices
    0.000000000000,  !- Vertex 1 X-coordinate {m}
    0.000000000000,  !- Vertex 1 Y-coordinate {m}
    12.580000000000,  !- Vertex 1 Z-coordinate {m}
    0.000000000000,  !- Vertex 2 X-coordinate {m}
    0.000000000000,  !- Vertex 2 Y-coordinate {m}
    3.910000000000,  !- Vertex 2 Z-coordinate {m}
    7.772760005483,  !- Vertex 3 X-coordinate {m}
    -1.599523221318,  !- Vertex 3 Y-coordinate {m}
    3.910000000000,  !- Vertex 3 Z-coordinate {m}
    7.772760005483,  !- Vertex 4 X-coordinate {m}
    -1.599523221318,  !- Vertex 4 Y-coordinate {m}
    12.580000000000;  !- Vertex 4 Z-coordinate {m}

  BuildingSurface:Detailed,
    1C1421,  !- Name
    Wall,  !- Surface Type
    EXT_WALL_IF_S0,  !- Construction Name
    B1_F0_SC,  !- Zone Name
    Outdoors,  !- Outside Boundary Condition
    ,  !- Outside Boundary Condition Object
    SunExposed,  !- Sun Exposure
    WindExposed,  !- Wind Exposure
    ,  !- TRNSYS 17 - additional surface data
    4,  !- Number of Vertices
    13.313760665876,  !- Vertex 1 X-coordinate {m}
    8.855196326266,  !- Vertex 1 Y-coordinate {m}
    12.580000000000,  !- Vertex 1 Z-coordinate {m}
    13.313760665876,  !- Vertex 2 X-coordinate {m}
    8.855196326266,  !- Vertex 2 Y-coordinate {m}
    3.910000000000,  !- Vertex 2 Z-coordinate {m}
    13.893796264487,  !- Vertex 3 X-coordinate {m}
    11.673834529015,  !- Vertex 3 Y-coordinate {m}
    3.910000000000,  !- Vertex 3 Z-coordinate {m}
    13.893796264487,  !- Vertex 4 X-coordinate {m}
    11.673834529015,  !- Vertex 4 Y-coordinate {m}
    12.580000000000;  !- Vertex 4 Z-coordinate {m}

  Zone,
    B1_F0_OF,  !- Name
    0.0,  !- Direction of Relative North {deg}
    56.265,  !- X Origin {m}
    0.955,  !- Y Origin {m}
    3.91,  !- Z Origin {m}
    ,  !- Type
    1;  !- Multiplier

  BuildingSurface:Detailed,
    3A243C,  !- Name
    Floor,  !- Surface Type
    ADJ_CEILING,  !- Construction Name
    B1_F0_OF,  !- Zone Name
    Zone,  !- Outside Boundary Condition
    B1_S1_CL,  !- Outside Boundary Condition Object
    NoSun,  !- Sun Exposure
    NoWind,  !- Wind Exposure
    ,  !- TRNSYS 17 - additional surface data
    4,  !- Number of Vertices
    12.707103380308,  !- Vertex 1 X-coordinate {m}
    51.818168740863,  !- Vertex 1 Y-coordinate {m}
    3.910000000000,  !- Vertex 1 Z-coordinate {m}
    16.201612885775,  !- Vertex 2 X-coordinate {m}
    11.875742320874,  !- Vertex 2 Y-coordinate {m}
    3.910000000000,  !- Vertex 2 Z-coordinate {m}
    -0.908031053950,  !- Vertex 3 X-coordinate {m}
    10.378842439183,  !- Vertex 3 Y-coordinate {m}
    3.910000000000,  !- Vertex 3 Z-coordinate {m}
    -4.402540559418,  !- Vertex 4 X-coordinate {m}
    50.321268859172,  !- Vertex 4 Y-coordinate {m}
    3.910000000000;  !- Vertex 4 Z-coordinate {m}

  BuildingSurface:Detailed,
    38D5CC,  !- Name
    Wall,  !- Surface Type
    ADJ_WALL,  !- Construction Name
    B1_F0_OF,  !- Zone Name
    Zone,  !- Outside Boundary Condition
    B2_F0_OF,  !- Outside Boundary Condition Object
    NoSun,  !- Sun Exposure
    NoWind,  !- Wind Exposure
    ,  !- TRNSYS 17 - additional surface data
    4,  !- Number of Vertices
    4.070095347853,  !- Vertex 1 X-coordinate {m}
    51.062528451241,  !- Vertex 1 Y-coordinate {m}
    7.990000000000,  !- Vertex 1 Z-coordinate {m}
    4.070095347853,  !- Vertex 2 X-coordinate {m}
    51.062528451241,  !- Vertex 2 Y-coordinate {m}
    3.910000000000,  !- Vertex 2 Z-coordinate {m}
    -4.402540559418,  !- Vertex 3 X-coordinate {m}
    50.321268859172,  !- Vertex 3 Y-coordinate {m}
    3.910000000000,  !- Vertex 3 Z-coordinate {m}
    -4.402540559418,  !- Vertex 4 X-coordinate {m}
    50.321268859172,  !- Vertex 4 Y-coordinate {m}
    7.990000000000;  !- Vertex 4 Z-coordinate {m}

  BuildingSurface:Detailed,
    97B41B,  !- Name
    Wall,  !- Surface Type
    ADJ_WALL,  !- Construction Name
    B1_F0_OF,  !- Zone Name
    Zone,  !- Outside Boundary Condition
    B2_F0_SC,  !- Outside Boundary Condition Object
    NoSun,  !- Sun Exposure
    NoWind,  !- Wind Exposure
    ,  !- TRNSYS 17 - additional surface data
    4,  !- Number of Vertices
    12.707103380308,  !- Vertex 1 X-coordinate {m}
    51.818168740863,  !- Vertex 1 Y-coordinate {m}
    7.990000000000,  !- Vertex 1 Z-coordinate {m}
    12.707103380308,  !- Vertex 2 X-coordinate {m}
    51.818168740863,  !- Vertex 2 Y-coordinate {m}
    3.910000000000,  !- Vertex 2 Z-coordinate {m}
    4.070095347853,  !- Vertex 3 X-coordinate {m}
    51.062528451241,  !- Vertex 3 Y-coordinate {m}
    3.910000000000,  !- Vertex 3 Z-coordinate {m}
    4.070095347853,  !- Vertex 4 X-coordinate {m}
    51.062528451241,  !- Vertex 4 Y-coordinate {m}
    7.990000000000;  !- Vertex 4 Z-coordinate {m}

  BuildingSurface:Detailed,
    6A5530,  !- Name
    Wall,  !- Surface Type
    EXT_WALL_SW_EF_L0,  !- Construction Name
    B1_F0_OF,  !- Zone Name
    Outdoors,  !- Outside Boundary Condition
    ,  !- Outside Boundary Condition Object
    SunExposed,  !- Sun Exposure
    WindExposed,  !- Wind Exposure
    ,  !- TRNSYS 17 - additional surface data
    4,  !- Number of Vertices
    -4.402540559418,  !- Vertex 1 X-coordinate {m}
    50.321268859172,  !- Vertex 1 Y-coordinate {m}
    7.990000000000,  !- Vertex 1 Z-coordinate {m}
    -4.402540559418,  !- Vertex 2 X-coordinate {m}
    50.321268859172,  !- Vertex 2 Y-coordinate {m}
    3.910000000000,  !- Vertex 2 Z-coordinate {m}
    -0.908031053950,  !- Vertex 3 X-coordinate {m}
    10.378842439183,  !- Vertex 3 Y-coordinate {m}
    3.910000000000,  !- Vertex 3 Z-coordinate {m}
    -0.908031053950,  !- Vertex 4 X-coordinate {m}
    10.378842439183,  !- Vertex 4 Y-coordinate {m}
    7.990000000000;  !- Vertex 4 Z-coordinate {m}

  BuildingSurface:Detailed,
    46356F,  !- Name
    Ceiling,  !- Surface Type
    ADJ_CEILING,  !- Construction Name
    B1_F0_OF,  !- Zone Name
    Zone,  !- Outside Boundary Condition
    B1_F1_CL,  !- Outside Boundary Condition Object
    NoSun,  !- Sun Exposure
    NoWind,  !- Wind Exposure
    ,  !- TRNSYS 17 - additional surface data
    4,  !- Number of Vertices
    4.070095347853,  !- Vertex 1 X-coordinate {m}
    51.062528451241,  !- Vertex 1 Y-coordinate {m}
    7.990000000000,  !- Vertex 1 Z-coordinate {m}
    6.518735940348,  !- Vertex 2 X-coordinate {m}
    23.074438408353,  !- Vertex 2 Y-coordinate {m}
    7.990000000000,  !- Vertex 2 Z-coordinate {m}
    15.155743972804,  !- Vertex 3 X-coordinate {m}
    23.830078697975,  !- Vertex 3 Y-coordinate {m}
    7.990000000000,  !- Vertex 3 Z-coordinate {m}
    12.707103380308,  !- Vertex 4 X-coordinate {m}
    51.818168740863,  !- Vertex 4 Y-coordinate {m}
    7.990000000000;  !- Vertex 4 Z-coordinate {m}

  BuildingSurface:Detailed,
    D87908,  !- Name
    Wall,  !- Surface Type
    ADJ_WALL,  !- Construction Name
    B1_F0_OF,  !- Zone Name
    Zone,  !- Outside Boundary Condition
    B1_F0_SC,  !- Outside Boundary Condition Object
    NoSun,  !- Sun Exposure
    NoWind,  !- Wind Exposure
    ,  !- TRNSYS 17 - additional surface data
    4,  !- Number of Vertices
    -0.908031053950,  !- Vertex 1 X-coordinate {m}
    10.378842439183,  !- Vertex 1 Y-coordinate {m}
    7.990000000000,  !- Vertex 1 Z-coordinate {m}
    -0.908031053950,  !- Vertex 2 X-coordinate {m}
    10.378842439183,  !- Vertex 2 Y-coordinate {m}
    3.910000000000,  !- Vertex 2 Z-coordinate {m}
    13.893796264487,  !- Vertex 3 X-coordinate {m}
    11.673834529015,  !- Vertex 3 Y-coordinate {m}
    3.910000000000,  !- Vertex 3 Z-coordinate {m}
    13.893796264487,  !- Vertex 4 X-coordinate {m}
    11.673834529015,  !- Vertex 4 Y-coordinate {m}
    7.990000000000;  !- Vertex 4 Z-coordinate {m}

  BuildingSurface:Detailed,
    F9E7FE,  !- Name
    Wall,  !- Surface Type
    EXT_WALL_IF_S0,  !- Construction Name
    B1_F0_OF,  !- Zone Name
    Outdoors,  !- Outside Boundary Condition
    ,  !- Outside Boundary Condition Object
    SunExposed,  !- Sun Exposure
    WindExposed,  !- Wind Exposure
    ,  !- TRNSYS 17 - additional surface data
    4,  !- Number of Vertices
    13.893796264487,  !- Vertex 1 X-coordinate {m}
    11.673834529015,  !- Vertex 1 Y-coordinate {m}
    7.990000000000,  !- Vertex 1 Z-coordinate {m}
    13.893796264487,  !- Vertex 2 X-coordinate {m}
    11.673834529015,  !- Vertex 2 Y-coordinate {m}
    3.910000000000,  !- Vertex 2 Z-coordinate {m}
    16.201612885775,  !- Vertex 3 X-coordinate {m}
    11.875742320874,  !- Vertex 3 Y-coordinate {m}
    3.910000000000,  !- Vertex 3 Z-coordinate {m}
    16.201612885775,  !- Vertex 4 X-coordinate {m}
    11.875742320874,  !- Vertex 4 Y-coordinate {m}
    7.990000000000;  !- Vertex 4 Z-coordinate {m}

  BuildingSurface:Detailed,
    7E2443,  !- Name
    Wall,  !- Surface Type
    EXT_WALL_IF_S0,  !- Construction Name
    B1_F0_OF,  !- Zone Name
    Outdoors,  !- Outside Boundary Condition
    ,  !- Outside Boundary Condition Object
    SunExposed,  !- Sun Exposure
    WindExposed,  !- Wind Exposure
    ,  !- TRNSYS 17 - additional surface data
    4,  !- Number of Vertices
    16.201612885775,  !- Vertex 1 X-coordinate {m}
    11.875742320874,  !- Vertex 1 Y-coordinate {m}
    7.990000000000,  !- Vertex 1 Z-coordinate {m}
    16.201612885775,  !- Vertex 2 X-coordinate {m}
    11.875742320874,  !- Vertex 2 Y-coordinate {m}
    3.910000000000,  !- Vertex 2 Z-coordinate {m}
    12.707103380308,  !- Vertex 3 X-coordinate {m}
    51.818168740863,  !- Vertex 3 Y-coordinate {m}
    3.910000000000,  !- Vertex 3 Z-coordinate {m}
    12.707103380308,  !- Vertex 4 X-coordinate {m}
    51.818168740863,  !- Vertex 4 Y-coordinate {m}
    7.990000000000;  !- Vertex 4 Z-coordinate {m}

  BuildingSurface:Detailed,
    287889,  !- Name
    Wall,  !- Surface Type
    ADJ_WALL,  !- Construction Name
    B1_F0_SC,  !- Zone Name
    Zone,  !- Outside Boundary Condition
    B1_F0_OF,  !- Outside Boundary Condition Object
    NoSun,  !- Sun Exposure
    NoWind,  !- Wind Exposure
    ,  !- TRNSYS 17 - additional surface data
    4,  !- Number of Vertices
    13.893796264487,  !- Vertex 1 X-coordinate {m}
    11.673834529015,  !- Vertex 1 Y-coordinate {m}
    7.990000000000,  !- Vertex 1 Z-coordinate {m}
    13.893796264487,  !- Vertex 2 X-coordinate {m}
    11.673834529015,  !- Vertex 2 Y-coordinate {m}
    3.910000000000,  !- Vertex 2 Z-coordinate {m}
    -0.908031053950,  !- Vertex 3 X-coordinate {m}
    10.378842439183,  !- Vertex 3 Y-coordinate {m}
    3.910000000000,  !- Vertex 3 Z-coordinate {m}
    -0.908031053950,  !- Vertex 4 X-coordinate {m}
    10.378842439183,  !- Vertex 4 Y-coordinate {m}
    7.990000000000;  !- Vertex 4 Z-coordinate {m}

  BuildingSurface:Detailed,
    17DCA3,  !- Name
    Roof,  !- Surface Type
    EXT_ROOF_SR,  !- Construction Name
    B2_F0_SC,  !- Zone Name
    Outdoors,  !- Outside Boundary Condition
    ,  !- Outside Boundary Condition Object
    SunExposed,  !- Sun Exposure
    WindExposed,  !- Wind Exposure
    ,  !- TRNSYS 17 - additional surface data
    4,  !- Number of Vertices
    2.593766487499,  !- Vertex 1 X-coordinate {m}
    67.937044541155,  !- Vertex 1 Y-coordinate {m}
    7.990000000000,  !- Vertex 1 Z-coordinate {m}
    2.988928359068,  !- Vertex 2 X-coordinate {m}
    63.420323681069,  !- Vertex 2 Y-coordinate {m}
    7.990000000000,  !- Vertex 2 Z-coordinate {m}
    12.582233580160,  !- Vertex 3 X-coordinate {m}
    64.259629133658,  !- Vertex 3 Y-coordinate {m}
    7.990000000000,  !- Vertex 3 Z-coordinate {m}
    12.187071708591,  !- Vertex 4 X-coordinate {m}
    68.776349993744,  !- Vertex 4 Y-coordinate {m}
    7.990000000000;  !- Vertex 4 Z-coordinate {m}

  Zone,
    B2_F1_OF,  !- Name
    0.0,  !- Direction of Relative North {deg}
    39.326026,  !- X Origin {m}
    0.0,  !- Y Origin {m}
    7.99,  !- Z Origin {m}
    ,  !- Type
    1;  !- Multiplier

  BuildingSurface:Detailed,
    EB8C35,  !- Name
    Floor,  !- Surface Type
    ADJ_CEILING,  !- Construction Name
    B2_F1_OF,  !- Zone Name
    Zone,  !- Outside Boundary Condition
    B2_F0_OF,  !- Outside Boundary Condition Object
    NoSun,  !- Sun Exposure
    NoWind,  !- Wind Exposure
    ,  !- TRNSYS 17 - additional surface data
    4,  !- Number of Vertices
    2.593766518227,  !- Vertex 1 X-coordinate {m}
    67.937044189933,  !- Vertex 1 Y-coordinate {m}
    7.990000000000,  !- Vertex 1 Z-coordinate {m}
    4.070095347853,  !- Vertex 2 X-coordinate {m}
    51.062528451241,  !- Vertex 2 Y-coordinate {m}
    7.990000000000,  !- Vertex 2 Z-coordinate {m}
    -5.353906496095,  !- Vertex 3 X-coordinate {m}
    50.238035124848,  !- Vertex 3 Y-coordinate {m}
    7.990000000000,  !- Vertex 3 Z-coordinate {m}
    -6.830235325721,  !- Vertex 4 X-coordinate {m}
    67.112550863540,  !- Vertex 4 Y-coordinate {m}
    7.990000000000;  !- Vertex 4 Z-coordinate {m}

  BuildingSurface:Detailed,
    1FC3FA,  !- Name
    Wall,  !- Surface Type
    EXT_WALL_NE_EF_AL,  !- Construction Name
    B2_F1_OF,  !- Zone Name
    Outdoors,  !- Outside Boundary Condition
    ,  !- Outside Boundary Condition Object
    SunExposed,  !- Sun Exposure
    WindExposed,  !- Wind Exposure
    ,  !- TRNSYS 17 - additional surface data
    4,  !- Number of Vertices
    2.988928359068,  !- Vertex 1 X-coordinate {m}
    63.420323681069,  !- Vertex 1 Y-coordinate {m}
    12.580000000000,  !- Vertex 1 Z-coordinate {m}
    2.988928359068,  !- Vertex 2 X-coordinate {m}
    63.420323681069,  !- Vertex 2 Y-coordinate {m}
    7.990000000000,  !- Vertex 2 Z-coordinate {m}
    2.593766518227,  !- Vertex 3 X-coordinate {m}
    67.937044189933,  !- Vertex 3 Y-coordinate {m}
    7.990000000000,  !- Vertex 3 Z-coordinate {m}
    2.593766518227,  !- Vertex 4 X-coordinate {m}
    67.937044189933,  !- Vertex 4 Y-coordinate {m}
    12.580000000000;  !- Vertex 4 Z-coordinate {m}

  BuildingSurface:Detailed,
    18C3EE,  !- Name
    Wall,  !- Surface Type
    ADJ_WALL,  !- Construction Name
    B2_F1_OF,  !- Zone Name
    Zone,  !- Outside Boundary Condition
    B2_F1_SC,  !- Outside Boundary Condition Object
    NoSun,  !- Sun Exposure
    NoWind,  !- Wind Exposure
    ,  !- TRNSYS 17 - additional surface data
    4,  !- Number of Vertices
    4.070095347853,  !- Vertex 1 X-coordinate {m}
    51.062528451241,  !- Vertex 1 Y-coordinate {m}
    12.580000000000,  !- Vertex 1 Z-coordinate {m}
    4.070095347853,  !- Vertex 2 X-coordinate {m}
    51.062528451241,  !- Vertex 2 Y-coordinate {m}
    7.990000000000,  !- Vertex 2 Z-coordinate {m}
    2.988928359068,  !- Vertex 3 X-coordinate {m}
    63.420323681069,  !- Vertex 3 Y-coordinate {m}
    7.990000000000,  !- Vertex 3 Z-coordinate {m}
    2.988928359068,  !- Vertex 4 X-coordinate {m}
    63.420323681069,  !- Vertex 4 Y-coordinate {m}
    12.580000000000;  !- Vertex 4 Z-coordinate {m}

  BuildingSurface:Detailed,
    E0DFF8,  !- Name
    Ceiling,  !- Surface Type
    ADJ_CEILING,  !- Construction Name
    B2_F1_OF,  !- Zone Name
    Zone,  !- Outside Boundary Condition
    B2_F2_CL,  !- Outside Boundary Condition Object
    NoSun,  !- Sun Exposure
    NoWind,  !- Wind Exposure
    ,  !- TRNSYS 17 - additional surface data
    4,  !- Number of Vertices
    -6.830235325721,  !- Vertex 1 X-coordinate {m}
    67.112550863540,  !- Vertex 1 Y-coordinate {m}
    12.580000000000,  !- Vertex 1 Z-coordinate {m}
    -5.353906496095,  !- Vertex 2 X-coordinate {m}
    50.238035124848,  !- Vertex 2 Y-coordinate {m}
    12.580000000000,  !- Vertex 2 Z-coordinate {m}
    4.070095347853,  !- Vertex 3 X-coordinate {m}
    51.062528451241,  !- Vertex 3 Y-coordinate {m}
    12.580000000000,  !- Vertex 3 Z-coordinate {m}
    2.593766518227,  !- Vertex 4 X-coordinate {m}
    67.937044189933,  !- Vertex 4 Y-coordinate {m}
    12.580000000000;  !- Vertex 4 Z-coordinate {m}

  BuildingSurface:Detailed,
    946C4F,  !- Name
    Wall,  !- Surface Type
    EXT_WALL_NE_EF_AL,  !- Construction Name
    B2_F1_OF,  !- Zone Name
    Outdoors,  !- Outside Boundary Condition
    ,  !- Outside Boundary Condition Object
    SunExposed,  !- Sun Exposure
    WindExposed,  !- Wind Exposure
    ,  !- TRNSYS 17 - additional surface data
    4,  !- Number of Vertices
    2.593766518227,  !- Vertex 1 X-coordinate {m}
    67.937044189933,  !- Vertex 1 Y-coordinate {m}
    12.580000000000,  !- Vertex 1 Z-coordinate {m}
    2.593766518227,  !- Vertex 2 X-coordinate {m}
    67.937044189933,  !- Vertex 2 Y-coordinate {m}
    7.990000000000,  !- Vertex 2 Z-coordinate {m}
    -6.830235325721,  !- Vertex 3 X-coordinate {m}
    67.112550863540,  !- Vertex 3 Y-coordinate {m}
    7.990000000000,  !- Vertex 3 Z-coordinate {m}
    -6.830235325721,  !- Vertex 4 X-coordinate {m}
    67.112550863540,  !- Vertex 4 Y-coordinate {m}
    12.580000000000;  !- Vertex 4 Z-coordinate {m}

  BuildingSurface:Detailed,
    FDD4D5,  !- Name
    Wall,  !- Surface Type
    EXT_WALL_SW_EF_RL,  !- Construction Name
    B2_F1_OF,  !- Zone Name
    Outdoors,  !- Outside Boundary Condition
    ,  !- Outside Boundary Condition Object
    SunExposed,  !- Sun Exposure
    WindExposed,  !- Wind Exposure
    ,  !- TRNSYS 17 - additional surface data
    4,  !- Number of Vertices
    -6.830235325721,  !- Vertex 1 X-coordinate {m}
    67.112550863540,  !- Vertex 1 Y-coordinate {m}
    12.580000000000,  !- Vertex 1 Z-coordinate {m}
    -6.830235325721,  !- Vertex 2 X-coordinate {m}
    67.112550863540,  !- Vertex 2 Y-coordinate {m}
    7.990000000000,  !- Vertex 2 Z-coordinate {m}
    -6.660281627363,  !- Vertex 3 X-coordinate {m}
    65.169971202261,  !- Vertex 3 Y-coordinate {m}
    7.990000000000,  !- Vertex 3 Z-coordinate {m}
    -6.660281627363,  !- Vertex 4 X-coordinate {m}
    65.169971202261,  !- Vertex 4 Y-coordinate {m}
    12.580000000000;  !- Vertex 4 Z-coordinate {m}

  BuildingSurface:Detailed,
    5C4A2A,  !- Name
    Wall,  !- Surface Type
    EXT_WALL_SW_EF_RL,  !- Construction Name
    B2_F1_OF,  !- Zone Name
    Outdoors,  !- Outside Boundary Condition
    ,  !- Outside Boundary Condition Object
    SunExposed,  !- Sun Exposure
    WindExposed,  !- Wind Exposure
    ,  !- TRNSYS 17 - additional surface data
    4,  !- Number of Vertices
    -5.353906496095,  !- Vertex 1 X-coordinate {m}
    50.238035124848,  !- Vertex 1 Y-coordinate {m}
    12.580000000000,  !- Vertex 1 Z-coordinate {m}
    -5.353906496095,  !- Vertex 2 X-coordinate {m}
    50.238035124848,  !- Vertex 2 Y-coordinate {m}
    7.990000000000,  !- Vertex 2 Z-coordinate {m}
    -4.402540559418,  !- Vertex 3 X-coordinate {m}
    50.321268859172,  !- Vertex 3 Y-coordinate {m}
    7.990000000000,  !- Vertex 3 Z-coordinate {m}
    -4.402540559418,  !- Vertex 4 X-coordinate {m}
    50.321268859172,  !- Vertex 4 Y-coordinate {m}
    12.580000000000;  !- Vertex 4 Z-coordinate {m}

  BuildingSurface:Detailed,
    74FAD5,  !- Name
    Wall,  !- Surface Type
    ADJ_WALL,  !- Construction Name
    B2_F1_OF,  !- Zone Name
    Zone,  !- Outside Boundary Condition
    B1_F1_CN,  !- Outside Boundary Condition Object
    NoSun,  !- Sun Exposure
    NoWind,  !- Wind Exposure
    ,  !- TRNSYS 17 - additional surface data
    4,  !- Number of Vertices
    -4.402540559418,  !- Vertex 1 X-coordinate {m}
    50.321268859172,  !- Vertex 1 Y-coordinate {m}
    12.580000000000,  !- Vertex 1 Z-coordinate {m}
    -4.402540559418,  !- Vertex 2 X-coordinate {m}
    50.321268859172,  !- Vertex 2 Y-coordinate {m}
    7.990000000000,  !- Vertex 2 Z-coordinate {m}
    4.070095347853,  !- Vertex 3 X-coordinate {m}
    51.062528451241,  !- Vertex 3 Y-coordinate {m}
    7.990000000000,  !- Vertex 3 Z-coordinate {m}
    4.070095347853,  !- Vertex 4 X-coordinate {m}
    51.062528451241,  !- Vertex 4 Y-coordinate {m}
    12.580000000000;  !- Vertex 4 Z-coordinate {m}

  Zone,
    B2_F1_SC,  !- Name
    0.0,  !- Direction of Relative North {deg}
    43.86,  !- X Origin {m}
    9.46,  !- Y Origin {m}
    7.99,  !- Z Origin {m}
    ,  !- Type
    1;  !- Multiplier

  BuildingSurface:Detailed,
    F7C48B,  !- Name
    Floor,  !- Surface Type
    ADJ_CEILING,  !- Construction Name
    B2_F1_SC,  !- Zone Name
    Zone,  !- Outside Boundary Condition
    B2_F0_SC,  !- Outside Boundary Condition Object
    NoSun,  !- Sun Exposure
    NoWind,  !- Wind Exposure
    ,  !- TRNSYS 17 - additional surface data
    4,  !- Number of Vertices
    12.582233580160,  !- Vertex 1 X-coordinate {m}
    64.259629133658,  !- Vertex 1 Y-coordinate {m}
    7.990000000000,  !- Vertex 1 Z-coordinate {m}
    13.663400568944,  !- Vertex 2 X-coordinate {m}
    51.901833903830,  !- Vertex 2 Y-coordinate {m}
    7.990000000000,  !- Vertex 2 Z-coordinate {m}
    4.070095347853,  !- Vertex 3 X-coordinate {m}
    51.062528451241,  !- Vertex 3 Y-coordinate {m}
    7.990000000000,  !- Vertex 3 Z-coordinate {m}
    2.988928359068,  !- Vertex 4 X-coordinate {m}
    63.420323681069,  !- Vertex 4 Y-coordinate {m}
    7.990000000000;  !- Vertex 4 Z-coordinate {m}

  BuildingSurface:Detailed,
    9CFC37,  !- Name
    Ceiling,  !- Surface Type
    ADJ_CEILING,  !- Construction Name
    B2_F1_SC,  !- Zone Name
    Zone,  !- Outside Boundary Condition
    B2_F2_SC,  !- Outside Boundary Condition Object
    NoSun,  !- Sun Exposure
    NoWind,  !- Wind Exposure
    ,  !- TRNSYS 17 - additional surface data
    4,  !- Number of Vertices
    2.988928359068,  !- Vertex 1 X-coordinate {m}
    63.420323681069,  !- Vertex 1 Y-coordinate {m}
    12.580000000000,  !- Vertex 1 Z-coordinate {m}
    4.070095347853,  !- Vertex 2 X-coordinate {m}
    51.062528451241,  !- Vertex 2 Y-coordinate {m}
    12.580000000000,  !- Vertex 2 Z-coordinate {m}
    13.663400568944,  !- Vertex 3 X-coordinate {m}
    51.901833903830,  !- Vertex 3 Y-coordinate {m}
    12.580000000000,  !- Vertex 3 Z-coordinate {m}
    12.582233580160,  !- Vertex 4 X-coordinate {m}
    64.259629133658,  !- Vertex 4 Y-coordinate {m}
    12.580000000000;  !- Vertex 4 Z-coordinate {m}

  BuildingSurface:Detailed,
    CF716B,  !- Name
    Wall,  !- Surface Type
    EXT_WALL_NE_EF_AL,  !- Construction Name
    B2_F1_SC,  !- Zone Name
    Outdoors,  !- Outside Boundary Condition
    ,  !- Outside Boundary Condition Object
    SunExposed,  !- Sun Exposure
    WindExposed,  !- Wind Exposure
    ,  !- TRNSYS 17 - additional surface data
    4,  !- Number of Vertices
    12.582233580160,  !- Vertex 1 X-coordinate {m}
    64.259629133658,  !- Vertex 1 Y-coordinate {m}
    12.580000000000,  !- Vertex 1 Z-coordinate {m}
    12.582233580160,  !- Vertex 2 X-coordinate {m}
    64.259629133658,  !- Vertex 2 Y-coordinate {m}
    7.990000000000,  !- Vertex 2 Z-coordinate {m}
    2.988928359068,  !- Vertex 3 X-coordinate {m}
    63.420323681069,  !- Vertex 3 Y-coordinate {m}
    7.990000000000,  !- Vertex 3 Z-coordinate {m}
    2.988928359068,  !- Vertex 4 X-coordinate {m}
    63.420323681069,  !- Vertex 4 Y-coordinate {m}
    12.580000000000;  !- Vertex 4 Z-coordinate {m}

  BuildingSurface:Detailed,
    D1A9FE,  !- Name
    Wall,  !- Surface Type
    EXT_WALL_IF_RL,  !- Construction Name
    B2_F1_SC,  !- Zone Name
    Outdoors,  !- Outside Boundary Condition
    ,  !- Outside Boundary Condition Object
    SunExposed,  !- Sun Exposure
    WindExposed,  !- Wind Exposure
    ,  !- TRNSYS 17 - additional surface data
    4,  !- Number of Vertices
    12.707103380308,  !- Vertex 1 X-coordinate {m}
    51.818168740863,  !- Vertex 1 Y-coordinate {m}
    12.580000000000,  !- Vertex 1 Z-coordinate {m}
    12.707103380308,  !- Vertex 2 X-coordinate {m}
    51.818168740863,  !- Vertex 2 Y-coordinate {m}
    7.990000000000,  !- Vertex 2 Z-coordinate {m}
    13.663400568944,  !- Vertex 3 X-coordinate {m}
    51.901833903830,  !- Vertex 3 Y-coordinate {m}
    7.990000000000,  !- Vertex 3 Z-coordinate {m}
    13.663400568944,  !- Vertex 4 X-coordinate {m}
    51.901833903830,  !- Vertex 4 Y-coordinate {m}
    12.580000000000;  !- Vertex 4 Z-coordinate {m}

  BuildingSurface:Detailed,
    C2DF83,  !- Name
    Wall,  !- Surface Type
    ADJ_WALL,  !- Construction Name
    B2_F1_SC,  !- Zone Name
    OtherSideCoefficients,  !- Outside Boundary Condition
    BOUNDARY=IDENTICAL,  !- Outside Boundary Condition Object
    NoSun,  !- Sun Exposure
    NoWind,  !- Wind Exposure
    0.0,  !- TRNSYS 17 - additional surface data
    4,  !- Number of Vertices
    13.663400568944,  !- Vertex 1 X-coordinate {m}
    51.901833903830,  !- Vertex 1 Y-coordinate {m}
    12.580000000000,  !- Vertex 1 Z-coordinate {m}
    13.663400568944,  !- Vertex 2 X-coordinate {m}
    51.901833903830,  !- Vertex 2 Y-coordinate {m}
    7.990000000000,  !- Vertex 2 Z-coordinate {m}
    12.582233580160,  !- Vertex 3 X-coordinate {m}
    64.259629133658,  !- Vertex 3 Y-coordinate {m}
    7.990000000000,  !- Vertex 3 Z-coordinate {m}
    12.582233580160,  !- Vertex 4 X-coordinate {m}
    64.259629133658,  !- Vertex 4 Y-coordinate {m}
    12.580000000000;  !- Vertex 4 Z-coordinate {m}

  BuildingSurface:Detailed,
    F77CA4,  !- Name
    Wall,  !- Surface Type
    ADJ_WALL,  !- Construction Name
    B2_F1_SC,  !- Zone Name
    Zone,  !- Outside Boundary Condition
    B2_F1_OF,  !- Outside Boundary Condition Object
    NoSun,  !- Sun Exposure
    NoWind,  !- Wind Exposure
    ,  !- TRNSYS 17 - additional surface data
    4,  !- Number of Vertices
    2.988928359068,  !- Vertex 1 X-coordinate {m}
    63.420323681069,  !- Vertex 1 Y-coordinate {m}
    12.580000000000,  !- Vertex 1 Z-coordinate {m}
    2.988928359068,  !- Vertex 2 X-coordinate {m}
    63.420323681069,  !- Vertex 2 Y-coordinate {m}
    7.990000000000,  !- Vertex 2 Z-coordinate {m}
    4.070095347853,  !- Vertex 3 X-coordinate {m}
    51.062528451241,  !- Vertex 3 Y-coordinate {m}
    7.990000000000,  !- Vertex 3 Z-coordinate {m}
    4.070095347853,  !- Vertex 4 X-coordinate {m}
    51.062528451241,  !- Vertex 4 Y-coordinate {m}
    12.580000000000;  !- Vertex 4 Z-coordinate {m}

  BuildingSurface:Detailed,
    E88351,  !- Name
    Wall,  !- Surface Type
    ADJ_WALL,  !- Construction Name
    B2_F1_SC,  !- Zone Name
    Zone,  !- Outside Boundary Condition
    B1_F1_CL,  !- Outside Boundary Condition Object
    NoSun,  !- Sun Exposure
    NoWind,  !- Wind Exposure
    ,  !- TRNSYS 17 - additional surface data
    4,  !- Number of Vertices
    4.070095347853,  !- Vertex 1 X-coordinate {m}
    51.062528451241,  !- Vertex 1 Y-coordinate {m}
    12.580000000000,  !- Vertex 1 Z-coordinate {m}
    4.070095347853,  !- Vertex 2 X-coordinate {m}
    51.062528451241,  !- Vertex 2 Y-coordinate {m}
    7.990000000000,  !- Vertex 2 Z-coordinate {m}
    12.707103380308,  !- Vertex 3 X-coordinate {m}
    51.818168740863,  !- Vertex 3 Y-coordinate {m}
    7.990000000000,  !- Vertex 3 Z-coordinate {m}
    12.707103380308,  !- Vertex 4 X-coordinate {m}
    51.818168740863,  !- Vertex 4 Y-coordinate {m}
    12.580000000000;  !- Vertex 4 Z-coordinate {m}

  Zone,
    B6_F1_LB,  !- Name
    0.0,  !- Direction of Relative North {deg}
    56.729463,  !- X Origin {m}
    67.860144,  !- Y Origin {m}
    7.99,  !- Z Origin {m}
    ,  !- Type
    1;  !- Multiplier

  BuildingSurface:Detailed,
    FC7B7A,  !- Name
    Floor,  !- Surface Type
    ADJ_CEILING,  !- Construction Name
    B6_F1_LB,  !- Zone Name
    Zone,  !- Outside Boundary Condition
    B6_F0_CL,  !- Outside Boundary Condition Object
    NoSun,  !- Sun Exposure
    NoWind,  !- Wind Exposure
    ,  !- TRNSYS 17 - additional surface data
    4,  !- Number of Vertices
    56.911828519733,  !- Vertex 1 X-coordinate {m}
    16.357320878178,  !- Vertex 1 Y-coordinate {m}
    7.990000000000,  !- Vertex 1 Z-coordinate {m}
    52.505893082225,  !- Vertex 2 X-coordinate {m}
    7.380253822592,  !- Vertex 2 Y-coordinate {m}
    7.990000000000,  !- Vertex 2 Z-coordinate {m}
    41.284559262741,  !- Vertex 3 X-coordinate {m}
    12.887673119476,  !- Vertex 3 Y-coordinate {m}
    7.990000000000,  !- Vertex 3 Z-coordinate {m}
    45.689599808048,  !- Vertex 4 X-coordinate {m}
    21.864319033099,  !- Vertex 4 Y-coordinate {m}
    7.990000000000;  !- Vertex 4 Z-coordinate {m}

  BuildingSurface:Detailed,
    36CA0C,  !- Name
    Ceiling,  !- Surface Type
    ADJ_CEILING,  !- Construction Name
    B6_F1_LB,  !- Zone Name
    Zone,  !- Outside Boundary Condition
    B6_F2_OF,  !- Outside Boundary Condition Object
    NoSun,  !- Sun Exposure
    NoWind,  !- Wind Exposure
    ,  !- TRNSYS 17 - additional surface data
    4,  !- Number of Vertices
    44.808863897137,  !- Vertex 1 X-coordinate {m}
    20.069544539119,  !- Vertex 1 Y-coordinate {m}
    12.580000000000,  !- Vertex 1 Z-coordinate {m}
    41.284559262741,  !- Vertex 2 X-coordinate {m}
    12.887673119476,  !- Vertex 2 Y-coordinate {m}
    12.580000000000,  !- Vertex 2 Z-coordinate {m}
    52.505893082225,  !- Vertex 3 X-coordinate {m}
    7.380253822592,  !- Vertex 3 Y-coordinate {m}
    12.580000000000,  !- Vertex 3 Z-coordinate {m}
    56.030641432231,  !- Vertex 4 X-coordinate {m}
    14.561907467061,  !- Vertex 4 Y-coordinate {m}
    12.580000000000;  !- Vertex 4 Z-coordinate {m}

  BuildingSurface:Detailed,
    C08D7D,  !- Name
    Wall,  !- Surface Type
    EXT_WALL_IF_RL,  !- Construction Name
    B6_F1_LB,  !- Zone Name
    Outdoors,  !- Outside Boundary Condition
    ,  !- Outside Boundary Condition Object
    SunExposed,  !- Sun Exposure
    WindExposed,  !- Wind Exposure
    ,  !- TRNSYS 17 - additional surface data
    4,  !- Number of Vertices
    62.288489505666,  !- Vertex 1 X-coordinate {m}
    55.689741033696,  !- Vertex 1 Y-coordinate {m}
    12.580000000000,  !- Vertex 1 Z-coordinate {m}
    62.288489505666,  !- Vertex 2 X-coordinate {m}
    55.689741033696,  !- Vertex 2 Y-coordinate {m}
    7.990000000000,  !- Vertex 2 Z-coordinate {m}
    41.284559262741,  !- Vertex 3 X-coordinate {m}
    12.887673119476,  !- Vertex 3 Y-coordinate {m}
    7.990000000000,  !- Vertex 3 Z-coordinate {m}
    41.284559262741,  !- Vertex 4 X-coordinate {m}
    12.887673119476,  !- Vertex 4 Y-coordinate {m}
    12.580000000000;  !- Vertex 4 Z-coordinate {m}

  BuildingSurface:Detailed,
    A2C15B,  !- Name
    Wall,  !- Surface Type
    ADJ_WALL,  !- Construction Name
    B6_F1_LB,  !- Zone Name
    OtherSideCoefficients,  !- Outside Boundary Condition
    BOUNDARY=IDENTICAL,  !- Outside Boundary Condition Object
    NoSun,  !- Sun Exposure
    NoWind,  !- Wind Exposure
    0.0,  !- TRNSYS 17 - additional surface data
    4,  !- Number of Vertices
    73.517257553134,  !- Vertex 1 X-coordinate {m}
    50.190783041650,  !- Vertex 1 Y-coordinate {m}
    12.580000000000,  !- Vertex 1 Z-coordinate {m}
    73.517257553134,  !- Vertex 2 X-coordinate {m}
    50.190783041650,  !- Vertex 2 Y-coordinate {m}
    7.990000000000,  !- Vertex 2 Z-coordinate {m}
    62.288489505666,  !- Vertex 3 X-coordinate {m}
    55.689741033696,  !- Vertex 3 Y-coordinate {m}
    7.990000000000,  !- Vertex 3 Z-coordinate {m}
    62.288489505666,  !- Vertex 4 X-coordinate {m}
    55.689741033696,  !- Vertex 4 Y-coordinate {m}
    12.580000000000;  !- Vertex 4 Z-coordinate {m}

  BuildingSurface:Detailed,
    9456BF,  !- Name
    Wall,  !- Surface Type
    EXT_WALL_NE_EF_AL,  !- Construction Name
    B6_F1_LB,  !- Zone Name
    Outdoors,  !- Outside Boundary Condition
    ,  !- Outside Boundary Condition Object
    SunExposed,  !- Sun Exposure
    WindExposed,  !- Wind Exposure
    ,  !- TRNSYS 17 - additional surface data
    4,  !- Number of Vertices
    52.505893082225,  !- Vertex 1 X-coordinate {m}
    7.380253822592,  !- Vertex 1 Y-coordinate {m}
    12.580000000000,  !- Vertex 1 Z-coordinate {m}
    52.505893082225,  !- Vertex 2 X-coordinate {m}
    7.380253822592,  !- Vertex 2 Y-coordinate {m}
    7.990000000000,  !- Vertex 2 Z-coordinate {m}
    73.517257553134,  !- Vertex 3 X-coordinate {m}
    50.190783041650,  !- Vertex 3 Y-coordinate {m}
    7.990000000000,  !- Vertex 3 Z-coordinate {m}
    73.517257553134,  !- Vertex 4 X-coordinate {m}
    50.190783041650,  !- Vertex 4 Y-coordinate {m}
    12.580000000000;  !- Vertex 4 Z-coordinate {m}

  BuildingSurface:Detailed,
    DE6A87,  !- Name
    Wall,  !- Surface Type
    ADJ_WALL,  !- Construction Name
    B6_F1_LB,  !- Zone Name
    OtherSideCoefficients,  !- Outside Boundary Condition
    BOUNDARY=IDENTICAL,  !- Outside Boundary Condition Object
    NoSun,  !- Sun Exposure
    NoWind,  !- Wind Exposure
    0.0,  !- TRNSYS 17 - additional surface data
    4,  !- Number of Vertices
    41.284559262741,  !- Vertex 1 X-coordinate {m}
    12.887673119476,  !- Vertex 1 Y-coordinate {m}
    12.580000000000,  !- Vertex 1 Z-coordinate {m}
    41.284559262741,  !- Vertex 2 X-coordinate {m}
    12.887673119476,  !- Vertex 2 Y-coordinate {m}
    7.990000000000,  !- Vertex 2 Z-coordinate {m}
    52.505893082225,  !- Vertex 3 X-coordinate {m}
    7.380253822592,  !- Vertex 3 Y-coordinate {m}
    7.990000000000,  !- Vertex 3 Z-coordinate {m}
    52.505893082225,  !- Vertex 4 X-coordinate {m}
    7.380253822592,  !- Vertex 4 Y-coordinate {m}
    12.580000000000;  !- Vertex 4 Z-coordinate {m}

  BuildingSurface:Detailed,
    707F7B,  !- Name
    Floor,  !- Surface Type
    ADJ_CEILING,  !- Construction Name
    B6_F1_LB,  !- Zone Name
    Zone,  !- Outside Boundary Condition
    B6_S1_CL1,  !- Outside Boundary Condition Object
    NoSun,  !- Sun Exposure
    NoWind,  !- Wind Exposure
    ,  !- TRNSYS 17 - additional surface data
    4,  !- Number of Vertices
    73.517257553134,  !- Vertex 1 X-coordinate {m}
    50.190783041650,  !- Vertex 1 Y-coordinate {m}
    7.990000000000,  !- Vertex 1 Z-coordinate {m}
    56.911828519733,  !- Vertex 2 X-coordinate {m}
    16.357320878178,  !- Vertex 2 Y-coordinate {m}
    7.990000000000,  !- Vertex 2 Z-coordinate {m}
    45.689599808048,  !- Vertex 3 X-coordinate {m}
    21.864319033099,  !- Vertex 3 Y-coordinate {m}
    7.990000000000,  !- Vertex 3 Z-coordinate {m}
    62.288489505666,  !- Vertex 4 X-coordinate {m}
    55.689741033696,  !- Vertex 4 Y-coordinate {m}
    7.990000000000;  !- Vertex 4 Z-coordinate {m}

  BuildingSurface:Detailed,
    B9FFCF,  !- Name
    Ceiling,  !- Surface Type
    ADJ_CEILING,  !- Construction Name
    B1_F0_OF,  !- Zone Name
    Zone,  !- Outside Boundary Condition
    B1_F1_CN,  !- Outside Boundary Condition Object
    NoSun,  !- Sun Exposure
    NoWind,  !- Wind Exposure
    ,  !- TRNSYS 17 - additional surface data
    4,  !- Number of Vertices
    -4.402540559418,  !- Vertex 1 X-coordinate {m}
    50.321268859172,  !- Vertex 1 Y-coordinate {m}
    7.990000000000,  !- Vertex 1 Z-coordinate {m}
    -0.908031053950,  !- Vertex 2 X-coordinate {m}
    10.378842439183,  !- Vertex 2 Y-coordinate {m}
    7.990000000000,  !- Vertex 2 Z-coordinate {m}
    7.564604853320,  !- Vertex 3 X-coordinate {m}
    11.120102031252,  !- Vertex 3 Y-coordinate {m}
    7.990000000000,  !- Vertex 3 Z-coordinate {m}
    4.070095347853,  !- Vertex 4 X-coordinate {m}
    51.062528451241,  !- Vertex 4 Y-coordinate {m}
    7.990000000000;  !- Vertex 4 Z-coordinate {m}

  BuildingSurface:Detailed,
    5643E4,  !- Name
    Ceiling,  !- Surface Type
    ADJ_CEILING,  !- Construction Name
    B1_F0_OF,  !- Zone Name
    Zone,  !- Outside Boundary Condition
    B1_F1_KT,  !- Outside Boundary Condition Object
    NoSun,  !- Sun Exposure
    NoWind,  !- Wind Exposure
    ,  !- TRNSYS 17 - additional surface data
    4,  !- Number of Vertices
    6.518735940348,  !- Vertex 1 X-coordinate {m}
    23.074438408353,  !- Vertex 1 Y-coordinate {m}
    7.990000000000,  !- Vertex 1 Z-coordinate {m}
    7.564604853320,  !- Vertex 2 X-coordinate {m}
    11.120102031252,  !- Vertex 2 Y-coordinate {m}
    7.990000000000,  !- Vertex 2 Z-coordinate {m}
    16.201612885775,  !- Vertex 3 X-coordinate {m}
    11.875742320874,  !- Vertex 3 Y-coordinate {m}
    7.990000000000,  !- Vertex 3 Z-coordinate {m}
    15.155743972804,  !- Vertex 4 X-coordinate {m}
    23.830078697975,  !- Vertex 4 Y-coordinate {m}
    7.990000000000;  !- Vertex 4 Z-coordinate {m}

  Zone,
    B1_F1_KT,  !- Name
    0.0,  !- Direction of Relative North {deg}
    84.36,  !- X Origin {m}
    9.46,  !- Y Origin {m}
    7.99,  !- Z Origin {m}
    ,  !- Type
    1;  !- Multiplier

  BuildingSurface:Detailed,
    5105E3,  !- Name
    Floor,  !- Surface Type
    ADJ_CEILING,  !- Construction Name
    B1_F1_KT,  !- Zone Name
    Zone,  !- Outside Boundary Condition
    B1_F0_OF,  !- Outside Boundary Condition Object
    NoSun,  !- Sun Exposure
    NoWind,  !- Wind Exposure
    ,  !- TRNSYS 17 - additional surface data
    4,  !- Number of Vertices
    15.155743972804,  !- Vertex 1 X-coordinate {m}
    23.830078697975,  !- Vertex 1 Y-coordinate {m}
    7.990000000000,  !- Vertex 1 Z-coordinate {m}
    16.201612885775,  !- Vertex 2 X-coordinate {m}
    11.875742320874,  !- Vertex 2 Y-coordinate {m}
    7.990000000000,  !- Vertex 2 Z-coordinate {m}
    7.564604853320,  !- Vertex 3 X-coordinate {m}
    11.120102031252,  !- Vertex 3 Y-coordinate {m}
    7.990000000000,  !- Vertex 3 Z-coordinate {m}
    6.518735940348,  !- Vertex 4 X-coordinate {m}
    23.074438408353,  !- Vertex 4 Y-coordinate {m}
    7.990000000000;  !- Vertex 4 Z-coordinate {m}

  BuildingSurface:Detailed,
    F25638,  !- Name
    Ceiling,  !- Surface Type
    ADJ_CEILING,  !- Construction Name
    B1_F1_KT,  !- Zone Name
    Zone,  !- Outside Boundary Condition
    B1_F2_CL,  !- Outside Boundary Condition Object
    NoSun,  !- Sun Exposure
    NoWind,  !- Wind Exposure
    ,  !- TRNSYS 17 - additional surface data
    4,  !- Number of Vertices
    6.518735940348,  !- Vertex 1 X-coordinate {m}
    23.074438408353,  !- Vertex 1 Y-coordinate {m}
    12.580000000000,  !- Vertex 1 Z-coordinate {m}
    7.564604853320,  !- Vertex 2 X-coordinate {m}
    11.120102031252,  !- Vertex 2 Y-coordinate {m}
    12.580000000000,  !- Vertex 2 Z-coordinate {m}
    16.201612885775,  !- Vertex 3 X-coordinate {m}
    11.875742320874,  !- Vertex 3 Y-coordinate {m}
    12.580000000000,  !- Vertex 3 Z-coordinate {m}
    15.155743972804,  !- Vertex 4 X-coordinate {m}
    23.830078697975,  !- Vertex 4 Y-coordinate {m}
    12.580000000000;  !- Vertex 4 Z-coordinate {m}

  BuildingSurface:Detailed,
    49B1AA,  !- Name
    Wall,  !- Surface Type
    EXT_WALL_IF_RL,  !- Construction Name
    B1_F1_KT,  !- Zone Name
    Outdoors,  !- Outside Boundary Condition
    ,  !- Outside Boundary Condition Object
    SunExposed,  !- Sun Exposure
    WindExposed,  !- Wind Exposure
    ,  !- TRNSYS 17 - additional surface data
    4,  !- Number of Vertices
    13.893796264487,  !- Vertex 1 X-coordinate {m}
    11.673834529015,  !- Vertex 1 Y-coordinate {m}
    12.580000000000,  !- Vertex 1 Z-coordinate {m}
    13.893796264487,  !- Vertex 2 X-coordinate {m}
    11.673834529015,  !- Vertex 2 Y-coordinate {m}
    7.990000000000,  !- Vertex 2 Z-coordinate {m}
    16.201612885775,  !- Vertex 3 X-coordinate {m}
    11.875742320874,  !- Vertex 3 Y-coordinate {m}
    7.990000000000,  !- Vertex 3 Z-coordinate {m}
    16.201612885775,  !- Vertex 4 X-coordinate {m}
    11.875742320874,  !- Vertex 4 Y-coordinate {m}
    12.580000000000;  !- Vertex 4 Z-coordinate {m}

  BuildingSurface:Detailed,
    57E632,  !- Name
    Wall,  !- Surface Type
    ADJ_WALL,  !- Construction Name
    B1_F1_KT,  !- Zone Name
    Zone,  !- Outside Boundary Condition
    B1_F1_CN,  !- Outside Boundary Condition Object
    NoSun,  !- Sun Exposure
    NoWind,  !- Wind Exposure
    ,  !- TRNSYS 17 - additional surface data
    4,  !- Number of Vertices
    6.518735940348,  !- Vertex 1 X-coordinate {m}
    23.074438408353,  !- Vertex 1 Y-coordinate {m}
    12.580000000000,  !- Vertex 1 Z-coordinate {m}
    6.518735940348,  !- Vertex 2 X-coordinate {m}
    23.074438408353,  !- Vertex 2 Y-coordinate {m}
    7.990000000000,  !- Vertex 2 Z-coordinate {m}
    7.564604853320,  !- Vertex 3 X-coordinate {m}
    11.120102031252,  !- Vertex 3 Y-coordinate {m}
    7.990000000000,  !- Vertex 3 Z-coordinate {m}
    7.564604853320,  !- Vertex 4 X-coordinate {m}
    11.120102031252,  !- Vertex 4 Y-coordinate {m}
    12.580000000000;  !- Vertex 4 Z-coordinate {m}

  BuildingSurface:Detailed,
    F5E0B3,  !- Name
    Wall,  !- Surface Type
    ADJ_WALL,  !- Construction Name
    B1_F1_KT,  !- Zone Name
    Zone,  !- Outside Boundary Condition
    B1_F1_CL,  !- Outside Boundary Condition Object
    NoSun,  !- Sun Exposure
    NoWind,  !- Wind Exposure
    ,  !- TRNSYS 17 - additional surface data
    4,  !- Number of Vertices
    15.155743972804,  !- Vertex 1 X-coordinate {m}
    23.830078697975,  !- Vertex 1 Y-coordinate {m}
    12.580000000000,  !- Vertex 1 Z-coordinate {m}
    15.155743972804,  !- Vertex 2 X-coordinate {m}
    23.830078697975,  !- Vertex 2 Y-coordinate {m}
    7.990000000000,  !- Vertex 2 Z-coordinate {m}
    6.518735940348,  !- Vertex 3 X-coordinate {m}
    23.074438408353,  !- Vertex 3 Y-coordinate {m}
    7.990000000000,  !- Vertex 3 Z-coordinate {m}
    6.518735940348,  !- Vertex 4 X-coordinate {m}
    23.074438408353,  !- Vertex 4 Y-coordinate {m}
    12.580000000000;  !- Vertex 4 Z-coordinate {m}

  BuildingSurface:Detailed,
    7786F1,  !- Name
    Wall,  !- Surface Type
    ADJ_WALL,  !- Construction Name
    B1_F1_KT,  !- Zone Name
    Zone,  !- Outside Boundary Condition
    B1_F0_SC,  !- Outside Boundary Condition Object
    NoSun,  !- Sun Exposure
    NoWind,  !- Wind Exposure
    ,  !- TRNSYS 17 - additional surface data
    4,  !- Number of Vertices
    7.564604853320,  !- Vertex 1 X-coordinate {m}
    11.120102031252,  !- Vertex 1 Y-coordinate {m}
    12.580000000000,  !- Vertex 1 Z-coordinate {m}
    7.564604853320,  !- Vertex 2 X-coordinate {m}
    11.120102031252,  !- Vertex 2 Y-coordinate {m}
    7.990000000000,  !- Vertex 2 Z-coordinate {m}
    13.893796264487,  !- Vertex 3 X-coordinate {m}
    11.673834529015,  !- Vertex 3 Y-coordinate {m}
    7.990000000000,  !- Vertex 3 Z-coordinate {m}
    13.893796264487,  !- Vertex 4 X-coordinate {m}
    11.673834529015,  !- Vertex 4 Y-coordinate {m}
    12.580000000000;  !- Vertex 4 Z-coordinate {m}

  BuildingSurface:Detailed,
    4977E0,  !- Name
    Wall,  !- Surface Type
    EXT_WALL_IF_RL,  !- Construction Name
    B1_F1_KT,  !- Zone Name
    Outdoors,  !- Outside Boundary Condition
    ,  !- Outside Boundary Condition Object
    SunExposed,  !- Sun Exposure
    WindExposed,  !- Wind Exposure
    ,  !- TRNSYS 17 - additional surface data
    4,  !- Number of Vertices
    16.201612885775,  !- Vertex 1 X-coordinate {m}
    11.875742320874,  !- Vertex 1 Y-coordinate {m}
    12.580000000000,  !- Vertex 1 Z-coordinate {m}
    16.201612885775,  !- Vertex 2 X-coordinate {m}
    11.875742320874,  !- Vertex 2 Y-coordinate {m}
    7.990000000000,  !- Vertex 2 Z-coordinate {m}
    15.155743972804,  !- Vertex 3 X-coordinate {m}
    23.830078697975,  !- Vertex 3 Y-coordinate {m}
    7.990000000000,  !- Vertex 3 Z-coordinate {m}
    15.155743972804,  !- Vertex 4 X-coordinate {m}
    23.830078697975,  !- Vertex 4 Y-coordinate {m}
    12.580000000000;  !- Vertex 4 Z-coordinate {m}

  Zone,
    B1_F1_CL,  !- Name
    0.0,  !- Direction of Relative North {deg}
    56.265,  !- X Origin {m}
    9.46,  !- Y Origin {m}
    7.99,  !- Z Origin {m}
    ,  !- Type
    1;  !- Multiplier

  BuildingSurface:Detailed,
    B99612,  !- Name
    Floor,  !- Surface Type
    ADJ_CEILING,  !- Construction Name
    B1_F1_CL,  !- Zone Name
    Zone,  !- Outside Boundary Condition
    B1_F0_OF,  !- Outside Boundary Condition Object
    NoSun,  !- Sun Exposure
    NoWind,  !- Wind Exposure
    ,  !- TRNSYS 17 - additional surface data
    4,  !- Number of Vertices
    12.707103380308,  !- Vertex 1 X-coordinate {m}
    51.818168740863,  !- Vertex 1 Y-coordinate {m}
    7.990000000000,  !- Vertex 1 Z-coordinate {m}
    15.155743972804,  !- Vertex 2 X-coordinate {m}
    23.830078697975,  !- Vertex 2 Y-coordinate {m}
    7.990000000000,  !- Vertex 2 Z-coordinate {m}
    6.518735940348,  !- Vertex 3 X-coordinate {m}
    23.074438408353,  !- Vertex 3 Y-coordinate {m}
    7.990000000000,  !- Vertex 3 Z-coordinate {m}
    4.070095347853,  !- Vertex 4 X-coordinate {m}
    51.062528451241,  !- Vertex 4 Y-coordinate {m}
    7.990000000000;  !- Vertex 4 Z-coordinate {m}

  BuildingSurface:Detailed,
    E0BB02,  !- Name
    Wall,  !- Surface Type
    EXT_WALL_IF_RL,  !- Construction Name
    B1_F1_CL,  !- Zone Name
    Outdoors,  !- Outside Boundary Condition
    ,  !- Outside Boundary Condition Object
    SunExposed,  !- Sun Exposure
    WindExposed,  !- Wind Exposure
    ,  !- TRNSYS 17 - additional surface data
    4,  !- Number of Vertices
    15.155743972804,  !- Vertex 1 X-coordinate {m}
    23.830078697975,  !- Vertex 1 Y-coordinate {m}
    12.580000000000,  !- Vertex 1 Z-coordinate {m}
    15.155743972804,  !- Vertex 2 X-coordinate {m}
    23.830078697975,  !- Vertex 2 Y-coordinate {m}
    7.990000000000,  !- Vertex 2 Z-coordinate {m}
    12.707103380308,  !- Vertex 3 X-coordinate {m}
    51.818168740863,  !- Vertex 3 Y-coordinate {m}
    7.990000000000,  !- Vertex 3 Z-coordinate {m}
    12.707103380308,  !- Vertex 4 X-coordinate {m}
    51.818168740863,  !- Vertex 4 Y-coordinate {m}
    12.580000000000;  !- Vertex 4 Z-coordinate {m}

  BuildingSurface:Detailed,
    F41E3B,  !- Name
    Ceiling,  !- Surface Type
    ADJ_CEILING,  !- Construction Name
    B1_F1_CL,  !- Zone Name
    Zone,  !- Outside Boundary Condition
    B1_F2_CL,  !- Outside Boundary Condition Object
    NoSun,  !- Sun Exposure
    NoWind,  !- Wind Exposure
    ,  !- TRNSYS 17 - additional surface data
    4,  !- Number of Vertices
    4.070095347853,  !- Vertex 1 X-coordinate {m}
    51.062528451241,  !- Vertex 1 Y-coordinate {m}
    12.580000000000,  !- Vertex 1 Z-coordinate {m}
    6.518735940348,  !- Vertex 2 X-coordinate {m}
    23.074438408353,  !- Vertex 2 Y-coordinate {m}
    12.580000000000,  !- Vertex 2 Z-coordinate {m}
    15.155743972804,  !- Vertex 3 X-coordinate {m}
    23.830078697975,  !- Vertex 3 Y-coordinate {m}
    12.580000000000,  !- Vertex 3 Z-coordinate {m}
    12.707103380308,  !- Vertex 4 X-coordinate {m}
    51.818168740863,  !- Vertex 4 Y-coordinate {m}
    12.580000000000;  !- Vertex 4 Z-coordinate {m}

  BuildingSurface:Detailed,
    55FAA5,  !- Name
    Wall,  !- Surface Type
    ADJ_WALL,  !- Construction Name
    B1_F1_CL,  !- Zone Name
    Zone,  !- Outside Boundary Condition
    B1_F1_KT,  !- Outside Boundary Condition Object
    NoSun,  !- Sun Exposure
    NoWind,  !- Wind Exposure
    ,  !- TRNSYS 17 - additional surface data
    4,  !- Number of Vertices
    6.518735940348,  !- Vertex 1 X-coordinate {m}
    23.074438408353,  !- Vertex 1 Y-coordinate {m}
    12.580000000000,  !- Vertex 1 Z-coordinate {m}
    6.518735940348,  !- Vertex 2 X-coordinate {m}
    23.074438408353,  !- Vertex 2 Y-coordinate {m}
    7.990000000000,  !- Vertex 2 Z-coordinate {m}
    15.155743972804,  !- Vertex 3 X-coordinate {m}
    23.830078697975,  !- Vertex 3 Y-coordinate {m}
    7.990000000000,  !- Vertex 3 Z-coordinate {m}
    15.155743972804,  !- Vertex 4 X-coordinate {m}
    23.830078697975,  !- Vertex 4 Y-coordinate {m}
    12.580000000000;  !- Vertex 4 Z-coordinate {m}

  BuildingSurface:Detailed,
    32B9BE,  !- Name
    Wall,  !- Surface Type
    ADJ_WALL,  !- Construction Name
    B1_F1_CL,  !- Zone Name
    Zone,  !- Outside Boundary Condition
    B1_F1_CN,  !- Outside Boundary Condition Object
    NoSun,  !- Sun Exposure
    NoWind,  !- Wind Exposure
    ,  !- TRNSYS 17 - additional surface data
    4,  !- Number of Vertices
    4.070095347853,  !- Vertex 1 X-coordinate {m}
    51.062528451241,  !- Vertex 1 Y-coordinate {m}
    12.580000000000,  !- Vertex 1 Z-coordinate {m}
    4.070095347853,  !- Vertex 2 X-coordinate {m}
    51.062528451241,  !- Vertex 2 Y-coordinate {m}
    7.990000000000,  !- Vertex 2 Z-coordinate {m}
    6.518735940348,  !- Vertex 3 X-coordinate {m}
    23.074438408353,  !- Vertex 3 Y-coordinate {m}
    7.990000000000,  !- Vertex 3 Z-coordinate {m}
    6.518735940348,  !- Vertex 4 X-coordinate {m}
    23.074438408353,  !- Vertex 4 Y-coordinate {m}
    12.580000000000;  !- Vertex 4 Z-coordinate {m}

  BuildingSurface:Detailed,
    35ABBF,  !- Name
    Wall,  !- Surface Type
    ADJ_WALL,  !- Construction Name
    B1_F1_CL,  !- Zone Name
    Zone,  !- Outside Boundary Condition
    B2_F1_SC,  !- Outside Boundary Condition Object
    NoSun,  !- Sun Exposure
    NoWind,  !- Wind Exposure
    ,  !- TRNSYS 17 - additional surface data
    4,  !- Number of Vertices
    12.707103380308,  !- Vertex 1 X-coordinate {m}
    51.818168740863,  !- Vertex 1 Y-coordinate {m}
    12.580000000000,  !- Vertex 1 Z-coordinate {m}
    12.707103380308,  !- Vertex 2 X-coordinate {m}
    51.818168740863,  !- Vertex 2 Y-coordinate {m}
    7.990000000000,  !- Vertex 2 Z-coordinate {m}
    4.070095347853,  !- Vertex 3 X-coordinate {m}
    51.062528451241,  !- Vertex 3 Y-coordinate {m}
    7.990000000000,  !- Vertex 3 Z-coordinate {m}
    4.070095347853,  !- Vertex 4 X-coordinate {m}
    51.062528451241,  !- Vertex 4 Y-coordinate {m}
    12.580000000000;  !- Vertex 4 Z-coordinate {m}

  Zone,
    B1_F1_CN,  !- Name
    0.0,  !- Direction of Relative North {deg}
    56.265,  !- X Origin {m}
    0.955,  !- Y Origin {m}
    7.99,  !- Z Origin {m}
    ,  !- Type
    1;  !- Multiplier

  BuildingSurface:Detailed,
    A844AF,  !- Name
    Floor,  !- Surface Type
    ADJ_CEILING,  !- Construction Name
    B1_F1_CN,  !- Zone Name
    Zone,  !- Outside Boundary Condition
    B1_F0_OF,  !- Outside Boundary Condition Object
    NoSun,  !- Sun Exposure
    NoWind,  !- Wind Exposure
    ,  !- TRNSYS 17 - additional surface data
    4,  !- Number of Vertices
    4.070095347853,  !- Vertex 1 X-coordinate {m}
    51.062528451241,  !- Vertex 1 Y-coordinate {m}
    7.990000000000,  !- Vertex 1 Z-coordinate {m}
    7.564604853320,  !- Vertex 2 X-coordinate {m}
    11.120102031252,  !- Vertex 2 Y-coordinate {m}
    7.990000000000,  !- Vertex 2 Z-coordinate {m}
    -0.908031053950,  !- Vertex 3 X-coordinate {m}
    10.378842439183,  !- Vertex 3 Y-coordinate {m}
    7.990000000000,  !- Vertex 3 Z-coordinate {m}
    -4.402540559418,  !- Vertex 4 X-coordinate {m}
    50.321268859172,  !- Vertex 4 Y-coordinate {m}
    7.990000000000;  !- Vertex 4 Z-coordinate {m}

  BuildingSurface:Detailed,
    3438A6,  !- Name
    Wall,  !- Surface Type
    ADJ_WALL,  !- Construction Name
    B1_F1_CN,  !- Zone Name
    Zone,  !- Outside Boundary Condition
    B1_F0_SC,  !- Outside Boundary Condition Object
    NoSun,  !- Sun Exposure
    NoWind,  !- Wind Exposure
    ,  !- TRNSYS 17 - additional surface data
    4,  !- Number of Vertices
    -0.908031053950,  !- Vertex 1 X-coordinate {m}
    10.378842439183,  !- Vertex 1 Y-coordinate {m}
    12.580000000000,  !- Vertex 1 Z-coordinate {m}
    -0.908031053950,  !- Vertex 2 X-coordinate {m}
    10.378842439183,  !- Vertex 2 Y-coordinate {m}
    7.990000000000,  !- Vertex 2 Z-coordinate {m}
    7.564604853320,  !- Vertex 3 X-coordinate {m}
    11.120102031252,  !- Vertex 3 Y-coordinate {m}
    7.990000000000,  !- Vertex 3 Z-coordinate {m}
    7.564604853320,  !- Vertex 4 X-coordinate {m}
    11.120102031252,  !- Vertex 4 Y-coordinate {m}
    12.580000000000;  !- Vertex 4 Z-coordinate {m}

  BuildingSurface:Detailed,
    D87E19,  !- Name
    Ceiling,  !- Surface Type
    ADJ_CEILING,  !- Construction Name
    B1_F1_CN,  !- Zone Name
    Zone,  !- Outside Boundary Condition
    B1_F2_CL,  !- Outside Boundary Condition Object
    NoSun,  !- Sun Exposure
    NoWind,  !- Wind Exposure
    ,  !- TRNSYS 17 - additional surface data
    4,  !- Number of Vertices
    -4.402540559418,  !- Vertex 1 X-coordinate {m}
    50.321268859172,  !- Vertex 1 Y-coordinate {m}
    12.580000000000,  !- Vertex 1 Z-coordinate {m}
    -0.908031053950,  !- Vertex 2 X-coordinate {m}
    10.378842439183,  !- Vertex 2 Y-coordinate {m}
    12.580000000000,  !- Vertex 2 Z-coordinate {m}
    7.564604853320,  !- Vertex 3 X-coordinate {m}
    11.120102031252,  !- Vertex 3 Y-coordinate {m}
    12.580000000000,  !- Vertex 3 Z-coordinate {m}
    4.070095347853,  !- Vertex 4 X-coordinate {m}
    51.062528451241,  !- Vertex 4 Y-coordinate {m}
    12.580000000000;  !- Vertex 4 Z-coordinate {m}

  BuildingSurface:Detailed,
    3604FB,  !- Name
    Wall,  !- Surface Type
    EXT_WALL_SW_EF_RL,  !- Construction Name
    B1_F1_CN,  !- Zone Name
    Outdoors,  !- Outside Boundary Condition
    ,  !- Outside Boundary Condition Object
    SunExposed,  !- Sun Exposure
    WindExposed,  !- Wind Exposure
    ,  !- TRNSYS 17 - additional surface data
    4,  !- Number of Vertices
    -4.402540559418,  !- Vertex 1 X-coordinate {m}
    50.321268859172,  !- Vertex 1 Y-coordinate {m}
    12.580000000000,  !- Vertex 1 Z-coordinate {m}
    -4.402540559418,  !- Vertex 2 X-coordinate {m}
    50.321268859172,  !- Vertex 2 Y-coordinate {m}
    7.990000000000,  !- Vertex 2 Z-coordinate {m}
    -3.888321677206,  !- Vertex 3 X-coordinate {m}
    44.443720140431,  !- Vertex 3 Y-coordinate {m}
    7.990000000000,  !- Vertex 3 Z-coordinate {m}
    -3.888321677206,  !- Vertex 4 X-coordinate {m}
    44.443720140431,  !- Vertex 4 Y-coordinate {m}
    12.580000000000;  !- Vertex 4 Z-coordinate {m}

  BuildingSurface:Detailed,
    C37EE7,  !- Name
    Wall,  !- Surface Type
    ADJ_WALL,  !- Construction Name
    B1_F1_CN,  !- Zone Name
    Zone,  !- Outside Boundary Condition
    B1_F1_KT,  !- Outside Boundary Condition Object
    NoSun,  !- Sun Exposure
    NoWind,  !- Wind Exposure
    ,  !- TRNSYS 17 - additional surface data
    4,  !- Number of Vertices
    7.564604853320,  !- Vertex 1 X-coordinate {m}
    11.120102031252,  !- Vertex 1 Y-coordinate {m}
    12.580000000000,  !- Vertex 1 Z-coordinate {m}
    7.564604853320,  !- Vertex 2 X-coordinate {m}
    11.120102031252,  !- Vertex 2 Y-coordinate {m}
    7.990000000000,  !- Vertex 2 Z-coordinate {m}
    6.518735940348,  !- Vertex 3 X-coordinate {m}
    23.074438408353,  !- Vertex 3 Y-coordinate {m}
    7.990000000000,  !- Vertex 3 Z-coordinate {m}
    6.518735940348,  !- Vertex 4 X-coordinate {m}
    23.074438408353,  !- Vertex 4 Y-coordinate {m}
    12.580000000000;  !- Vertex 4 Z-coordinate {m}

  BuildingSurface:Detailed,
    231A9F,  !- Name
    Wall,  !- Surface Type
    ADJ_WALL,  !- Construction Name
    B1_F1_CN,  !- Zone Name
    Zone,  !- Outside Boundary Condition
    B2_F1_OF,  !- Outside Boundary Condition Object
    NoSun,  !- Sun Exposure
    NoWind,  !- Wind Exposure
    ,  !- TRNSYS 17 - additional surface data
    4,  !- Number of Vertices
    4.070095347853,  !- Vertex 1 X-coordinate {m}
    51.062528451241,  !- Vertex 1 Y-coordinate {m}
    12.580000000000,  !- Vertex 1 Z-coordinate {m}
    4.070095347853,  !- Vertex 2 X-coordinate {m}
    51.062528451241,  !- Vertex 2 Y-coordinate {m}
    7.990000000000,  !- Vertex 2 Z-coordinate {m}
    -4.402540559418,  !- Vertex 3 X-coordinate {m}
    50.321268859172,  !- Vertex 3 Y-coordinate {m}
    7.990000000000,  !- Vertex 3 Z-coordinate {m}
    -4.402540559418,  !- Vertex 4 X-coordinate {m}
    50.321268859172,  !- Vertex 4 Y-coordinate {m}
    12.580000000000;  !- Vertex 4 Z-coordinate {m}

  BuildingSurface:Detailed,
    AAAA20,  !- Name
    Wall,  !- Surface Type
    ADJ_WALL,  !- Construction Name
    B1_F1_CN,  !- Zone Name
    Zone,  !- Outside Boundary Condition
    B1_F1_CL,  !- Outside Boundary Condition Object
    NoSun,  !- Sun Exposure
    NoWind,  !- Wind Exposure
    ,  !- TRNSYS 17 - additional surface data
    4,  !- Number of Vertices
    6.518735940348,  !- Vertex 1 X-coordinate {m}
    23.074438408353,  !- Vertex 1 Y-coordinate {m}
    12.580000000000,  !- Vertex 1 Z-coordinate {m}
    6.518735940348,  !- Vertex 2 X-coordinate {m}
    23.074438408353,  !- Vertex 2 Y-coordinate {m}
    7.990000000000,  !- Vertex 2 Z-coordinate {m}
    4.070095347853,  !- Vertex 3 X-coordinate {m}
    51.062528451241,  !- Vertex 3 Y-coordinate {m}
    7.990000000000,  !- Vertex 3 Z-coordinate {m}
    4.070095347853,  !- Vertex 4 X-coordinate {m}
    51.062528451241,  !- Vertex 4 Y-coordinate {m}
    12.580000000000;  !- Vertex 4 Z-coordinate {m}

  Zone,
    B2_F2_SC,  !- Name
    0.0,  !- Direction of Relative North {deg}
    43.86,  !- X Origin {m}
    9.46,  !- Y Origin {m}
    12.58,  !- Z Origin {m}
    ,  !- Type
    1;  !- Multiplier

  BuildingSurface:Detailed,
    17EB69,  !- Name
    Floor,  !- Surface Type
    ADJ_CEILING,  !- Construction Name
    B2_F2_SC,  !- Zone Name
    Zone,  !- Outside Boundary Condition
    B2_F1_SC,  !- Outside Boundary Condition Object
    NoSun,  !- Sun Exposure
    NoWind,  !- Wind Exposure
    ,  !- TRNSYS 17 - additional surface data
    4,  !- Number of Vertices
    12.582233580160,  !- Vertex 1 X-coordinate {m}
    64.259629133658,  !- Vertex 1 Y-coordinate {m}
    12.580000000000,  !- Vertex 1 Z-coordinate {m}
    13.663400568944,  !- Vertex 2 X-coordinate {m}
    51.901833903830,  !- Vertex 2 Y-coordinate {m}
    12.580000000000,  !- Vertex 2 Z-coordinate {m}
    4.070095347853,  !- Vertex 3 X-coordinate {m}
    51.062528451241,  !- Vertex 3 Y-coordinate {m}
    12.580000000000,  !- Vertex 3 Z-coordinate {m}
    2.988928359068,  !- Vertex 4 X-coordinate {m}
    63.420323681069,  !- Vertex 4 Y-coordinate {m}
    12.580000000000;  !- Vertex 4 Z-coordinate {m}

  BuildingSurface:Detailed,
    320018,  !- Name
    Wall,  !- Surface Type
    ADJ_WALL,  !- Construction Name
    B2_F2_SC,  !- Zone Name
    Zone,  !- Outside Boundary Condition
    B1_F2_CL,  !- Outside Boundary Condition Object
    NoSun,  !- Sun Exposure
    NoWind,  !- Wind Exposure
    ,  !- TRNSYS 17 - additional surface data
    4,  !- Number of Vertices
    4.070095347853,  !- Vertex 1 X-coordinate {m}
    51.062528451241,  !- Vertex 1 Y-coordinate {m}
    17.170000000000,  !- Vertex 1 Z-coordinate {m}
    4.070095347853,  !- Vertex 2 X-coordinate {m}
    51.062528451241,  !- Vertex 2 Y-coordinate {m}
    12.580000000000,  !- Vertex 2 Z-coordinate {m}
    12.707103380308,  !- Vertex 3 X-coordinate {m}
    51.818168740863,  !- Vertex 3 Y-coordinate {m}
    12.580000000000,  !- Vertex 3 Z-coordinate {m}
    12.707103380308,  !- Vertex 4 X-coordinate {m}
    51.818168740863,  !- Vertex 4 Y-coordinate {m}
    17.170000000000;  !- Vertex 4 Z-coordinate {m}

  BuildingSurface:Detailed,
    EB93F2,  !- Name
    Ceiling,  !- Surface Type
    ADJ_CEILING,  !- Construction Name
    B2_F2_SC,  !- Zone Name
    Zone,  !- Outside Boundary Condition
    B2_F3_SC,  !- Outside Boundary Condition Object
    NoSun,  !- Sun Exposure
    NoWind,  !- Wind Exposure
    ,  !- TRNSYS 17 - additional surface data
    4,  !- Number of Vertices
    2.988928359068,  !- Vertex 1 X-coordinate {m}
    63.420323681069,  !- Vertex 1 Y-coordinate {m}
    17.170000000000,  !- Vertex 1 Z-coordinate {m}
    4.070095347853,  !- Vertex 2 X-coordinate {m}
    51.062528451241,  !- Vertex 2 Y-coordinate {m}
    17.170000000000,  !- Vertex 2 Z-coordinate {m}
    13.663400568944,  !- Vertex 3 X-coordinate {m}
    51.901833903830,  !- Vertex 3 Y-coordinate {m}
    17.170000000000,  !- Vertex 3 Z-coordinate {m}
    12.582233580160,  !- Vertex 4 X-coordinate {m}
    64.259629133658,  !- Vertex 4 Y-coordinate {m}
    17.170000000000;  !- Vertex 4 Z-coordinate {m}

  BuildingSurface:Detailed,
    68AEB4,  !- Name
    Wall,  !- Surface Type
    EXT_WALL_IF_RL,  !- Construction Name
    B2_F2_SC,  !- Zone Name
    Outdoors,  !- Outside Boundary Condition
    ,  !- Outside Boundary Condition Object
    SunExposed,  !- Sun Exposure
    WindExposed,  !- Wind Exposure
    ,  !- TRNSYS 17 - additional surface data
    4,  !- Number of Vertices
    12.707103380308,  !- Vertex 1 X-coordinate {m}
    51.818168740863,  !- Vertex 1 Y-coordinate {m}
    17.170000000000,  !- Vertex 1 Z-coordinate {m}
    12.707103380308,  !- Vertex 2 X-coordinate {m}
    51.818168740863,  !- Vertex 2 Y-coordinate {m}
    12.580000000000,  !- Vertex 2 Z-coordinate {m}
    13.663400568944,  !- Vertex 3 X-coordinate {m}
    51.901833903830,  !- Vertex 3 Y-coordinate {m}
    12.580000000000,  !- Vertex 3 Z-coordinate {m}
    13.663400568944,  !- Vertex 4 X-coordinate {m}
    51.901833903830,  !- Vertex 4 Y-coordinate {m}
    17.170000000000;  !- Vertex 4 Z-coordinate {m}

  BuildingSurface:Detailed,
    20A48A,  !- Name
    Wall,  !- Surface Type
    ADJ_WALL,  !- Construction Name
    B2_F2_SC,  !- Zone Name
    Zone,  !- Outside Boundary Condition
    B2_F2_CL,  !- Outside Boundary Condition Object
    NoSun,  !- Sun Exposure
    NoWind,  !- Wind Exposure
    ,  !- TRNSYS 17 - additional surface data
    4,  !- Number of Vertices
    2.988928359068,  !- Vertex 1 X-coordinate {m}
    63.420323681069,  !- Vertex 1 Y-coordinate {m}
    17.170000000000,  !- Vertex 1 Z-coordinate {m}
    2.988928359068,  !- Vertex 2 X-coordinate {m}
    63.420323681069,  !- Vertex 2 Y-coordinate {m}
    12.580000000000,  !- Vertex 2 Z-coordinate {m}
    4.070095347853,  !- Vertex 3 X-coordinate {m}
    51.062528451241,  !- Vertex 3 Y-coordinate {m}
    12.580000000000,  !- Vertex 3 Z-coordinate {m}
    4.070095347853,  !- Vertex 4 X-coordinate {m}
    51.062528451241,  !- Vertex 4 Y-coordinate {m}
    17.170000000000;  !- Vertex 4 Z-coordinate {m}

  BuildingSurface:Detailed,
    611B27,  !- Name
    Wall,  !- Surface Type
    EXT_WALL_NE_EF_AL,  !- Construction Name
    B2_F2_SC,  !- Zone Name
    Outdoors,  !- Outside Boundary Condition
    ,  !- Outside Boundary Condition Object
    SunExposed,  !- Sun Exposure
    WindExposed,  !- Wind Exposure
    ,  !- TRNSYS 17 - additional surface data
    4,  !- Number of Vertices
    12.582233580160,  !- Vertex 1 X-coordinate {m}
    64.259629133658,  !- Vertex 1 Y-coordinate {m}
    17.170000000000,  !- Vertex 1 Z-coordinate {m}
    12.582233580160,  !- Vertex 2 X-coordinate {m}
    64.259629133658,  !- Vertex 2 Y-coordinate {m}
    12.580000000000,  !- Vertex 2 Z-coordinate {m}
    2.988928359068,  !- Vertex 3 X-coordinate {m}
    63.420323681069,  !- Vertex 3 Y-coordinate {m}
    12.580000000000,  !- Vertex 3 Z-coordinate {m}
    2.988928359068,  !- Vertex 4 X-coordinate {m}
    63.420323681069,  !- Vertex 4 Y-coordinate {m}
    17.170000000000;  !- Vertex 4 Z-coordinate {m}

  BuildingSurface:Detailed,
    D3C8F7,  !- Name
    Wall,  !- Surface Type
    ADJ_WALL,  !- Construction Name
    B2_F2_SC,  !- Zone Name
    OtherSideCoefficients,  !- Outside Boundary Condition
    BOUNDARY=IDENTICAL,  !- Outside Boundary Condition Object
    NoSun,  !- Sun Exposure
    NoWind,  !- Wind Exposure
    0.0,  !- TRNSYS 17 - additional surface data
    4,  !- Number of Vertices
    13.663400568944,  !- Vertex 1 X-coordinate {m}
    51.901833903830,  !- Vertex 1 Y-coordinate {m}
    17.170000000000,  !- Vertex 1 Z-coordinate {m}
    13.663400568944,  !- Vertex 2 X-coordinate {m}
    51.901833903830,  !- Vertex 2 Y-coordinate {m}
    12.580000000000,  !- Vertex 2 Z-coordinate {m}
    12.582233580160,  !- Vertex 3 X-coordinate {m}
    64.259629133658,  !- Vertex 3 Y-coordinate {m}
    12.580000000000,  !- Vertex 3 Z-coordinate {m}
    12.582233580160,  !- Vertex 4 X-coordinate {m}
    64.259629133658,  !- Vertex 4 Y-coordinate {m}
    17.170000000000;  !- Vertex 4 Z-coordinate {m}

  Zone,
    B2_F2_CL,  !- Name
    0.0,  !- Direction of Relative North {deg}
    39.326026,  !- X Origin {m}
    0.0,  !- Y Origin {m}
    12.58,  !- Z Origin {m}
    ,  !- Type
    1;  !- Multiplier

  BuildingSurface:Detailed,
    495408,  !- Name
    Floor,  !- Surface Type
    ADJ_CEILING,  !- Construction Name
    B2_F2_CL,  !- Zone Name
    Zone,  !- Outside Boundary Condition
    B2_F1_OF,  !- Outside Boundary Condition Object
    NoSun,  !- Sun Exposure
    NoWind,  !- Wind Exposure
    ,  !- TRNSYS 17 - additional surface data
    4,  !- Number of Vertices
    2.593766487499,  !- Vertex 1 X-coordinate {m}
    67.937044541155,  !- Vertex 1 Y-coordinate {m}
    12.580000000000,  !- Vertex 1 Z-coordinate {m}
    4.070095347853,  !- Vertex 2 X-coordinate {m}
    51.062528451241,  !- Vertex 2 Y-coordinate {m}
    12.580000000000,  !- Vertex 2 Z-coordinate {m}
    -5.353906496095,  !- Vertex 3 X-coordinate {m}
    50.238035124848,  !- Vertex 3 Y-coordinate {m}
    12.580000000000,  !- Vertex 3 Z-coordinate {m}
    -6.830235356449,  !- Vertex 4 X-coordinate {m}
    67.112551214762,  !- Vertex 4 Y-coordinate {m}
    12.580000000000;  !- Vertex 4 Z-coordinate {m}

  BuildingSurface:Detailed,
    BB3B32,  !- Name
    Wall,  !- Surface Type
    ADJ_WALL,  !- Construction Name
    B2_F2_CL,  !- Zone Name
    Zone,  !- Outside Boundary Condition
    B2_F2_SC,  !- Outside Boundary Condition Object
    NoSun,  !- Sun Exposure
    NoWind,  !- Wind Exposure
    ,  !- TRNSYS 17 - additional surface data
    4,  !- Number of Vertices
    4.070095347853,  !- Vertex 1 X-coordinate {m}
    51.062528451241,  !- Vertex 1 Y-coordinate {m}
    17.170000000000,  !- Vertex 1 Z-coordinate {m}
    4.070095347853,  !- Vertex 2 X-coordinate {m}
    51.062528451241,  !- Vertex 2 Y-coordinate {m}
    12.580000000000,  !- Vertex 2 Z-coordinate {m}
    2.988928359068,  !- Vertex 3 X-coordinate {m}
    63.420323681069,  !- Vertex 3 Y-coordinate {m}
    12.580000000000,  !- Vertex 3 Z-coordinate {m}
    2.988928359068,  !- Vertex 4 X-coordinate {m}
    63.420323681069,  !- Vertex 4 Y-coordinate {m}
    17.170000000000;  !- Vertex 4 Z-coordinate {m}

  BuildingSurface:Detailed,
    A8F124,  !- Name
    Ceiling,  !- Surface Type
    ADJ_CEILING,  !- Construction Name
    B2_F2_CL,  !- Zone Name
    Zone,  !- Outside Boundary Condition
    B2_F3_LB,  !- Outside Boundary Condition Object
    NoSun,  !- Sun Exposure
    NoWind,  !- Wind Exposure
    ,  !- TRNSYS 17 - additional surface data
    4,  !- Number of Vertices
    -6.830235356449,  !- Vertex 1 X-coordinate {m}
    67.112551214762,  !- Vertex 1 Y-coordinate {m}
    17.170000000000,  !- Vertex 1 Z-coordinate {m}
    -5.353906496095,  !- Vertex 2 X-coordinate {m}
    50.238035124848,  !- Vertex 2 Y-coordinate {m}
    17.170000000000,  !- Vertex 2 Z-coordinate {m}
    4.070095347853,  !- Vertex 3 X-coordinate {m}
    51.062528451241,  !- Vertex 3 Y-coordinate {m}
    17.170000000000,  !- Vertex 3 Z-coordinate {m}
    2.593766487499,  !- Vertex 4 X-coordinate {m}
    67.937044541155,  !- Vertex 4 Y-coordinate {m}
    17.170000000000;  !- Vertex 4 Z-coordinate {m}

  BuildingSurface:Detailed,
    262966,  !- Name
    Wall,  !- Surface Type
    EXT_WALL_SW_EF_RL,  !- Construction Name
    B2_F2_CL,  !- Zone Name
    Outdoors,  !- Outside Boundary Condition
    ,  !- Outside Boundary Condition Object
    SunExposed,  !- Sun Exposure
    WindExposed,  !- Wind Exposure
    ,  !- TRNSYS 17 - additional surface data
    4,  !- Number of Vertices
    -6.830235356449,  !- Vertex 1 X-coordinate {m}
    67.112551214762,  !- Vertex 1 Y-coordinate {m}
    17.170000000000,  !- Vertex 1 Z-coordinate {m}
    -6.830235356449,  !- Vertex 2 X-coordinate {m}
    67.112551214762,  !- Vertex 2 Y-coordinate {m}
    12.580000000000,  !- Vertex 2 Z-coordinate {m}
    -6.660281627363,  !- Vertex 3 X-coordinate {m}
    65.169971202261,  !- Vertex 3 Y-coordinate {m}
    12.580000000000,  !- Vertex 3 Z-coordinate {m}
    -6.660281627363,  !- Vertex 4 X-coordinate {m}
    65.169971202261,  !- Vertex 4 Y-coordinate {m}
    17.170000000000;  !- Vertex 4 Z-coordinate {m}

  BuildingSurface:Detailed,
    64F9A2,  !- Name
    Wall,  !- Surface Type
    ADJ_WALL,  !- Construction Name
    B2_F2_CL,  !- Zone Name
    Zone,  !- Outside Boundary Condition
    B1_F2_CL,  !- Outside Boundary Condition Object
    NoSun,  !- Sun Exposure
    NoWind,  !- Wind Exposure
    ,  !- TRNSYS 17 - additional surface data
    4,  !- Number of Vertices
    -4.402540559418,  !- Vertex 1 X-coordinate {m}
    50.321268859172,  !- Vertex 1 Y-coordinate {m}
    17.170000000000,  !- Vertex 1 Z-coordinate {m}
    -4.402540559418,  !- Vertex 2 X-coordinate {m}
    50.321268859172,  !- Vertex 2 Y-coordinate {m}
    12.580000000000,  !- Vertex 2 Z-coordinate {m}
    4.070095347853,  !- Vertex 3 X-coordinate {m}
    51.062528451241,  !- Vertex 3 Y-coordinate {m}
    12.580000000000,  !- Vertex 3 Z-coordinate {m}
    4.070095347853,  !- Vertex 4 X-coordinate {m}
    51.062528451241,  !- Vertex 4 Y-coordinate {m}
    17.170000000000;  !- Vertex 4 Z-coordinate {m}

  BuildingSurface:Detailed,
    8F0FDF,  !- Name
    Wall,  !- Surface Type
    EXT_WALL_NE_EF_AL,  !- Construction Name
    B2_F2_CL,  !- Zone Name
    Outdoors,  !- Outside Boundary Condition
    ,  !- Outside Boundary Condition Object
    SunExposed,  !- Sun Exposure
    WindExposed,  !- Wind Exposure
    ,  !- TRNSYS 17 - additional surface data
    4,  !- Number of Vertices
    2.593766487499,  !- Vertex 1 X-coordinate {m}
    67.937044541155,  !- Vertex 1 Y-coordinate {m}
    17.170000000000,  !- Vertex 1 Z-coordinate {m}
    2.593766487499,  !- Vertex 2 X-coordinate {m}
    67.937044541155,  !- Vertex 2 Y-coordinate {m}
    12.580000000000,  !- Vertex 2 Z-coordinate {m}
    -6.830235356449,  !- Vertex 3 X-coordinate {m}
    67.112551214762,  !- Vertex 3 Y-coordinate {m}
    12.580000000000,  !- Vertex 3 Z-coordinate {m}
    -6.830235356449,  !- Vertex 4 X-coordinate {m}
    67.112551214762,  !- Vertex 4 Y-coordinate {m}
    17.170000000000;  !- Vertex 4 Z-coordinate {m}

  BuildingSurface:Detailed,
    BDE2EC,  !- Name
    Wall,  !- Surface Type
    EXT_WALL_NE_EF_AL,  !- Construction Name
    B2_F2_CL,  !- Zone Name
    Outdoors,  !- Outside Boundary Condition
    ,  !- Outside Boundary Condition Object
    SunExposed,  !- Sun Exposure
    WindExposed,  !- Wind Exposure
    ,  !- TRNSYS 17 - additional surface data
    4,  !- Number of Vertices
    2.988928359068,  !- Vertex 1 X-coordinate {m}
    63.420323681069,  !- Vertex 1 Y-coordinate {m}
    17.170000000000,  !- Vertex 1 Z-coordinate {m}
    2.988928359068,  !- Vertex 2 X-coordinate {m}
    63.420323681069,  !- Vertex 2 Y-coordinate {m}
    12.580000000000,  !- Vertex 2 Z-coordinate {m}
    2.593766487499,  !- Vertex 3 X-coordinate {m}
    67.937044541155,  !- Vertex 3 Y-coordinate {m}
    12.580000000000,  !- Vertex 3 Z-coordinate {m}
    2.593766487499,  !- Vertex 4 X-coordinate {m}
    67.937044541155,  !- Vertex 4 Y-coordinate {m}
    17.170000000000;  !- Vertex 4 Z-coordinate {m}

  BuildingSurface:Detailed,
    59E4F9,  !- Name
    Wall,  !- Surface Type
    EXT_WALL_SW_EF_RL,  !- Construction Name
    B2_F2_CL,  !- Zone Name
    Outdoors,  !- Outside Boundary Condition
    ,  !- Outside Boundary Condition Object
    SunExposed,  !- Sun Exposure
    WindExposed,  !- Wind Exposure
    ,  !- TRNSYS 17 - additional surface data
    4,  !- Number of Vertices
    -5.353906496095,  !- Vertex 1 X-coordinate {m}
    50.238035124848,  !- Vertex 1 Y-coordinate {m}
    17.170000000000,  !- Vertex 1 Z-coordinate {m}
    -5.353906496095,  !- Vertex 2 X-coordinate {m}
    50.238035124848,  !- Vertex 2 Y-coordinate {m}
    12.580000000000,  !- Vertex 2 Z-coordinate {m}
    -4.402540559418,  !- Vertex 3 X-coordinate {m}
    50.321268859172,  !- Vertex 3 Y-coordinate {m}
    12.580000000000,  !- Vertex 3 Z-coordinate {m}
    -4.402540559418,  !- Vertex 4 X-coordinate {m}
    50.321268859172,  !- Vertex 4 Y-coordinate {m}
    17.170000000000;  !- Vertex 4 Z-coordinate {m}

  Zone,
    B1_F2_CL,  !- Name
    0.0,  !- Direction of Relative North {deg}
    56.265,  !- X Origin {m}
    0.955,  !- Y Origin {m}
    12.58,  !- Z Origin {m}
    ,  !- Type
    1;  !- Multiplier

  BuildingSurface:Detailed,
    B4CB7E,  !- Name
    Floor,  !- Surface Type
    ADJ_CEILING,  !- Construction Name
    B1_F2_CL,  !- Zone Name
    Zone,  !- Outside Boundary Condition
    B1_F1_CL,  !- Outside Boundary Condition Object
    NoSun,  !- Sun Exposure
    NoWind,  !- Wind Exposure
    ,  !- TRNSYS 17 - additional surface data
    4,  !- Number of Vertices
    12.707103380308,  !- Vertex 1 X-coordinate {m}
    51.818168740863,  !- Vertex 1 Y-coordinate {m}
    12.580000000000,  !- Vertex 1 Z-coordinate {m}
    15.155743972804,  !- Vertex 2 X-coordinate {m}
    23.830078697975,  !- Vertex 2 Y-coordinate {m}
    12.580000000000,  !- Vertex 2 Z-coordinate {m}
    6.518735940348,  !- Vertex 3 X-coordinate {m}
    23.074438408353,  !- Vertex 3 Y-coordinate {m}
    12.580000000000,  !- Vertex 3 Z-coordinate {m}
    4.070095347853,  !- Vertex 4 X-coordinate {m}
    51.062528451241,  !- Vertex 4 Y-coordinate {m}
    12.580000000000;  !- Vertex 4 Z-coordinate {m}

  BuildingSurface:Detailed,
    C6A3C2,  !- Name
    Ceiling,  !- Surface Type
    ADJ_CEILING,  !- Construction Name
    B1_F2_CL,  !- Zone Name
    Zone,  !- Outside Boundary Condition
    B1_F3_LB,  !- Outside Boundary Condition Object
    NoSun,  !- Sun Exposure
    NoWind,  !- Wind Exposure
    ,  !- TRNSYS 17 - additional surface data
    4,  !- Number of Vertices
    -4.402540559418,  !- Vertex 1 X-coordinate {m}
    50.321268859172,  !- Vertex 1 Y-coordinate {m}
    17.170000000000,  !- Vertex 1 Z-coordinate {m}
    -0.908031053950,  !- Vertex 2 X-coordinate {m}
    10.378842439183,  !- Vertex 2 Y-coordinate {m}
    17.170000000000,  !- Vertex 2 Z-coordinate {m}
    16.201612885775,  !- Vertex 3 X-coordinate {m}
    11.875742320874,  !- Vertex 3 Y-coordinate {m}
    17.170000000000,  !- Vertex 3 Z-coordinate {m}
    12.707103380308,  !- Vertex 4 X-coordinate {m}
    51.818168740863,  !- Vertex 4 Y-coordinate {m}
    17.170000000000;  !- Vertex 4 Z-coordinate {m}

  BuildingSurface:Detailed,
    766882,  !- Name
    Wall,  !- Surface Type
    EXT_WALL_SW_EF_RL,  !- Construction Name
    B1_F2_CL,  !- Zone Name
    Outdoors,  !- Outside Boundary Condition
    ,  !- Outside Boundary Condition Object
    SunExposed,  !- Sun Exposure
    WindExposed,  !- Wind Exposure
    ,  !- TRNSYS 17 - additional surface data
    4,  !- Number of Vertices
    -4.402540559418,  !- Vertex 1 X-coordinate {m}
    50.321268859172,  !- Vertex 1 Y-coordinate {m}
    17.170000000000,  !- Vertex 1 Z-coordinate {m}
    -4.402540559418,  !- Vertex 2 X-coordinate {m}
    50.321268859172,  !- Vertex 2 Y-coordinate {m}
    12.580000000000,  !- Vertex 2 Z-coordinate {m}
    -3.888321677206,  !- Vertex 3 X-coordinate {m}
    44.443720140431,  !- Vertex 3 Y-coordinate {m}
    12.580000000000,  !- Vertex 3 Z-coordinate {m}
    -3.888321677206,  !- Vertex 4 X-coordinate {m}
    44.443720140431,  !- Vertex 4 Y-coordinate {m}
    17.170000000000;  !- Vertex 4 Z-coordinate {m}

  BuildingSurface:Detailed,
    D942A5,  !- Name
    Wall,  !- Surface Type
    EXT_WALL_IF_RL,  !- Construction Name
    B1_F2_CL,  !- Zone Name
    Outdoors,  !- Outside Boundary Condition
    ,  !- Outside Boundary Condition Object
    SunExposed,  !- Sun Exposure
    WindExposed,  !- Wind Exposure
    ,  !- TRNSYS 17 - additional surface data
    4,  !- Number of Vertices
    13.893796264487,  !- Vertex 1 X-coordinate {m}
    11.673834529015,  !- Vertex 1 Y-coordinate {m}
    17.170000000000,  !- Vertex 1 Z-coordinate {m}
    13.893796264487,  !- Vertex 2 X-coordinate {m}
    11.673834529015,  !- Vertex 2 Y-coordinate {m}
    12.580000000000,  !- Vertex 2 Z-coordinate {m}
    16.201612885775,  !- Vertex 3 X-coordinate {m}
    11.875742320874,  !- Vertex 3 Y-coordinate {m}
    12.580000000000,  !- Vertex 3 Z-coordinate {m}
    16.201612885775,  !- Vertex 4 X-coordinate {m}
    11.875742320874,  !- Vertex 4 Y-coordinate {m}
    17.170000000000;  !- Vertex 4 Z-coordinate {m}

  BuildingSurface:Detailed,
    EC500A,  !- Name
    Wall,  !- Surface Type
    ADJ_WALL,  !- Construction Name
    B1_F2_CL,  !- Zone Name
    Zone,  !- Outside Boundary Condition
    B2_F2_CL,  !- Outside Boundary Condition Object
    NoSun,  !- Sun Exposure
    NoWind,  !- Wind Exposure
    ,  !- TRNSYS 17 - additional surface data
    4,  !- Number of Vertices
    4.070095347853,  !- Vertex 1 X-coordinate {m}
    51.062528451241,  !- Vertex 1 Y-coordinate {m}
    17.170000000000,  !- Vertex 1 Z-coordinate {m}
    4.070095347853,  !- Vertex 2 X-coordinate {m}
    51.062528451241,  !- Vertex 2 Y-coordinate {m}
    12.580000000000,  !- Vertex 2 Z-coordinate {m}
    -4.402540559418,  !- Vertex 3 X-coordinate {m}
    50.321268859172,  !- Vertex 3 Y-coordinate {m}
    12.580000000000,  !- Vertex 3 Z-coordinate {m}
    -4.402540559418,  !- Vertex 4 X-coordinate {m}
    50.321268859172,  !- Vertex 4 Y-coordinate {m}
    17.170000000000;  !- Vertex 4 Z-coordinate {m}

  BuildingSurface:Detailed,
    664829,  !- Name
    Wall,  !- Surface Type
    ADJ_WALL,  !- Construction Name
    B1_F2_CL,  !- Zone Name
    Zone,  !- Outside Boundary Condition
    B1_F2_SC,  !- Outside Boundary Condition Object
    NoSun,  !- Sun Exposure
    NoWind,  !- Wind Exposure
    ,  !- TRNSYS 17 - additional surface data
    4,  !- Number of Vertices
    -0.908031053950,  !- Vertex 1 X-coordinate {m}
    10.378842439183,  !- Vertex 1 Y-coordinate {m}
    17.170000000000,  !- Vertex 1 Z-coordinate {m}
    -0.908031053950,  !- Vertex 2 X-coordinate {m}
    10.378842439183,  !- Vertex 2 Y-coordinate {m}
    12.580000000000,  !- Vertex 2 Z-coordinate {m}
    13.893796264487,  !- Vertex 3 X-coordinate {m}
    11.673834529015,  !- Vertex 3 Y-coordinate {m}
    12.580000000000,  !- Vertex 3 Z-coordinate {m}
    13.893796264487,  !- Vertex 4 X-coordinate {m}
    11.673834529015,  !- Vertex 4 Y-coordinate {m}
    17.170000000000;  !- Vertex 4 Z-coordinate {m}

  BuildingSurface:Detailed,
    F1FBD4,  !- Name
    Wall,  !- Surface Type
    ADJ_WALL,  !- Construction Name
    B1_F2_CL,  !- Zone Name
    Zone,  !- Outside Boundary Condition
    B2_F2_SC,  !- Outside Boundary Condition Object
    NoSun,  !- Sun Exposure
    NoWind,  !- Wind Exposure
    ,  !- TRNSYS 17 - additional surface data
    4,  !- Number of Vertices
    12.707103380308,  !- Vertex 1 X-coordinate {m}
    51.818168740863,  !- Vertex 1 Y-coordinate {m}
    17.170000000000,  !- Vertex 1 Z-coordinate {m}
    12.707103380308,  !- Vertex 2 X-coordinate {m}
    51.818168740863,  !- Vertex 2 Y-coordinate {m}
    12.580000000000,  !- Vertex 2 Z-coordinate {m}
    4.070095347853,  !- Vertex 3 X-coordinate {m}
    51.062528451241,  !- Vertex 3 Y-coordinate {m}
    12.580000000000,  !- Vertex 3 Z-coordinate {m}
    4.070095347853,  !- Vertex 4 X-coordinate {m}
    51.062528451241,  !- Vertex 4 Y-coordinate {m}
    17.170000000000;  !- Vertex 4 Z-coordinate {m}

  BuildingSurface:Detailed,
    A867DC,  !- Name
    Wall,  !- Surface Type
    EXT_WALL_IF_RL,  !- Construction Name
    B1_F2_CL,  !- Zone Name
    Outdoors,  !- Outside Boundary Condition
    ,  !- Outside Boundary Condition Object
    SunExposed,  !- Sun Exposure
    WindExposed,  !- Wind Exposure
    ,  !- TRNSYS 17 - additional surface data
    4,  !- Number of Vertices
    16.201612885775,  !- Vertex 1 X-coordinate {m}
    11.875742320874,  !- Vertex 1 Y-coordinate {m}
    17.170000000000,  !- Vertex 1 Z-coordinate {m}
    16.201612885775,  !- Vertex 2 X-coordinate {m}
    11.875742320874,  !- Vertex 2 Y-coordinate {m}
    12.580000000000,  !- Vertex 2 Z-coordinate {m}
    12.707103380308,  !- Vertex 3 X-coordinate {m}
    51.818168740863,  !- Vertex 3 Y-coordinate {m}
    12.580000000000,  !- Vertex 3 Z-coordinate {m}
    12.707103380308,  !- Vertex 4 X-coordinate {m}
    51.818168740863,  !- Vertex 4 Y-coordinate {m}
    17.170000000000;  !- Vertex 4 Z-coordinate {m}

  BuildingSurface:Detailed,
    A1C97B,  !- Name
    Floor,  !- Surface Type
    ADJ_CEILING,  !- Construction Name
    B1_F2_CL,  !- Zone Name
    Zone,  !- Outside Boundary Condition
    B1_F1_CN,  !- Outside Boundary Condition Object
    NoSun,  !- Sun Exposure
    NoWind,  !- Wind Exposure
    ,  !- TRNSYS 17 - additional surface data
    4,  !- Number of Vertices
    4.070095347853,  !- Vertex 1 X-coordinate {m}
    51.062528451241,  !- Vertex 1 Y-coordinate {m}
    12.580000000000,  !- Vertex 1 Z-coordinate {m}
    7.564604853320,  !- Vertex 2 X-coordinate {m}
    11.120102031252,  !- Vertex 2 Y-coordinate {m}
    12.580000000000,  !- Vertex 2 Z-coordinate {m}
    -0.908031053950,  !- Vertex 3 X-coordinate {m}
    10.378842439183,  !- Vertex 3 Y-coordinate {m}
    12.580000000000,  !- Vertex 3 Z-coordinate {m}
    -4.402540559418,  !- Vertex 4 X-coordinate {m}
    50.321268859172,  !- Vertex 4 Y-coordinate {m}
    12.580000000000;  !- Vertex 4 Z-coordinate {m}

  BuildingSurface:Detailed,
    E5B160,  !- Name
    Floor,  !- Surface Type
    ADJ_CEILING,  !- Construction Name
    B1_F2_CL,  !- Zone Name
    Zone,  !- Outside Boundary Condition
    B1_F1_KT,  !- Outside Boundary Condition Object
    NoSun,  !- Sun Exposure
    NoWind,  !- Wind Exposure
    ,  !- TRNSYS 17 - additional surface data
    4,  !- Number of Vertices
    15.155743972804,  !- Vertex 1 X-coordinate {m}
    23.830078697975,  !- Vertex 1 Y-coordinate {m}
    12.580000000000,  !- Vertex 1 Z-coordinate {m}
    16.201612885775,  !- Vertex 2 X-coordinate {m}
    11.875742320874,  !- Vertex 2 Y-coordinate {m}
    12.580000000000,  !- Vertex 2 Z-coordinate {m}
    7.564604853320,  !- Vertex 3 X-coordinate {m}
    11.120102031252,  !- Vertex 3 Y-coordinate {m}
    12.580000000000,  !- Vertex 3 Z-coordinate {m}
    6.518735940348,  !- Vertex 4 X-coordinate {m}
    23.074438408353,  !- Vertex 4 Y-coordinate {m}
    12.580000000000;  !- Vertex 4 Z-coordinate {m}

  Zone,
    B1_F2_SC,  !- Name
    0.0,  !- Direction of Relative North {deg}
    96.36,  !- X Origin {m}
    0.955,  !- Y Origin {m}
    12.58,  !- Z Origin {m}
    ,  !- Type
    1;  !- Multiplier

  BuildingSurface:Detailed,
    8D1A7D,  !- Name
    Floor,  !- Surface Type
    ADJ_CEILING,  !- Construction Name
    B1_F2_SC,  !- Zone Name
    Zone,  !- Outside Boundary Condition
    B1_F0_SC,  !- Outside Boundary Condition Object
    NoSun,  !- Sun Exposure
    NoWind,  !- Wind Exposure
    ,  !- TRNSYS 17 - additional surface data
    4,  !- Number of Vertices
    13.893796264487,  !- Vertex 1 X-coordinate {m}
    11.673834529015,  !- Vertex 1 Y-coordinate {m}
    12.580000000000,  !- Vertex 1 Z-coordinate {m}
    11.024619423024,  !- Vertex 2 X-coordinate {m}
    -2.268709539582,  !- Vertex 2 Y-coordinate {m}
    12.580000000000,  !- Vertex 2 Z-coordinate {m}
    0.000000000000,  !- Vertex 3 X-coordinate {m}
    0.000000000000,  !- Vertex 3 Y-coordinate {m}
    12.580000000000,  !- Vertex 3 Z-coordinate {m}
    -0.908031053950,  !- Vertex 4 X-coordinate {m}
    10.378842439183,  !- Vertex 4 Y-coordinate {m}
    12.580000000000;  !- Vertex 4 Z-coordinate {m}

  BuildingSurface:Detailed,
    50F275,  !- Name
    Ceiling,  !- Surface Type
    ADJ_CEILING,  !- Construction Name
    B1_F2_SC,  !- Zone Name
    Zone,  !- Outside Boundary Condition
    B1_F4_SC,  !- Outside Boundary Condition Object
    NoSun,  !- Sun Exposure
    NoWind,  !- Wind Exposure
    ,  !- TRNSYS 17 - additional surface data
    4,  !- Number of Vertices
    -0.908031053950,  !- Vertex 1 X-coordinate {m}
    10.378842439183,  !- Vertex 1 Y-coordinate {m}
    21.760000000000,  !- Vertex 1 Z-coordinate {m}
    0.000000000000,  !- Vertex 2 X-coordinate {m}
    0.000000000000,  !- Vertex 2 Y-coordinate {m}
    21.760000000000,  !- Vertex 2 Z-coordinate {m}
    11.024619423024,  !- Vertex 3 X-coordinate {m}
    -2.268709539582,  !- Vertex 3 Y-coordinate {m}
    21.760000000000,  !- Vertex 3 Z-coordinate {m}
    13.893796264487,  !- Vertex 4 X-coordinate {m}
    11.673834529015,  !- Vertex 4 Y-coordinate {m}
    21.760000000000;  !- Vertex 4 Z-coordinate {m}

  BuildingSurface:Detailed,
    748F07,  !- Name
    Wall,  !- Surface Type
    EXT_WALL_SW_EF_GL,  !- Construction Name
    B1_F2_SC,  !- Zone Name
    Outdoors,  !- Outside Boundary Condition
    ,  !- Outside Boundary Condition Object
    SunExposed,  !- Sun Exposure
    WindExposed,  !- Wind Exposure
    ,  !- TRNSYS 17 - additional surface data
    4,  !- Number of Vertices
    -0.908031053950,  !- Vertex 1 X-coordinate {m}
    10.378842439183,  !- Vertex 1 Y-coordinate {m}
    21.760000000000,  !- Vertex 1 Z-coordinate {m}
    -0.908031053950,  !- Vertex 2 X-coordinate {m}
    10.378842439183,  !- Vertex 2 Y-coordinate {m}
    12.580000000000,  !- Vertex 2 Z-coordinate {m}
    -0.592963043918,  !- Vertex 3 X-coordinate {m}
    6.777598605582,  !- Vertex 3 Y-coordinate {m}
    12.580000000000,  !- Vertex 3 Z-coordinate {m}
    -0.592963043918,  !- Vertex 4 X-coordinate {m}
    6.777598605582,  !- Vertex 4 Y-coordinate {m}
    21.760000000000;  !- Vertex 4 Z-coordinate {m}

  BuildingSurface:Detailed,
    A998F9,  !- Name
    Wall,  !- Surface Type
    ADJ_WALL,  !- Construction Name
    B1_F2_SC,  !- Zone Name
    Zone,  !- Outside Boundary Condition
    B1_F3_LB,  !- Outside Boundary Condition Object
    NoSun,  !- Sun Exposure
    NoWind,  !- Wind Exposure
    ,  !- TRNSYS 17 - additional surface data
    4,  !- Number of Vertices
    13.893796264487,  !- Vertex 1 X-coordinate {m}
    11.673834529015,  !- Vertex 1 Y-coordinate {m}
    21.760000000000,  !- Vertex 1 Z-coordinate {m}
    13.893796264487,  !- Vertex 2 X-coordinate {m}
    11.673834529015,  !- Vertex 2 Y-coordinate {m}
    17.170000000000,  !- Vertex 2 Z-coordinate {m}
    -0.908031053950,  !- Vertex 3 X-coordinate {m}
    10.378842439183,  !- Vertex 3 Y-coordinate {m}
    17.170000000000,  !- Vertex 3 Z-coordinate {m}
    -0.908031053950,  !- Vertex 4 X-coordinate {m}
    10.378842439183,  !- Vertex 4 Y-coordinate {m}
    21.760000000000;  !- Vertex 4 Z-coordinate {m}

  BuildingSurface:Detailed,
    BDBCDF,  !- Name
    Wall,  !- Surface Type
    EXT_WALL_IF_RL,  !- Construction Name
    B1_F2_SC,  !- Zone Name
    Outdoors,  !- Outside Boundary Condition
    ,  !- Outside Boundary Condition Object
    SunExposed,  !- Sun Exposure
    WindExposed,  !- Wind Exposure
    ,  !- TRNSYS 17 - additional surface data
    4,  !- Number of Vertices
    13.313760665876,  !- Vertex 1 X-coordinate {m}
    8.855196326266,  !- Vertex 1 Y-coordinate {m}
    21.760000000000,  !- Vertex 1 Z-coordinate {m}
    13.313760665876,  !- Vertex 2 X-coordinate {m}
    8.855196326266,  !- Vertex 2 Y-coordinate {m}
    12.580000000000,  !- Vertex 2 Z-coordinate {m}
    13.893796264487,  !- Vertex 3 X-coordinate {m}
    11.673834529015,  !- Vertex 3 Y-coordinate {m}
    12.580000000000,  !- Vertex 3 Z-coordinate {m}
    13.893796264487,  !- Vertex 4 X-coordinate {m}
    11.673834529015,  !- Vertex 4 Y-coordinate {m}
    21.760000000000;  !- Vertex 4 Z-coordinate {m}

  BuildingSurface:Detailed,
    593347,  !- Name
    Wall,  !- Surface Type
    ADJ_WALL,  !- Construction Name
    B1_F2_SC,  !- Zone Name
    OtherSideCoefficients,  !- Outside Boundary Condition
    BOUNDARY=IDENTICAL,  !- Outside Boundary Condition Object
    NoSun,  !- Sun Exposure
    NoWind,  !- Wind Exposure
    0.0,  !- TRNSYS 17 - additional surface data
    4,  !- Number of Vertices
    11.024619423024,  !- Vertex 1 X-coordinate {m}
    -2.268709539582,  !- Vertex 1 Y-coordinate {m}
    21.760000000000,  !- Vertex 1 Z-coordinate {m}
    11.024619423024,  !- Vertex 2 X-coordinate {m}
    -2.268709539582,  !- Vertex 2 Y-coordinate {m}
    12.580000000000,  !- Vertex 2 Z-coordinate {m}
    13.313760665876,  !- Vertex 3 X-coordinate {m}
    8.855196326266,  !- Vertex 3 Y-coordinate {m}
    12.580000000000,  !- Vertex 3 Z-coordinate {m}
    13.313760665876,  !- Vertex 4 X-coordinate {m}
    8.855196326266,  !- Vertex 4 Y-coordinate {m}
    21.760000000000;  !- Vertex 4 Z-coordinate {m}

  BuildingSurface:Detailed,
    349964,  !- Name
    Wall,  !- Surface Type
    ADJ_WALL,  !- Construction Name
    B1_F2_SC,  !- Zone Name
    Zone,  !- Outside Boundary Condition
    B1_F2_CL,  !- Outside Boundary Condition Object
    NoSun,  !- Sun Exposure
    NoWind,  !- Wind Exposure
    ,  !- TRNSYS 17 - additional surface data
    4,  !- Number of Vertices
    13.893796264487,  !- Vertex 1 X-coordinate {m}
    11.673834529015,  !- Vertex 1 Y-coordinate {m}
    17.170000000000,  !- Vertex 1 Z-coordinate {m}
    13.893796264487,  !- Vertex 2 X-coordinate {m}
    11.673834529015,  !- Vertex 2 Y-coordinate {m}
    12.580000000000,  !- Vertex 2 Z-coordinate {m}
    -0.908031053950,  !- Vertex 3 X-coordinate {m}
    10.378842439183,  !- Vertex 3 Y-coordinate {m}
    12.580000000000,  !- Vertex 3 Z-coordinate {m}
    -0.908031053950,  !- Vertex 4 X-coordinate {m}
    10.378842439183,  !- Vertex 4 Y-coordinate {m}
    17.170000000000;  !- Vertex 4 Z-coordinate {m}

  BuildingSurface:Detailed,
    90A76B,  !- Name
    Ceiling,  !- Surface Type
    ADJ_CEILING,  !- Construction Name
    B6_F1_LB,  !- Zone Name
    Zone,  !- Outside Boundary Condition
    B6_F2_LB,  !- Outside Boundary Condition Object
    NoSun,  !- Sun Exposure
    NoWind,  !- Wind Exposure
    ,  !- TRNSYS 17 - additional surface data
    4,  !- Number of Vertices
    62.288489505666,  !- Vertex 1 X-coordinate {m}
    55.689741033696,  !- Vertex 1 Y-coordinate {m}
    12.580000000000,  !- Vertex 1 Z-coordinate {m}
    44.808863897137,  !- Vertex 2 X-coordinate {m}
    20.069544539119,  !- Vertex 2 Y-coordinate {m}
    12.580000000000,  !- Vertex 2 Z-coordinate {m}
    56.030641432231,  !- Vertex 3 X-coordinate {m}
    14.561907467061,  !- Vertex 3 Y-coordinate {m}
    12.580000000000,  !- Vertex 3 Z-coordinate {m}
    73.517257553134,  !- Vertex 4 X-coordinate {m}
    50.190783041650,  !- Vertex 4 Y-coordinate {m}
    12.580000000000;  !- Vertex 4 Z-coordinate {m}

  Zone,
    B6_F2_LB,  !- Name
    0.0,  !- Direction of Relative North {deg}
    56.729463,  !- X Origin {m}
    67.860144,  !- Y Origin {m}
    12.58,  !- Z Origin {m}
    ,  !- Type
    1;  !- Multiplier

  BuildingSurface:Detailed,
    F17E03,  !- Name
    Floor,  !- Surface Type
    ADJ_CEILING,  !- Construction Name
    B6_F2_LB,  !- Zone Name
    Zone,  !- Outside Boundary Condition
    B6_F1_LB,  !- Outside Boundary Condition Object
    NoSun,  !- Sun Exposure
    NoWind,  !- Wind Exposure
    ,  !- TRNSYS 17 - additional surface data
    4,  !- Number of Vertices
    73.517257553134,  !- Vertex 1 X-coordinate {m}
    50.190783041650,  !- Vertex 1 Y-coordinate {m}
    12.580000000000,  !- Vertex 1 Z-coordinate {m}
    56.030641432231,  !- Vertex 2 X-coordinate {m}
    14.561907467061,  !- Vertex 2 Y-coordinate {m}
    12.580000000000,  !- Vertex 2 Z-coordinate {m}
    44.808863897137,  !- Vertex 3 X-coordinate {m}
    20.069544539119,  !- Vertex 3 Y-coordinate {m}
    12.580000000000,  !- Vertex 3 Z-coordinate {m}
    62.288489786191,  !- Vertex 4 X-coordinate {m}
    55.689740800071,  !- Vertex 4 Y-coordinate {m}
    12.580000000000;  !- Vertex 4 Z-coordinate {m}

  BuildingSurface:Detailed,
    3EB900,  !- Name
    Ceiling,  !- Surface Type
    ADJ_CEILING,  !- Construction Name
    B6_F2_LB,  !- Zone Name
    Zone,  !- Outside Boundary Condition
    B6_F3_OF,  !- Outside Boundary Condition Object
    NoSun,  !- Sun Exposure
    NoWind,  !- Wind Exposure
    ,  !- TRNSYS 17 - additional surface data
    4,  !- Number of Vertices
    46.571016269985,  !- Vertex 1 X-coordinate {m}
    23.660480281161,  !- Vertex 1 Y-coordinate {m}
    17.170000000000,  !- Vertex 1 Z-coordinate {m}
    44.808863897137,  !- Vertex 2 X-coordinate {m}
    20.069544539119,  !- Vertex 2 Y-coordinate {m}
    17.170000000000,  !- Vertex 2 Z-coordinate {m}
    56.030641432231,  !- Vertex 3 X-coordinate {m}
    14.561907467061,  !- Vertex 3 Y-coordinate {m}
    17.170000000000,  !- Vertex 3 Z-coordinate {m}
    57.793015607234,  !- Vertex 4 X-coordinate {m}
    18.152734289297,  !- Vertex 4 Y-coordinate {m}
    17.170000000000;  !- Vertex 4 Z-coordinate {m}

  BuildingSurface:Detailed,
    6CFA21,  !- Name
    Wall,  !- Surface Type
    ADJ_WALL,  !- Construction Name
    B6_F2_LB,  !- Zone Name
    OtherSideCoefficients,  !- Outside Boundary Condition
    BOUNDARY=IDENTICAL,  !- Outside Boundary Condition Object
    NoSun,  !- Sun Exposure
    NoWind,  !- Wind Exposure
    0.0,  !- TRNSYS 17 - additional surface data
    4,  !- Number of Vertices
    73.517257553134,  !- Vertex 1 X-coordinate {m}
    50.190783041650,  !- Vertex 1 Y-coordinate {m}
    17.170000000000,  !- Vertex 1 Z-coordinate {m}
    73.517257553134,  !- Vertex 2 X-coordinate {m}
    50.190783041650,  !- Vertex 2 Y-coordinate {m}
    12.580000000000,  !- Vertex 2 Z-coordinate {m}
    62.288489786191,  !- Vertex 3 X-coordinate {m}
    55.689740800071,  !- Vertex 3 Y-coordinate {m}
    12.580000000000,  !- Vertex 3 Z-coordinate {m}
    62.288489786191,  !- Vertex 4 X-coordinate {m}
    55.689740800071,  !- Vertex 4 Y-coordinate {m}
    17.170000000000;  !- Vertex 4 Z-coordinate {m}

  BuildingSurface:Detailed,
    C33312,  !- Name
    Wall,  !- Surface Type
    EXT_WALL_IF_RL,  !- Construction Name
    B6_F2_LB,  !- Zone Name
    Outdoors,  !- Outside Boundary Condition
    ,  !- Outside Boundary Condition Object
    SunExposed,  !- Sun Exposure
    WindExposed,  !- Wind Exposure
    ,  !- TRNSYS 17 - additional surface data
    4,  !- Number of Vertices
    62.288489786191,  !- Vertex 1 X-coordinate {m}
    55.689740800071,  !- Vertex 1 Y-coordinate {m}
    17.170000000000,  !- Vertex 1 Z-coordinate {m}
    62.288489786191,  !- Vertex 2 X-coordinate {m}
    55.689740800071,  !- Vertex 2 Y-coordinate {m}
    12.580000000000,  !- Vertex 2 Z-coordinate {m}
    44.808863897137,  !- Vertex 3 X-coordinate {m}
    20.069544539119,  !- Vertex 3 Y-coordinate {m}
    12.580000000000,  !- Vertex 3 Z-coordinate {m}
    44.808863897137,  !- Vertex 4 X-coordinate {m}
    20.069544539119,  !- Vertex 4 Y-coordinate {m}
    17.170000000000;  !- Vertex 4 Z-coordinate {m}

  BuildingSurface:Detailed,
    E6F13C,  !- Name
    Wall,  !- Surface Type
    EXT_WALL_NE_EF_AL,  !- Construction Name
    B6_F2_LB,  !- Zone Name
    Outdoors,  !- Outside Boundary Condition
    ,  !- Outside Boundary Condition Object
    SunExposed,  !- Sun Exposure
    WindExposed,  !- Wind Exposure
    ,  !- TRNSYS 17 - additional surface data
    4,  !- Number of Vertices
    56.030641432231,  !- Vertex 1 X-coordinate {m}
    14.561907467061,  !- Vertex 1 Y-coordinate {m}
    17.170000000000,  !- Vertex 1 Z-coordinate {m}
    56.030641432231,  !- Vertex 2 X-coordinate {m}
    14.561907467061,  !- Vertex 2 Y-coordinate {m}
    12.580000000000,  !- Vertex 2 Z-coordinate {m}
    73.517257553134,  !- Vertex 3 X-coordinate {m}
    50.190783041650,  !- Vertex 3 Y-coordinate {m}
    12.580000000000,  !- Vertex 3 Z-coordinate {m}
    73.517257553134,  !- Vertex 4 X-coordinate {m}
    50.190783041650,  !- Vertex 4 Y-coordinate {m}
    17.170000000000;  !- Vertex 4 Z-coordinate {m}

  BuildingSurface:Detailed,
    4DBB16,  !- Name
    Wall,  !- Surface Type
    ADJ_WALL,  !- Construction Name
    B6_F2_LB,  !- Zone Name
    Zone,  !- Outside Boundary Condition
    B6_F2_OF,  !- Outside Boundary Condition Object
    NoSun,  !- Sun Exposure
    NoWind,  !- Wind Exposure
    ,  !- TRNSYS 17 - additional surface data
    4,  !- Number of Vertices
    44.808863897137,  !- Vertex 1 X-coordinate {m}
    20.069544539119,  !- Vertex 1 Y-coordinate {m}
    17.170000000000,  !- Vertex 1 Z-coordinate {m}
    44.808863897137,  !- Vertex 2 X-coordinate {m}
    20.069544539119,  !- Vertex 2 Y-coordinate {m}
    12.580000000000,  !- Vertex 2 Z-coordinate {m}
    56.030641432231,  !- Vertex 3 X-coordinate {m}
    14.561907467061,  !- Vertex 3 Y-coordinate {m}
    12.580000000000,  !- Vertex 3 Z-coordinate {m}
    56.030641432231,  !- Vertex 4 X-coordinate {m}
    14.561907467061,  !- Vertex 4 Y-coordinate {m}
    17.170000000000;  !- Vertex 4 Z-coordinate {m}

  Zone,
    B6_F2_OF,  !- Name
    0.0,  !- Direction of Relative North {deg}
    90.690664,  !- X Origin {m}
    47.342529,  !- Y Origin {m}
    12.58,  !- Z Origin {m}
    ,  !- Type
    1;  !- Multiplier

  BuildingSurface:Detailed,
    548454,  !- Name
    Floor,  !- Surface Type
    ADJ_CEILING,  !- Construction Name
    B6_F2_OF,  !- Zone Name
    Zone,  !- Outside Boundary Condition
    B6_F1_LB,  !- Outside Boundary Condition Object
    NoSun,  !- Sun Exposure
    NoWind,  !- Wind Exposure
    ,  !- TRNSYS 17 - additional surface data
    4,  !- Number of Vertices
    56.030641432231,  !- Vertex 1 X-coordinate {m}
    14.561907467061,  !- Vertex 1 Y-coordinate {m}
    12.580000000000,  !- Vertex 1 Z-coordinate {m}
    52.505893082225,  !- Vertex 2 X-coordinate {m}
    7.380253822592,  !- Vertex 2 Y-coordinate {m}
    12.580000000000,  !- Vertex 2 Z-coordinate {m}
    41.284559262741,  !- Vertex 3 X-coordinate {m}
    12.887673119476,  !- Vertex 3 Y-coordinate {m}
    12.580000000000,  !- Vertex 3 Z-coordinate {m}
    44.808864203461,  !- Vertex 4 X-coordinate {m}
    20.069544448307,  !- Vertex 4 Y-coordinate {m}
    12.580000000000;  !- Vertex 4 Z-coordinate {m}

  BuildingSurface:Detailed,
    57144B,  !- Name
    Ceiling,  !- Surface Type
    ADJ_CEILING,  !- Construction Name
    B6_F2_OF,  !- Zone Name
    Zone,  !- Outside Boundary Condition
    B6_F3_OF,  !- Outside Boundary Condition Object
    NoSun,  !- Sun Exposure
    NoWind,  !- Wind Exposure
    ,  !- TRNSYS 17 - additional surface data
    4,  !- Number of Vertices
    44.808864203461,  !- Vertex 1 X-coordinate {m}
    20.069544448307,  !- Vertex 1 Y-coordinate {m}
    17.170000000000,  !- Vertex 1 Z-coordinate {m}
    41.284559262741,  !- Vertex 2 X-coordinate {m}
    12.887673119476,  !- Vertex 2 Y-coordinate {m}
    17.170000000000,  !- Vertex 2 Z-coordinate {m}
    52.505893082225,  !- Vertex 3 X-coordinate {m}
    7.380253822592,  !- Vertex 3 Y-coordinate {m}
    17.170000000000,  !- Vertex 3 Z-coordinate {m}
    56.030641432231,  !- Vertex 4 X-coordinate {m}
    14.561907467061,  !- Vertex 4 Y-coordinate {m}
    17.170000000000;  !- Vertex 4 Z-coordinate {m}

  BuildingSurface:Detailed,
    DB206A,  !- Name
    Wall,  !- Surface Type
    EXT_WALL_NE_EF_AL,  !- Construction Name
    B6_F2_OF,  !- Zone Name
    Outdoors,  !- Outside Boundary Condition
    ,  !- Outside Boundary Condition Object
    SunExposed,  !- Sun Exposure
    WindExposed,  !- Wind Exposure
    ,  !- TRNSYS 17 - additional surface data
    4,  !- Number of Vertices
    52.505893082225,  !- Vertex 1 X-coordinate {m}
    7.380253822592,  !- Vertex 1 Y-coordinate {m}
    17.170000000000,  !- Vertex 1 Z-coordinate {m}
    52.505893082225,  !- Vertex 2 X-coordinate {m}
    7.380253822592,  !- Vertex 2 Y-coordinate {m}
    12.580000000000,  !- Vertex 2 Z-coordinate {m}
    56.030641432231,  !- Vertex 3 X-coordinate {m}
    14.561907467061,  !- Vertex 3 Y-coordinate {m}
    12.580000000000,  !- Vertex 3 Z-coordinate {m}
    56.030641432231,  !- Vertex 4 X-coordinate {m}
    14.561907467061,  !- Vertex 4 Y-coordinate {m}
    17.170000000000;  !- Vertex 4 Z-coordinate {m}

  BuildingSurface:Detailed,
    FD319A,  !- Name
    Wall,  !- Surface Type
    EXT_WALL_IF_RL,  !- Construction Name
    B6_F2_OF,  !- Zone Name
    Outdoors,  !- Outside Boundary Condition
    ,  !- Outside Boundary Condition Object
    SunExposed,  !- Sun Exposure
    WindExposed,  !- Wind Exposure
    0.0,  !- TRNSYS 17 - additional surface data
    4,  !- Number of Vertices
    44.808864203461,  !- Vertex 1 X-coordinate {m}
    20.069544448307,  !- Vertex 1 Y-coordinate {m}
    17.170000000000,  !- Vertex 1 Z-coordinate {m}
    44.808864203461,  !- Vertex 2 X-coordinate {m}
    20.069544448307,  !- Vertex 2 Y-coordinate {m}
    12.580000000000,  !- Vertex 2 Z-coordinate {m}
    41.284559262741,  !- Vertex 3 X-coordinate {m}
    12.887673119476,  !- Vertex 3 Y-coordinate {m}
    12.580000000000,  !- Vertex 3 Z-coordinate {m}
    41.284559262741,  !- Vertex 4 X-coordinate {m}
    12.887673119476,  !- Vertex 4 Y-coordinate {m}
    17.170000000000;  !- Vertex 4 Z-coordinate {m}

  BuildingSurface:Detailed,
    1B78AC,  !- Name
    Wall,  !- Surface Type
    ADJ_WALL,  !- Construction Name
    B6_F2_OF,  !- Zone Name
    OtherSideCoefficients,  !- Outside Boundary Condition
    BOUNDARY=IDENTICAL,  !- Outside Boundary Condition Object
    NoSun,  !- Sun Exposure
    NoWind,  !- Wind Exposure
    0.0,  !- TRNSYS 17 - additional surface data
    4,  !- Number of Vertices
    41.284559262741,  !- Vertex 1 X-coordinate {m}
    12.887673119476,  !- Vertex 1 Y-coordinate {m}
    17.170000000000,  !- Vertex 1 Z-coordinate {m}
    41.284559262741,  !- Vertex 2 X-coordinate {m}
    12.887673119476,  !- Vertex 2 Y-coordinate {m}
    12.580000000000,  !- Vertex 2 Z-coordinate {m}
    52.505893082225,  !- Vertex 3 X-coordinate {m}
    7.380253822592,  !- Vertex 3 Y-coordinate {m}
    12.580000000000,  !- Vertex 3 Z-coordinate {m}
    52.505893082225,  !- Vertex 4 X-coordinate {m}
    7.380253822592,  !- Vertex 4 Y-coordinate {m}
    17.170000000000;  !- Vertex 4 Z-coordinate {m}

  BuildingSurface:Detailed,
    D5613A,  !- Name
    Wall,  !- Surface Type
    ADJ_WALL,  !- Construction Name
    B6_F2_OF,  !- Zone Name
    Zone,  !- Outside Boundary Condition
    B6_F2_LB,  !- Outside Boundary Condition Object
    NoSun,  !- Sun Exposure
    NoWind,  !- Wind Exposure
    ,  !- TRNSYS 17 - additional surface data
    4,  !- Number of Vertices
    56.030641432231,  !- Vertex 1 X-coordinate {m}
    14.561907467061,  !- Vertex 1 Y-coordinate {m}
    17.170000000000,  !- Vertex 1 Z-coordinate {m}
    56.030641432231,  !- Vertex 2 X-coordinate {m}
    14.561907467061,  !- Vertex 2 Y-coordinate {m}
    12.580000000000,  !- Vertex 2 Z-coordinate {m}
    44.808864203461,  !- Vertex 3 X-coordinate {m}
    20.069544448307,  !- Vertex 3 Y-coordinate {m}
    12.580000000000,  !- Vertex 3 Z-coordinate {m}
    44.808864203461,  !- Vertex 4 X-coordinate {m}
    20.069544448307,  !- Vertex 4 Y-coordinate {m}
    17.170000000000;  !- Vertex 4 Z-coordinate {m}

  Zone,
    B2_F3_SC,  !- Name
    0.0,  !- Direction of Relative North {deg}
    43.86,  !- X Origin {m}
    9.46,  !- Y Origin {m}
    17.17,  !- Z Origin {m}
    ,  !- Type
    1;  !- Multiplier

  BuildingSurface:Detailed,
    CFBF21,  !- Name
    Floor,  !- Surface Type
    ADJ_CEILING,  !- Construction Name
    B2_F3_SC,  !- Zone Name
    Zone,  !- Outside Boundary Condition
    B2_F2_SC,  !- Outside Boundary Condition Object
    NoSun,  !- Sun Exposure
    NoWind,  !- Wind Exposure
    ,  !- TRNSYS 17 - additional surface data
    4,  !- Number of Vertices
    12.582233491957,  !- Vertex 1 X-coordinate {m}
    64.259629125942,  !- Vertex 1 Y-coordinate {m}
    17.170000000000,  !- Vertex 1 Z-coordinate {m}
    13.663400568944,  !- Vertex 2 X-coordinate {m}
    51.901833903830,  !- Vertex 2 Y-coordinate {m}
    17.170000000000,  !- Vertex 2 Z-coordinate {m}
    4.070095347853,  !- Vertex 3 X-coordinate {m}
    51.062528451241,  !- Vertex 3 Y-coordinate {m}
    17.170000000000,  !- Vertex 3 Z-coordinate {m}
    2.988928359068,  !- Vertex 4 X-coordinate {m}
    63.420323681069,  !- Vertex 4 Y-coordinate {m}
    17.170000000000;  !- Vertex 4 Z-coordinate {m}

  BuildingSurface:Detailed,
    53850F,  !- Name
    Wall,  !- Surface Type
    ADJ_WALL,  !- Construction Name
    B2_F3_SC,  !- Zone Name
    Zone,  !- Outside Boundary Condition
    B1_F3_LB,  !- Outside Boundary Condition Object
    NoSun,  !- Sun Exposure
    NoWind,  !- Wind Exposure
    ,  !- TRNSYS 17 - additional surface data
    4,  !- Number of Vertices
    4.070095347853,  !- Vertex 1 X-coordinate {m}
    51.062528451241,  !- Vertex 1 Y-coordinate {m}
    21.760000000000,  !- Vertex 1 Z-coordinate {m}
    4.070095347853,  !- Vertex 2 X-coordinate {m}
    51.062528451241,  !- Vertex 2 Y-coordinate {m}
    17.170000000000,  !- Vertex 2 Z-coordinate {m}
    12.707103380308,  !- Vertex 3 X-coordinate {m}
    51.818168740863,  !- Vertex 3 Y-coordinate {m}
    17.170000000000,  !- Vertex 3 Z-coordinate {m}
    12.707103380308,  !- Vertex 4 X-coordinate {m}
    51.818168740863,  !- Vertex 4 Y-coordinate {m}
    21.760000000000;  !- Vertex 4 Z-coordinate {m}

  BuildingSurface:Detailed,
    8F9F23,  !- Name
    Ceiling,  !- Surface Type
    ADJ_CEILING,  !- Construction Name
    B2_F3_SC,  !- Zone Name
    Zone,  !- Outside Boundary Condition
    B2_F4_SC,  !- Outside Boundary Condition Object
    NoSun,  !- Sun Exposure
    NoWind,  !- Wind Exposure
    ,  !- TRNSYS 17 - additional surface data
    4,  !- Number of Vertices
    2.988928359068,  !- Vertex 1 X-coordinate {m}
    63.420323681069,  !- Vertex 1 Y-coordinate {m}
    21.760000000000,  !- Vertex 1 Z-coordinate {m}
    4.070095347853,  !- Vertex 2 X-coordinate {m}
    51.062528451241,  !- Vertex 2 Y-coordinate {m}
    21.760000000000,  !- Vertex 2 Z-coordinate {m}
    13.663400568944,  !- Vertex 3 X-coordinate {m}
    51.901833903830,  !- Vertex 3 Y-coordinate {m}
    21.760000000000,  !- Vertex 3 Z-coordinate {m}
    12.582233491957,  !- Vertex 4 X-coordinate {m}
    64.259629125942,  !- Vertex 4 Y-coordinate {m}
    21.760000000000;  !- Vertex 4 Z-coordinate {m}

  BuildingSurface:Detailed,
    72FD7F,  !- Name
    Wall,  !- Surface Type
    EXT_WALL_IF_RL,  !- Construction Name
    B2_F3_SC,  !- Zone Name
    Outdoors,  !- Outside Boundary Condition
    ,  !- Outside Boundary Condition Object
    SunExposed,  !- Sun Exposure
    WindExposed,  !- Wind Exposure
    ,  !- TRNSYS 17 - additional surface data
    4,  !- Number of Vertices
    12.707103380308,  !- Vertex 1 X-coordinate {m}
    51.818168740863,  !- Vertex 1 Y-coordinate {m}
    21.760000000000,  !- Vertex 1 Z-coordinate {m}
    12.707103380308,  !- Vertex 2 X-coordinate {m}
    51.818168740863,  !- Vertex 2 Y-coordinate {m}
    17.170000000000,  !- Vertex 2 Z-coordinate {m}
    13.663400568944,  !- Vertex 3 X-coordinate {m}
    51.901833903830,  !- Vertex 3 Y-coordinate {m}
    17.170000000000,  !- Vertex 3 Z-coordinate {m}
    13.663400568944,  !- Vertex 4 X-coordinate {m}
    51.901833903830,  !- Vertex 4 Y-coordinate {m}
    21.760000000000;  !- Vertex 4 Z-coordinate {m}

  BuildingSurface:Detailed,
    439FB8,  !- Name
    Wall,  !- Surface Type
    ADJ_WALL,  !- Construction Name
    B2_F3_SC,  !- Zone Name
    Zone,  !- Outside Boundary Condition
    B2_F3_LB,  !- Outside Boundary Condition Object
    NoSun,  !- Sun Exposure
    NoWind,  !- Wind Exposure
    ,  !- TRNSYS 17 - additional surface data
    4,  !- Number of Vertices
    2.988928359068,  !- Vertex 1 X-coordinate {m}
    63.420323681069,  !- Vertex 1 Y-coordinate {m}
    21.760000000000,  !- Vertex 1 Z-coordinate {m}
    2.988928359068,  !- Vertex 2 X-coordinate {m}
    63.420323681069,  !- Vertex 2 Y-coordinate {m}
    17.170000000000,  !- Vertex 2 Z-coordinate {m}
    4.070095347853,  !- Vertex 3 X-coordinate {m}
    51.062528451241,  !- Vertex 3 Y-coordinate {m}
    17.170000000000,  !- Vertex 3 Z-coordinate {m}
    4.070095347853,  !- Vertex 4 X-coordinate {m}
    51.062528451241,  !- Vertex 4 Y-coordinate {m}
    21.760000000000;  !- Vertex 4 Z-coordinate {m}

  BuildingSurface:Detailed,
    E2F99C,  !- Name
    Wall,  !- Surface Type
    EXT_WALL_NE_EF_AL,  !- Construction Name
    B2_F3_SC,  !- Zone Name
    Outdoors,  !- Outside Boundary Condition
    ,  !- Outside Boundary Condition Object
    SunExposed,  !- Sun Exposure
    WindExposed,  !- Wind Exposure
    0.0,  !- TRNSYS 17 - additional surface data
    4,  !- Number of Vertices
    12.582233491957,  !- Vertex 1 X-coordinate {m}
    64.259629125942,  !- Vertex 1 Y-coordinate {m}
    21.760000000000,  !- Vertex 1 Z-coordinate {m}
    12.582233491957,  !- Vertex 2 X-coordinate {m}
    64.259629125942,  !- Vertex 2 Y-coordinate {m}
    17.170000000000,  !- Vertex 2 Z-coordinate {m}
    2.988928359068,  !- Vertex 3 X-coordinate {m}
    63.420323681069,  !- Vertex 3 Y-coordinate {m}
    17.170000000000,  !- Vertex 3 Z-coordinate {m}
    2.988928359068,  !- Vertex 4 X-coordinate {m}
    63.420323681069,  !- Vertex 4 Y-coordinate {m}
    21.760000000000;  !- Vertex 4 Z-coordinate {m}

  BuildingSurface:Detailed,
    6B1E35,  !- Name
    Wall,  !- Surface Type
    ADJ_WALL,  !- Construction Name
    B2_F3_SC,  !- Zone Name
    OtherSideCoefficients,  !- Outside Boundary Condition
    BOUNDARY=IDENTICAL,  !- Outside Boundary Condition Object
    NoSun,  !- Sun Exposure
    NoWind,  !- Wind Exposure
    0.0,  !- TRNSYS 17 - additional surface data
    4,  !- Number of Vertices
    13.663400568944,  !- Vertex 1 X-coordinate {m}
    51.901833903830,  !- Vertex 1 Y-coordinate {m}
    21.760000000000,  !- Vertex 1 Z-coordinate {m}
    13.663400568944,  !- Vertex 2 X-coordinate {m}
    51.901833903830,  !- Vertex 2 Y-coordinate {m}
    17.170000000000,  !- Vertex 2 Z-coordinate {m}
    12.582233491957,  !- Vertex 3 X-coordinate {m}
    64.259629125942,  !- Vertex 3 Y-coordinate {m}
    17.170000000000,  !- Vertex 3 Z-coordinate {m}
    12.582233491957,  !- Vertex 4 X-coordinate {m}
    64.259629125942,  !- Vertex 4 Y-coordinate {m}
    21.760000000000;  !- Vertex 4 Z-coordinate {m}

  Zone,
    B2_F3_LB,  !- Name
    0.0,  !- Direction of Relative North {deg}
    39.326026,  !- X Origin {m}
    0.0,  !- Y Origin {m}
    17.17,  !- Z Origin {m}
    ,  !- Type
    1;  !- Multiplier

  BuildingSurface:Detailed,
    BC1F83,  !- Name
    Floor,  !- Surface Type
    ADJ_CEILING,  !- Construction Name
    B2_F3_LB,  !- Zone Name
    Zone,  !- Outside Boundary Condition
    B2_F2_CL,  !- Outside Boundary Condition Object
    NoSun,  !- Sun Exposure
    NoWind,  !- Wind Exposure
    ,  !- TRNSYS 17 - additional surface data
    4,  !- Number of Vertices
    2.593766487499,  !- Vertex 1 X-coordinate {m}
    67.937044541155,  !- Vertex 1 Y-coordinate {m}
    17.170000000000,  !- Vertex 1 Z-coordinate {m}
    4.070095347853,  !- Vertex 2 X-coordinate {m}
    51.062528451241,  !- Vertex 2 Y-coordinate {m}
    17.170000000000,  !- Vertex 2 Z-coordinate {m}
    -5.353906496095,  !- Vertex 3 X-coordinate {m}
    50.238035124848,  !- Vertex 3 Y-coordinate {m}
    17.170000000000,  !- Vertex 3 Z-coordinate {m}
    -6.830235356449,  !- Vertex 4 X-coordinate {m}
    67.112551214762,  !- Vertex 4 Y-coordinate {m}
    17.170000000000;  !- Vertex 4 Z-coordinate {m}

  BuildingSurface:Detailed,
    5DAEDD,  !- Name
    Wall,  !- Surface Type
    EXT_WALL_SW_EF_RL,  !- Construction Name
    B2_F3_LB,  !- Zone Name
    Outdoors,  !- Outside Boundary Condition
    ,  !- Outside Boundary Condition Object
    SunExposed,  !- Sun Exposure
    WindExposed,  !- Wind Exposure
    ,  !- TRNSYS 17 - additional surface data
    4,  !- Number of Vertices
    -5.353906496095,  !- Vertex 1 X-coordinate {m}
    50.238035124848,  !- Vertex 1 Y-coordinate {m}
    21.760000000000,  !- Vertex 1 Z-coordinate {m}
    -5.353906496095,  !- Vertex 2 X-coordinate {m}
    50.238035124848,  !- Vertex 2 Y-coordinate {m}
    17.170000000000,  !- Vertex 2 Z-coordinate {m}
    -4.402540559418,  !- Vertex 3 X-coordinate {m}
    50.321268859172,  !- Vertex 3 Y-coordinate {m}
    17.170000000000,  !- Vertex 3 Z-coordinate {m}
    -4.402540559418,  !- Vertex 4 X-coordinate {m}
    50.321268859172,  !- Vertex 4 Y-coordinate {m}
    21.760000000000;  !- Vertex 4 Z-coordinate {m}

  BuildingSurface:Detailed,
    4A5EC2,  !- Name
    Wall,  !- Surface Type
    ADJ_WALL,  !- Construction Name
    B2_F3_LB,  !- Zone Name
    Zone,  !- Outside Boundary Condition
    B2_F3_SC,  !- Outside Boundary Condition Object
    NoSun,  !- Sun Exposure
    NoWind,  !- Wind Exposure
    ,  !- TRNSYS 17 - additional surface data
    4,  !- Number of Vertices
    4.070095347853,  !- Vertex 1 X-coordinate {m}
    51.062528451241,  !- Vertex 1 Y-coordinate {m}
    21.760000000000,  !- Vertex 1 Z-coordinate {m}
    4.070095347853,  !- Vertex 2 X-coordinate {m}
    51.062528451241,  !- Vertex 2 Y-coordinate {m}
    17.170000000000,  !- Vertex 2 Z-coordinate {m}
    2.988928359068,  !- Vertex 3 X-coordinate {m}
    63.420323681069,  !- Vertex 3 Y-coordinate {m}
    17.170000000000,  !- Vertex 3 Z-coordinate {m}
    2.988928359068,  !- Vertex 4 X-coordinate {m}
    63.420323681069,  !- Vertex 4 Y-coordinate {m}
    21.760000000000;  !- Vertex 4 Z-coordinate {m}

  BuildingSurface:Detailed,
    FC7F93,  !- Name
    Ceiling,  !- Surface Type
    ADJ_CEILING,  !- Construction Name
    B2_F3_LB,  !- Zone Name
    Zone,  !- Outside Boundary Condition
    B2_F4_CL,  !- Outside Boundary Condition Object
    NoSun,  !- Sun Exposure
    NoWind,  !- Wind Exposure
    ,  !- TRNSYS 17 - additional surface data
    4,  !- Number of Vertices
    -6.830235356449,  !- Vertex 1 X-coordinate {m}
    67.112551214762,  !- Vertex 1 Y-coordinate {m}
    21.760000000000,  !- Vertex 1 Z-coordinate {m}
    -5.353906496095,  !- Vertex 2 X-coordinate {m}
    50.238035124848,  !- Vertex 2 Y-coordinate {m}
    21.760000000000,  !- Vertex 2 Z-coordinate {m}
    4.070095347853,  !- Vertex 3 X-coordinate {m}
    51.062528451241,  !- Vertex 3 Y-coordinate {m}
    21.760000000000,  !- Vertex 3 Z-coordinate {m}
    2.593766487499,  !- Vertex 4 X-coordinate {m}
    67.937044541155,  !- Vertex 4 Y-coordinate {m}
    21.760000000000;  !- Vertex 4 Z-coordinate {m}

  BuildingSurface:Detailed,
    BB6519,  !- Name
    Wall,  !- Surface Type
    EXT_WALL_SW_EF_RL,  !- Construction Name
    B2_F3_LB,  !- Zone Name
    Outdoors,  !- Outside Boundary Condition
    ,  !- Outside Boundary Condition Object
    SunExposed,  !- Sun Exposure
    WindExposed,  !- Wind Exposure
    ,  !- TRNSYS 17 - additional surface data
    4,  !- Number of Vertices
    -6.830235356449,  !- Vertex 1 X-coordinate {m}
    67.112551214762,  !- Vertex 1 Y-coordinate {m}
    21.760000000000,  !- Vertex 1 Z-coordinate {m}
    -6.830235356449,  !- Vertex 2 X-coordinate {m}
    67.112551214762,  !- Vertex 2 Y-coordinate {m}
    17.170000000000,  !- Vertex 2 Z-coordinate {m}
    -6.660281627363,  !- Vertex 3 X-coordinate {m}
    65.169971202261,  !- Vertex 3 Y-coordinate {m}
    17.170000000000,  !- Vertex 3 Z-coordinate {m}
    -6.660281627363,  !- Vertex 4 X-coordinate {m}
    65.169971202261,  !- Vertex 4 Y-coordinate {m}
    21.760000000000;  !- Vertex 4 Z-coordinate {m}

  BuildingSurface:Detailed,
    A82EBD,  !- Name
    Wall,  !- Surface Type
    ADJ_WALL,  !- Construction Name
    B2_F3_LB,  !- Zone Name
    Zone,  !- Outside Boundary Condition
    B1_F3_LB,  !- Outside Boundary Condition Object
    NoSun,  !- Sun Exposure
    NoWind,  !- Wind Exposure
    ,  !- TRNSYS 17 - additional surface data
    4,  !- Number of Vertices
    -4.402540559418,  !- Vertex 1 X-coordinate {m}
    50.321268859172,  !- Vertex 1 Y-coordinate {m}
    21.760000000000,  !- Vertex 1 Z-coordinate {m}
    -4.402540559418,  !- Vertex 2 X-coordinate {m}
    50.321268859172,  !- Vertex 2 Y-coordinate {m}
    17.170000000000,  !- Vertex 2 Z-coordinate {m}
    4.070095347853,  !- Vertex 3 X-coordinate {m}
    51.062528451241,  !- Vertex 3 Y-coordinate {m}
    17.170000000000,  !- Vertex 3 Z-coordinate {m}
    4.070095347853,  !- Vertex 4 X-coordinate {m}
    51.062528451241,  !- Vertex 4 Y-coordinate {m}
    21.760000000000;  !- Vertex 4 Z-coordinate {m}

  BuildingSurface:Detailed,
    36A241,  !- Name
    Wall,  !- Surface Type
    EXT_WALL_NE_EF_AL,  !- Construction Name
    B2_F3_LB,  !- Zone Name
    Outdoors,  !- Outside Boundary Condition
    ,  !- Outside Boundary Condition Object
    SunExposed,  !- Sun Exposure
    WindExposed,  !- Wind Exposure
    ,  !- TRNSYS 17 - additional surface data
    4,  !- Number of Vertices
    2.593766487499,  !- Vertex 1 X-coordinate {m}
    67.937044541155,  !- Vertex 1 Y-coordinate {m}
    21.760000000000,  !- Vertex 1 Z-coordinate {m}
    2.593766487499,  !- Vertex 2 X-coordinate {m}
    67.937044541155,  !- Vertex 2 Y-coordinate {m}
    17.170000000000,  !- Vertex 2 Z-coordinate {m}
    -6.830235356449,  !- Vertex 3 X-coordinate {m}
    67.112551214762,  !- Vertex 3 Y-coordinate {m}
    17.170000000000,  !- Vertex 3 Z-coordinate {m}
    -6.830235356449,  !- Vertex 4 X-coordinate {m}
    67.112551214762,  !- Vertex 4 Y-coordinate {m}
    21.760000000000;  !- Vertex 4 Z-coordinate {m}

  BuildingSurface:Detailed,
    C32016,  !- Name
    Wall,  !- Surface Type
    EXT_WALL_NE_EF_AL,  !- Construction Name
    B2_F3_LB,  !- Zone Name
    Outdoors,  !- Outside Boundary Condition
    ,  !- Outside Boundary Condition Object
    SunExposed,  !- Sun Exposure
    WindExposed,  !- Wind Exposure
    ,  !- TRNSYS 17 - additional surface data
    4,  !- Number of Vertices
    2.988928359068,  !- Vertex 1 X-coordinate {m}
    63.420323681069,  !- Vertex 1 Y-coordinate {m}
    21.760000000000,  !- Vertex 1 Z-coordinate {m}
    2.988928359068,  !- Vertex 2 X-coordinate {m}
    63.420323681069,  !- Vertex 2 Y-coordinate {m}
    17.170000000000,  !- Vertex 2 Z-coordinate {m}
    2.593766487499,  !- Vertex 3 X-coordinate {m}
    67.937044541155,  !- Vertex 3 Y-coordinate {m}
    17.170000000000,  !- Vertex 3 Z-coordinate {m}
    2.593766487499,  !- Vertex 4 X-coordinate {m}
    67.937044541155,  !- Vertex 4 Y-coordinate {m}
    21.760000000000;  !- Vertex 4 Z-coordinate {m}

  Zone,
    B1_F3_LB,  !- Name
    0.0,  !- Direction of Relative North {deg}
    56.265,  !- X Origin {m}
    0.955,  !- Y Origin {m}
    17.17,  !- Z Origin {m}
    ,  !- Type
    1;  !- Multiplier

  BuildingSurface:Detailed,
    F4977A,  !- Name
    Floor,  !- Surface Type
    ADJ_CEILING,  !- Construction Name
    B1_F3_LB,  !- Zone Name
    Zone,  !- Outside Boundary Condition
    B1_F2_CL,  !- Outside Boundary Condition Object
    NoSun,  !- Sun Exposure
    NoWind,  !- Wind Exposure
    ,  !- TRNSYS 17 - additional surface data
    4,  !- Number of Vertices
    12.707103380308,  !- Vertex 1 X-coordinate {m}
    51.818168740863,  !- Vertex 1 Y-coordinate {m}
    17.170000000000,  !- Vertex 1 Z-coordinate {m}
    16.201612885775,  !- Vertex 2 X-coordinate {m}
    11.875742320874,  !- Vertex 2 Y-coordinate {m}
    17.170000000000,  !- Vertex 2 Z-coordinate {m}
    -0.908031053950,  !- Vertex 3 X-coordinate {m}
    10.378842439183,  !- Vertex 3 Y-coordinate {m}
    17.170000000000,  !- Vertex 3 Z-coordinate {m}
    -4.402540559418,  !- Vertex 4 X-coordinate {m}
    50.321268859172,  !- Vertex 4 Y-coordinate {m}
    17.170000000000;  !- Vertex 4 Z-coordinate {m}

  BuildingSurface:Detailed,
    298928,  !- Name
    Ceiling,  !- Surface Type
    ADJ_CEILING,  !- Construction Name
    B1_F3_LB,  !- Zone Name
    Zone,  !- Outside Boundary Condition
    B1_F4_CL,  !- Outside Boundary Condition Object
    NoSun,  !- Sun Exposure
    NoWind,  !- Wind Exposure
    ,  !- TRNSYS 17 - additional surface data
    4,  !- Number of Vertices
    -4.402540559418,  !- Vertex 1 X-coordinate {m}
    50.321268859172,  !- Vertex 1 Y-coordinate {m}
    21.760000000000,  !- Vertex 1 Z-coordinate {m}
    -0.908031053950,  !- Vertex 2 X-coordinate {m}
    10.378842439183,  !- Vertex 2 Y-coordinate {m}
    21.760000000000,  !- Vertex 2 Z-coordinate {m}
    16.201612885775,  !- Vertex 3 X-coordinate {m}
    11.875742320874,  !- Vertex 3 Y-coordinate {m}
    21.760000000000,  !- Vertex 3 Z-coordinate {m}
    12.707103380308,  !- Vertex 4 X-coordinate {m}
    51.818168740863,  !- Vertex 4 Y-coordinate {m}
    21.760000000000;  !- Vertex 4 Z-coordinate {m}

  BuildingSurface:Detailed,
    A5579D,  !- Name
    Wall,  !- Surface Type
    EXT_WALL_SW_EF_RL,  !- Construction Name
    B1_F3_LB,  !- Zone Name
    Outdoors,  !- Outside Boundary Condition
    ,  !- Outside Boundary Condition Object
    SunExposed,  !- Sun Exposure
    WindExposed,  !- Wind Exposure
    ,  !- TRNSYS 17 - additional surface data
    4,  !- Number of Vertices
    -4.402540559418,  !- Vertex 1 X-coordinate {m}
    50.321268859172,  !- Vertex 1 Y-coordinate {m}
    21.760000000000,  !- Vertex 1 Z-coordinate {m}
    -4.402540559418,  !- Vertex 2 X-coordinate {m}
    50.321268859172,  !- Vertex 2 Y-coordinate {m}
    17.170000000000,  !- Vertex 2 Z-coordinate {m}
    -3.888321677206,  !- Vertex 3 X-coordinate {m}
    44.443720140431,  !- Vertex 3 Y-coordinate {m}
    17.170000000000,  !- Vertex 3 Z-coordinate {m}
    -3.888321677206,  !- Vertex 4 X-coordinate {m}
    44.443720140431,  !- Vertex 4 Y-coordinate {m}
    21.760000000000;  !- Vertex 4 Z-coordinate {m}

  BuildingSurface:Detailed,
    ABD3DB,  !- Name
    Wall,  !- Surface Type
    ADJ_WALL,  !- Construction Name
    B1_F3_LB,  !- Zone Name
    Zone,  !- Outside Boundary Condition
    B1_F2_SC,  !- Outside Boundary Condition Object
    NoSun,  !- Sun Exposure
    NoWind,  !- Wind Exposure
    ,  !- TRNSYS 17 - additional surface data
    4,  !- Number of Vertices
    -0.908031053950,  !- Vertex 1 X-coordinate {m}
    10.378842439183,  !- Vertex 1 Y-coordinate {m}
    21.760000000000,  !- Vertex 1 Z-coordinate {m}
    -0.908031053950,  !- Vertex 2 X-coordinate {m}
    10.378842439183,  !- Vertex 2 Y-coordinate {m}
    17.170000000000,  !- Vertex 2 Z-coordinate {m}
    13.893796264487,  !- Vertex 3 X-coordinate {m}
    11.673834529015,  !- Vertex 3 Y-coordinate {m}
    17.170000000000,  !- Vertex 3 Z-coordinate {m}
    13.893796264487,  !- Vertex 4 X-coordinate {m}
    11.673834529015,  !- Vertex 4 Y-coordinate {m}
    21.760000000000;  !- Vertex 4 Z-coordinate {m}

  BuildingSurface:Detailed,
    C576E9,  !- Name
    Wall,  !- Surface Type
    EXT_WALL_IF_RL,  !- Construction Name
    B1_F3_LB,  !- Zone Name
    Outdoors,  !- Outside Boundary Condition
    ,  !- Outside Boundary Condition Object
    SunExposed,  !- Sun Exposure
    WindExposed,  !- Wind Exposure
    ,  !- TRNSYS 17 - additional surface data
    4,  !- Number of Vertices
    13.893796264487,  !- Vertex 1 X-coordinate {m}
    11.673834529015,  !- Vertex 1 Y-coordinate {m}
    21.760000000000,  !- Vertex 1 Z-coordinate {m}
    13.893796264487,  !- Vertex 2 X-coordinate {m}
    11.673834529015,  !- Vertex 2 Y-coordinate {m}
    17.170000000000,  !- Vertex 2 Z-coordinate {m}
    16.201612885775,  !- Vertex 3 X-coordinate {m}
    11.875742320874,  !- Vertex 3 Y-coordinate {m}
    17.170000000000,  !- Vertex 3 Z-coordinate {m}
    16.201612885775,  !- Vertex 4 X-coordinate {m}
    11.875742320874,  !- Vertex 4 Y-coordinate {m}
    21.760000000000;  !- Vertex 4 Z-coordinate {m}

  BuildingSurface:Detailed,
    90F15A,  !- Name
    Wall,  !- Surface Type
    ADJ_WALL,  !- Construction Name
    B1_F3_LB,  !- Zone Name
    Zone,  !- Outside Boundary Condition
    B2_F3_LB,  !- Outside Boundary Condition Object
    NoSun,  !- Sun Exposure
    NoWind,  !- Wind Exposure
    ,  !- TRNSYS 17 - additional surface data
    4,  !- Number of Vertices
    4.070095347853,  !- Vertex 1 X-coordinate {m}
    51.062528451241,  !- Vertex 1 Y-coordinate {m}
    21.760000000000,  !- Vertex 1 Z-coordinate {m}
    4.070095347853,  !- Vertex 2 X-coordinate {m}
    51.062528451241,  !- Vertex 2 Y-coordinate {m}
    17.170000000000,  !- Vertex 2 Z-coordinate {m}
    -4.402540559418,  !- Vertex 3 X-coordinate {m}
    50.321268859172,  !- Vertex 3 Y-coordinate {m}
    17.170000000000,  !- Vertex 3 Z-coordinate {m}
    -4.402540559418,  !- Vertex 4 X-coordinate {m}
    50.321268859172,  !- Vertex 4 Y-coordinate {m}
    21.760000000000;  !- Vertex 4 Z-coordinate {m}

  BuildingSurface:Detailed,
    230544,  !- Name
    Wall,  !- Surface Type
    ADJ_WALL,  !- Construction Name
    B1_F3_LB,  !- Zone Name
    Zone,  !- Outside Boundary Condition
    B2_F3_SC,  !- Outside Boundary Condition Object
    NoSun,  !- Sun Exposure
    NoWind,  !- Wind Exposure
    ,  !- TRNSYS 17 - additional surface data
    4,  !- Number of Vertices
    12.707103380308,  !- Vertex 1 X-coordinate {m}
    51.818168740863,  !- Vertex 1 Y-coordinate {m}
    21.760000000000,  !- Vertex 1 Z-coordinate {m}
    12.707103380308,  !- Vertex 2 X-coordinate {m}
    51.818168740863,  !- Vertex 2 Y-coordinate {m}
    17.170000000000,  !- Vertex 2 Z-coordinate {m}
    4.070095347853,  !- Vertex 3 X-coordinate {m}
    51.062528451241,  !- Vertex 3 Y-coordinate {m}
    17.170000000000,  !- Vertex 3 Z-coordinate {m}
    4.070095347853,  !- Vertex 4 X-coordinate {m}
    51.062528451241,  !- Vertex 4 Y-coordinate {m}
    21.760000000000;  !- Vertex 4 Z-coordinate {m}

  BuildingSurface:Detailed,
    E78E15,  !- Name
    Wall,  !- Surface Type
    EXT_WALL_IF_RL,  !- Construction Name
    B1_F3_LB,  !- Zone Name
    Outdoors,  !- Outside Boundary Condition
    ,  !- Outside Boundary Condition Object
    SunExposed,  !- Sun Exposure
    WindExposed,  !- Wind Exposure
    ,  !- TRNSYS 17 - additional surface data
    4,  !- Number of Vertices
    16.201612885775,  !- Vertex 1 X-coordinate {m}
    11.875742320874,  !- Vertex 1 Y-coordinate {m}
    21.760000000000,  !- Vertex 1 Z-coordinate {m}
    16.201612885775,  !- Vertex 2 X-coordinate {m}
    11.875742320874,  !- Vertex 2 Y-coordinate {m}
    17.170000000000,  !- Vertex 2 Z-coordinate {m}
    12.707103380308,  !- Vertex 3 X-coordinate {m}
    51.818168740863,  !- Vertex 3 Y-coordinate {m}
    17.170000000000,  !- Vertex 3 Z-coordinate {m}
    12.707103380308,  !- Vertex 4 X-coordinate {m}
    51.818168740863,  !- Vertex 4 Y-coordinate {m}
    21.760000000000;  !- Vertex 4 Z-coordinate {m}

  BuildingSurface:Detailed,
    777ED8,  !- Name
    Ceiling,  !- Surface Type
    ADJ_CEILING,  !- Construction Name
    B6_F2_LB,  !- Zone Name
    Zone,  !- Outside Boundary Condition
    B6_F3_LB,  !- Outside Boundary Condition Object
    NoSun,  !- Sun Exposure
    NoWind,  !- Wind Exposure
    ,  !- TRNSYS 17 - additional surface data
    4,  !- Number of Vertices
    62.288489786191,  !- Vertex 1 X-coordinate {m}
    55.689740800071,  !- Vertex 1 Y-coordinate {m}
    17.170000000000,  !- Vertex 1 Z-coordinate {m}
    46.571016269985,  !- Vertex 2 X-coordinate {m}
    23.660480281161,  !- Vertex 2 Y-coordinate {m}
    17.170000000000,  !- Vertex 2 Z-coordinate {m}
    57.793015607234,  !- Vertex 3 X-coordinate {m}
    18.152734289297,  !- Vertex 3 Y-coordinate {m}
    17.170000000000,  !- Vertex 3 Z-coordinate {m}
    73.517257553134,  !- Vertex 4 X-coordinate {m}
    50.190783041650,  !- Vertex 4 Y-coordinate {m}
    17.170000000000;  !- Vertex 4 Z-coordinate {m}

  Zone,
    B6_F3_LB,  !- Name
    0.0,  !- Direction of Relative North {deg}
    56.729463,  !- X Origin {m}
    67.860144,  !- Y Origin {m}
    17.17,  !- Z Origin {m}
    ,  !- Type
    1;  !- Multiplier

  BuildingSurface:Detailed,
    BD59DB,  !- Name
    Floor,  !- Surface Type
    ADJ_CEILING,  !- Construction Name
    B6_F3_LB,  !- Zone Name
    Zone,  !- Outside Boundary Condition
    B6_F2_LB,  !- Outside Boundary Condition Object
    NoSun,  !- Sun Exposure
    NoWind,  !- Wind Exposure
    ,  !- TRNSYS 17 - additional surface data
    4,  !- Number of Vertices
    73.517257553134,  !- Vertex 1 X-coordinate {m}
    50.190783041650,  !- Vertex 1 Y-coordinate {m}
    17.170000000000,  !- Vertex 1 Z-coordinate {m}
    57.793015607234,  !- Vertex 2 X-coordinate {m}
    18.152734289297,  !- Vertex 2 Y-coordinate {m}
    17.170000000000,  !- Vertex 2 Z-coordinate {m}
    46.571016269985,  !- Vertex 3 X-coordinate {m}
    23.660480281161,  !- Vertex 3 Y-coordinate {m}
    17.170000000000,  !- Vertex 3 Z-coordinate {m}
    62.288489505666,  !- Vertex 4 X-coordinate {m}
    55.689741033696,  !- Vertex 4 Y-coordinate {m}
    17.170000000000;  !- Vertex 4 Z-coordinate {m}

  BuildingSurface:Detailed,
    1E46D9,  !- Name
    Wall,  !- Surface Type
    ADJ_WALL,  !- Construction Name
    B6_F3_LB,  !- Zone Name
    OtherSideCoefficients,  !- Outside Boundary Condition
    BOUNDARY=IDENTICAL,  !- Outside Boundary Condition Object
    NoSun,  !- Sun Exposure
    NoWind,  !- Wind Exposure
    0.0,  !- TRNSYS 17 - additional surface data
    4,  !- Number of Vertices
    73.517257553134,  !- Vertex 1 X-coordinate {m}
    50.190783041650,  !- Vertex 1 Y-coordinate {m}
    21.760000000000,  !- Vertex 1 Z-coordinate {m}
    73.517257553134,  !- Vertex 2 X-coordinate {m}
    50.190783041650,  !- Vertex 2 Y-coordinate {m}
    17.170000000000,  !- Vertex 2 Z-coordinate {m}
    62.288489505666,  !- Vertex 3 X-coordinate {m}
    55.689741033696,  !- Vertex 3 Y-coordinate {m}
    17.170000000000,  !- Vertex 3 Z-coordinate {m}
    62.288489505666,  !- Vertex 4 X-coordinate {m}
    55.689741033696,  !- Vertex 4 Y-coordinate {m}
    21.760000000000;  !- Vertex 4 Z-coordinate {m}

  BuildingSurface:Detailed,
    23C9E7,  !- Name
    Ceiling,  !- Surface Type
    ADJ_CEILING,  !- Construction Name
    B6_F3_LB,  !- Zone Name
    Zone,  !- Outside Boundary Condition
    B6_F4_LB,  !- Outside Boundary Condition Object
    NoSun,  !- Sun Exposure
    NoWind,  !- Wind Exposure
    ,  !- TRNSYS 17 - additional surface data
    4,  !- Number of Vertices
    62.288489505666,  !- Vertex 1 X-coordinate {m}
    55.689741033696,  !- Vertex 1 Y-coordinate {m}
    21.760000000000,  !- Vertex 1 Z-coordinate {m}
    46.571016269985,  !- Vertex 2 X-coordinate {m}
    23.660480281161,  !- Vertex 2 Y-coordinate {m}
    21.760000000000,  !- Vertex 2 Z-coordinate {m}
    57.793015607234,  !- Vertex 3 X-coordinate {m}
    18.152734289297,  !- Vertex 3 Y-coordinate {m}
    21.760000000000,  !- Vertex 3 Z-coordinate {m}
    73.517257553134,  !- Vertex 4 X-coordinate {m}
    50.190783041650,  !- Vertex 4 Y-coordinate {m}
    21.760000000000;  !- Vertex 4 Z-coordinate {m}

  BuildingSurface:Detailed,
    EB5B01,  !- Name
    Wall,  !- Surface Type
    EXT_WALL_IF_RL,  !- Construction Name
    B6_F3_LB,  !- Zone Name
    Outdoors,  !- Outside Boundary Condition
    ,  !- Outside Boundary Condition Object
    SunExposed,  !- Sun Exposure
    WindExposed,  !- Wind Exposure
    ,  !- TRNSYS 17 - additional surface data
    4,  !- Number of Vertices
    62.288489505666,  !- Vertex 1 X-coordinate {m}
    55.689741033696,  !- Vertex 1 Y-coordinate {m}
    21.760000000000,  !- Vertex 1 Z-coordinate {m}
    62.288489505666,  !- Vertex 2 X-coordinate {m}
    55.689741033696,  !- Vertex 2 Y-coordinate {m}
    17.170000000000,  !- Vertex 2 Z-coordinate {m}
    46.571016269985,  !- Vertex 3 X-coordinate {m}
    23.660480281161,  !- Vertex 3 Y-coordinate {m}
    17.170000000000,  !- Vertex 3 Z-coordinate {m}
    46.571016269985,  !- Vertex 4 X-coordinate {m}
    23.660480281161,  !- Vertex 4 Y-coordinate {m}
    21.760000000000;  !- Vertex 4 Z-coordinate {m}

  BuildingSurface:Detailed,
    D6F34C,  !- Name
    Wall,  !- Surface Type
    ADJ_WALL,  !- Construction Name
    B6_F3_LB,  !- Zone Name
    Zone,  !- Outside Boundary Condition
    B6_F3_OF,  !- Outside Boundary Condition Object
    NoSun,  !- Sun Exposure
    NoWind,  !- Wind Exposure
    ,  !- TRNSYS 17 - additional surface data
    4,  !- Number of Vertices
    46.571016269985,  !- Vertex 1 X-coordinate {m}
    23.660480281161,  !- Vertex 1 Y-coordinate {m}
    21.760000000000,  !- Vertex 1 Z-coordinate {m}
    46.571016269985,  !- Vertex 2 X-coordinate {m}
    23.660480281161,  !- Vertex 2 Y-coordinate {m}
    17.170000000000,  !- Vertex 2 Z-coordinate {m}
    57.793015607234,  !- Vertex 3 X-coordinate {m}
    18.152734289297,  !- Vertex 3 Y-coordinate {m}
    17.170000000000,  !- Vertex 3 Z-coordinate {m}
    57.793015607234,  !- Vertex 4 X-coordinate {m}
    18.152734289297,  !- Vertex 4 Y-coordinate {m}
    21.760000000000;  !- Vertex 4 Z-coordinate {m}

  BuildingSurface:Detailed,
    545B0F,  !- Name
    Wall,  !- Surface Type
    EXT_WALL_NE_EF_AL,  !- Construction Name
    B6_F3_LB,  !- Zone Name
    Outdoors,  !- Outside Boundary Condition
    ,  !- Outside Boundary Condition Object
    SunExposed,  !- Sun Exposure
    WindExposed,  !- Wind Exposure
    ,  !- TRNSYS 17 - additional surface data
    4,  !- Number of Vertices
    57.793015607234,  !- Vertex 1 X-coordinate {m}
    18.152734289297,  !- Vertex 1 Y-coordinate {m}
    21.760000000000,  !- Vertex 1 Z-coordinate {m}
    57.793015607234,  !- Vertex 2 X-coordinate {m}
    18.152734289297,  !- Vertex 2 Y-coordinate {m}
    17.170000000000,  !- Vertex 2 Z-coordinate {m}
    73.517257553134,  !- Vertex 3 X-coordinate {m}
    50.190783041650,  !- Vertex 3 Y-coordinate {m}
    17.170000000000,  !- Vertex 3 Z-coordinate {m}
    73.517257553134,  !- Vertex 4 X-coordinate {m}
    50.190783041650,  !- Vertex 4 Y-coordinate {m}
    21.760000000000;  !- Vertex 4 Z-coordinate {m}

  Zone,
    B6_F3_OF,  !- Name
    0.0,  !- Direction of Relative North {deg}
    87.266974,  !- X Origin {m}
    49.410946,  !- Y Origin {m}
    17.17,  !- Z Origin {m}
    ,  !- Type
    1;  !- Multiplier

  BuildingSurface:Detailed,
    24CD83,  !- Name
    Floor,  !- Surface Type
    ADJ_CEILING,  !- Construction Name
    B6_F3_OF,  !- Zone Name
    Zone,  !- Outside Boundary Condition
    B6_F2_OF,  !- Outside Boundary Condition Object
    NoSun,  !- Sun Exposure
    NoWind,  !- Wind Exposure
    ,  !- TRNSYS 17 - additional surface data
    4,  !- Number of Vertices
    56.030641432231,  !- Vertex 1 X-coordinate {m}
    14.561907467061,  !- Vertex 1 Y-coordinate {m}
    17.170000000000,  !- Vertex 1 Z-coordinate {m}
    52.505893082225,  !- Vertex 2 X-coordinate {m}
    7.380253822592,  !- Vertex 2 Y-coordinate {m}
    17.170000000000,  !- Vertex 2 Z-coordinate {m}
    41.284559262741,  !- Vertex 3 X-coordinate {m}
    12.887673119476,  !- Vertex 3 Y-coordinate {m}
    17.170000000000,  !- Vertex 3 Z-coordinate {m}
    44.808864203461,  !- Vertex 4 X-coordinate {m}
    20.069544448307,  !- Vertex 4 Y-coordinate {m}
    17.170000000000;  !- Vertex 4 Z-coordinate {m}

  BuildingSurface:Detailed,
    2376E9,  !- Name
    Wall,  !- Surface Type
    ADJ_WALL,  !- Construction Name
    B6_F3_OF,  !- Zone Name
    OtherSideCoefficients,  !- Outside Boundary Condition
    BOUNDARY=IDENTICAL,  !- Outside Boundary Condition Object
    NoSun,  !- Sun Exposure
    NoWind,  !- Wind Exposure
    0.0,  !- TRNSYS 17 - additional surface data
    4,  !- Number of Vertices
    41.284559262741,  !- Vertex 1 X-coordinate {m}
    12.887673119476,  !- Vertex 1 Y-coordinate {m}
    21.760000000000,  !- Vertex 1 Z-coordinate {m}
    41.284559262741,  !- Vertex 2 X-coordinate {m}
    12.887673119476,  !- Vertex 2 Y-coordinate {m}
    17.170000000000,  !- Vertex 2 Z-coordinate {m}
    52.505893082225,  !- Vertex 3 X-coordinate {m}
    7.380253822592,  !- Vertex 3 Y-coordinate {m}
    17.170000000000,  !- Vertex 3 Z-coordinate {m}
    52.505893082225,  !- Vertex 4 X-coordinate {m}
    7.380253822592,  !- Vertex 4 Y-coordinate {m}
    21.760000000000;  !- Vertex 4 Z-coordinate {m}

  BuildingSurface:Detailed,
    5973A4,  !- Name
    Ceiling,  !- Surface Type
    ADJ_CEILING,  !- Construction Name
    B6_F3_OF,  !- Zone Name
    Zone,  !- Outside Boundary Condition
    B6_F4_LB,  !- Outside Boundary Condition Object
    NoSun,  !- Sun Exposure
    NoWind,  !- Wind Exposure
    ,  !- TRNSYS 17 - additional surface data
    4,  !- Number of Vertices
    46.571016269985,  !- Vertex 1 X-coordinate {m}
    23.660480281161,  !- Vertex 1 Y-coordinate {m}
    21.760000000000,  !- Vertex 1 Z-coordinate {m}
    41.284559262741,  !- Vertex 2 X-coordinate {m}
    12.887673119476,  !- Vertex 2 Y-coordinate {m}
    21.760000000000,  !- Vertex 2 Z-coordinate {m}
    52.505893082225,  !- Vertex 3 X-coordinate {m}
    7.380253822592,  !- Vertex 3 Y-coordinate {m}
    21.760000000000,  !- Vertex 3 Z-coordinate {m}
    57.793015607234,  !- Vertex 4 X-coordinate {m}
    18.152734289297,  !- Vertex 4 Y-coordinate {m}
    21.760000000000;  !- Vertex 4 Z-coordinate {m}

  BuildingSurface:Detailed,
    F73EBB,  !- Name
    Wall,  !- Surface Type
    EXT_WALL_IF_RL,  !- Construction Name
    B6_F3_OF,  !- Zone Name
    Outdoors,  !- Outside Boundary Condition
    ,  !- Outside Boundary Condition Object
    SunExposed,  !- Sun Exposure
    WindExposed,  !- Wind Exposure
    ,  !- TRNSYS 17 - additional surface data
    4,  !- Number of Vertices
    46.571016269985,  !- Vertex 1 X-coordinate {m}
    23.660480281161,  !- Vertex 1 Y-coordinate {m}
    21.760000000000,  !- Vertex 1 Z-coordinate {m}
    46.571016269985,  !- Vertex 2 X-coordinate {m}
    23.660480281161,  !- Vertex 2 Y-coordinate {m}
    17.170000000000,  !- Vertex 2 Z-coordinate {m}
    41.284559262741,  !- Vertex 3 X-coordinate {m}
    12.887673119476,  !- Vertex 3 Y-coordinate {m}
    17.170000000000,  !- Vertex 3 Z-coordinate {m}
    41.284559262741,  !- Vertex 4 X-coordinate {m}
    12.887673119476,  !- Vertex 4 Y-coordinate {m}
    21.760000000000;  !- Vertex 4 Z-coordinate {m}

  BuildingSurface:Detailed,
    CB1377,  !- Name
    Wall,  !- Surface Type
    ADJ_WALL,  !- Construction Name
    B6_F3_OF,  !- Zone Name
    Zone,  !- Outside Boundary Condition
    B6_F3_LB,  !- Outside Boundary Condition Object
    NoSun,  !- Sun Exposure
    NoWind,  !- Wind Exposure
    ,  !- TRNSYS 17 - additional surface data
    4,  !- Number of Vertices
    57.793015607234,  !- Vertex 1 X-coordinate {m}
    18.152734289297,  !- Vertex 1 Y-coordinate {m}
    21.760000000000,  !- Vertex 1 Z-coordinate {m}
    57.793015607234,  !- Vertex 2 X-coordinate {m}
    18.152734289297,  !- Vertex 2 Y-coordinate {m}
    17.170000000000,  !- Vertex 2 Z-coordinate {m}
    46.571016269985,  !- Vertex 3 X-coordinate {m}
    23.660480281161,  !- Vertex 3 Y-coordinate {m}
    17.170000000000,  !- Vertex 3 Z-coordinate {m}
    46.571016269985,  !- Vertex 4 X-coordinate {m}
    23.660480281161,  !- Vertex 4 Y-coordinate {m}
    21.760000000000;  !- Vertex 4 Z-coordinate {m}

  BuildingSurface:Detailed,
    8E85EC,  !- Name
    Wall,  !- Surface Type
    EXT_WALL_NE_EF_AL,  !- Construction Name
    B6_F3_OF,  !- Zone Name
    Outdoors,  !- Outside Boundary Condition
    ,  !- Outside Boundary Condition Object
    SunExposed,  !- Sun Exposure
    WindExposed,  !- Wind Exposure
    ,  !- TRNSYS 17 - additional surface data
    4,  !- Number of Vertices
    52.505893082225,  !- Vertex 1 X-coordinate {m}
    7.380253822592,  !- Vertex 1 Y-coordinate {m}
    21.760000000000,  !- Vertex 1 Z-coordinate {m}
    52.505893082225,  !- Vertex 2 X-coordinate {m}
    7.380253822592,  !- Vertex 2 Y-coordinate {m}
    17.170000000000,  !- Vertex 2 Z-coordinate {m}
    57.793015607234,  !- Vertex 3 X-coordinate {m}
    18.152734289297,  !- Vertex 3 Y-coordinate {m}
    17.170000000000,  !- Vertex 3 Z-coordinate {m}
    57.793015607234,  !- Vertex 4 X-coordinate {m}
    18.152734289297,  !- Vertex 4 Y-coordinate {m}
    21.760000000000;  !- Vertex 4 Z-coordinate {m}

  BuildingSurface:Detailed,
    207770,  !- Name
    Floor,  !- Surface Type
    ADJ_CEILING,  !- Construction Name
    B6_F3_OF,  !- Zone Name
    Zone,  !- Outside Boundary Condition
    B6_F2_LB,  !- Outside Boundary Condition Object
    NoSun,  !- Sun Exposure
    NoWind,  !- Wind Exposure
    ,  !- TRNSYS 17 - additional surface data
    4,  !- Number of Vertices
    57.793015607234,  !- Vertex 1 X-coordinate {m}
    18.152734289297,  !- Vertex 1 Y-coordinate {m}
    17.170000000000,  !- Vertex 1 Z-coordinate {m}
    56.030641432231,  !- Vertex 2 X-coordinate {m}
    14.561907467061,  !- Vertex 2 Y-coordinate {m}
    17.170000000000,  !- Vertex 2 Z-coordinate {m}
    44.808864203461,  !- Vertex 3 X-coordinate {m}
    20.069544448307,  !- Vertex 3 Y-coordinate {m}
    17.170000000000,  !- Vertex 3 Z-coordinate {m}
    46.571016269985,  !- Vertex 4 X-coordinate {m}
    23.660480281161,  !- Vertex 4 Y-coordinate {m}
    17.170000000000;  !- Vertex 4 Z-coordinate {m}

  Zone,
    B2_F4_SC,  !- Name
    0.0,  !- Direction of Relative North {deg}
    43.86,  !- X Origin {m}
    9.46,  !- Y Origin {m}
    21.76,  !- Z Origin {m}
    ,  !- Type
    1;  !- Multiplier

  BuildingSurface:Detailed,
    CF6319,  !- Name
    Floor,  !- Surface Type
    ADJ_CEILING,  !- Construction Name
    B2_F4_SC,  !- Zone Name
    Zone,  !- Outside Boundary Condition
    B2_F3_SC,  !- Outside Boundary Condition Object
    NoSun,  !- Sun Exposure
    NoWind,  !- Wind Exposure
    ,  !- TRNSYS 17 - additional surface data
    4,  !- Number of Vertices
    12.582233580160,  !- Vertex 1 X-coordinate {m}
    64.259629133658,  !- Vertex 1 Y-coordinate {m}
    21.760000000000,  !- Vertex 1 Z-coordinate {m}
    13.663400568944,  !- Vertex 2 X-coordinate {m}
    51.901833903830,  !- Vertex 2 Y-coordinate {m}
    21.760000000000,  !- Vertex 2 Z-coordinate {m}
    4.070095347853,  !- Vertex 3 X-coordinate {m}
    51.062528451241,  !- Vertex 3 Y-coordinate {m}
    21.760000000000,  !- Vertex 3 Z-coordinate {m}
    2.988928359068,  !- Vertex 4 X-coordinate {m}
    63.420323681069,  !- Vertex 4 Y-coordinate {m}
    21.760000000000;  !- Vertex 4 Z-coordinate {m}

  BuildingSurface:Detailed,
    6AF848,  !- Name
    Ceiling,  !- Surface Type
    ADJ_CEILING,  !- Construction Name
    B2_F4_SC,  !- Zone Name
    Zone,  !- Outside Boundary Condition
    B2_F5_SC,  !- Outside Boundary Condition Object
    NoSun,  !- Sun Exposure
    NoWind,  !- Wind Exposure
    ,  !- TRNSYS 17 - additional surface data
    4,  !- Number of Vertices
    2.988928359068,  !- Vertex 1 X-coordinate {m}
    63.420323681069,  !- Vertex 1 Y-coordinate {m}
    26.350000000000,  !- Vertex 1 Z-coordinate {m}
    4.070095347853,  !- Vertex 2 X-coordinate {m}
    51.062528451241,  !- Vertex 2 Y-coordinate {m}
    26.350000000000,  !- Vertex 2 Z-coordinate {m}
    13.663400568944,  !- Vertex 3 X-coordinate {m}
    51.901833903830,  !- Vertex 3 Y-coordinate {m}
    26.350000000000,  !- Vertex 3 Z-coordinate {m}
    12.582233580160,  !- Vertex 4 X-coordinate {m}
    64.259629133658,  !- Vertex 4 Y-coordinate {m}
    26.350000000000;  !- Vertex 4 Z-coordinate {m}

  BuildingSurface:Detailed,
    F1FA20,  !- Name
    Wall,  !- Surface Type
    EXT_WALL_IF_RL,  !- Construction Name
    B2_F4_SC,  !- Zone Name
    Outdoors,  !- Outside Boundary Condition
    ,  !- Outside Boundary Condition Object
    SunExposed,  !- Sun Exposure
    WindExposed,  !- Wind Exposure
    ,  !- TRNSYS 17 - additional surface data
    4,  !- Number of Vertices
    12.707103380308,  !- Vertex 1 X-coordinate {m}
    51.818168740863,  !- Vertex 1 Y-coordinate {m}
    26.350000000000,  !- Vertex 1 Z-coordinate {m}
    12.707103380308,  !- Vertex 2 X-coordinate {m}
    51.818168740863,  !- Vertex 2 Y-coordinate {m}
    21.760000000000,  !- Vertex 2 Z-coordinate {m}
    13.663400568944,  !- Vertex 3 X-coordinate {m}
    51.901833903830,  !- Vertex 3 Y-coordinate {m}
    21.760000000000,  !- Vertex 3 Z-coordinate {m}
    13.663400568944,  !- Vertex 4 X-coordinate {m}
    51.901833903830,  !- Vertex 4 Y-coordinate {m}
    26.350000000000;  !- Vertex 4 Z-coordinate {m}

  BuildingSurface:Detailed,
    1C4DEB,  !- Name
    Wall,  !- Surface Type
    ADJ_WALL,  !- Construction Name
    B2_F4_SC,  !- Zone Name
    Zone,  !- Outside Boundary Condition
    B2_F4_CL,  !- Outside Boundary Condition Object
    NoSun,  !- Sun Exposure
    NoWind,  !- Wind Exposure
    ,  !- TRNSYS 17 - additional surface data
    4,  !- Number of Vertices
    2.988928359068,  !- Vertex 1 X-coordinate {m}
    63.420323681069,  !- Vertex 1 Y-coordinate {m}
    26.350000000000,  !- Vertex 1 Z-coordinate {m}
    2.988928359068,  !- Vertex 2 X-coordinate {m}
    63.420323681069,  !- Vertex 2 Y-coordinate {m}
    21.760000000000,  !- Vertex 2 Z-coordinate {m}
    4.070095347853,  !- Vertex 3 X-coordinate {m}
    51.062528451241,  !- Vertex 3 Y-coordinate {m}
    21.760000000000,  !- Vertex 3 Z-coordinate {m}
    4.070095347853,  !- Vertex 4 X-coordinate {m}
    51.062528451241,  !- Vertex 4 Y-coordinate {m}
    26.350000000000;  !- Vertex 4 Z-coordinate {m}

  BuildingSurface:Detailed,
    EDC019,  !- Name
    Wall,  !- Surface Type
    EXT_WALL_NE_EF_AL,  !- Construction Name
    B2_F4_SC,  !- Zone Name
    Outdoors,  !- Outside Boundary Condition
    ,  !- Outside Boundary Condition Object
    SunExposed,  !- Sun Exposure
    WindExposed,  !- Wind Exposure
    ,  !- TRNSYS 17 - additional surface data
    4,  !- Number of Vertices
    12.582233580160,  !- Vertex 1 X-coordinate {m}
    64.259629133658,  !- Vertex 1 Y-coordinate {m}
    26.350000000000,  !- Vertex 1 Z-coordinate {m}
    12.582233580160,  !- Vertex 2 X-coordinate {m}
    64.259629133658,  !- Vertex 2 Y-coordinate {m}
    21.760000000000,  !- Vertex 2 Z-coordinate {m}
    2.988928359068,  !- Vertex 3 X-coordinate {m}
    63.420323681069,  !- Vertex 3 Y-coordinate {m}
    21.760000000000,  !- Vertex 3 Z-coordinate {m}
    2.988928359068,  !- Vertex 4 X-coordinate {m}
    63.420323681069,  !- Vertex 4 Y-coordinate {m}
    26.350000000000;  !- Vertex 4 Z-coordinate {m}

  BuildingSurface:Detailed,
    8972A5,  !- Name
    Wall,  !- Surface Type
    ADJ_WALL,  !- Construction Name
    B2_F4_SC,  !- Zone Name
    Zone,  !- Outside Boundary Condition
    B1_F4_CL,  !- Outside Boundary Condition Object
    NoSun,  !- Sun Exposure
    NoWind,  !- Wind Exposure
    ,  !- TRNSYS 17 - additional surface data
    4,  !- Number of Vertices
    4.070095347853,  !- Vertex 1 X-coordinate {m}
    51.062528451241,  !- Vertex 1 Y-coordinate {m}
    26.350000000000,  !- Vertex 1 Z-coordinate {m}
    4.070095347853,  !- Vertex 2 X-coordinate {m}
    51.062528451241,  !- Vertex 2 Y-coordinate {m}
    21.760000000000,  !- Vertex 2 Z-coordinate {m}
    12.707103380308,  !- Vertex 3 X-coordinate {m}
    51.818168740863,  !- Vertex 3 Y-coordinate {m}
    21.760000000000,  !- Vertex 3 Z-coordinate {m}
    12.707103380308,  !- Vertex 4 X-coordinate {m}
    51.818168740863,  !- Vertex 4 Y-coordinate {m}
    26.350000000000;  !- Vertex 4 Z-coordinate {m}

  BuildingSurface:Detailed,
    2E9111,  !- Name
    Wall,  !- Surface Type
    ADJ_WALL,  !- Construction Name
    B2_F4_SC,  !- Zone Name
    OtherSideCoefficients,  !- Outside Boundary Condition
    BOUNDARY=IDENTICAL,  !- Outside Boundary Condition Object
    NoSun,  !- Sun Exposure
    NoWind,  !- Wind Exposure
    0.0,  !- TRNSYS 17 - additional surface data
    4,  !- Number of Vertices
    13.663400568944,  !- Vertex 1 X-coordinate {m}
    51.901833903830,  !- Vertex 1 Y-coordinate {m}
    26.350000000000,  !- Vertex 1 Z-coordinate {m}
    13.663400568944,  !- Vertex 2 X-coordinate {m}
    51.901833903830,  !- Vertex 2 Y-coordinate {m}
    21.760000000000,  !- Vertex 2 Z-coordinate {m}
    12.582233580160,  !- Vertex 3 X-coordinate {m}
    64.259629133658,  !- Vertex 3 Y-coordinate {m}
    21.760000000000,  !- Vertex 3 Z-coordinate {m}
    12.582233580160,  !- Vertex 4 X-coordinate {m}
    64.259629133658,  !- Vertex 4 Y-coordinate {m}
    26.350000000000;  !- Vertex 4 Z-coordinate {m}

  Zone,
    B2_F4_CL,  !- Name
    0.0,  !- Direction of Relative North {deg}
    39.326026,  !- X Origin {m}
    0.0,  !- Y Origin {m}
    21.76,  !- Z Origin {m}
    ,  !- Type
    1;  !- Multiplier

  BuildingSurface:Detailed,
    A63A83,  !- Name
    Floor,  !- Surface Type
    ADJ_CEILING,  !- Construction Name
    B2_F4_CL,  !- Zone Name
    Zone,  !- Outside Boundary Condition
    B2_F3_LB,  !- Outside Boundary Condition Object
    NoSun,  !- Sun Exposure
    NoWind,  !- Wind Exposure
    ,  !- TRNSYS 17 - additional surface data
    4,  !- Number of Vertices
    2.593766487499,  !- Vertex 1 X-coordinate {m}
    67.937044541155,  !- Vertex 1 Y-coordinate {m}
    21.760000000000,  !- Vertex 1 Z-coordinate {m}
    4.070095347853,  !- Vertex 2 X-coordinate {m}
    51.062528451241,  !- Vertex 2 Y-coordinate {m}
    21.760000000000,  !- Vertex 2 Z-coordinate {m}
    -5.353906496095,  !- Vertex 3 X-coordinate {m}
    50.238035124848,  !- Vertex 3 Y-coordinate {m}
    21.760000000000,  !- Vertex 3 Z-coordinate {m}
    -6.830235356449,  !- Vertex 4 X-coordinate {m}
    67.112551214762,  !- Vertex 4 Y-coordinate {m}
    21.760000000000;  !- Vertex 4 Z-coordinate {m}

  BuildingSurface:Detailed,
    FB4656,  !- Name
    Wall,  !- Surface Type
    ADJ_WALL,  !- Construction Name
    B2_F4_CL,  !- Zone Name
    Zone,  !- Outside Boundary Condition
    B1_F4_CL,  !- Outside Boundary Condition Object
    NoSun,  !- Sun Exposure
    NoWind,  !- Wind Exposure
    ,  !- TRNSYS 17 - additional surface data
    4,  !- Number of Vertices
    -4.402540559418,  !- Vertex 1 X-coordinate {m}
    50.321268859172,  !- Vertex 1 Y-coordinate {m}
    26.350000000000,  !- Vertex 1 Z-coordinate {m}
    -4.402540559418,  !- Vertex 2 X-coordinate {m}
    50.321268859172,  !- Vertex 2 Y-coordinate {m}
    21.760000000000,  !- Vertex 2 Z-coordinate {m}
    4.070095347853,  !- Vertex 3 X-coordinate {m}
    51.062528451241,  !- Vertex 3 Y-coordinate {m}
    21.760000000000,  !- Vertex 3 Z-coordinate {m}
    4.070095347853,  !- Vertex 4 X-coordinate {m}
    51.062528451241,  !- Vertex 4 Y-coordinate {m}
    26.350000000000;  !- Vertex 4 Z-coordinate {m}

  BuildingSurface:Detailed,
    4AC671,  !- Name
    Ceiling,  !- Surface Type
    ADJ_CEILING,  !- Construction Name
    B2_F4_CL,  !- Zone Name
    Zone,  !- Outside Boundary Condition
    B2_F5_OF,  !- Outside Boundary Condition Object
    NoSun,  !- Sun Exposure
    NoWind,  !- Wind Exposure
    ,  !- TRNSYS 17 - additional surface data
    4,  !- Number of Vertices
    -6.830235356449,  !- Vertex 1 X-coordinate {m}
    67.112551214762,  !- Vertex 1 Y-coordinate {m}
    26.350000000000,  !- Vertex 1 Z-coordinate {m}
    -5.353906496095,  !- Vertex 2 X-coordinate {m}
    50.238035124848,  !- Vertex 2 Y-coordinate {m}
    26.350000000000,  !- Vertex 2 Z-coordinate {m}
    4.070095347853,  !- Vertex 3 X-coordinate {m}
    51.062528451241,  !- Vertex 3 Y-coordinate {m}
    26.350000000000,  !- Vertex 3 Z-coordinate {m}
    2.593766487499,  !- Vertex 4 X-coordinate {m}
    67.937044541155,  !- Vertex 4 Y-coordinate {m}
    26.350000000000;  !- Vertex 4 Z-coordinate {m}

  BuildingSurface:Detailed,
    B43CFA,  !- Name
    Wall,  !- Surface Type
    EXT_WALL_SW_EF_RL,  !- Construction Name
    B2_F4_CL,  !- Zone Name
    Outdoors,  !- Outside Boundary Condition
    ,  !- Outside Boundary Condition Object
    SunExposed,  !- Sun Exposure
    WindExposed,  !- Wind Exposure
    ,  !- TRNSYS 17 - additional surface data
    4,  !- Number of Vertices
    -6.830235356449,  !- Vertex 1 X-coordinate {m}
    67.112551214762,  !- Vertex 1 Y-coordinate {m}
    26.350000000000,  !- Vertex 1 Z-coordinate {m}
    -6.830235356449,  !- Vertex 2 X-coordinate {m}
    67.112551214762,  !- Vertex 2 Y-coordinate {m}
    21.760000000000,  !- Vertex 2 Z-coordinate {m}
    -6.660281627363,  !- Vertex 3 X-coordinate {m}
    65.169971202261,  !- Vertex 3 Y-coordinate {m}
    21.760000000000,  !- Vertex 3 Z-coordinate {m}
    -6.660281627363,  !- Vertex 4 X-coordinate {m}
    65.169971202261,  !- Vertex 4 Y-coordinate {m}
    26.350000000000;  !- Vertex 4 Z-coordinate {m}

  BuildingSurface:Detailed,
    D8FC2A,  !- Name
    Wall,  !- Surface Type
    EXT_WALL_SW_EF_RL,  !- Construction Name
    B2_F4_CL,  !- Zone Name
    Outdoors,  !- Outside Boundary Condition
    ,  !- Outside Boundary Condition Object
    SunExposed,  !- Sun Exposure
    WindExposed,  !- Wind Exposure
    ,  !- TRNSYS 17 - additional surface data
    4,  !- Number of Vertices
    -5.353906496095,  !- Vertex 1 X-coordinate {m}
    50.238035124848,  !- Vertex 1 Y-coordinate {m}
    26.350000000000,  !- Vertex 1 Z-coordinate {m}
    -5.353906496095,  !- Vertex 2 X-coordinate {m}
    50.238035124848,  !- Vertex 2 Y-coordinate {m}
    21.760000000000,  !- Vertex 2 Z-coordinate {m}
    -4.402540559418,  !- Vertex 3 X-coordinate {m}
    50.321268859172,  !- Vertex 3 Y-coordinate {m}
    21.760000000000,  !- Vertex 3 Z-coordinate {m}
    -4.402540559418,  !- Vertex 4 X-coordinate {m}
    50.321268859172,  !- Vertex 4 Y-coordinate {m}
    26.350000000000;  !- Vertex 4 Z-coordinate {m}

  BuildingSurface:Detailed,
    45C0F0,  !- Name
    Wall,  !- Surface Type
    EXT_WALL_NE_EF_AL,  !- Construction Name
    B2_F4_CL,  !- Zone Name
    Outdoors,  !- Outside Boundary Condition
    ,  !- Outside Boundary Condition Object
    SunExposed,  !- Sun Exposure
    WindExposed,  !- Wind Exposure
    ,  !- TRNSYS 17 - additional surface data
    4,  !- Number of Vertices
    2.593766487499,  !- Vertex 1 X-coordinate {m}
    67.937044541155,  !- Vertex 1 Y-coordinate {m}
    26.350000000000,  !- Vertex 1 Z-coordinate {m}
    2.593766487499,  !- Vertex 2 X-coordinate {m}
    67.937044541155,  !- Vertex 2 Y-coordinate {m}
    21.760000000000,  !- Vertex 2 Z-coordinate {m}
    -6.830235356449,  !- Vertex 3 X-coordinate {m}
    67.112551214762,  !- Vertex 3 Y-coordinate {m}
    21.760000000000,  !- Vertex 3 Z-coordinate {m}
    -6.830235356449,  !- Vertex 4 X-coordinate {m}
    67.112551214762,  !- Vertex 4 Y-coordinate {m}
    26.350000000000;  !- Vertex 4 Z-coordinate {m}

  BuildingSurface:Detailed,
    E803E3,  !- Name
    Wall,  !- Surface Type
    EXT_WALL_NE_EF_AL,  !- Construction Name
    B2_F4_CL,  !- Zone Name
    Outdoors,  !- Outside Boundary Condition
    ,  !- Outside Boundary Condition Object
    SunExposed,  !- Sun Exposure
    WindExposed,  !- Wind Exposure
    ,  !- TRNSYS 17 - additional surface data
    4,  !- Number of Vertices
    2.988928359068,  !- Vertex 1 X-coordinate {m}
    63.420323681069,  !- Vertex 1 Y-coordinate {m}
    26.350000000000,  !- Vertex 1 Z-coordinate {m}
    2.988928359068,  !- Vertex 2 X-coordinate {m}
    63.420323681069,  !- Vertex 2 Y-coordinate {m}
    21.760000000000,  !- Vertex 2 Z-coordinate {m}
    2.593766487499,  !- Vertex 3 X-coordinate {m}
    67.937044541155,  !- Vertex 3 Y-coordinate {m}
    21.760000000000,  !- Vertex 3 Z-coordinate {m}
    2.593766487499,  !- Vertex 4 X-coordinate {m}
    67.937044541155,  !- Vertex 4 Y-coordinate {m}
    26.350000000000;  !- Vertex 4 Z-coordinate {m}

  BuildingSurface:Detailed,
    6DF82A,  !- Name
    Wall,  !- Surface Type
    ADJ_WALL,  !- Construction Name
    B2_F4_CL,  !- Zone Name
    Zone,  !- Outside Boundary Condition
    B2_F4_SC,  !- Outside Boundary Condition Object
    NoSun,  !- Sun Exposure
    NoWind,  !- Wind Exposure
    ,  !- TRNSYS 17 - additional surface data
    4,  !- Number of Vertices
    4.070095347853,  !- Vertex 1 X-coordinate {m}
    51.062528451241,  !- Vertex 1 Y-coordinate {m}
    26.350000000000,  !- Vertex 1 Z-coordinate {m}
    4.070095347853,  !- Vertex 2 X-coordinate {m}
    51.062528451241,  !- Vertex 2 Y-coordinate {m}
    21.760000000000,  !- Vertex 2 Z-coordinate {m}
    2.988928359068,  !- Vertex 3 X-coordinate {m}
    63.420323681069,  !- Vertex 3 Y-coordinate {m}
    21.760000000000,  !- Vertex 3 Z-coordinate {m}
    2.988928359068,  !- Vertex 4 X-coordinate {m}
    63.420323681069,  !- Vertex 4 Y-coordinate {m}
    26.350000000000;  !- Vertex 4 Z-coordinate {m}

  Zone,
    B1_F4_CL,  !- Name
    0.0,  !- Direction of Relative North {deg}
    56.265,  !- X Origin {m}
    0.955,  !- Y Origin {m}
    21.76,  !- Z Origin {m}
    ,  !- Type
    1;  !- Multiplier

  BuildingSurface:Detailed,
    622B5F,  !- Name
    Floor,  !- Surface Type
    ADJ_CEILING,  !- Construction Name
    B1_F4_CL,  !- Zone Name
    Zone,  !- Outside Boundary Condition
    B1_F3_LB,  !- Outside Boundary Condition Object
    NoSun,  !- Sun Exposure
    NoWind,  !- Wind Exposure
    ,  !- TRNSYS 17 - additional surface data
    4,  !- Number of Vertices
    12.707103380308,  !- Vertex 1 X-coordinate {m}
    51.818168740863,  !- Vertex 1 Y-coordinate {m}
    21.760000000000,  !- Vertex 1 Z-coordinate {m}
    16.201612885775,  !- Vertex 2 X-coordinate {m}
    11.875742320874,  !- Vertex 2 Y-coordinate {m}
    21.760000000000,  !- Vertex 2 Z-coordinate {m}
    -0.908031053950,  !- Vertex 3 X-coordinate {m}
    10.378842439183,  !- Vertex 3 Y-coordinate {m}
    21.760000000000,  !- Vertex 3 Z-coordinate {m}
    -4.402540559418,  !- Vertex 4 X-coordinate {m}
    50.321268859172,  !- Vertex 4 Y-coordinate {m}
    21.760000000000;  !- Vertex 4 Z-coordinate {m}

  BuildingSurface:Detailed,
    BED4D4,  !- Name
    Wall,  !- Surface Type
    EXT_WALL_IF_RL,  !- Construction Name
    B1_F4_CL,  !- Zone Name
    Outdoors,  !- Outside Boundary Condition
    ,  !- Outside Boundary Condition Object
    SunExposed,  !- Sun Exposure
    WindExposed,  !- Wind Exposure
    ,  !- TRNSYS 17 - additional surface data
    4,  !- Number of Vertices
    16.201612885775,  !- Vertex 1 X-coordinate {m}
    11.875742320874,  !- Vertex 1 Y-coordinate {m}
    26.350000000000,  !- Vertex 1 Z-coordinate {m}
    16.201612885775,  !- Vertex 2 X-coordinate {m}
    11.875742320874,  !- Vertex 2 Y-coordinate {m}
    21.760000000000,  !- Vertex 2 Z-coordinate {m}
    12.707103380308,  !- Vertex 3 X-coordinate {m}
    51.818168740863,  !- Vertex 3 Y-coordinate {m}
    21.760000000000,  !- Vertex 3 Z-coordinate {m}
    12.707103380308,  !- Vertex 4 X-coordinate {m}
    51.818168740863,  !- Vertex 4 Y-coordinate {m}
    26.350000000000;  !- Vertex 4 Z-coordinate {m}

  BuildingSurface:Detailed,
    63D283,  !- Name
    Ceiling,  !- Surface Type
    ADJ_CEILING,  !- Construction Name
    B1_F4_CL,  !- Zone Name
    Zone,  !- Outside Boundary Condition
    B1_F5_CL,  !- Outside Boundary Condition Object
    NoSun,  !- Sun Exposure
    NoWind,  !- Wind Exposure
    ,  !- TRNSYS 17 - additional surface data
    4,  !- Number of Vertices
    -4.402540559418,  !- Vertex 1 X-coordinate {m}
    50.321268859172,  !- Vertex 1 Y-coordinate {m}
    26.350000000000,  !- Vertex 1 Z-coordinate {m}
    -0.908031053950,  !- Vertex 2 X-coordinate {m}
    10.378842439183,  !- Vertex 2 Y-coordinate {m}
    26.350000000000,  !- Vertex 2 Z-coordinate {m}
    16.201612885775,  !- Vertex 3 X-coordinate {m}
    11.875742320874,  !- Vertex 3 Y-coordinate {m}
    26.350000000000,  !- Vertex 3 Z-coordinate {m}
    12.707103380308,  !- Vertex 4 X-coordinate {m}
    51.818168740863,  !- Vertex 4 Y-coordinate {m}
    26.350000000000;  !- Vertex 4 Z-coordinate {m}

  BuildingSurface:Detailed,
    507FE5,  !- Name
    Wall,  !- Surface Type
    EXT_WALL_SW_EF_RL,  !- Construction Name
    B1_F4_CL,  !- Zone Name
    Outdoors,  !- Outside Boundary Condition
    ,  !- Outside Boundary Condition Object
    SunExposed,  !- Sun Exposure
    WindExposed,  !- Wind Exposure
    ,  !- TRNSYS 17 - additional surface data
    4,  !- Number of Vertices
    -4.402540559418,  !- Vertex 1 X-coordinate {m}
    50.321268859172,  !- Vertex 1 Y-coordinate {m}
    26.350000000000,  !- Vertex 1 Z-coordinate {m}
    -4.402540559418,  !- Vertex 2 X-coordinate {m}
    50.321268859172,  !- Vertex 2 Y-coordinate {m}
    21.760000000000,  !- Vertex 2 Z-coordinate {m}
    -3.888321677206,  !- Vertex 3 X-coordinate {m}
    44.443720140431,  !- Vertex 3 Y-coordinate {m}
    21.760000000000,  !- Vertex 3 Z-coordinate {m}
    -3.888321677206,  !- Vertex 4 X-coordinate {m}
    44.443720140431,  !- Vertex 4 Y-coordinate {m}
    26.350000000000;  !- Vertex 4 Z-coordinate {m}

  BuildingSurface:Detailed,
    14B158,  !- Name
    Wall,  !- Surface Type
    EXT_WALL_IF_RL,  !- Construction Name
    B1_F4_CL,  !- Zone Name
    Outdoors,  !- Outside Boundary Condition
    ,  !- Outside Boundary Condition Object
    SunExposed,  !- Sun Exposure
    WindExposed,  !- Wind Exposure
    ,  !- TRNSYS 17 - additional surface data
    4,  !- Number of Vertices
    13.893796264487,  !- Vertex 1 X-coordinate {m}
    11.673834529015,  !- Vertex 1 Y-coordinate {m}
    26.350000000000,  !- Vertex 1 Z-coordinate {m}
    13.893796264487,  !- Vertex 2 X-coordinate {m}
    11.673834529015,  !- Vertex 2 Y-coordinate {m}
    21.760000000000,  !- Vertex 2 Z-coordinate {m}
    16.201612885775,  !- Vertex 3 X-coordinate {m}
    11.875742320874,  !- Vertex 3 Y-coordinate {m}
    21.760000000000,  !- Vertex 3 Z-coordinate {m}
    16.201612885775,  !- Vertex 4 X-coordinate {m}
    11.875742320874,  !- Vertex 4 Y-coordinate {m}
    26.350000000000;  !- Vertex 4 Z-coordinate {m}

  BuildingSurface:Detailed,
    95C5BC,  !- Name
    Wall,  !- Surface Type
    ADJ_WALL,  !- Construction Name
    B1_F4_CL,  !- Zone Name
    Zone,  !- Outside Boundary Condition
    B2_F4_CL,  !- Outside Boundary Condition Object
    NoSun,  !- Sun Exposure
    NoWind,  !- Wind Exposure
    ,  !- TRNSYS 17 - additional surface data
    4,  !- Number of Vertices
    4.070095347853,  !- Vertex 1 X-coordinate {m}
    51.062528451241,  !- Vertex 1 Y-coordinate {m}
    26.350000000000,  !- Vertex 1 Z-coordinate {m}
    4.070095347853,  !- Vertex 2 X-coordinate {m}
    51.062528451241,  !- Vertex 2 Y-coordinate {m}
    21.760000000000,  !- Vertex 2 Z-coordinate {m}
    -4.402540559418,  !- Vertex 3 X-coordinate {m}
    50.321268859172,  !- Vertex 3 Y-coordinate {m}
    21.760000000000,  !- Vertex 3 Z-coordinate {m}
    -4.402540559418,  !- Vertex 4 X-coordinate {m}
    50.321268859172,  !- Vertex 4 Y-coordinate {m}
    26.350000000000;  !- Vertex 4 Z-coordinate {m}

  BuildingSurface:Detailed,
    A43E06,  !- Name
    Wall,  !- Surface Type
    ADJ_WALL,  !- Construction Name
    B1_F4_CL,  !- Zone Name
    Zone,  !- Outside Boundary Condition
    B1_F4_SC,  !- Outside Boundary Condition Object
    NoSun,  !- Sun Exposure
    NoWind,  !- Wind Exposure
    ,  !- TRNSYS 17 - additional surface data
    4,  !- Number of Vertices
    -0.908031053950,  !- Vertex 1 X-coordinate {m}
    10.378842439183,  !- Vertex 1 Y-coordinate {m}
    26.350000000000,  !- Vertex 1 Z-coordinate {m}
    -0.908031053950,  !- Vertex 2 X-coordinate {m}
    10.378842439183,  !- Vertex 2 Y-coordinate {m}
    21.760000000000,  !- Vertex 2 Z-coordinate {m}
    13.893796264487,  !- Vertex 3 X-coordinate {m}
    11.673834529015,  !- Vertex 3 Y-coordinate {m}
    21.760000000000,  !- Vertex 3 Z-coordinate {m}
    13.893796264487,  !- Vertex 4 X-coordinate {m}
    11.673834529015,  !- Vertex 4 Y-coordinate {m}
    26.350000000000;  !- Vertex 4 Z-coordinate {m}

  BuildingSurface:Detailed,
    46EC59,  !- Name
    Wall,  !- Surface Type
    ADJ_WALL,  !- Construction Name
    B1_F4_CL,  !- Zone Name
    Zone,  !- Outside Boundary Condition
    B2_F4_SC,  !- Outside Boundary Condition Object
    NoSun,  !- Sun Exposure
    NoWind,  !- Wind Exposure
    ,  !- TRNSYS 17 - additional surface data
    4,  !- Number of Vertices
    12.707103380308,  !- Vertex 1 X-coordinate {m}
    51.818168740863,  !- Vertex 1 Y-coordinate {m}
    26.350000000000,  !- Vertex 1 Z-coordinate {m}
    12.707103380308,  !- Vertex 2 X-coordinate {m}
    51.818168740863,  !- Vertex 2 Y-coordinate {m}
    21.760000000000,  !- Vertex 2 Z-coordinate {m}
    4.070095347853,  !- Vertex 3 X-coordinate {m}
    51.062528451241,  !- Vertex 3 Y-coordinate {m}
    21.760000000000,  !- Vertex 3 Z-coordinate {m}
    4.070095347853,  !- Vertex 4 X-coordinate {m}
    51.062528451241,  !- Vertex 4 Y-coordinate {m}
    26.350000000000;  !- Vertex 4 Z-coordinate {m}

  Zone,
    B1_F4_SC,  !- Name
    0.0,  !- Direction of Relative North {deg}
    96.36,  !- X Origin {m}
    0.955,  !- Y Origin {m}
    21.76,  !- Z Origin {m}
    ,  !- Type
    1;  !- Multiplier

  BuildingSurface:Detailed,
    2D74C1,  !- Name
    Floor,  !- Surface Type
    ADJ_CEILING,  !- Construction Name
    B1_F4_SC,  !- Zone Name
    Zone,  !- Outside Boundary Condition
    B1_F2_SC,  !- Outside Boundary Condition Object
    NoSun,  !- Sun Exposure
    NoWind,  !- Wind Exposure
    ,  !- TRNSYS 17 - additional surface data
    4,  !- Number of Vertices
    13.893796264487,  !- Vertex 1 X-coordinate {m}
    11.673834529015,  !- Vertex 1 Y-coordinate {m}
    21.760000000000,  !- Vertex 1 Z-coordinate {m}
    11.024619423024,  !- Vertex 2 X-coordinate {m}
    -2.268709539582,  !- Vertex 2 Y-coordinate {m}
    21.760000000000,  !- Vertex 2 Z-coordinate {m}
    0.000000000000,  !- Vertex 3 X-coordinate {m}
    0.000000000000,  !- Vertex 3 Y-coordinate {m}
    21.760000000000,  !- Vertex 3 Z-coordinate {m}
    -0.908031053950,  !- Vertex 4 X-coordinate {m}
    10.378842439183,  !- Vertex 4 Y-coordinate {m}
    21.760000000000;  !- Vertex 4 Z-coordinate {m}

  BuildingSurface:Detailed,
    93C87D,  !- Name
    Roof,  !- Surface Type
    EXT_ROOF_SR,  !- Construction Name
    B1_F4_SC,  !- Zone Name
    Outdoors,  !- Outside Boundary Condition
    ,  !- Outside Boundary Condition Object
    SunExposed,  !- Sun Exposure
    WindExposed,  !- Wind Exposure
    ,  !- TRNSYS 17 - additional surface data
    4,  !- Number of Vertices
    -0.908031053950,  !- Vertex 1 X-coordinate {m}
    10.378842439183,  !- Vertex 1 Y-coordinate {m}
    30.940000000000,  !- Vertex 1 Z-coordinate {m}
    0.000000000000,  !- Vertex 2 X-coordinate {m}
    0.000000000000,  !- Vertex 2 Y-coordinate {m}
    30.940000000000,  !- Vertex 2 Z-coordinate {m}
    11.024619423024,  !- Vertex 3 X-coordinate {m}
    -2.268709539582,  !- Vertex 3 Y-coordinate {m}
    30.940000000000,  !- Vertex 3 Z-coordinate {m}
    13.893796264487,  !- Vertex 4 X-coordinate {m}
    11.673834529015,  !- Vertex 4 Y-coordinate {m}
    30.940000000000;  !- Vertex 4 Z-coordinate {m}

  BuildingSurface:Detailed,
    139156,  !- Name
    Wall,  !- Surface Type
    ADJ_WALL,  !- Construction Name
    B1_F4_SC,  !- Zone Name
    OtherSideCoefficients,  !- Outside Boundary Condition
    BOUNDARY=IDENTICAL,  !- Outside Boundary Condition Object
    NoSun,  !- Sun Exposure
    NoWind,  !- Wind Exposure
    0.0,  !- TRNSYS 17 - additional surface data
    4,  !- Number of Vertices
    11.024619423024,  !- Vertex 1 X-coordinate {m}
    -2.268709539582,  !- Vertex 1 Y-coordinate {m}
    30.940000000000,  !- Vertex 1 Z-coordinate {m}
    11.024619423024,  !- Vertex 2 X-coordinate {m}
    -2.268709539582,  !- Vertex 2 Y-coordinate {m}
    21.760000000000,  !- Vertex 2 Z-coordinate {m}
    13.313760665876,  !- Vertex 3 X-coordinate {m}
    8.855196326266,  !- Vertex 3 Y-coordinate {m}
    21.760000000000,  !- Vertex 3 Z-coordinate {m}
    13.313760665876,  !- Vertex 4 X-coordinate {m}
    8.855196326266,  !- Vertex 4 Y-coordinate {m}
    30.940000000000;  !- Vertex 4 Z-coordinate {m}

  BuildingSurface:Detailed,
    E2D9E7,  !- Name
    Wall,  !- Surface Type
    EXT_WALL_SW_EF_RL,  !- Construction Name
    B1_F4_SC,  !- Zone Name
    Outdoors,  !- Outside Boundary Condition
    ,  !- Outside Boundary Condition Object
    SunExposed,  !- Sun Exposure
    WindExposed,  !- Wind Exposure
    ,  !- TRNSYS 17 - additional surface data
    4,  !- Number of Vertices
    -0.592963043918,  !- Vertex 1 X-coordinate {m}
    6.777598605582,  !- Vertex 1 Y-coordinate {m}
    30.940000000000,  !- Vertex 1 Z-coordinate {m}
    -0.592963043918,  !- Vertex 2 X-coordinate {m}
    6.777598605582,  !- Vertex 2 Y-coordinate {m}
    21.760000000000,  !- Vertex 2 Z-coordinate {m}
    0.000000000000,  !- Vertex 3 X-coordinate {m}
    0.000000000000,  !- Vertex 3 Y-coordinate {m}
    21.760000000000,  !- Vertex 3 Z-coordinate {m}
    0.000000000000,  !- Vertex 4 X-coordinate {m}
    0.000000000000,  !- Vertex 4 Y-coordinate {m}
    30.940000000000;  !- Vertex 4 Z-coordinate {m}

  BuildingSurface:Detailed,
    809397,  !- Name
    Wall,  !- Surface Type
    EXT_WALL_SW_EF_GL,  !- Construction Name
    B1_F4_SC,  !- Zone Name
    Outdoors,  !- Outside Boundary Condition
    ,  !- Outside Boundary Condition Object
    SunExposed,  !- Sun Exposure
    WindExposed,  !- Wind Exposure
    ,  !- TRNSYS 17 - additional surface data
    4,  !- Number of Vertices
    7.772760005483,  !- Vertex 1 X-coordinate {m}
    -1.599523221318,  !- Vertex 1 Y-coordinate {m}
    26.350000000000,  !- Vertex 1 Z-coordinate {m}
    7.772760005483,  !- Vertex 2 X-coordinate {m}
    -1.599523221318,  !- Vertex 2 Y-coordinate {m}
    21.760000000000,  !- Vertex 2 Z-coordinate {m}
    11.024619423024,  !- Vertex 3 X-coordinate {m}
    -2.268709539582,  !- Vertex 3 Y-coordinate {m}
    21.760000000000,  !- Vertex 3 Z-coordinate {m}
    11.024619423024,  !- Vertex 4 X-coordinate {m}
    -2.268709539582,  !- Vertex 4 Y-coordinate {m}
    26.350000000000;  !- Vertex 4 Z-coordinate {m}

  BuildingSurface:Detailed,
    9BD55D,  !- Name
    Wall,  !- Surface Type
    ADJ_WALL,  !- Construction Name
    B1_F4_SC,  !- Zone Name
    Zone,  !- Outside Boundary Condition
    B1_F5_CL,  !- Outside Boundary Condition Object
    NoSun,  !- Sun Exposure
    NoWind,  !- Wind Exposure
    ,  !- TRNSYS 17 - additional surface data
    4,  !- Number of Vertices
    13.893796264487,  !- Vertex 1 X-coordinate {m}
    11.673834529015,  !- Vertex 1 Y-coordinate {m}
    30.940000000000,  !- Vertex 1 Z-coordinate {m}
    13.893796264487,  !- Vertex 2 X-coordinate {m}
    11.673834529015,  !- Vertex 2 Y-coordinate {m}
    26.350000000000,  !- Vertex 2 Z-coordinate {m}
    -0.908031053950,  !- Vertex 3 X-coordinate {m}
    10.378842439183,  !- Vertex 3 Y-coordinate {m}
    26.350000000000,  !- Vertex 3 Z-coordinate {m}
    -0.908031053950,  !- Vertex 4 X-coordinate {m}
    10.378842439183,  !- Vertex 4 Y-coordinate {m}
    30.940000000000;  !- Vertex 4 Z-coordinate {m}

  BuildingSurface:Detailed,
    52F178,  !- Name
    Wall,  !- Surface Type
    EXT_WALL_IF_RL,  !- Construction Name
    B1_F4_SC,  !- Zone Name
    Outdoors,  !- Outside Boundary Condition
    ,  !- Outside Boundary Condition Object
    SunExposed,  !- Sun Exposure
    WindExposed,  !- Wind Exposure
    ,  !- TRNSYS 17 - additional surface data
    4,  !- Number of Vertices
    13.313760665876,  !- Vertex 1 X-coordinate {m}
    8.855196326266,  !- Vertex 1 Y-coordinate {m}
    30.940000000000,  !- Vertex 1 Z-coordinate {m}
    13.313760665876,  !- Vertex 2 X-coordinate {m}
    8.855196326266,  !- Vertex 2 Y-coordinate {m}
    21.760000000000,  !- Vertex 2 Z-coordinate {m}
    13.893796264487,  !- Vertex 3 X-coordinate {m}
    11.673834529015,  !- Vertex 3 Y-coordinate {m}
    21.760000000000,  !- Vertex 3 Z-coordinate {m}
    13.893796264487,  !- Vertex 4 X-coordinate {m}
    11.673834529015,  !- Vertex 4 Y-coordinate {m}
    30.940000000000;  !- Vertex 4 Z-coordinate {m}

  Zone,
    B6_F4_LB,  !- Name
    0.0,  !- Direction of Relative North {deg}
    56.729463,  !- X Origin {m}
    67.860144,  !- Y Origin {m}
    21.76,  !- Z Origin {m}
    ,  !- Type
    1;  !- Multiplier

  BuildingSurface:Detailed,
    E402BF,  !- Name
    Floor,  !- Surface Type
    ADJ_CEILING,  !- Construction Name
    B6_F4_LB,  !- Zone Name
    Zone,  !- Outside Boundary Condition
    B6_F3_OF,  !- Outside Boundary Condition Object
    NoSun,  !- Sun Exposure
    NoWind,  !- Wind Exposure
    ,  !- TRNSYS 17 - additional surface data
    4,  !- Number of Vertices
    57.793015607234,  !- Vertex 1 X-coordinate {m}
    18.152734289297,  !- Vertex 1 Y-coordinate {m}
    21.760000000000,  !- Vertex 1 Z-coordinate {m}
    52.505893082225,  !- Vertex 2 X-coordinate {m}
    7.380253822592,  !- Vertex 2 Y-coordinate {m}
    21.760000000000,  !- Vertex 2 Z-coordinate {m}
    41.284559262741,  !- Vertex 3 X-coordinate {m}
    12.887673119476,  !- Vertex 3 Y-coordinate {m}
    21.760000000000,  !- Vertex 3 Z-coordinate {m}
    46.571016269985,  !- Vertex 4 X-coordinate {m}
    23.660480281161,  !- Vertex 4 Y-coordinate {m}
    21.760000000000;  !- Vertex 4 Z-coordinate {m}

  BuildingSurface:Detailed,
    631840,  !- Name
    Roof,  !- Surface Type
    EXT_ROOF_SR,  !- Construction Name
    B6_F4_LB,  !- Zone Name
    Outdoors,  !- Outside Boundary Condition
    ,  !- Outside Boundary Condition Object
    SunExposed,  !- Sun Exposure
    WindExposed,  !- Wind Exposure
    ,  !- TRNSYS 17 - additional surface data
    4,  !- Number of Vertices
    62.288489786191,  !- Vertex 1 X-coordinate {m}
    55.689740800071,  !- Vertex 1 Y-coordinate {m}
    26.350000000000,  !- Vertex 1 Z-coordinate {m}
    41.284559262741,  !- Vertex 2 X-coordinate {m}
    12.887673119476,  !- Vertex 2 Y-coordinate {m}
    26.350000000000,  !- Vertex 2 Z-coordinate {m}
    52.505893082225,  !- Vertex 3 X-coordinate {m}
    7.380253822592,  !- Vertex 3 Y-coordinate {m}
    26.350000000000,  !- Vertex 3 Z-coordinate {m}
    73.517257553134,  !- Vertex 4 X-coordinate {m}
    50.190783041650,  !- Vertex 4 Y-coordinate {m}
    26.350000000000;  !- Vertex 4 Z-coordinate {m}

  BuildingSurface:Detailed,
    F1D81E,  !- Name
    Wall,  !- Surface Type
    EXT_WALL_IF_RL,  !- Construction Name
    B6_F4_LB,  !- Zone Name
    Outdoors,  !- Outside Boundary Condition
    ,  !- Outside Boundary Condition Object
    SunExposed,  !- Sun Exposure
    WindExposed,  !- Wind Exposure
    ,  !- TRNSYS 17 - additional surface data
    4,  !- Number of Vertices
    62.288489786191,  !- Vertex 1 X-coordinate {m}
    55.689740800071,  !- Vertex 1 Y-coordinate {m}
    26.350000000000,  !- Vertex 1 Z-coordinate {m}
    62.288489786191,  !- Vertex 2 X-coordinate {m}
    55.689740800071,  !- Vertex 2 Y-coordinate {m}
    21.760000000000,  !- Vertex 2 Z-coordinate {m}
    41.284559262741,  !- Vertex 3 X-coordinate {m}
    12.887673119476,  !- Vertex 3 Y-coordinate {m}
    21.760000000000,  !- Vertex 3 Z-coordinate {m}
    41.284559262741,  !- Vertex 4 X-coordinate {m}
    12.887673119476,  !- Vertex 4 Y-coordinate {m}
    26.350000000000;  !- Vertex 4 Z-coordinate {m}

  BuildingSurface:Detailed,
    605E6B,  !- Name
    Wall,  !- Surface Type
    ADJ_WALL,  !- Construction Name
    B6_F4_LB,  !- Zone Name
    OtherSideCoefficients,  !- Outside Boundary Condition
    BOUNDARY=IDENTICAL,  !- Outside Boundary Condition Object
    NoSun,  !- Sun Exposure
    NoWind,  !- Wind Exposure
    0.0,  !- TRNSYS 17 - additional surface data
    4,  !- Number of Vertices
    41.284559262741,  !- Vertex 1 X-coordinate {m}
    12.887673119476,  !- Vertex 1 Y-coordinate {m}
    26.350000000000,  !- Vertex 1 Z-coordinate {m}
    41.284559262741,  !- Vertex 2 X-coordinate {m}
    12.887673119476,  !- Vertex 2 Y-coordinate {m}
    21.760000000000,  !- Vertex 2 Z-coordinate {m}
    52.505893082225,  !- Vertex 3 X-coordinate {m}
    7.380253822592,  !- Vertex 3 Y-coordinate {m}
    21.760000000000,  !- Vertex 3 Z-coordinate {m}
    52.505893082225,  !- Vertex 4 X-coordinate {m}
    7.380253822592,  !- Vertex 4 Y-coordinate {m}
    26.350000000000;  !- Vertex 4 Z-coordinate {m}

  BuildingSurface:Detailed,
    9D348B,  !- Name
    Wall,  !- Surface Type
    ADJ_WALL,  !- Construction Name
    B6_F4_LB,  !- Zone Name
    OtherSideCoefficients,  !- Outside Boundary Condition
    BOUNDARY=IDENTICAL,  !- Outside Boundary Condition Object
    NoSun,  !- Sun Exposure
    NoWind,  !- Wind Exposure
    0.0,  !- TRNSYS 17 - additional surface data
    4,  !- Number of Vertices
    73.517257553134,  !- Vertex 1 X-coordinate {m}
    50.190783041650,  !- Vertex 1 Y-coordinate {m}
    26.350000000000,  !- Vertex 1 Z-coordinate {m}
    73.517257553134,  !- Vertex 2 X-coordinate {m}
    50.190783041650,  !- Vertex 2 Y-coordinate {m}
    21.760000000000,  !- Vertex 2 Z-coordinate {m}
    62.288489786191,  !- Vertex 3 X-coordinate {m}
    55.689740800071,  !- Vertex 3 Y-coordinate {m}
    21.760000000000,  !- Vertex 3 Z-coordinate {m}
    62.288489786191,  !- Vertex 4 X-coordinate {m}
    55.689740800071,  !- Vertex 4 Y-coordinate {m}
    26.350000000000;  !- Vertex 4 Z-coordinate {m}

  BuildingSurface:Detailed,
    82AE15,  !- Name
    Wall,  !- Surface Type
    EXT_WALL_NE_EF_AL,  !- Construction Name
    B6_F4_LB,  !- Zone Name
    Outdoors,  !- Outside Boundary Condition
    ,  !- Outside Boundary Condition Object
    SunExposed,  !- Sun Exposure
    WindExposed,  !- Wind Exposure
    ,  !- TRNSYS 17 - additional surface data
    4,  !- Number of Vertices
    52.505893082225,  !- Vertex 1 X-coordinate {m}
    7.380253822592,  !- Vertex 1 Y-coordinate {m}
    26.350000000000,  !- Vertex 1 Z-coordinate {m}
    52.505893082225,  !- Vertex 2 X-coordinate {m}
    7.380253822592,  !- Vertex 2 Y-coordinate {m}
    21.760000000000,  !- Vertex 2 Z-coordinate {m}
    73.517257553134,  !- Vertex 3 X-coordinate {m}
    50.190783041650,  !- Vertex 3 Y-coordinate {m}
    21.760000000000,  !- Vertex 3 Z-coordinate {m}
    73.517257553134,  !- Vertex 4 X-coordinate {m}
    50.190783041650,  !- Vertex 4 Y-coordinate {m}
    26.350000000000;  !- Vertex 4 Z-coordinate {m}

  BuildingSurface:Detailed,
    25717A,  !- Name
    Floor,  !- Surface Type
    ADJ_CEILING,  !- Construction Name
    B6_F4_LB,  !- Zone Name
    Zone,  !- Outside Boundary Condition
    B6_F3_LB,  !- Outside Boundary Condition Object
    NoSun,  !- Sun Exposure
    NoWind,  !- Wind Exposure
    ,  !- TRNSYS 17 - additional surface data
    4,  !- Number of Vertices
    73.517257553134,  !- Vertex 1 X-coordinate {m}
    50.190783041650,  !- Vertex 1 Y-coordinate {m}
    21.760000000000,  !- Vertex 1 Z-coordinate {m}
    57.793015607234,  !- Vertex 2 X-coordinate {m}
    18.152734289297,  !- Vertex 2 Y-coordinate {m}
    21.760000000000,  !- Vertex 2 Z-coordinate {m}
    46.571016269985,  !- Vertex 3 X-coordinate {m}
    23.660480281161,  !- Vertex 3 Y-coordinate {m}
    21.760000000000,  !- Vertex 3 Z-coordinate {m}
    62.288489786191,  !- Vertex 4 X-coordinate {m}
    55.689740800071,  !- Vertex 4 Y-coordinate {m}
    21.760000000000;  !- Vertex 4 Z-coordinate {m}

  BuildingSurface:Detailed,
    AFB758,  !- Name
    Wall,  !- Surface Type
    ADJ_WALL,  !- Construction Name
    B1_F4_SC,  !- Zone Name
    Zone,  !- Outside Boundary Condition
    B1_F4_CL,  !- Outside Boundary Condition Object
    NoSun,  !- Sun Exposure
    NoWind,  !- Wind Exposure
    ,  !- TRNSYS 17 - additional surface data
    4,  !- Number of Vertices
    13.893796264487,  !- Vertex 1 X-coordinate {m}
    11.673834529015,  !- Vertex 1 Y-coordinate {m}
    26.350000000000,  !- Vertex 1 Z-coordinate {m}
    13.893796264487,  !- Vertex 2 X-coordinate {m}
    11.673834529015,  !- Vertex 2 Y-coordinate {m}
    21.760000000000,  !- Vertex 2 Z-coordinate {m}
    -0.908031053950,  !- Vertex 3 X-coordinate {m}
    10.378842439183,  !- Vertex 3 Y-coordinate {m}
    21.760000000000,  !- Vertex 3 Z-coordinate {m}
    -0.908031053950,  !- Vertex 4 X-coordinate {m}
    10.378842439183,  !- Vertex 4 Y-coordinate {m}
    26.350000000000;  !- Vertex 4 Z-coordinate {m}

  Zone,
    B2_F5_SC,  !- Name
    0.0,  !- Direction of Relative North {deg}
    43.86,  !- X Origin {m}
    9.46,  !- Y Origin {m}
    26.35,  !- Z Origin {m}
    ,  !- Type
    1;  !- Multiplier

  BuildingSurface:Detailed,
    F98215,  !- Name
    Floor,  !- Surface Type
    ADJ_CEILING,  !- Construction Name
    B2_F5_SC,  !- Zone Name
    Zone,  !- Outside Boundary Condition
    B2_F4_SC,  !- Outside Boundary Condition Object
    NoSun,  !- Sun Exposure
    NoWind,  !- Wind Exposure
    ,  !- TRNSYS 17 - additional surface data
    4,  !- Number of Vertices
    12.582233580160,  !- Vertex 1 X-coordinate {m}
    64.259629133658,  !- Vertex 1 Y-coordinate {m}
    26.350000000000,  !- Vertex 1 Z-coordinate {m}
    13.663400568944,  !- Vertex 2 X-coordinate {m}
    51.901833903830,  !- Vertex 2 Y-coordinate {m}
    26.350000000000,  !- Vertex 2 Z-coordinate {m}
    4.070095347853,  !- Vertex 3 X-coordinate {m}
    51.062528451241,  !- Vertex 3 Y-coordinate {m}
    26.350000000000,  !- Vertex 3 Z-coordinate {m}
    2.988928359068,  !- Vertex 4 X-coordinate {m}
    63.420323681069,  !- Vertex 4 Y-coordinate {m}
    26.350000000000;  !- Vertex 4 Z-coordinate {m}

  BuildingSurface:Detailed,
    B632D9,  !- Name
    Roof,  !- Surface Type
    EXT_ROOF_SR,  !- Construction Name
    B2_F5_SC,  !- Zone Name
    Outdoors,  !- Outside Boundary Condition
    ,  !- Outside Boundary Condition Object
    SunExposed,  !- Sun Exposure
    WindExposed,  !- Wind Exposure
    ,  !- TRNSYS 17 - additional surface data
    4,  !- Number of Vertices
    2.988928359068,  !- Vertex 1 X-coordinate {m}
    63.420323681069,  !- Vertex 1 Y-coordinate {m}
    30.940000000000,  !- Vertex 1 Z-coordinate {m}
    4.070095347853,  !- Vertex 2 X-coordinate {m}
    51.062528451241,  !- Vertex 2 Y-coordinate {m}
    30.940000000000,  !- Vertex 2 Z-coordinate {m}
    13.663400568944,  !- Vertex 3 X-coordinate {m}
    51.901833903830,  !- Vertex 3 Y-coordinate {m}
    30.940000000000,  !- Vertex 3 Z-coordinate {m}
    12.582233580160,  !- Vertex 4 X-coordinate {m}
    64.259629133658,  !- Vertex 4 Y-coordinate {m}
    30.940000000000;  !- Vertex 4 Z-coordinate {m}

  BuildingSurface:Detailed,
    555450,  !- Name
    Wall,  !- Surface Type
    ADJ_WALL,  !- Construction Name
    B2_F5_SC,  !- Zone Name
    Zone,  !- Outside Boundary Condition
    B2_F5_OF,  !- Outside Boundary Condition Object
    NoSun,  !- Sun Exposure
    NoWind,  !- Wind Exposure
    ,  !- TRNSYS 17 - additional surface data
    4,  !- Number of Vertices
    2.988928359068,  !- Vertex 1 X-coordinate {m}
    63.420323681069,  !- Vertex 1 Y-coordinate {m}
    30.940000000000,  !- Vertex 1 Z-coordinate {m}
    2.988928359068,  !- Vertex 2 X-coordinate {m}
    63.420323681069,  !- Vertex 2 Y-coordinate {m}
    26.350000000000,  !- Vertex 2 Z-coordinate {m}
    4.070095347853,  !- Vertex 3 X-coordinate {m}
    51.062528451241,  !- Vertex 3 Y-coordinate {m}
    26.350000000000,  !- Vertex 3 Z-coordinate {m}
    4.070095347853,  !- Vertex 4 X-coordinate {m}
    51.062528451241,  !- Vertex 4 Y-coordinate {m}
    30.940000000000;  !- Vertex 4 Z-coordinate {m}

  BuildingSurface:Detailed,
    55D449,  !- Name
    Wall,  !- Surface Type
    EXT_WALL_NE_EF_AL,  !- Construction Name
    B2_F5_SC,  !- Zone Name
    Outdoors,  !- Outside Boundary Condition
    ,  !- Outside Boundary Condition Object
    SunExposed,  !- Sun Exposure
    WindExposed,  !- Wind Exposure
    ,  !- TRNSYS 17 - additional surface data
    4,  !- Number of Vertices
    12.582233580160,  !- Vertex 1 X-coordinate {m}
    64.259629133658,  !- Vertex 1 Y-coordinate {m}
    30.940000000000,  !- Vertex 1 Z-coordinate {m}
    12.582233580160,  !- Vertex 2 X-coordinate {m}
    64.259629133658,  !- Vertex 2 Y-coordinate {m}
    26.350000000000,  !- Vertex 2 Z-coordinate {m}
    2.988928359068,  !- Vertex 3 X-coordinate {m}
    63.420323681069,  !- Vertex 3 Y-coordinate {m}
    26.350000000000,  !- Vertex 3 Z-coordinate {m}
    2.988928359068,  !- Vertex 4 X-coordinate {m}
    63.420323681069,  !- Vertex 4 Y-coordinate {m}
    30.940000000000;  !- Vertex 4 Z-coordinate {m}

  BuildingSurface:Detailed,
    FCB14A,  !- Name
    Wall,  !- Surface Type
    ADJ_WALL,  !- Construction Name
    B2_F5_SC,  !- Zone Name
    Zone,  !- Outside Boundary Condition
    B1_F5_CL,  !- Outside Boundary Condition Object
    NoSun,  !- Sun Exposure
    NoWind,  !- Wind Exposure
    ,  !- TRNSYS 17 - additional surface data
    4,  !- Number of Vertices
    4.070095347853,  !- Vertex 1 X-coordinate {m}
    51.062528451241,  !- Vertex 1 Y-coordinate {m}
    30.940000000000,  !- Vertex 1 Z-coordinate {m}
    4.070095347853,  !- Vertex 2 X-coordinate {m}
    51.062528451241,  !- Vertex 2 Y-coordinate {m}
    26.350000000000,  !- Vertex 2 Z-coordinate {m}
    12.707103380308,  !- Vertex 3 X-coordinate {m}
    51.818168740863,  !- Vertex 3 Y-coordinate {m}
    26.350000000000,  !- Vertex 3 Z-coordinate {m}
    12.707103380308,  !- Vertex 4 X-coordinate {m}
    51.818168740863,  !- Vertex 4 Y-coordinate {m}
    30.940000000000;  !- Vertex 4 Z-coordinate {m}

  BuildingSurface:Detailed,
    82C51D,  !- Name
    Wall,  !- Surface Type
    EXT_WALL_IF_RL,  !- Construction Name
    B2_F5_SC,  !- Zone Name
    Outdoors,  !- Outside Boundary Condition
    ,  !- Outside Boundary Condition Object
    SunExposed,  !- Sun Exposure
    WindExposed,  !- Wind Exposure
    ,  !- TRNSYS 17 - additional surface data
    4,  !- Number of Vertices
    12.707103380308,  !- Vertex 1 X-coordinate {m}
    51.818168740863,  !- Vertex 1 Y-coordinate {m}
    30.940000000000,  !- Vertex 1 Z-coordinate {m}
    12.707103380308,  !- Vertex 2 X-coordinate {m}
    51.818168740863,  !- Vertex 2 Y-coordinate {m}
    26.350000000000,  !- Vertex 2 Z-coordinate {m}
    13.663400568944,  !- Vertex 3 X-coordinate {m}
    51.901833903830,  !- Vertex 3 Y-coordinate {m}
    26.350000000000,  !- Vertex 3 Z-coordinate {m}
    13.663400568944,  !- Vertex 4 X-coordinate {m}
    51.901833903830,  !- Vertex 4 Y-coordinate {m}
    30.940000000000;  !- Vertex 4 Z-coordinate {m}

  BuildingSurface:Detailed,
    188307,  !- Name
    Wall,  !- Surface Type
    ADJ_WALL,  !- Construction Name
    B2_F5_SC,  !- Zone Name
    OtherSideCoefficients,  !- Outside Boundary Condition
    BOUNDARY=IDENTICAL,  !- Outside Boundary Condition Object
    NoSun,  !- Sun Exposure
    NoWind,  !- Wind Exposure
    0.0,  !- TRNSYS 17 - additional surface data
    4,  !- Number of Vertices
    13.663400568944,  !- Vertex 1 X-coordinate {m}
    51.901833903830,  !- Vertex 1 Y-coordinate {m}
    30.940000000000,  !- Vertex 1 Z-coordinate {m}
    13.663400568944,  !- Vertex 2 X-coordinate {m}
    51.901833903830,  !- Vertex 2 Y-coordinate {m}
    26.350000000000,  !- Vertex 2 Z-coordinate {m}
    12.582233580160,  !- Vertex 3 X-coordinate {m}
    64.259629133658,  !- Vertex 3 Y-coordinate {m}
    26.350000000000,  !- Vertex 3 Z-coordinate {m}
    12.582233580160,  !- Vertex 4 X-coordinate {m}
    64.259629133658,  !- Vertex 4 Y-coordinate {m}
    30.940000000000;  !- Vertex 4 Z-coordinate {m}

  Zone,
    B2_F5_OF,  !- Name
    0.0,  !- Direction of Relative North {deg}
    39.326026,  !- X Origin {m}
    0.0,  !- Y Origin {m}
    26.35,  !- Z Origin {m}
    ,  !- Type
    1;  !- Multiplier

  BuildingSurface:Detailed,
    F6B9F8,  !- Name
    Floor,  !- Surface Type
    ADJ_CEILING,  !- Construction Name
    B2_F5_OF,  !- Zone Name
    Zone,  !- Outside Boundary Condition
    B2_F4_CL,  !- Outside Boundary Condition Object
    NoSun,  !- Sun Exposure
    NoWind,  !- Wind Exposure
    ,  !- TRNSYS 17 - additional surface data
    4,  !- Number of Vertices
    2.593766487499,  !- Vertex 1 X-coordinate {m}
    67.937044541155,  !- Vertex 1 Y-coordinate {m}
    26.350000000000,  !- Vertex 1 Z-coordinate {m}
    4.070095347853,  !- Vertex 2 X-coordinate {m}
    51.062528451241,  !- Vertex 2 Y-coordinate {m}
    26.350000000000,  !- Vertex 2 Z-coordinate {m}
    -5.353906496095,  !- Vertex 3 X-coordinate {m}
    50.238035124848,  !- Vertex 3 Y-coordinate {m}
    26.350000000000,  !- Vertex 3 Z-coordinate {m}
    -6.830235356449,  !- Vertex 4 X-coordinate {m}
    67.112551214762,  !- Vertex 4 Y-coordinate {m}
    26.350000000000;  !- Vertex 4 Z-coordinate {m}

  BuildingSurface:Detailed,
    87BBAE,  !- Name
    Wall,  !- Surface Type
    EXT_WALL_SW_EF_RL,  !- Construction Name
    B2_F5_OF,  !- Zone Name
    Outdoors,  !- Outside Boundary Condition
    ,  !- Outside Boundary Condition Object
    SunExposed,  !- Sun Exposure
    WindExposed,  !- Wind Exposure
    ,  !- TRNSYS 17 - additional surface data
    4,  !- Number of Vertices
    -5.523860194453,  !- Vertex 1 X-coordinate {m}
    52.180614786127,  !- Vertex 1 Y-coordinate {m}
    30.940000000000,  !- Vertex 1 Z-coordinate {m}
    -5.523860194453,  !- Vertex 2 X-coordinate {m}
    52.180614786127,  !- Vertex 2 Y-coordinate {m}
    26.350000000000,  !- Vertex 2 Z-coordinate {m}
    -5.353906496095,  !- Vertex 3 X-coordinate {m}
    50.238035124848,  !- Vertex 3 Y-coordinate {m}
    26.350000000000,  !- Vertex 3 Z-coordinate {m}
    -5.353906496095,  !- Vertex 4 X-coordinate {m}
    50.238035124848,  !- Vertex 4 Y-coordinate {m}
    30.940000000000;  !- Vertex 4 Z-coordinate {m}

  BuildingSurface:Detailed,
    BE6E2F,  !- Name
    Roof,  !- Surface Type
    EXT_ROOF_SR,  !- Construction Name
    B2_F5_OF,  !- Zone Name
    Outdoors,  !- Outside Boundary Condition
    ,  !- Outside Boundary Condition Object
    SunExposed,  !- Sun Exposure
    WindExposed,  !- Wind Exposure
    ,  !- TRNSYS 17 - additional surface data
    4,  !- Number of Vertices
    -6.830235356449,  !- Vertex 1 X-coordinate {m}
    67.112551214762,  !- Vertex 1 Y-coordinate {m}
    30.940000000000,  !- Vertex 1 Z-coordinate {m}
    -5.353906496095,  !- Vertex 2 X-coordinate {m}
    50.238035124848,  !- Vertex 2 Y-coordinate {m}
    30.940000000000,  !- Vertex 2 Z-coordinate {m}
    4.070095347853,  !- Vertex 3 X-coordinate {m}
    51.062528451241,  !- Vertex 3 Y-coordinate {m}
    30.940000000000,  !- Vertex 3 Z-coordinate {m}
    2.593766487499,  !- Vertex 4 X-coordinate {m}
    67.937044541155,  !- Vertex 4 Y-coordinate {m}
    30.940000000000;  !- Vertex 4 Z-coordinate {m}

  BuildingSurface:Detailed,
    D5CE6D,  !- Name
    Wall,  !- Surface Type
    EXT_WALL_NE_EF_AL,  !- Construction Name
    B2_F5_OF,  !- Zone Name
    Outdoors,  !- Outside Boundary Condition
    ,  !- Outside Boundary Condition Object
    SunExposed,  !- Sun Exposure
    WindExposed,  !- Wind Exposure
    ,  !- TRNSYS 17 - additional surface data
    4,  !- Number of Vertices
    2.988928359068,  !- Vertex 1 X-coordinate {m}
    63.420323681069,  !- Vertex 1 Y-coordinate {m}
    30.940000000000,  !- Vertex 1 Z-coordinate {m}
    2.988928359068,  !- Vertex 2 X-coordinate {m}
    63.420323681069,  !- Vertex 2 Y-coordinate {m}
    26.350000000000,  !- Vertex 2 Z-coordinate {m}
    2.593766487499,  !- Vertex 3 X-coordinate {m}
    67.937044541155,  !- Vertex 3 Y-coordinate {m}
    26.350000000000,  !- Vertex 3 Z-coordinate {m}
    2.593766487499,  !- Vertex 4 X-coordinate {m}
    67.937044541155,  !- Vertex 4 Y-coordinate {m}
    30.940000000000;  !- Vertex 4 Z-coordinate {m}

  BuildingSurface:Detailed,
    432105,  !- Name
    Wall,  !- Surface Type
    EXT_WALL_NE_EF_AL,  !- Construction Name
    B2_F5_OF,  !- Zone Name
    Outdoors,  !- Outside Boundary Condition
    ,  !- Outside Boundary Condition Object
    SunExposed,  !- Sun Exposure
    WindExposed,  !- Wind Exposure
    ,  !- TRNSYS 17 - additional surface data
    4,  !- Number of Vertices
    2.593766487499,  !- Vertex 1 X-coordinate {m}
    67.937044541155,  !- Vertex 1 Y-coordinate {m}
    30.940000000000,  !- Vertex 1 Z-coordinate {m}
    2.593766487499,  !- Vertex 2 X-coordinate {m}
    67.937044541155,  !- Vertex 2 Y-coordinate {m}
    26.350000000000,  !- Vertex 2 Z-coordinate {m}
    -6.830235356449,  !- Vertex 3 X-coordinate {m}
    67.112551214762,  !- Vertex 3 Y-coordinate {m}
    26.350000000000,  !- Vertex 3 Z-coordinate {m}
    -6.830235356449,  !- Vertex 4 X-coordinate {m}
    67.112551214762,  !- Vertex 4 Y-coordinate {m}
    30.940000000000;  !- Vertex 4 Z-coordinate {m}

  BuildingSurface:Detailed,
    6396E2,  !- Name
    Wall,  !- Surface Type
    EXT_WALL_SW_EF_RL,  !- Construction Name
    B2_F5_OF,  !- Zone Name
    Outdoors,  !- Outside Boundary Condition
    ,  !- Outside Boundary Condition Object
    SunExposed,  !- Sun Exposure
    WindExposed,  !- Wind Exposure
    ,  !- TRNSYS 17 - additional surface data
    4,  !- Number of Vertices
    -5.353906496095,  !- Vertex 1 X-coordinate {m}
    50.238035124848,  !- Vertex 1 Y-coordinate {m}
    30.940000000000,  !- Vertex 1 Z-coordinate {m}
    -5.353906496095,  !- Vertex 2 X-coordinate {m}
    50.238035124848,  !- Vertex 2 Y-coordinate {m}
    26.350000000000,  !- Vertex 2 Z-coordinate {m}
    -4.402540559418,  !- Vertex 3 X-coordinate {m}
    50.321268859172,  !- Vertex 3 Y-coordinate {m}
    26.350000000000,  !- Vertex 3 Z-coordinate {m}
    -4.402540559418,  !- Vertex 4 X-coordinate {m}
    50.321268859172,  !- Vertex 4 Y-coordinate {m}
    30.940000000000;  !- Vertex 4 Z-coordinate {m}

  BuildingSurface:Detailed,
    7BBF55,  !- Name
    Wall,  !- Surface Type
    ADJ_WALL,  !- Construction Name
    B2_F5_OF,  !- Zone Name
    Zone,  !- Outside Boundary Condition
    B1_F5_CL,  !- Outside Boundary Condition Object
    NoSun,  !- Sun Exposure
    NoWind,  !- Wind Exposure
    ,  !- TRNSYS 17 - additional surface data
    4,  !- Number of Vertices
    -4.402540559418,  !- Vertex 1 X-coordinate {m}
    50.321268859172,  !- Vertex 1 Y-coordinate {m}
    30.940000000000,  !- Vertex 1 Z-coordinate {m}
    -4.402540559418,  !- Vertex 2 X-coordinate {m}
    50.321268859172,  !- Vertex 2 Y-coordinate {m}
    26.350000000000,  !- Vertex 2 Z-coordinate {m}
    4.070095347853,  !- Vertex 3 X-coordinate {m}
    51.062528451241,  !- Vertex 3 Y-coordinate {m}
    26.350000000000,  !- Vertex 3 Z-coordinate {m}
    4.070095347853,  !- Vertex 4 X-coordinate {m}
    51.062528451241,  !- Vertex 4 Y-coordinate {m}
    30.940000000000;  !- Vertex 4 Z-coordinate {m}

  BuildingSurface:Detailed,
    EF63C8,  !- Name
    Wall,  !- Surface Type
    ADJ_WALL,  !- Construction Name
    B2_F5_OF,  !- Zone Name
    Zone,  !- Outside Boundary Condition
    B2_F5_SC,  !- Outside Boundary Condition Object
    NoSun,  !- Sun Exposure
    NoWind,  !- Wind Exposure
    ,  !- TRNSYS 17 - additional surface data
    4,  !- Number of Vertices
    4.070095347853,  !- Vertex 1 X-coordinate {m}
    51.062528451241,  !- Vertex 1 Y-coordinate {m}
    30.940000000000,  !- Vertex 1 Z-coordinate {m}
    4.070095347853,  !- Vertex 2 X-coordinate {m}
    51.062528451241,  !- Vertex 2 Y-coordinate {m}
    26.350000000000,  !- Vertex 2 Z-coordinate {m}
    2.988928359068,  !- Vertex 3 X-coordinate {m}
    63.420323681069,  !- Vertex 3 Y-coordinate {m}
    26.350000000000,  !- Vertex 3 Z-coordinate {m}
    2.988928359068,  !- Vertex 4 X-coordinate {m}
    63.420323681069,  !- Vertex 4 Y-coordinate {m}
    30.940000000000;  !- Vertex 4 Z-coordinate {m}

  Zone,
    B1_F5_CL,  !- Name
    0.0,  !- Direction of Relative North {deg}
    56.265,  !- X Origin {m}
    0.955,  !- Y Origin {m}
    26.35,  !- Z Origin {m}
    ,  !- Type
    1;  !- Multiplier

  BuildingSurface:Detailed,
    794287,  !- Name
    Floor,  !- Surface Type
    ADJ_CEILING,  !- Construction Name
    B1_F5_CL,  !- Zone Name
    Zone,  !- Outside Boundary Condition
    B1_F4_CL,  !- Outside Boundary Condition Object
    NoSun,  !- Sun Exposure
    NoWind,  !- Wind Exposure
    ,  !- TRNSYS 17 - additional surface data
    4,  !- Number of Vertices
    12.707103380308,  !- Vertex 1 X-coordinate {m}
    51.818168740863,  !- Vertex 1 Y-coordinate {m}
    26.350000000000,  !- Vertex 1 Z-coordinate {m}
    16.201612885775,  !- Vertex 2 X-coordinate {m}
    11.875742320874,  !- Vertex 2 Y-coordinate {m}
    26.350000000000,  !- Vertex 2 Z-coordinate {m}
    -0.908031053950,  !- Vertex 3 X-coordinate {m}
    10.378842439183,  !- Vertex 3 Y-coordinate {m}
    26.350000000000,  !- Vertex 3 Z-coordinate {m}
    -4.402540559418,  !- Vertex 4 X-coordinate {m}
    50.321268859172,  !- Vertex 4 Y-coordinate {m}
    26.350000000000;  !- Vertex 4 Z-coordinate {m}

  BuildingSurface:Detailed,
    4A6C0B,  !- Name
    Roof,  !- Surface Type
    EXT_ROOF_SR,  !- Construction Name
    B1_F5_CL,  !- Zone Name
    Outdoors,  !- Outside Boundary Condition
    ,  !- Outside Boundary Condition Object
    SunExposed,  !- Sun Exposure
    WindExposed,  !- Wind Exposure
    ,  !- TRNSYS 17 - additional surface data
    4,  !- Number of Vertices
    -4.402540559418,  !- Vertex 1 X-coordinate {m}
    50.321268859172,  !- Vertex 1 Y-coordinate {m}
    30.940000000000,  !- Vertex 1 Z-coordinate {m}
    -0.908031053950,  !- Vertex 2 X-coordinate {m}
    10.378842439183,  !- Vertex 2 Y-coordinate {m}
    30.940000000000,  !- Vertex 2 Z-coordinate {m}
    16.201612885775,  !- Vertex 3 X-coordinate {m}
    11.875742320874,  !- Vertex 3 Y-coordinate {m}
    30.940000000000,  !- Vertex 3 Z-coordinate {m}
    12.707103380308,  !- Vertex 4 X-coordinate {m}
    51.818168740863,  !- Vertex 4 Y-coordinate {m}
    30.940000000000;  !- Vertex 4 Z-coordinate {m}

  BuildingSurface:Detailed,
    F87805,  !- Name
    Wall,  !- Surface Type
    EXT_WALL_IF_RL,  !- Construction Name
    B1_F5_CL,  !- Zone Name
    Outdoors,  !- Outside Boundary Condition
    ,  !- Outside Boundary Condition Object
    SunExposed,  !- Sun Exposure
    WindExposed,  !- Wind Exposure
    ,  !- TRNSYS 17 - additional surface data
    4,  !- Number of Vertices
    16.201612885775,  !- Vertex 1 X-coordinate {m}
    11.875742320874,  !- Vertex 1 Y-coordinate {m}
    30.940000000000,  !- Vertex 1 Z-coordinate {m}
    16.201612885775,  !- Vertex 2 X-coordinate {m}
    11.875742320874,  !- Vertex 2 Y-coordinate {m}
    26.350000000000,  !- Vertex 2 Z-coordinate {m}
    12.707103380308,  !- Vertex 3 X-coordinate {m}
    51.818168740863,  !- Vertex 3 Y-coordinate {m}
    26.350000000000,  !- Vertex 3 Z-coordinate {m}
    12.707103380308,  !- Vertex 4 X-coordinate {m}
    51.818168740863,  !- Vertex 4 Y-coordinate {m}
    30.940000000000;  !- Vertex 4 Z-coordinate {m}

  BuildingSurface:Detailed,
    DECBF0,  !- Name
    Wall,  !- Surface Type
    EXT_WALL_SW_EF_GL,  !- Construction Name
    B1_F5_CL,  !- Zone Name
    Outdoors,  !- Outside Boundary Condition
    ,  !- Outside Boundary Condition Object
    SunExposed,  !- Sun Exposure
    WindExposed,  !- Wind Exposure
    ,  !- TRNSYS 17 - additional surface data
    4,  !- Number of Vertices
    -3.888321677206,  !- Vertex 1 X-coordinate {m}
    44.443720140431,  !- Vertex 1 Y-coordinate {m}
    30.940000000000,  !- Vertex 1 Z-coordinate {m}
    -3.888321677206,  !- Vertex 2 X-coordinate {m}
    44.443720140431,  !- Vertex 2 Y-coordinate {m}
    26.350000000000,  !- Vertex 2 Z-coordinate {m}
    -0.908031053950,  !- Vertex 3 X-coordinate {m}
    10.378842439183,  !- Vertex 3 Y-coordinate {m}
    26.350000000000,  !- Vertex 3 Z-coordinate {m}
    -0.908031053950,  !- Vertex 4 X-coordinate {m}
    10.378842439183,  !- Vertex 4 Y-coordinate {m}
    30.940000000000;  !- Vertex 4 Z-coordinate {m}

  BuildingSurface:Detailed,
    5D6CC0,  !- Name
    Wall,  !- Surface Type
    EXT_WALL_IF_RL,  !- Construction Name
    B1_F5_CL,  !- Zone Name
    Outdoors,  !- Outside Boundary Condition
    ,  !- Outside Boundary Condition Object
    SunExposed,  !- Sun Exposure
    WindExposed,  !- Wind Exposure
    ,  !- TRNSYS 17 - additional surface data
    4,  !- Number of Vertices
    13.893796264487,  !- Vertex 1 X-coordinate {m}
    11.673834529015,  !- Vertex 1 Y-coordinate {m}
    30.940000000000,  !- Vertex 1 Z-coordinate {m}
    13.893796264487,  !- Vertex 2 X-coordinate {m}
    11.673834529015,  !- Vertex 2 Y-coordinate {m}
    26.350000000000,  !- Vertex 2 Z-coordinate {m}
    16.201612885775,  !- Vertex 3 X-coordinate {m}
    11.875742320874,  !- Vertex 3 Y-coordinate {m}
    26.350000000000,  !- Vertex 3 Z-coordinate {m}
    16.201612885775,  !- Vertex 4 X-coordinate {m}
    11.875742320874,  !- Vertex 4 Y-coordinate {m}
    30.940000000000;  !- Vertex 4 Z-coordinate {m}

  BuildingSurface:Detailed,
    7DD381,  !- Name
    Wall,  !- Surface Type
    ADJ_WALL,  !- Construction Name
    B1_F5_CL,  !- Zone Name
    Zone,  !- Outside Boundary Condition
    B2_F5_OF,  !- Outside Boundary Condition Object
    NoSun,  !- Sun Exposure
    NoWind,  !- Wind Exposure
    ,  !- TRNSYS 17 - additional surface data
    4,  !- Number of Vertices
    4.070095347853,  !- Vertex 1 X-coordinate {m}
    51.062528451241,  !- Vertex 1 Y-coordinate {m}
    30.940000000000,  !- Vertex 1 Z-coordinate {m}
    4.070095347853,  !- Vertex 2 X-coordinate {m}
    51.062528451241,  !- Vertex 2 Y-coordinate {m}
    26.350000000000,  !- Vertex 2 Z-coordinate {m}
    -4.402540559418,  !- Vertex 3 X-coordinate {m}
    50.321268859172,  !- Vertex 3 Y-coordinate {m}
    26.350000000000,  !- Vertex 3 Z-coordinate {m}
    -4.402540559418,  !- Vertex 4 X-coordinate {m}
    50.321268859172,  !- Vertex 4 Y-coordinate {m}
    30.940000000000;  !- Vertex 4 Z-coordinate {m}

  BuildingSurface:Detailed,
    11AFA7,  !- Name
    Wall,  !- Surface Type
    ADJ_WALL,  !- Construction Name
    B1_F5_CL,  !- Zone Name
    Zone,  !- Outside Boundary Condition
    B1_F4_SC,  !- Outside Boundary Condition Object
    NoSun,  !- Sun Exposure
    NoWind,  !- Wind Exposure
    ,  !- TRNSYS 17 - additional surface data
    4,  !- Number of Vertices
    -0.908031053950,  !- Vertex 1 X-coordinate {m}
    10.378842439183,  !- Vertex 1 Y-coordinate {m}
    30.940000000000,  !- Vertex 1 Z-coordinate {m}
    -0.908031053950,  !- Vertex 2 X-coordinate {m}
    10.378842439183,  !- Vertex 2 Y-coordinate {m}
    26.350000000000,  !- Vertex 2 Z-coordinate {m}
    13.893796264487,  !- Vertex 3 X-coordinate {m}
    11.673834529015,  !- Vertex 3 Y-coordinate {m}
    26.350000000000,  !- Vertex 3 Z-coordinate {m}
    13.893796264487,  !- Vertex 4 X-coordinate {m}
    11.673834529015,  !- Vertex 4 Y-coordinate {m}
    30.940000000000;  !- Vertex 4 Z-coordinate {m}

  BuildingSurface:Detailed,
    24117D,  !- Name
    Wall,  !- Surface Type
    ADJ_WALL,  !- Construction Name
    B1_F5_CL,  !- Zone Name
    Zone,  !- Outside Boundary Condition
    B2_F5_SC,  !- Outside Boundary Condition Object
    NoSun,  !- Sun Exposure
    NoWind,  !- Wind Exposure
    ,  !- TRNSYS 17 - additional surface data
    4,  !- Number of Vertices
    12.707103380308,  !- Vertex 1 X-coordinate {m}
    51.818168740863,  !- Vertex 1 Y-coordinate {m}
    30.940000000000,  !- Vertex 1 Z-coordinate {m}
    12.707103380308,  !- Vertex 2 X-coordinate {m}
    51.818168740863,  !- Vertex 2 Y-coordinate {m}
    26.350000000000,  !- Vertex 2 Z-coordinate {m}
    4.070095347853,  !- Vertex 3 X-coordinate {m}
    51.062528451241,  !- Vertex 3 Y-coordinate {m}
    26.350000000000,  !- Vertex 3 Z-coordinate {m}
    4.070095347853,  !- Vertex 4 X-coordinate {m}
    51.062528451241,  !- Vertex 4 Y-coordinate {m}
    30.940000000000;  !- Vertex 4 Z-coordinate {m}

  FenestrationSurface:Detailed,
    6A73F8,  !- Name
    Window,  !- Surface Type
    EXT_WINDOW_DG,  !- Construction Name
    ED4000,  !- Building Surface Name
    ,  !- Outside Boundary Condition Object
    ,  !- TRNSYS 17 - additional surface data
    ,  !- Shading Control Name
    ,  !- Frame and Divider Name
    ,  !- Multiplier
    4,  !- Number of Vertices
    -6.655923840226,  !- Vertex 1 X-coordinate {m}
    65.120161467357,  !- Vertex 1 Y-coordinate {m}
    30.150000000000,  !- Vertex 1 Z-coordinate {m}
    -6.655923840226,  !- Vertex 2 X-coordinate {m}
    65.120161467357,  !- Vertex 2 Y-coordinate {m}
    27.150000000000,  !- Vertex 2 Z-coordinate {m}
    -5.528217981590,  !- Vertex 3 X-coordinate {m}
    52.230424521031,  !- Vertex 3 Y-coordinate {m}
    27.150000000000,  !- Vertex 3 Z-coordinate {m}
    -5.528217981590,  !- Vertex 4 X-coordinate {m}
    52.230424521031,  !- Vertex 4 Y-coordinate {m}
    30.150000000000;  !- Vertex 4 Z-coordinate {m}

  FenestrationSurface:Detailed,
    726ECC,  !- Name
    Window,  !- Surface Type
    EXT_WINDOW_DG,  !- Construction Name
    FC7733,  !- Building Surface Name
    ,  !- Outside Boundary Condition Object
    ,  !- TRNSYS 17 - additional surface data
    ,  !- Shading Control Name
    ,  !- Frame and Divider Name
    ,  !- Multiplier
    4,  !- Number of Vertices
    -6.655923840226,  !- Vertex 1 X-coordinate {m}
    65.120161467357,  !- Vertex 1 Y-coordinate {m}
    25.560000000000,  !- Vertex 1 Z-coordinate {m}
    -6.655923840226,  !- Vertex 2 X-coordinate {m}
    65.120161467357,  !- Vertex 2 Y-coordinate {m}
    22.560000000000,  !- Vertex 2 Z-coordinate {m}
    -5.528217981590,  !- Vertex 3 X-coordinate {m}
    52.230424521031,  !- Vertex 3 Y-coordinate {m}
    22.560000000000,  !- Vertex 3 Z-coordinate {m}
    -5.528217981590,  !- Vertex 4 X-coordinate {m}
    52.230424521031,  !- Vertex 4 Y-coordinate {m}
    25.560000000000;  !- Vertex 4 Z-coordinate {m}

  FenestrationSurface:Detailed,
    A33B41,  !- Name
    Window,  !- Surface Type
    EXT_WINDOW_DG,  !- Construction Name
    ADCA2B,  !- Building Surface Name
    ,  !- Outside Boundary Condition Object
    ,  !- TRNSYS 17 - additional surface data
    ,  !- Shading Control Name
    ,  !- Frame and Divider Name
    ,  !- Multiplier
    4,  !- Number of Vertices
    -6.655923840226,  !- Vertex 1 X-coordinate {m}
    65.120161467357,  !- Vertex 1 Y-coordinate {m}
    20.970000000000,  !- Vertex 1 Z-coordinate {m}
    -6.655923840226,  !- Vertex 2 X-coordinate {m}
    65.120161467357,  !- Vertex 2 Y-coordinate {m}
    17.970000000000,  !- Vertex 2 Z-coordinate {m}
    -5.528217981590,  !- Vertex 3 X-coordinate {m}
    52.230424521031,  !- Vertex 3 Y-coordinate {m}
    17.970000000000,  !- Vertex 3 Z-coordinate {m}
    -5.528217981590,  !- Vertex 4 X-coordinate {m}
    52.230424521031,  !- Vertex 4 Y-coordinate {m}
    20.970000000000;  !- Vertex 4 Z-coordinate {m}

  FenestrationSurface:Detailed,
    34EAC1,  !- Name
    Window,  !- Surface Type
    EXT_WINDOW_DG,  !- Construction Name
    26574F,  !- Building Surface Name
    ,  !- Outside Boundary Condition Object
    ,  !- TRNSYS 17 - additional surface data
    ,  !- Shading Control Name
    ,  !- Frame and Divider Name
    ,  !- Multiplier
    4,  !- Number of Vertices
    -6.655923840226,  !- Vertex 1 X-coordinate {m}
    65.120161467357,  !- Vertex 1 Y-coordinate {m}
    16.380000000000,  !- Vertex 1 Z-coordinate {m}
    -6.655923840226,  !- Vertex 2 X-coordinate {m}
    65.120161467357,  !- Vertex 2 Y-coordinate {m}
    13.380000000000,  !- Vertex 2 Z-coordinate {m}
    -5.528217981590,  !- Vertex 3 X-coordinate {m}
    52.230424521031,  !- Vertex 3 Y-coordinate {m}
    13.380000000000,  !- Vertex 3 Z-coordinate {m}
    -5.528217981590,  !- Vertex 4 X-coordinate {m}
    52.230424521031,  !- Vertex 4 Y-coordinate {m}
    16.380000000000;  !- Vertex 4 Z-coordinate {m}

  FenestrationSurface:Detailed,
    B5D342,  !- Name
    Window,  !- Surface Type
    EXT_WINDOW_DG,  !- Construction Name
    EBA029,  !- Building Surface Name
    ,  !- Outside Boundary Condition Object
    ,  !- TRNSYS 17 - additional surface data
    ,  !- Shading Control Name
    ,  !- Frame and Divider Name
    ,  !- Multiplier
    4,  !- Number of Vertices
    -6.655923840226,  !- Vertex 1 X-coordinate {m}
    65.120161467357,  !- Vertex 1 Y-coordinate {m}
    11.790000000000,  !- Vertex 1 Z-coordinate {m}
    -6.655923840226,  !- Vertex 2 X-coordinate {m}
    65.120161467357,  !- Vertex 2 Y-coordinate {m}
    8.790000000000,  !- Vertex 2 Z-coordinate {m}
    -5.528217981590,  !- Vertex 3 X-coordinate {m}
    52.230424521031,  !- Vertex 3 Y-coordinate {m}
    8.790000000000,  !- Vertex 3 Z-coordinate {m}
    -5.528217981590,  !- Vertex 4 X-coordinate {m}
    52.230424521031,  !- Vertex 4 Y-coordinate {m}
    11.790000000000;  !- Vertex 4 Z-coordinate {m}

  FenestrationSurface:Detailed,
    FF631B,  !- Name
    Window,  !- Surface Type
    EXT_WINDOW_DG,  !- Construction Name
    DECBF0,  !- Building Surface Name
    ,  !- Outside Boundary Condition Object
    ,  !- TRNSYS 17 - additional surface data
    ,  !- Shading Control Name
    ,  !- Frame and Divider Name
    ,  !- Multiplier
    4,  !- Number of Vertices
    -3.883963890069,  !- Vertex 1 X-coordinate {m}
    44.393910405526,  !- Vertex 1 Y-coordinate {m}
    30.150000000000,  !- Vertex 1 Z-coordinate {m}
    -3.883963890069,  !- Vertex 2 X-coordinate {m}
    44.393910405526,  !- Vertex 2 Y-coordinate {m}
    27.150000000000,  !- Vertex 2 Z-coordinate {m}
    -0.908031053950,  !- Vertex 3 X-coordinate {m}
    10.378842439183,  !- Vertex 3 Y-coordinate {m}
    27.150000000000,  !- Vertex 3 Z-coordinate {m}
    -0.908031053950,  !- Vertex 4 X-coordinate {m}
    10.378842439183,  !- Vertex 4 Y-coordinate {m}
    30.150000000000;  !- Vertex 4 Z-coordinate {m}

  FenestrationSurface:Detailed,
    A2357C,  !- Name
    Window,  !- Surface Type
    EXT_WINDOW_DG,  !- Construction Name
    46D347,  !- Building Surface Name
    ,  !- Outside Boundary Condition Object
    ,  !- TRNSYS 17 - additional surface data
    ,  !- Shading Control Name
    ,  !- Frame and Divider Name
    ,  !- Multiplier
    4,  !- Number of Vertices
    -3.883963890069,  !- Vertex 1 X-coordinate {m}
    44.393910405526,  !- Vertex 1 Y-coordinate {m}
    25.560000000000,  !- Vertex 1 Z-coordinate {m}
    -3.883963890069,  !- Vertex 2 X-coordinate {m}
    44.393910405526,  !- Vertex 2 Y-coordinate {m}
    22.560000000000,  !- Vertex 2 Z-coordinate {m}
    -0.908031053950,  !- Vertex 3 X-coordinate {m}
    10.378842439183,  !- Vertex 3 Y-coordinate {m}
    22.560000000000,  !- Vertex 3 Z-coordinate {m}
    -0.908031053950,  !- Vertex 4 X-coordinate {m}
    10.378842439183,  !- Vertex 4 Y-coordinate {m}
    25.560000000000;  !- Vertex 4 Z-coordinate {m}

  FenestrationSurface:Detailed,
    DFB579,  !- Name
    Window,  !- Surface Type
    EXT_WINDOW_DG,  !- Construction Name
    4BF298,  !- Building Surface Name
    ,  !- Outside Boundary Condition Object
    ,  !- TRNSYS 17 - additional surface data
    ,  !- Shading Control Name
    ,  !- Frame and Divider Name
    ,  !- Multiplier
    4,  !- Number of Vertices
    -3.883963890069,  !- Vertex 1 X-coordinate {m}
    44.393910405526,  !- Vertex 1 Y-coordinate {m}
    20.970000000000,  !- Vertex 1 Z-coordinate {m}
    -3.883963890069,  !- Vertex 2 X-coordinate {m}
    44.393910405526,  !- Vertex 2 Y-coordinate {m}
    17.970000000000,  !- Vertex 2 Z-coordinate {m}
    -0.908031053950,  !- Vertex 3 X-coordinate {m}
    10.378842439183,  !- Vertex 3 Y-coordinate {m}
    17.970000000000,  !- Vertex 3 Z-coordinate {m}
    -0.908031053950,  !- Vertex 4 X-coordinate {m}
    10.378842439183,  !- Vertex 4 Y-coordinate {m}
    20.970000000000;  !- Vertex 4 Z-coordinate {m}

  FenestrationSurface:Detailed,
    428C4E,  !- Name
    Window,  !- Surface Type
    EXT_WINDOW_DG,  !- Construction Name
    645F2E,  !- Building Surface Name
    ,  !- Outside Boundary Condition Object
    ,  !- TRNSYS 17 - additional surface data
    ,  !- Shading Control Name
    ,  !- Frame and Divider Name
    ,  !- Multiplier
    4,  !- Number of Vertices
    -3.883963890069,  !- Vertex 1 X-coordinate {m}
    44.393910405526,  !- Vertex 1 Y-coordinate {m}
    16.380000000000,  !- Vertex 1 Z-coordinate {m}
    -3.883963890069,  !- Vertex 2 X-coordinate {m}
    44.393910405526,  !- Vertex 2 Y-coordinate {m}
    13.380000000000,  !- Vertex 2 Z-coordinate {m}
    -0.908031053950,  !- Vertex 3 X-coordinate {m}
    10.378842439183,  !- Vertex 3 Y-coordinate {m}
    13.380000000000,  !- Vertex 3 Z-coordinate {m}
    -0.908031053950,  !- Vertex 4 X-coordinate {m}
    10.378842439183,  !- Vertex 4 Y-coordinate {m}
    16.380000000000;  !- Vertex 4 Z-coordinate {m}

  FenestrationSurface:Detailed,
    9C1079,  !- Name
    Window,  !- Surface Type
    EXT_WINDOW_DG,  !- Construction Name
    566494,  !- Building Surface Name
    ,  !- Outside Boundary Condition Object
    ,  !- TRNSYS 17 - additional surface data
    ,  !- Shading Control Name
    ,  !- Frame and Divider Name
    ,  !- Multiplier
    4,  !- Number of Vertices
    -3.883963890069,  !- Vertex 1 X-coordinate {m}
    44.393910405526,  !- Vertex 1 Y-coordinate {m}
    11.790000000000,  !- Vertex 1 Z-coordinate {m}
    -3.883963890069,  !- Vertex 2 X-coordinate {m}
    44.393910405526,  !- Vertex 2 Y-coordinate {m}
    8.790000000000,  !- Vertex 2 Z-coordinate {m}
    -0.908031053950,  !- Vertex 3 X-coordinate {m}
    10.378842439183,  !- Vertex 3 Y-coordinate {m}
    8.790000000000,  !- Vertex 3 Z-coordinate {m}
    -0.908031053950,  !- Vertex 4 X-coordinate {m}
    10.378842439183,  !- Vertex 4 Y-coordinate {m}
    11.790000000000;  !- Vertex 4 Z-coordinate {m}

  FenestrationSurface:Detailed,
    FE33C0,  !- Name
    Window,  !- Surface Type
    EXT_WINDOW_DG,  !- Construction Name
    E6FDFE,  !- Building Surface Name
    ,  !- Outside Boundary Condition Object
    ,  !- TRNSYS 17 - additional surface data
    ,  !- Shading Control Name
    ,  !- Frame and Divider Name
    ,  !- Multiplier
    4,  !- Number of Vertices
    -0.908031053948,  !- Vertex 1 X-coordinate {m}
    10.378842439183,  !- Vertex 1 Y-coordinate {m}
    30.150000000000,  !- Vertex 1 Z-coordinate {m}
    -0.908031053948,  !- Vertex 2 X-coordinate {m}
    10.378842439183,  !- Vertex 2 Y-coordinate {m}
    27.150000000000,  !- Vertex 2 Z-coordinate {m}
    -0.597320831053,  !- Vertex 3 X-coordinate {m}
    6.827408340486,  !- Vertex 3 Y-coordinate {m}
    27.150000000000,  !- Vertex 3 Z-coordinate {m}
    -0.597320831053,  !- Vertex 4 X-coordinate {m}
    6.827408340486,  !- Vertex 4 Y-coordinate {m}
    30.150000000000;  !- Vertex 4 Z-coordinate {m}

  FenestrationSurface:Detailed,
    7B1659,  !- Name
    Window,  !- Surface Type
    EXT_WINDOW_DG,  !- Construction Name
    E6FDFE,  !- Building Surface Name
    ,  !- Outside Boundary Condition Object
    ,  !- TRNSYS 17 - additional surface data
    ,  !- Shading Control Name
    ,  !- Frame and Divider Name
    ,  !- Multiplier
    4,  !- Number of Vertices
    -0.908031053948,  !- Vertex 1 X-coordinate {m}
    10.378842439183,  !- Vertex 1 Y-coordinate {m}
    25.560000000000,  !- Vertex 1 Z-coordinate {m}
    -0.908031053948,  !- Vertex 2 X-coordinate {m}
    10.378842439183,  !- Vertex 2 Y-coordinate {m}
    22.560000000000,  !- Vertex 2 Z-coordinate {m}
    -0.597320831053,  !- Vertex 3 X-coordinate {m}
    6.827408340486,  !- Vertex 3 Y-coordinate {m}
    22.560000000000,  !- Vertex 3 Z-coordinate {m}
    -0.597320831053,  !- Vertex 4 X-coordinate {m}
    6.827408340486,  !- Vertex 4 Y-coordinate {m}
    25.560000000000;  !- Vertex 4 Z-coordinate {m}

  FenestrationSurface:Detailed,
    DBBFF6,  !- Name
    Window,  !- Surface Type
    EXT_WINDOW_DG,  !- Construction Name
    748F07,  !- Building Surface Name
    ,  !- Outside Boundary Condition Object
    ,  !- TRNSYS 17 - additional surface data
    ,  !- Shading Control Name
    ,  !- Frame and Divider Name
    ,  !- Multiplier
    4,  !- Number of Vertices
    -0.908031053948,  !- Vertex 1 X-coordinate {m}
    10.378842439183,  !- Vertex 1 Y-coordinate {m}
    20.970000000000,  !- Vertex 1 Z-coordinate {m}
    -0.908031053948,  !- Vertex 2 X-coordinate {m}
    10.378842439183,  !- Vertex 2 Y-coordinate {m}
    17.970000000000,  !- Vertex 2 Z-coordinate {m}
    -0.597320831053,  !- Vertex 3 X-coordinate {m}
    6.827408340486,  !- Vertex 3 Y-coordinate {m}
    17.970000000000,  !- Vertex 3 Z-coordinate {m}
    -0.597320831053,  !- Vertex 4 X-coordinate {m}
    6.827408340486,  !- Vertex 4 Y-coordinate {m}
    20.970000000000;  !- Vertex 4 Z-coordinate {m}

  FenestrationSurface:Detailed,
    79E171,  !- Name
    Window,  !- Surface Type
    EXT_WINDOW_DG,  !- Construction Name
    748F07,  !- Building Surface Name
    ,  !- Outside Boundary Condition Object
    ,  !- TRNSYS 17 - additional surface data
    ,  !- Shading Control Name
    ,  !- Frame and Divider Name
    ,  !- Multiplier
    4,  !- Number of Vertices
    -0.908031053948,  !- Vertex 1 X-coordinate {m}
    10.378842439183,  !- Vertex 1 Y-coordinate {m}
    16.380000000000,  !- Vertex 1 Z-coordinate {m}
    -0.908031053948,  !- Vertex 2 X-coordinate {m}
    10.378842439183,  !- Vertex 2 Y-coordinate {m}
    13.380000000000,  !- Vertex 2 Z-coordinate {m}
    -0.597320831053,  !- Vertex 3 X-coordinate {m}
    6.827408340486,  !- Vertex 3 Y-coordinate {m}
    13.380000000000,  !- Vertex 3 Z-coordinate {m}
    -0.597320831053,  !- Vertex 4 X-coordinate {m}
    6.827408340486,  !- Vertex 4 Y-coordinate {m}
    16.380000000000;  !- Vertex 4 Z-coordinate {m}

  FenestrationSurface:Detailed,
    4661BC,  !- Name
    Window,  !- Surface Type
    EXT_WINDOW_DG,  !- Construction Name
    D5890F,  !- Building Surface Name
    ,  !- Outside Boundary Condition Object
    ,  !- TRNSYS 17 - additional surface data
    ,  !- Shading Control Name
    ,  !- Frame and Divider Name
    ,  !- Multiplier
    4,  !- Number of Vertices
    -0.908031053948,  !- Vertex 1 X-coordinate {m}
    10.378842439183,  !- Vertex 1 Y-coordinate {m}
    11.790000000000,  !- Vertex 1 Z-coordinate {m}
    -0.908031053948,  !- Vertex 2 X-coordinate {m}
    10.378842439183,  !- Vertex 2 Y-coordinate {m}
    8.790000000000,  !- Vertex 2 Z-coordinate {m}
    -0.597320831053,  !- Vertex 3 X-coordinate {m}
    6.827408340486,  !- Vertex 3 Y-coordinate {m}
    8.790000000000,  !- Vertex 3 Z-coordinate {m}
    -0.597320831053,  !- Vertex 4 X-coordinate {m}
    6.827408340486,  !- Vertex 4 Y-coordinate {m}
    11.790000000000;  !- Vertex 4 Z-coordinate {m}


  BuildingSurface:Detailed,
    D65126,  !- Name
    Wall,  !- Surface Type
    ADJ_WALL,  !- Construction Name
    B1_F0_SC,  !- Zone Name
    Zone,  !- Outside Boundary Condition
    B1_F1_CN,  !- Outside Boundary Condition Object
    NoSun,  !- Sun Exposure
    NoWind,  !- Wind Exposure
    ,  !- TRNSYS 17 - additional surface data
    4,  !- Number of Vertices
    7.564604853320,  !- Vertex 1 X-coordinate {m}
    11.120102031252,  !- Vertex 1 Y-coordinate {m}
    12.580000000000,  !- Vertex 1 Z-coordinate {m}
    7.564604853320,  !- Vertex 2 X-coordinate {m}
    11.120102031252,  !- Vertex 2 Y-coordinate {m}
    7.990000000000,  !- Vertex 2 Z-coordinate {m}
    -0.908031053950,  !- Vertex 3 X-coordinate {m}
    10.378842439183,  !- Vertex 3 Y-coordinate {m}
    7.990000000000,  !- Vertex 3 Z-coordinate {m}
    -0.908031053950,  !- Vertex 4 X-coordinate {m}
    10.378842439183,  !- Vertex 4 Y-coordinate {m}
    12.580000000000;  !- Vertex 4 Z-coordinate {m}

  FenestrationSurface:Detailed,
    193B92,  !- Name
    Window,  !- Surface Type
    EXT_WINDOW_SG,  !- Construction Name
    14E777,  !- Building Surface Name
    ,  !- Outside Boundary Condition Object
    ,  !- TRNSYS 17 - additional surface data
    ,  !- Shading Control Name
    ,  !- Frame and Divider Name
    ,  !- Multiplier
    4,  !- Number of Vertices
    -0.867939412284,  !- Vertex 1 X-coordinate {m}
    9.920592878061,  !- Vertex 1 Y-coordinate {m}
    6.910000000000,  !- Vertex 1 Z-coordinate {m}
    -0.867939412284,  !- Vertex 2 X-coordinate {m}
    9.920592878061,  !- Vertex 2 Y-coordinate {m}
    4.710000000000,  !- Vertex 2 Z-coordinate {m}
    -0.619545545454,  !- Vertex 3 X-coordinate {m}
    7.081437988500,  !- Vertex 3 Y-coordinate {m}
    4.710000000000,  !- Vertex 3 Z-coordinate {m}
    -0.619545545454,  !- Vertex 4 X-coordinate {m}
    7.081437988500,  !- Vertex 4 Y-coordinate {m}
    6.910000000000;  !- Vertex 4 Z-coordinate {m}

  FenestrationSurface:Detailed,
    1FC373,  !- Name
    Window,  !- Surface Type
    EXT_WINDOW_SG,  !- Construction Name
    6A5530,  !- Building Surface Name
    ,  !- Outside Boundary Condition Object
    ,  !- TRNSYS 17 - additional surface data
    ,  !- Shading Control Name
    ,  !- Frame and Divider Name
    ,  !- Multiplier
    4,  !- Number of Vertices
    -3.759984846011,  !- Vertex 1 X-coordinate {m}
    42.976823447490,  !- Vertex 1 Y-coordinate {m}
    6.910000000000,  !- Vertex 1 Z-coordinate {m}
    -3.759984846011,  !- Vertex 2 X-coordinate {m}
    42.976823447490,  !- Vertex 2 Y-coordinate {m}
    4.710000000000,  !- Vertex 2 Z-coordinate {m}
    -1.550586767358,  !- Vertex 3 X-coordinate {m}
    17.723287850865,  !- Vertex 3 Y-coordinate {m}
    4.710000000000,  !- Vertex 3 Z-coordinate {m}
    -1.550586767358,  !- Vertex 4 X-coordinate {m}
    17.723287850865,  !- Vertex 4 Y-coordinate {m}
    6.910000000000;  !- Vertex 4 Z-coordinate {m}

  FenestrationSurface:Detailed,
    532ABB,  !- Name
    Window,  !- Surface Type
    EXT_WINDOW_SG,  !- Construction Name
    E2D9E7,  !- Building Surface Name
    ,  !- Outside Boundary Condition Object
    ,  !- TRNSYS 17 - additional surface data
    ,  !- Shading Control Name
    ,  !- Frame and Divider Name
    ,  !- Multiplier
    4,  !- Number of Vertices
    -0.386403933606,  !- Vertex 1 X-coordinate {m}
    4.416617171104,  !- Vertex 1 Y-coordinate {m}
    27.850000000000,  !- Vertex 1 Z-coordinate {m}
    -0.386403933606,  !- Vertex 2 X-coordinate {m}
    4.416617171104,  !- Vertex 2 Y-coordinate {m}
    24.850000000000,  !- Vertex 2 Z-coordinate {m}
    -0.200762201553,  !- Vertex 3 X-coordinate {m}
    2.294722464169,  !- Vertex 3 Y-coordinate {m}
    24.850000000000,  !- Vertex 3 Z-coordinate {m}
    -0.200762201553,  !- Vertex 4 X-coordinate {m}
    2.294722464169,  !- Vertex 4 Y-coordinate {m}
    27.850000000000;  !- Vertex 4 Z-coordinate {m}

  FenestrationSurface:Detailed,
    4E48C4,  !- Name
    Window,  !- Surface Type
    EXT_WINDOW_SG,  !- Construction Name
    3F7AEE,  !- Building Surface Name
    ,  !- Outside Boundary Condition Object
    ,  !- TRNSYS 17 - additional surface data
    ,  !- Shading Control Name
    ,  !- Frame and Divider Name
    ,  !- Multiplier
    4,  !- Number of Vertices
    -0.386403933606,  !- Vertex 1 X-coordinate {m}
    4.416617171104,  !- Vertex 1 Y-coordinate {m}
    19.170000000000,  !- Vertex 1 Z-coordinate {m}
    -0.386403933606,  !- Vertex 2 X-coordinate {m}
    4.416617171104,  !- Vertex 2 Y-coordinate {m}
    15.170000000000,  !- Vertex 2 Z-coordinate {m}
    -0.200762201553,  !- Vertex 3 X-coordinate {m}
    2.294722464169,  !- Vertex 3 Y-coordinate {m}
    15.170000000000,  !- Vertex 3 Z-coordinate {m}
    -0.200762201553,  !- Vertex 4 X-coordinate {m}
    2.294722464169,  !- Vertex 4 Y-coordinate {m}
    19.170000000000;  !- Vertex 4 Z-coordinate {m}

  FenestrationSurface:Detailed,
    2958D3,  !- Name
    Window,  !- Surface Type
    EXT_WINDOW_SG,  !- Construction Name
    719426,  !- Building Surface Name
    ,  !- Outside Boundary Condition Object
    ,  !- TRNSYS 17 - additional surface data
    ,  !- Shading Control Name
    ,  !- Frame and Divider Name
    ,  !- Multiplier
    4,  !- Number of Vertices
    -0.386403933606,  !- Vertex 1 X-coordinate {m}
    4.416617171104,  !- Vertex 1 Y-coordinate {m}
    9.490000000000,  !- Vertex 1 Z-coordinate {m}
    -0.386403933606,  !- Vertex 2 X-coordinate {m}
    4.416617171104,  !- Vertex 2 Y-coordinate {m}
    6.490000000000,  !- Vertex 2 Z-coordinate {m}
    -0.200762201553,  !- Vertex 3 X-coordinate {m}
    2.294722464169,  !- Vertex 3 Y-coordinate {m}
    6.490000000000,  !- Vertex 3 Z-coordinate {m}
    -0.200762201553,  !- Vertex 4 X-coordinate {m}
    2.294722464169,  !- Vertex 4 Y-coordinate {m}
    9.490000000000;  !- Vertex 4 Z-coordinate {m}

  FenestrationSurface:Detailed,
    47152E,  !- Name
    Door,  !- Surface Type
    ,  !- Construction Name
    40DD51,  !- Building Surface Name
    ,  !- Outside Boundary Condition Object
    ,  !- TRNSYS 17 - additional surface data
    ,  !- Shading Control Name
    ,  !- Frame and Divider Name
    ,  !- Multiplier
    4,  !- Number of Vertices
    -6.397114862136,  !- Vertex 1 X-coordinate {m}
    62.161961311373,  !- Vertex 1 Y-coordinate {m}
    6.710000000000,  !- Vertex 1 Z-coordinate {m}
    -6.397114862136,  !- Vertex 2 X-coordinate {m}
    62.161961311373,  !- Vertex 2 Y-coordinate {m}
    3.910000000000,  !- Vertex 2 Z-coordinate {m}
    -5.787024662902,  !- Vertex 3 X-coordinate {m}
    55.188598424731,  !- Vertex 3 Y-coordinate {m}
    3.910000000000,  !- Vertex 3 Z-coordinate {m}
    -5.787024662902,  !- Vertex 4 X-coordinate {m}
    55.188598424731,  !- Vertex 4 Y-coordinate {m}
    6.710000000000;  !- Vertex 4 Z-coordinate {m}

  FenestrationSurface:Detailed,
    1EE283,  !- Name
    Window,  !- Surface Type
    EXT_WINDOW_SG,  !- Construction Name
    40DD51,  !- Building Surface Name
    ,  !- Outside Boundary Condition Object
    ,  !- TRNSYS 17 - additional surface data
    ,  !- Shading Control Name
    ,  !- Frame and Divider Name
    ,  !- Multiplier
    4,  !- Number of Vertices
    -6.784957917364,  !- Vertex 1 X-coordinate {m}
    66.595027717882,  !- Vertex 1 Y-coordinate {m}
    5.985000000000,  !- Vertex 1 Z-coordinate {m}
    -6.784957917364,  !- Vertex 2 X-coordinate {m}
    66.595027717882,  !- Vertex 2 Y-coordinate {m}
    4.635000000000,  !- Vertex 2 Z-coordinate {m}
    -6.440692733510,  !- Vertex 3 X-coordinate {m}
    62.660058660419,  !- Vertex 3 Y-coordinate {m}
    4.635000000000,  !- Vertex 3 Z-coordinate {m}
    -6.440692733510,  !- Vertex 4 X-coordinate {m}
    62.660058660419,  !- Vertex 4 Y-coordinate {m}
    5.985000000000;  !- Vertex 4 Z-coordinate {m}

  FenestrationSurface:Detailed,
    564CB1,  !- Name
    Window,  !- Surface Type
    EXT_WINDOW_SG,  !- Construction Name
    40DD51,  !- Building Surface Name
    ,  !- Outside Boundary Condition Object
    ,  !- TRNSYS 17 - additional surface data
    ,  !- Shading Control Name
    ,  !- Frame and Divider Name
    ,  !- Multiplier
    4,  !- Number of Vertices
    -5.743446791529,  !- Vertex 1 X-coordinate {m}
    54.690501075685,  !- Vertex 1 Y-coordinate {m}
    5.985000000000,  !- Vertex 1 Z-coordinate {m}
    -5.743446791529,  !- Vertex 2 X-coordinate {m}
    54.690501075685,  !- Vertex 2 Y-coordinate {m}
    4.635000000000,  !- Vertex 2 Z-coordinate {m}
    -5.399181607675,  !- Vertex 3 X-coordinate {m}
    50.755532018223,  !- Vertex 3 Y-coordinate {m}
    4.635000000000,  !- Vertex 3 Z-coordinate {m}
    -5.399181607675,  !- Vertex 4 X-coordinate {m}
    50.755532018223,  !- Vertex 4 Y-coordinate {m}
    5.985000000000;  !- Vertex 4 Z-coordinate {m}

  FenestrationSurface:Detailed,
    E98102,  !- Name
    Window,  !- Surface Type
    EXT_WINDOW_SG,  !- Construction Name
    FDD4D5,  !- Building Surface Name
    ,  !- Outside Boundary Condition Object
    ,  !- TRNSYS 17 - additional surface data
    ,  !- Shading Control Name
    ,  !- Frame and Divider Name
    ,  !- Multiplier
    4,  !- Number of Vertices
    -6.821519751446,  !- Vertex 1 X-coordinate {m}
    67.012931393731,  !- Vertex 1 Y-coordinate {m}
    12.025000000000,  !- Vertex 1 Z-coordinate {m}
    -6.821519751446,  !- Vertex 2 X-coordinate {m}
    67.012931393731,  !- Vertex 2 Y-coordinate {m}
    8.545000000000,  !- Vertex 2 Z-coordinate {m}
    -6.664639414500,  !- Vertex 3 X-coordinate {m}
    65.219780937166,  !- Vertex 3 Y-coordinate {m}
    8.545000000000,  !- Vertex 3 Z-coordinate {m}
    -6.664639414500,  !- Vertex 4 X-coordinate {m}
    65.219780937166,  !- Vertex 4 Y-coordinate {m}
    12.025000000000;  !- Vertex 4 Z-coordinate {m}

  FenestrationSurface:Detailed,
    F42A75,  !- Name
    Window,  !- Surface Type
    EXT_WINDOW_SG,  !- Construction Name
    752725,  !- Building Surface Name
    ,  !- Outside Boundary Condition Object
    ,  !- TRNSYS 17 - additional surface data
    ,  !- Shading Control Name
    ,  !- Frame and Divider Name
    ,  !- Multiplier
    4,  !- Number of Vertices
    -5.519502407316,  !- Vertex 1 X-coordinate {m}
    52.130805051222,  !- Vertex 1 Y-coordinate {m}
    12.025000000000,  !- Vertex 1 Z-coordinate {m}
    -5.519502407316,  !- Vertex 2 X-coordinate {m}
    52.130805051222,  !- Vertex 2 Y-coordinate {m}
    8.545000000000,  !- Vertex 2 Z-coordinate {m}
    -5.362622070370,  !- Vertex 3 X-coordinate {m}
    50.337654594657,  !- Vertex 3 Y-coordinate {m}
    8.545000000000,  !- Vertex 3 Z-coordinate {m}
    -5.362622070370,  !- Vertex 4 X-coordinate {m}
    50.337654594657,  !- Vertex 4 Y-coordinate {m}
    12.025000000000;  !- Vertex 4 Z-coordinate {m}

  BuildingSurface:Detailed,
    32E7CC,  !- Name
    Wall,  !- Surface Type
    EXT_WALL_SW_EF_RL,  !- Construction Name
    B1_F2_SC,  !- Zone Name
    Outdoors,  !- Outside Boundary Condition
    ,  !- Outside Boundary Condition Object
    SunExposed,  !- Sun Exposure
    WindExposed,  !- Wind Exposure
    ,  !- TRNSYS 17 - additional surface data
    4,  !- Number of Vertices
    0.000000000000,  !- Vertex 1 X-coordinate {m}
    0.000000000000,  !- Vertex 1 Y-coordinate {m}
    21.760000000000,  !- Vertex 1 Z-coordinate {m}
    0.000000000000,  !- Vertex 2 X-coordinate {m}
    0.000000000000,  !- Vertex 2 Y-coordinate {m}
    12.580000000000,  !- Vertex 2 Z-coordinate {m}
    7.772760005483,  !- Vertex 3 X-coordinate {m}
    -1.599523221318,  !- Vertex 3 Y-coordinate {m}
    12.580000000000,  !- Vertex 3 Z-coordinate {m}
    7.772760005483,  !- Vertex 4 X-coordinate {m}
    -1.599523221318,  !- Vertex 4 Y-coordinate {m}
    21.760000000000;  !- Vertex 4 Z-coordinate {m}

  FenestrationSurface:Detailed,
    32CAB3,  !- Name
    Window,  !- Surface Type
    EXT_WINDOW_SG,  !- Construction Name
    FBAC5D,  !- Building Surface Name
    ,  !- Outside Boundary Condition Object
    ,  !- TRNSYS 17 - additional surface data
    ,  !- Shading Control Name
    ,  !- Frame and Divider Name
    ,  !- Multiplier
    4,  !- Number of Vertices
    1.763056310714,  !- Vertex 1 X-coordinate {m}
    -0.362811859300,  !- Vertex 1 Y-coordinate {m}
    30.038000000000,  !- Vertex 1 Z-coordinate {m}
    1.763056310714,  !- Vertex 2 X-coordinate {m}
    -0.362811859300,  !- Vertex 2 Y-coordinate {m}
    21.872000000000,  !- Vertex 2 Z-coordinate {m}
    4.701483495240,  !- Vertex 3 X-coordinate {m}
    -0.967498291466,  !- Vertex 3 Y-coordinate {m}
    21.872000000000,  !- Vertex 3 Z-coordinate {m}
    4.701483495240,  !- Vertex 4 X-coordinate {m}
    -0.967498291466,  !- Vertex 4 Y-coordinate {m}
    30.038000000000;  !- Vertex 4 Z-coordinate {m}

  FenestrationSurface:Detailed,
    47705D,  !- Name
    Window,  !- Surface Type
    EXT_WINDOW_SG,  !- Construction Name
    32E7CC,  !- Building Surface Name
    ,  !- Outside Boundary Condition Object
    ,  !- TRNSYS 17 - additional surface data
    ,  !- Shading Control Name
    ,  !- Frame and Divider Name
    ,  !- Multiplier
    4,  !- Number of Vertices
    1.763056310714,  !- Vertex 1 X-coordinate {m}
    -0.362811859300,  !- Vertex 1 Y-coordinate {m}
    21.637600000000,  !- Vertex 1 Z-coordinate {m}
    1.763056310714,  !- Vertex 2 X-coordinate {m}
    -0.362811859300,  !- Vertex 2 Y-coordinate {m}
    12.702400000000,  !- Vertex 2 Z-coordinate {m}
    4.701483495240,  !- Vertex 3 X-coordinate {m}
    -0.967498291466,  !- Vertex 3 Y-coordinate {m}
    12.702400000000,  !- Vertex 3 Z-coordinate {m}
    4.701483495240,  !- Vertex 4 X-coordinate {m}
    -0.967498291466,  !- Vertex 4 Y-coordinate {m}
    21.637600000000;  !- Vertex 4 Z-coordinate {m}

  FenestrationSurface:Detailed,
    81B64D,  !- Name
    Window,  !- Surface Type
    EXT_WINDOW_SG,  !- Construction Name
    5C186E,  !- Building Surface Name
    ,  !- Outside Boundary Condition Object
    ,  !- TRNSYS 17 - additional surface data
    ,  !- Shading Control Name
    ,  !- Frame and Divider Name
    ,  !- Multiplier
    4,  !- Number of Vertices
    1.763056310714,  !- Vertex 1 X-coordinate {m}
    -0.362811859300,  !- Vertex 1 Y-coordinate {m}
    12.464400000000,  !- Vertex 1 Z-coordinate {m}
    1.763056310714,  !- Vertex 2 X-coordinate {m}
    -0.362811859300,  !- Vertex 2 Y-coordinate {m}
    4.025600000000,  !- Vertex 2 Z-coordinate {m}
    4.701483495240,  !- Vertex 3 X-coordinate {m}
    -0.967498291466,  !- Vertex 3 Y-coordinate {m}
    4.025600000000,  !- Vertex 3 Z-coordinate {m}
    4.701483495240,  !- Vertex 4 X-coordinate {m}
    -0.967498291466,  !- Vertex 4 Y-coordinate {m}
    12.464400000000;  !- Vertex 4 Z-coordinate {m}

  FenestrationSurface:Detailed,
    C113D9,  !- Name
    Window,  !- Surface Type
    EXT_WINDOW_SG,  !- Construction Name
    147F4F,  !- Building Surface Name
    ,  !- Outside Boundary Condition Object
    ,  !- TRNSYS 17 - additional surface data
    ,  !- Shading Control Name
    ,  !- Frame and Divider Name
    ,  !- Multiplier
    4,  !- Number of Vertices
    7.823862548410,  !- Vertex 1 X-coordinate {m}
    -1.610039396270,  !- Vertex 1 Y-coordinate {m}
    6.908470237396,  !- Vertex 1 Z-coordinate {m}
    7.823862548410,  !- Vertex 2 X-coordinate {m}
    -1.610039396270,  !- Vertex 2 Y-coordinate {m}
    4.708470237396,  !- Vertex 2 Z-coordinate {m}
    10.762289732936,  !- Vertex 3 X-coordinate {m}
    -2.214725828437,  !- Vertex 3 Y-coordinate {m}
    4.708470237396,  !- Vertex 3 Z-coordinate {m}
    10.762289732936,  !- Vertex 4 X-coordinate {m}
    -2.214725828437,  !- Vertex 4 Y-coordinate {m}
    6.908470237396;  !- Vertex 4 Z-coordinate {m}

  FenestrationSurface:Detailed,
    EEE9BD,  !- Name
    Window,  !- Surface Type
    EXT_WINDOW_SG,  !- Construction Name
    F87805,  !- Building Surface Name
    ,  !- Outside Boundary Condition Object
    ,  !- TRNSYS 17 - additional surface data
    ,  !- Shading Control Name
    ,  !- Frame and Divider Name
    ,  !- Multiplier
    4,  !- Number of Vertices
    15.859308706134,  !- Vertex 1 X-coordinate {m}
    15.788296997630,  !- Vertex 1 Y-coordinate {m}
    30.150000000000,  !- Vertex 1 Z-coordinate {m}
    15.859308706134,  !- Vertex 2 X-coordinate {m}
    15.788296997630,  !- Vertex 2 Y-coordinate {m}
    27.150000000000,  !- Vertex 2 Z-coordinate {m}
    13.049407559949,  !- Vertex 3 X-coordinate {m}
    47.905614064108,  !- Vertex 3 Y-coordinate {m}
    27.150000000000,  !- Vertex 3 Z-coordinate {m}
    13.049407559949,  !- Vertex 4 X-coordinate {m}
    47.905614064108,  !- Vertex 4 Y-coordinate {m}
    30.150000000000;  !- Vertex 4 Z-coordinate {m}

  FenestrationSurface:Detailed,
    14ABEE,  !- Name
    Window,  !- Surface Type
    EXT_WINDOW_SG,  !- Construction Name
    BED4D4,  !- Building Surface Name
    ,  !- Outside Boundary Condition Object
    ,  !- TRNSYS 17 - additional surface data
    ,  !- Shading Control Name
    ,  !- Frame and Divider Name
    ,  !- Multiplier
    4,  !- Number of Vertices
    15.859308706134,  !- Vertex 1 X-coordinate {m}
    15.788296997630,  !- Vertex 1 Y-coordinate {m}
    25.560000000000,  !- Vertex 1 Z-coordinate {m}
    15.859308706134,  !- Vertex 2 X-coordinate {m}
    15.788296997630,  !- Vertex 2 Y-coordinate {m}
    22.560000000000,  !- Vertex 2 Z-coordinate {m}
    13.049407559949,  !- Vertex 3 X-coordinate {m}
    47.905614064108,  !- Vertex 3 Y-coordinate {m}
    22.560000000000,  !- Vertex 3 Z-coordinate {m}
    13.049407559949,  !- Vertex 4 X-coordinate {m}
    47.905614064108,  !- Vertex 4 Y-coordinate {m}
    25.560000000000;  !- Vertex 4 Z-coordinate {m}

  FenestrationSurface:Detailed,
    CB6837,  !- Name
    Window,  !- Surface Type
    EXT_WINDOW_SG,  !- Construction Name
    E78E15,  !- Building Surface Name
    ,  !- Outside Boundary Condition Object
    ,  !- TRNSYS 17 - additional surface data
    ,  !- Shading Control Name
    ,  !- Frame and Divider Name
    ,  !- Multiplier
    4,  !- Number of Vertices
    15.859308706134,  !- Vertex 1 X-coordinate {m}
    15.788296997630,  !- Vertex 1 Y-coordinate {m}
    20.970000000000,  !- Vertex 1 Z-coordinate {m}
    15.859308706134,  !- Vertex 2 X-coordinate {m}
    15.788296997630,  !- Vertex 2 Y-coordinate {m}
    17.970000000000,  !- Vertex 2 Z-coordinate {m}
    13.049407559949,  !- Vertex 3 X-coordinate {m}
    47.905614064108,  !- Vertex 3 Y-coordinate {m}
    17.970000000000,  !- Vertex 3 Z-coordinate {m}
    13.049407559949,  !- Vertex 4 X-coordinate {m}
    47.905614064108,  !- Vertex 4 Y-coordinate {m}
    20.970000000000;  !- Vertex 4 Z-coordinate {m}

  FenestrationSurface:Detailed,
    147C92,  !- Name
    Window,  !- Surface Type
    EXT_WINDOW_SG,  !- Construction Name
    A867DC,  !- Building Surface Name
    ,  !- Outside Boundary Condition Object
    ,  !- TRNSYS 17 - additional surface data
    ,  !- Shading Control Name
    ,  !- Frame and Divider Name
    ,  !- Multiplier
    4,  !- Number of Vertices
    15.859308706134,  !- Vertex 1 X-coordinate {m}
    15.788296997630,  !- Vertex 1 Y-coordinate {m}
    16.380000000000,  !- Vertex 1 Z-coordinate {m}
    15.859308706134,  !- Vertex 2 X-coordinate {m}
    15.788296997630,  !- Vertex 2 Y-coordinate {m}
    13.380000000000,  !- Vertex 2 Z-coordinate {m}
    13.049407559949,  !- Vertex 3 X-coordinate {m}
    47.905614064108,  !- Vertex 3 Y-coordinate {m}
    13.380000000000,  !- Vertex 3 Z-coordinate {m}
    13.049407559949,  !- Vertex 4 X-coordinate {m}
    47.905614064108,  !- Vertex 4 Y-coordinate {m}
    16.380000000000;  !- Vertex 4 Z-coordinate {m}

  FenestrationSurface:Detailed,
    45869F,  !- Name
    Window,  !- Surface Type
    EXT_WINDOW_SG,  !- Construction Name
    4977E0,  !- Building Surface Name
    ,  !- Outside Boundary Condition Object
    ,  !- TRNSYS 17 - additional surface data
    ,  !- Shading Control Name
    ,  !- Frame and Divider Name
    ,  !- Multiplier
    4,  !- Number of Vertices
    15.859308706134,  !- Vertex 1 X-coordinate {m}
    15.788296997630,  !- Vertex 1 Y-coordinate {m}
    11.790000000000,  !- Vertex 1 Z-coordinate {m}
    15.859308706134,  !- Vertex 2 X-coordinate {m}
    15.788296997630,  !- Vertex 2 Y-coordinate {m}
    8.790000000000,  !- Vertex 2 Z-coordinate {m}
    15.155743972804,  !- Vertex 3 X-coordinate {m}
    23.830078697975,  !- Vertex 3 Y-coordinate {m}
    8.790000000000,  !- Vertex 3 Z-coordinate {m}
    15.155743972804,  !- Vertex 4 X-coordinate {m}
    23.830078697975,  !- Vertex 4 Y-coordinate {m}
    11.790000000000;  !- Vertex 4 Z-coordinate {m}

  FenestrationSurface:Detailed,
    EE2824,  !- Name
    Window,  !- Surface Type
    EXT_WINDOW_SG,  !- Construction Name
    E0BB02,  !- Building Surface Name
    ,  !- Outside Boundary Condition Object
    ,  !- TRNSYS 17 - additional surface data
    ,  !- Shading Control Name
    ,  !- Frame and Divider Name
    ,  !- Multiplier
    4,  !- Number of Vertices
    15.155743972804,  !- Vertex 1 X-coordinate {m}
    23.830078697975,  !- Vertex 1 Y-coordinate {m}
    11.790000000000,  !- Vertex 1 Z-coordinate {m}
    15.155743972804,  !- Vertex 2 X-coordinate {m}
    23.830078697975,  !- Vertex 2 Y-coordinate {m}
    8.790000000000,  !- Vertex 2 Z-coordinate {m}
    13.049407559949,  !- Vertex 3 X-coordinate {m}
    47.905614064108,  !- Vertex 3 Y-coordinate {m}
    8.790000000000,  !- Vertex 3 Z-coordinate {m}
    13.049407559949,  !- Vertex 4 X-coordinate {m}
    47.905614064108,  !- Vertex 4 Y-coordinate {m}
    11.790000000000;  !- Vertex 4 Z-coordinate {m}

  FenestrationSurface:Detailed,
    6DE9B8,  !- Name
    Window,  !- Surface Type
    EXT_WINDOW_SG,  !- Construction Name
    7E2443,  !- Building Surface Name
    ,  !- Outside Boundary Condition Object
    ,  !- TRNSYS 17 - additional surface data
    ,  !- Shading Control Name
    ,  !- Frame and Divider Name
    ,  !- Multiplier
    4,  !- Number of Vertices
    15.834469319450,  !- Vertex 1 X-coordinate {m}
    16.072212486586,  !- Vertex 1 Y-coordinate {m}
    7.010000000000,  !- Vertex 1 Z-coordinate {m}
    15.834469319450,  !- Vertex 2 X-coordinate {m}
    16.072212486586,  !- Vertex 2 Y-coordinate {m}
    4.710000000000,  !- Vertex 2 Z-coordinate {m}
    13.074246946633,  !- Vertex 3 X-coordinate {m}
    47.621698575151,  !- Vertex 3 Y-coordinate {m}
    4.710000000000,  !- Vertex 3 Z-coordinate {m}
    13.074246946633,  !- Vertex 4 X-coordinate {m}
    47.621698575151,  !- Vertex 4 Y-coordinate {m}
    7.010000000000;  !- Vertex 4 Z-coordinate {m}

  FenestrationSurface:Detailed,
    570A67,  !- Name
    Door,  !- Surface Type
    ,  !- Construction Name
    14EE47,  !- Building Surface Name
    ,  !- Outside Boundary Condition Object
    ,  !- TRNSYS 17 - additional surface data
    ,  !- Shading Control Name
    ,  !- Frame and Divider Name
    ,  !- Multiplier
    4,  !- Number of Vertices
    14.737614296971,  !- Vertex 1 X-coordinate {m}
    28.609322762070,  !- Vertex 1 Y-coordinate {m}
    3.300000000000,  !- Vertex 1 Z-coordinate {m}
    14.737614296971,  !- Vertex 2 X-coordinate {m}
    28.609322762070,  !- Vertex 2 Y-coordinate {m}
    0.000000000000,  !- Vertex 2 Z-coordinate {m}
    14.171101969112,  !- Vertex 3 X-coordinate {m}
    35.084588299667,  !- Vertex 3 Y-coordinate {m}
    0.000000000000,  !- Vertex 3 Z-coordinate {m}
    14.171101969112,  !- Vertex 4 X-coordinate {m}
    35.084588299667,  !- Vertex 4 Y-coordinate {m}
    3.300000000000;  !- Vertex 4 Z-coordinate {m}

  FenestrationSurface:Detailed,
    885B80,  !- Name
    Window,  !- Surface Type
    EXT_WINDOW_SG,  !- Construction Name
    14EE47,  !- Building Surface Name
    ,  !- Outside Boundary Condition Object
    ,  !- TRNSYS 17 - additional surface data
    ,  !- Shading Control Name
    ,  !- Frame and Divider Name
    ,  !- Multiplier
    4,  !- Number of Vertices
    15.878047190824,  !- Vertex 1 X-coordinate {m}
    15.574115137540,  !- Vertex 1 Y-coordinate {m}
    3.100000000000,  !- Vertex 1 Z-coordinate {m}
    15.878047190824,  !- Vertex 2 X-coordinate {m}
    15.574115137540,  !- Vertex 2 Y-coordinate {m}
    0.800000000000,  !- Vertex 2 Z-coordinate {m}
    14.781192168345,  !- Vertex 3 X-coordinate {m}
    28.111225413025,  !- Vertex 3 Y-coordinate {m}
    0.800000000000,  !- Vertex 3 Z-coordinate {m}
    14.781192168345,  !- Vertex 4 X-coordinate {m}
    28.111225413025,  !- Vertex 4 Y-coordinate {m}
    3.100000000000;  !- Vertex 4 Z-coordinate {m}

  FenestrationSurface:Detailed,
    4AC286,  !- Name
    Window,  !- Surface Type
    EXT_WINDOW_SG,  !- Construction Name
    14EE47,  !- Building Surface Name
    ,  !- Outside Boundary Condition Object
    ,  !- TRNSYS 17 - additional surface data
    ,  !- Shading Control Name
    ,  !- Frame and Divider Name
    ,  !- Multiplier
    4,  !- Number of Vertices
    14.127524097738,  !- Vertex 1 X-coordinate {m}
    35.582685648713,  !- Vertex 1 Y-coordinate {m}
    3.100000000000,  !- Vertex 1 Z-coordinate {m}
    14.127524097738,  !- Vertex 2 X-coordinate {m}
    35.582685648713,  !- Vertex 2 Y-coordinate {m}
    0.800000000000,  !- Vertex 2 Z-coordinate {m}
    13.030669075259,  !- Vertex 3 X-coordinate {m}
    48.119795924197,  !- Vertex 3 Y-coordinate {m}
    0.800000000000,  !- Vertex 3 Z-coordinate {m}
    13.030669075259,  !- Vertex 4 X-coordinate {m}
    48.119795924197,  !- Vertex 4 Y-coordinate {m}
    3.100000000000;  !- Vertex 4 Z-coordinate {m}

  FenestrationSurface:Detailed,
    8BC98E,  !- Name
    Window,  !- Surface Type
    EXT_WINDOW_SG,  !- Construction Name
    52F178,  !- Building Surface Name
    ,  !- Outside Boundary Condition Object
    ,  !- TRNSYS 17 - additional surface data
    ,  !- Shading Control Name
    ,  !- Frame and Divider Name
    ,  !- Multiplier
    4,  !- Number of Vertices
    13.351855913087,  !- Vertex 1 X-coordinate {m}
    9.040317238483,  !- Vertex 1 Y-coordinate {m}
    29.350000000000,  !- Vertex 1 Z-coordinate {m}
    13.351855913087,  !- Vertex 2 X-coordinate {m}
    9.040317238483,  !- Vertex 2 Y-coordinate {m}
    23.350000000000,  !- Vertex 2 Z-coordinate {m}
    13.855761299480,  !- Vertex 3 X-coordinate {m}
    11.489006553517,  !- Vertex 3 Y-coordinate {m}
    23.350000000000,  !- Vertex 3 Z-coordinate {m}
    13.855761299480,  !- Vertex 4 X-coordinate {m}
    11.489006553517,  !- Vertex 4 Y-coordinate {m}
    29.350000000000;  !- Vertex 4 Z-coordinate {m}

  FenestrationSurface:Detailed,
    FAEC78,  !- Name
    Window,  !- Surface Type
    EXT_WINDOW_SG,  !- Construction Name
    BDBCDF,  !- Building Surface Name
    ,  !- Outside Boundary Condition Object
    ,  !- TRNSYS 17 - additional surface data
    ,  !- Shading Control Name
    ,  !- Frame and Divider Name
    ,  !- Multiplier
    4,  !- Number of Vertices
    13.351855913087,  !- Vertex 1 X-coordinate {m}
    9.040317238483,  !- Vertex 1 Y-coordinate {m}
    20.170000000000,  !- Vertex 1 Z-coordinate {m}
    13.351855913087,  !- Vertex 2 X-coordinate {m}
    9.040317238483,  !- Vertex 2 Y-coordinate {m}
    14.170000000000,  !- Vertex 2 Z-coordinate {m}
    13.855761299480,  !- Vertex 3 X-coordinate {m}
    11.489006553517,  !- Vertex 3 Y-coordinate {m}
    14.170000000000,  !- Vertex 3 Z-coordinate {m}
    13.855761299480,  !- Vertex 4 X-coordinate {m}
    11.489006553517,  !- Vertex 4 Y-coordinate {m}
    20.170000000000;  !- Vertex 4 Z-coordinate {m}

  FenestrationSurface:Detailed,
    6A057F,  !- Name
    Window,  !- Surface Type
    EXT_WINDOW_SG,  !- Construction Name
    1C1421,  !- Building Surface Name
    ,  !- Outside Boundary Condition Object
    ,  !- TRNSYS 17 - additional surface data
    ,  !- Shading Control Name
    ,  !- Frame and Divider Name
    ,  !- Multiplier
    4,  !- Number of Vertices
    13.351855913087,  !- Vertex 1 X-coordinate {m}
    9.040317238483,  !- Vertex 1 Y-coordinate {m}
    10.612400000000,  !- Vertex 1 Z-coordinate {m}
    13.351855913087,  !- Vertex 2 X-coordinate {m}
    9.040317238483,  !- Vertex 2 Y-coordinate {m}
    5.367600000000,  !- Vertex 2 Z-coordinate {m}
    13.855761299480,  !- Vertex 3 X-coordinate {m}
    11.489006553517,  !- Vertex 3 Y-coordinate {m}
    5.367600000000,  !- Vertex 3 Z-coordinate {m}
    13.855761299480,  !- Vertex 4 X-coordinate {m}
    11.489006553517,  !- Vertex 4 Y-coordinate {m}
    10.612400000000;  !- Vertex 4 Z-coordinate {m}

  FenestrationSurface:Detailed,
    C6B866,  !- Name
    Door,  !- Surface Type
    ,  !- Construction Name
    376070,  !- Building Surface Name
    ,  !- Outside Boundary Condition Object
    ,  !- TRNSYS 17 - additional surface data
    ,  !- Shading Control Name
    ,  !- Frame and Divider Name
    ,  !- Multiplier
    4,  !- Number of Vertices
    13.418371424091,  !- Vertex 1 X-coordinate {m}
    9.363544228068,  !- Vertex 1 Y-coordinate {m}
    3.300000000000,  !- Vertex 1 Z-coordinate {m}
    13.418371424091,  !- Vertex 2 X-coordinate {m}
    9.363544228068,  !- Vertex 2 Y-coordinate {m}
    0.000000000000,  !- Vertex 2 Z-coordinate {m}
    13.789245788476,  !- Vertex 3 X-coordinate {m}
    11.165779563932,  !- Vertex 3 Y-coordinate {m}
    0.000000000000,  !- Vertex 3 Z-coordinate {m}
    13.789245788476,  !- Vertex 4 X-coordinate {m}
    11.165779563932,  !- Vertex 4 Y-coordinate {m}
    3.300000000000;  !- Vertex 4 Z-coordinate {m}

  FenestrationSurface:Detailed,
    8D700D,  !- Name
    Window,  !- Surface Type
    EXT_WINDOW_SG,  !- Construction Name
    F1D81E,  !- Building Surface Name
    ,  !- Outside Boundary Condition Object
    ,  !- TRNSYS 17 - additional surface data
    ,  !- Shading Control Name
    ,  !- Frame and Divider Name
    ,  !- Multiplier
    4,  !- Number of Vertices
    59.830727809203,  !- Vertex 1 X-coordinate {m}
    50.681283246644,  !- Vertex 1 Y-coordinate {m}
    25.460000000000,  !- Vertex 1 Z-coordinate {m}
    59.830727809203,  !- Vertex 2 X-coordinate {m}
    50.681283246644,  !- Vertex 2 Y-coordinate {m}
    22.560000000000,  !- Vertex 2 Z-coordinate {m}
    43.742276939946,  !- Vertex 3 X-coordinate {m}
    17.896040398260,  !- Vertex 3 Y-coordinate {m}
    22.560000000000,  !- Vertex 3 Z-coordinate {m}
    43.742276939946,  !- Vertex 4 X-coordinate {m}
    17.896040398261,  !- Vertex 4 Y-coordinate {m}
    25.460000000000;  !- Vertex 4 Z-coordinate {m}

  FenestrationSurface:Detailed,
    A9A38B,  !- Name
    Window,  !- Surface Type
    EXT_WINDOW_SG,  !- Construction Name
    EB5B01,  !- Building Surface Name
    ,  !- Outside Boundary Condition Object
    ,  !- TRNSYS 17 - additional surface data
    ,  !- Shading Control Name
    ,  !- Frame and Divider Name
    ,  !- Multiplier
    4,  !- Number of Vertices
    59.830727533012,  !- Vertex 1 X-coordinate {m}
    50.681283382177,  !- Vertex 1 Y-coordinate {m}
    20.870000000000,  !- Vertex 1 Z-coordinate {m}
    59.830727533012,  !- Vertex 2 X-coordinate {m}
    50.681283382177,  !- Vertex 2 Y-coordinate {m}
    17.970000000000,  !- Vertex 2 Z-coordinate {m}
    46.571016269985,  !- Vertex 3 X-coordinate {m}
    23.660480281161,  !- Vertex 3 Y-coordinate {m}
    17.970000000000,  !- Vertex 3 Z-coordinate {m}
    46.571016269985,  !- Vertex 4 X-coordinate {m}
    23.660480281161,  !- Vertex 4 Y-coordinate {m}
    20.870000000000;  !- Vertex 4 Z-coordinate {m}

  FenestrationSurface:Detailed,
    7FDC2A,  !- Name
    Window,  !- Surface Type
    EXT_WINDOW_SG,  !- Construction Name
    F73EBB,  !- Building Surface Name
    ,  !- Outside Boundary Condition Object
    ,  !- TRNSYS 17 - additional surface data
    ,  !- Shading Control Name
    ,  !- Frame and Divider Name
    ,  !- Multiplier
    4,  !- Number of Vertices
    46.571016269985,  !- Vertex 1 X-coordinate {m}
    23.660480281161,  !- Vertex 1 Y-coordinate {m}
    20.870000000000,  !- Vertex 1 Z-coordinate {m}
    46.571016269985,  !- Vertex 2 X-coordinate {m}
    23.660480281161,  !- Vertex 2 Y-coordinate {m}
    17.970000000000,  !- Vertex 2 Z-coordinate {m}
    43.742276917607,  !- Vertex 3 X-coordinate {m}
    17.896040409224,  !- Vertex 3 Y-coordinate {m}
    17.970000000000,  !- Vertex 3 Z-coordinate {m}
    43.742276917607,  !- Vertex 4 X-coordinate {m}
    17.896040409224,  !- Vertex 4 Y-coordinate {m}
    20.870000000000;  !- Vertex 4 Z-coordinate {m}

  FenestrationSurface:Detailed,
    15A0BC,  !- Name
    Window,  !- Surface Type
    EXT_WINDOW_SG,  !- Construction Name
    C33312,  !- Building Surface Name
    ,  !- Outside Boundary Condition Object
    ,  !- TRNSYS 17 - additional surface data
    ,  !- Shading Control Name
    ,  !- Frame and Divider Name
    ,  !- Multiplier
    4,  !- Number of Vertices
    59.830727801689,  !- Vertex 1 X-coordinate {m}
    50.681283250331,  !- Vertex 1 Y-coordinate {m}
    16.280000000000,  !- Vertex 1 Z-coordinate {m}
    59.830727801689,  !- Vertex 2 X-coordinate {m}
    50.681283250331,  !- Vertex 2 Y-coordinate {m}
    13.380000000000,  !- Vertex 2 Z-coordinate {m}
    44.808863920672,  !- Vertex 3 X-coordinate {m}
    20.069544587079,  !- Vertex 3 Y-coordinate {m}
    13.380000000000,  !- Vertex 3 Z-coordinate {m}
    44.808863920672,  !- Vertex 4 X-coordinate {m}
    20.069544587079,  !- Vertex 4 Y-coordinate {m}
    16.280000000000;  !- Vertex 4 Z-coordinate {m}

  FenestrationSurface:Detailed,
    98F3B3,  !- Name
    Window,  !- Surface Type
    EXT_WINDOW_SG,  !- Construction Name
    FD319A,  !- Building Surface Name
    ,  !- Outside Boundary Condition Object
    ,  !- TRNSYS 17 - additional surface data
    ,  !- Shading Control Name
    ,  !- Frame and Divider Name
    ,  !- Multiplier
    4,  !- Number of Vertices
    44.808864203461,  !- Vertex 1 X-coordinate {m}
    20.069544448307,  !- Vertex 1 Y-coordinate {m}
    16.280000000000,  !- Vertex 1 Z-coordinate {m}
    44.808864203461,  !- Vertex 2 X-coordinate {m}
    20.069544448307,  !- Vertex 2 Y-coordinate {m}
    13.380000000000,  !- Vertex 2 Z-coordinate {m}
    43.742277099886,  !- Vertex 3 X-coordinate {m}
    17.896040319774,  !- Vertex 3 Y-coordinate {m}
    13.380000000000,  !- Vertex 3 Z-coordinate {m}
    43.742277099886,  !- Vertex 4 X-coordinate {m}
    17.896040319774,  !- Vertex 4 Y-coordinate {m}
    16.280000000000;  !- Vertex 4 Z-coordinate {m}

  FenestrationSurface:Detailed,
    E9DCE7,  !- Name
    Window,  !- Surface Type
    EXT_WINDOW_SG,  !- Construction Name
    C08D7D,  !- Building Surface Name
    ,  !- Outside Boundary Condition Object
    ,  !- TRNSYS 17 - additional surface data
    ,  !- Shading Control Name
    ,  !- Frame and Divider Name
    ,  !- Multiplier
    4,  !- Number of Vertices
    59.830727527992,  !- Vertex 1 X-coordinate {m}
    50.681283384641,  !- Vertex 1 Y-coordinate {m}
    11.690000000000,  !- Vertex 1 Z-coordinate {m}
    59.830727527992,  !- Vertex 2 X-coordinate {m}
    50.681283384641,  !- Vertex 2 Y-coordinate {m}
    8.790000000000,  !- Vertex 2 Z-coordinate {m}
    43.742276902680,  !- Vertex 3 X-coordinate {m}
    17.896040416548,  !- Vertex 3 Y-coordinate {m}
    8.790000000000,  !- Vertex 3 Z-coordinate {m}
    43.742276902680,  !- Vertex 4 X-coordinate {m}
    17.896040416548,  !- Vertex 4 Y-coordinate {m}
    11.690000000000;  !- Vertex 4 Z-coordinate {m}

  FenestrationSurface:Detailed,
    71BB7D,  !- Name
    Window,  !- Surface Type
    EXT_WINDOW_SG,  !- Construction Name
    12F867,  !- Building Surface Name
    ,  !- Outside Boundary Condition Object
    ,  !- TRNSYS 17 - additional surface data
    ,  !- Shading Control Name
    ,  !- Frame and Divider Name
    ,  !- Multiplier
    4,  !- Number of Vertices
    45.634532548241,  !- Vertex 1 X-coordinate {m}
    21.752102292381,  !- Vertex 1 Y-coordinate {m}
    3.300000000000,  !- Vertex 1 Z-coordinate {m}
    45.634532548241,  !- Vertex 2 X-coordinate {m}
    21.752102292381,  !- Vertex 2 Y-coordinate {m}
    1.500000000000,  !- Vertex 2 Z-coordinate {m}
    41.339626522549,  !- Vertex 3 X-coordinate {m}
    12.999889860195,  !- Vertex 3 Y-coordinate {m}
    1.500000000000,  !- Vertex 3 Z-coordinate {m}
    41.339626522549,  !- Vertex 4 X-coordinate {m}
    12.999889860195,  !- Vertex 4 Y-coordinate {m}
    3.300000000000;  !- Vertex 4 Z-coordinate {m}

  FenestrationSurface:Detailed,
    8739EB,  !- Name
    Window,  !- Surface Type
    EXT_WINDOW_SG,  !- Construction Name
    EBDC5E,  !- Building Surface Name
    ,  !- Outside Boundary Condition Object
    ,  !- TRNSYS 17 - additional surface data
    ,  !- Shading Control Name
    ,  !- Frame and Divider Name
    ,  !- Multiplier
    4,  !- Number of Vertices
    45.634532548241,  !- Vertex 1 X-coordinate {m}
    21.752102292381,  !- Vertex 1 Y-coordinate {m}
    7.210000000000,  !- Vertex 1 Z-coordinate {m}
    45.634532548241,  !- Vertex 2 X-coordinate {m}
    21.752102292381,  !- Vertex 2 Y-coordinate {m}
    4.960000000000,  !- Vertex 2 Z-coordinate {m}
    41.339626522549,  !- Vertex 3 X-coordinate {m}
    12.999889860195,  !- Vertex 3 Y-coordinate {m}
    4.960000000000,  !- Vertex 3 Z-coordinate {m}
    41.339626522549,  !- Vertex 4 X-coordinate {m}
    12.999889860195,  !- Vertex 4 Y-coordinate {m}
    7.210000000000;  !- Vertex 4 Z-coordinate {m}

  FenestrationSurface:Detailed,
    1B8B9B,  !- Name
    Door,  !- Surface Type
    ,  !- Construction Name
    199120,  !- Building Surface Name
    ,  !- Outside Boundary Condition Object
    ,  !- TRNSYS 17 - additional surface data
    ,  !- Shading Control Name
    ,  !- Frame and Divider Name
    ,  !- Multiplier
    4,  !- Number of Vertices
    54.191840123720,  !- Vertex 1 X-coordinate {m}
    39.190289135145,  !- Vertex 1 Y-coordinate {m}
    3.300000000000,  !- Vertex 1 Z-coordinate {m}
    54.191840123720,  !- Vertex 2 X-coordinate {m}
    39.190289135145,  !- Vertex 2 Y-coordinate {m}
    0.000000000000,  !- Vertex 2 Z-coordinate {m}
    51.328342613738,  !- Vertex 3 X-coordinate {m}
    33.355018617823,  !- Vertex 3 Y-coordinate {m}
    0.000000000000,  !- Vertex 3 Z-coordinate {m}
    51.328342613738,  !- Vertex 4 X-coordinate {m}
    33.355018617823,  !- Vertex 4 Y-coordinate {m}
    3.300000000000;  !- Vertex 4 Z-coordinate {m}

  FenestrationSurface:Detailed,
    F39C0E,  !- Name
    Window,  !- Surface Type
    EXT_WINDOW_SG,  !- Construction Name
    199120,  !- Building Surface Name
    ,  !- Outside Boundary Condition Object
    ,  !- TRNSYS 17 - additional surface data
    ,  !- Shading Control Name
    ,  !- Frame and Divider Name
    ,  !- Multiplier
    4,  !- Number of Vertices
    58.487086388693,  !- Vertex 1 X-coordinate {m}
    47.943194911129,  !- Vertex 1 Y-coordinate {m}
    7.210000000000,  !- Vertex 1 Z-coordinate {m}
    58.487086388693,  !- Vertex 2 X-coordinate {m}
    47.943194911129,  !- Vertex 2 Y-coordinate {m}
    3.410000000000,  !- Vertex 2 Z-coordinate {m}
    47.033096348766,  !- Vertex 3 X-coordinate {m}
    24.602112841840,  !- Vertex 3 Y-coordinate {m}
    3.410000000000,  !- Vertex 3 Z-coordinate {m}
    47.033096348766,  !- Vertex 4 X-coordinate {m}
    24.602112841840,  !- Vertex 4 Y-coordinate {m}
    7.210000000000;  !- Vertex 4 Z-coordinate {m}

  FenestrationSurface:Detailed,
    53E402,  !- Name
    Window,  !- Surface Type
    EXT_WINDOW_SG,  !- Construction Name
    6EE34E,  !- Building Surface Name
    ,  !- Outside Boundary Condition Object
    ,  !- TRNSYS 17 - additional surface data
    ,  !- Shading Control Name
    ,  !- Frame and Divider Name
    ,  !- Multiplier
    4,  !- Number of Vertices
    -3.759984846011,  !- Vertex 1 X-coordinate {m}
    42.976823447490,  !- Vertex 1 Y-coordinate {m}
    3.120000000000,  !- Vertex 1 Z-coordinate {m}
    -3.759984846011,  !- Vertex 2 X-coordinate {m}
    42.976823447490,  !- Vertex 2 Y-coordinate {m}
    0.800000000000,  !- Vertex 2 Z-coordinate {m}
    -1.550586767358,  !- Vertex 3 X-coordinate {m}
    17.723287850865,  !- Vertex 3 Y-coordinate {m}
    0.800000000000,  !- Vertex 3 Z-coordinate {m}
    -1.550586767358,  !- Vertex 4 X-coordinate {m}
    17.723287850865,  !- Vertex 4 Y-coordinate {m}
    3.120000000000;  !- Vertex 4 Z-coordinate {m}

  FenestrationSurface:Detailed,
    100B7C,  !- Name
    Window,  !- Surface Type
    EXT_WINDOW_SG,  !- Construction Name
    840AA7,  !- Building Surface Name
    ,  !- Outside Boundary Condition Object
    ,  !- TRNSYS 17 - additional surface data
    ,  !- Shading Control Name
    ,  !- Frame and Divider Name
    ,  !- Multiplier
    4,  !- Number of Vertices
    -0.867939412286,  !- Vertex 1 X-coordinate {m}
    9.920592878061,  !- Vertex 1 Y-coordinate {m}
    3.120000000000,  !- Vertex 1 Z-coordinate {m}
    -0.867939412286,  !- Vertex 2 X-coordinate {m}
    9.920592878061,  !- Vertex 2 Y-coordinate {m}
    0.800000000000,  !- Vertex 2 Z-coordinate {m}
    -0.619545545455,  !- Vertex 3 X-coordinate {m}
    7.081437988500,  !- Vertex 3 Y-coordinate {m}
    0.800000000000,  !- Vertex 3 Z-coordinate {m}
    -0.619545545455,  !- Vertex 4 X-coordinate {m}
    7.081437988500,  !- Vertex 4 Y-coordinate {m}
    3.120000000000;  !- Vertex 4 Z-coordinate {m}

  FenestrationSurface:Detailed,
    552ECF,  !- Name
    Window,  !- Surface Type
    EXT_WINDOW_SG,  !- Construction Name
    55D449,  !- Building Surface Name
    ,  !- Outside Boundary Condition Object
    ,  !- TRNSYS 17 - additional surface data
    ,  !- Shading Control Name
    ,  !- Frame and Divider Name
    ,  !- Multiplier
    4,  !- Number of Vertices
    12.582233491957,  !- Vertex 1 X-coordinate {m}
    64.259629125941,  !- Vertex 1 Y-coordinate {m}
    30.250000000000,  !- Vertex 1 Z-coordinate {m}
    12.582233491957,  !- Vertex 2 X-coordinate {m}
    64.259629125941,  !- Vertex 2 Y-coordinate {m}
    27.150000000000,  !- Vertex 2 Z-coordinate {m}
    5.315042979112,  !- Vertex 3 X-coordinate {m}
    63.623832340385,  !- Vertex 3 Y-coordinate {m}
    27.150000000000,  !- Vertex 3 Z-coordinate {m}
    5.315042979112,  !- Vertex 4 X-coordinate {m}
    63.623832340385,  !- Vertex 4 Y-coordinate {m}
    30.250000000000;  !- Vertex 4 Z-coordinate {m}

  FenestrationSurface:Detailed,
    45D0FF,  !- Name
    Window,  !- Surface Type
    EXT_WINDOW_SG,  !- Construction Name
    EDC019,  !- Building Surface Name
    ,  !- Outside Boundary Condition Object
    ,  !- TRNSYS 17 - additional surface data
    ,  !- Shading Control Name
    ,  !- Frame and Divider Name
    ,  !- Multiplier
    4,  !- Number of Vertices
    12.582233491957,  !- Vertex 1 X-coordinate {m}
    64.259629125941,  !- Vertex 1 Y-coordinate {m}
    25.660000000000,  !- Vertex 1 Z-coordinate {m}
    12.582233491957,  !- Vertex 2 X-coordinate {m}
    64.259629125941,  !- Vertex 2 Y-coordinate {m}
    22.560000000000,  !- Vertex 2 Z-coordinate {m}
    5.315042979112,  !- Vertex 3 X-coordinate {m}
    63.623832340385,  !- Vertex 3 Y-coordinate {m}
    22.560000000000,  !- Vertex 3 Z-coordinate {m}
    5.315042979112,  !- Vertex 4 X-coordinate {m}
    63.623832340385,  !- Vertex 4 Y-coordinate {m}
    25.660000000000;  !- Vertex 4 Z-coordinate {m}

  FenestrationSurface:Detailed,
    A47E39,  !- Name
    Window,  !- Surface Type
    EXT_WINDOW_SG,  !- Construction Name
    E2F99C,  !- Building Surface Name
    ,  !- Outside Boundary Condition Object
    ,  !- TRNSYS 17 - additional surface data
    ,  !- Shading Control Name
    ,  !- Frame and Divider Name
    ,  !- Multiplier
    4,  !- Number of Vertices
    12.582233491957,  !- Vertex 1 X-coordinate {m}
    64.259629125942,  !- Vertex 1 Y-coordinate {m}
    21.070000000000,  !- Vertex 1 Z-coordinate {m}
    12.582233491957,  !- Vertex 2 X-coordinate {m}
    64.259629125942,  !- Vertex 2 Y-coordinate {m}
    17.970000000000,  !- Vertex 2 Z-coordinate {m}
    5.315042979112,  !- Vertex 3 X-coordinate {m}
    63.623832340385,  !- Vertex 3 Y-coordinate {m}
    17.970000000000,  !- Vertex 3 Z-coordinate {m}
    5.315042979112,  !- Vertex 4 X-coordinate {m}
    63.623832340385,  !- Vertex 4 Y-coordinate {m}
    21.070000000000;  !- Vertex 4 Z-coordinate {m}

  FenestrationSurface:Detailed,
    CD6CA2,  !- Name
    Window,  !- Surface Type
    EXT_WINDOW_SG,  !- Construction Name
    611B27,  !- Building Surface Name
    ,  !- Outside Boundary Condition Object
    ,  !- TRNSYS 17 - additional surface data
    ,  !- Shading Control Name
    ,  !- Frame and Divider Name
    ,  !- Multiplier
    4,  !- Number of Vertices
    12.582233580160,  !- Vertex 1 X-coordinate {m}
    64.259629133658,  !- Vertex 1 Y-coordinate {m}
    16.480000000000,  !- Vertex 1 Z-coordinate {m}
    12.582233580160,  !- Vertex 2 X-coordinate {m}
    64.259629133658,  !- Vertex 2 Y-coordinate {m}
    13.380000000000,  !- Vertex 2 Z-coordinate {m}
    5.315042979112,  !- Vertex 3 X-coordinate {m}
    63.623832340385,  !- Vertex 3 Y-coordinate {m}
    13.380000000000,  !- Vertex 3 Z-coordinate {m}
    5.315042979112,  !- Vertex 4 X-coordinate {m}
    63.623832340385,  !- Vertex 4 Y-coordinate {m}
    16.480000000000;  !- Vertex 4 Z-coordinate {m}

  FenestrationSurface:Detailed,
    24682D,  !- Name
    Window,  !- Surface Type
    EXT_WINDOW_SG,  !- Construction Name
    CF716B,  !- Building Surface Name
    ,  !- Outside Boundary Condition Object
    ,  !- TRNSYS 17 - additional surface data
    ,  !- Shading Control Name
    ,  !- Frame and Divider Name
    ,  !- Multiplier
    4,  !- Number of Vertices
    12.582233580160,  !- Vertex 1 X-coordinate {m}
    64.259629133658,  !- Vertex 1 Y-coordinate {m}
    11.890000000000,  !- Vertex 1 Z-coordinate {m}
    12.582233580160,  !- Vertex 2 X-coordinate {m}
    64.259629133658,  !- Vertex 2 Y-coordinate {m}
    8.790000000000,  !- Vertex 2 Z-coordinate {m}
    5.315042979112,  !- Vertex 3 X-coordinate {m}
    63.623832340385,  !- Vertex 3 Y-coordinate {m}
    8.790000000000,  !- Vertex 3 Z-coordinate {m}
    5.315042979112,  !- Vertex 4 X-coordinate {m}
    63.623832340385,  !- Vertex 4 Y-coordinate {m}
    11.890000000000;  !- Vertex 4 Z-coordinate {m}

  FenestrationSurface:Detailed,
    81A1E9,  !- Name
    Window,  !- Surface Type
    EXT_WINDOW_SG,  !- Construction Name
    63C225,  !- Building Surface Name
    ,  !- Outside Boundary Condition Object
    ,  !- TRNSYS 17 - additional surface data
    ,  !- Shading Control Name
    ,  !- Frame and Divider Name
    ,  !- Multiplier
    4,  !- Number of Vertices
    12.187071708591,  !- Vertex 1 X-coordinate {m}
    68.776349993744,  !- Vertex 1 Y-coordinate {m}
    7.300000000000,  !- Vertex 1 Z-coordinate {m}
    12.187071708591,  !- Vertex 2 X-coordinate {m}
    68.776349993744,  !- Vertex 2 Y-coordinate {m}
    6.600000000000,  !- Vertex 2 Z-coordinate {m}
    7.390443958811,  !- Vertex 3 X-coordinate {m}
    68.356699442485,  !- Vertex 3 Y-coordinate {m}
    6.600000000000,  !- Vertex 3 Z-coordinate {m}
    7.390443958811,  !- Vertex 4 X-coordinate {m}
    68.356699442485,  !- Vertex 4 Y-coordinate {m}
    7.300000000000;  !- Vertex 4 Z-coordinate {m}

  FenestrationSurface:Detailed,
    2C2DA6,  !- Name
    Window,  !- Surface Type
    EXT_WINDOW_SG,  !- Construction Name
    63C225,  !- Building Surface Name
    ,  !- Outside Boundary Condition Object
    ,  !- TRNSYS 17 - additional surface data
    ,  !- Shading Control Name
    ,  !- Frame and Divider Name
    ,  !- Multiplier
    4,  !- Number of Vertices
    6.394249260719,  !- Vertex 1 X-coordinate {m}
    68.269543699737,  !- Vertex 1 Y-coordinate {m}
    7.300000000000,  !- Vertex 1 Z-coordinate {m}
    6.394249260719,  !- Vertex 2 X-coordinate {m}
    68.269543699737,  !- Vertex 2 Y-coordinate {m}
    5.600000000000,  !- Vertex 2 Z-coordinate {m}
    3.923686409452,  !- Vertex 3 X-coordinate {m}
    68.053397457723,  !- Vertex 3 Y-coordinate {m}
    5.600000000000,  !- Vertex 3 Z-coordinate {m}
    3.923686409452,  !- Vertex 4 X-coordinate {m}
    68.053397457723,  !- Vertex 4 Y-coordinate {m}
    7.300000000000;  !- Vertex 4 Z-coordinate {m}

  FenestrationSurface:Detailed,
    480EBF,  !- Name
    Window,  !- Surface Type
    EXT_WINDOW_SG,  !- Construction Name
    D5CE6D,  !- Building Surface Name
    ,  !- Outside Boundary Condition Object
    ,  !- TRNSYS 17 - additional surface data
    ,  !- Shading Control Name
    ,  !- Frame and Divider Name
    ,  !- Multiplier
    4,  !- Number of Vertices
    2.889398766899,  !- Vertex 1 X-coordinate {m}
    64.557952125227,  !- Vertex 1 Y-coordinate {m}
    30.250000000000,  !- Vertex 1 Z-coordinate {m}
    2.889398766899,  !- Vertex 2 X-coordinate {m}
    64.557952125227,  !- Vertex 2 Y-coordinate {m}
    27.150000000000,  !- Vertex 2 Z-coordinate {m}
    2.693298345717,  !- Vertex 3 X-coordinate {m}
    66.799390195934,  !- Vertex 3 Y-coordinate {m}
    27.150000000000,  !- Vertex 3 Z-coordinate {m}
    2.693298345717,  !- Vertex 4 X-coordinate {m}
    66.799390195934,  !- Vertex 4 Y-coordinate {m}
    30.250000000000;  !- Vertex 4 Z-coordinate {m}

  FenestrationSurface:Detailed,
    1F886B,  !- Name
    Window,  !- Surface Type
    EXT_WINDOW_SG,  !- Construction Name
    E803E3,  !- Building Surface Name
    ,  !- Outside Boundary Condition Object
    ,  !- TRNSYS 17 - additional surface data
    ,  !- Shading Control Name
    ,  !- Frame and Divider Name
    ,  !- Multiplier
    4,  !- Number of Vertices
    2.889398766899,  !- Vertex 1 X-coordinate {m}
    64.557952125227,  !- Vertex 1 Y-coordinate {m}
    25.660000000000,  !- Vertex 1 Z-coordinate {m}
    2.889398766899,  !- Vertex 2 X-coordinate {m}
    64.557952125227,  !- Vertex 2 Y-coordinate {m}
    22.560000000000,  !- Vertex 2 Z-coordinate {m}
    2.693298345717,  !- Vertex 3 X-coordinate {m}
    66.799390195934,  !- Vertex 3 Y-coordinate {m}
    22.560000000000,  !- Vertex 3 Z-coordinate {m}
    2.693298345717,  !- Vertex 4 X-coordinate {m}
    66.799390195934,  !- Vertex 4 Y-coordinate {m}
    25.660000000000;  !- Vertex 4 Z-coordinate {m}

  FenestrationSurface:Detailed,
    5635B6,  !- Name
    Window,  !- Surface Type
    EXT_WINDOW_SG,  !- Construction Name
    C32016,  !- Building Surface Name
    ,  !- Outside Boundary Condition Object
    ,  !- TRNSYS 17 - additional surface data
    ,  !- Shading Control Name
    ,  !- Frame and Divider Name
    ,  !- Multiplier
    4,  !- Number of Vertices
    2.889398766899,  !- Vertex 1 X-coordinate {m}
    64.557952125227,  !- Vertex 1 Y-coordinate {m}
    20.970000000000,  !- Vertex 1 Z-coordinate {m}
    2.889398766899,  !- Vertex 2 X-coordinate {m}
    64.557952125227,  !- Vertex 2 Y-coordinate {m}
    17.970000000000,  !- Vertex 2 Z-coordinate {m}
    2.693298345717,  !- Vertex 3 X-coordinate {m}
    66.799390195934,  !- Vertex 3 Y-coordinate {m}
    17.970000000000,  !- Vertex 3 Z-coordinate {m}
    2.693298345717,  !- Vertex 4 X-coordinate {m}
    66.799390195934,  !- Vertex 4 Y-coordinate {m}
    20.970000000000;  !- Vertex 4 Z-coordinate {m}

  FenestrationSurface:Detailed,
    B47504,  !- Name
    Window,  !- Surface Type
    EXT_WINDOW_SG,  !- Construction Name
    BDE2EC,  !- Building Surface Name
    ,  !- Outside Boundary Condition Object
    ,  !- TRNSYS 17 - additional surface data
    ,  !- Shading Control Name
    ,  !- Frame and Divider Name
    ,  !- Multiplier
    4,  !- Number of Vertices
    2.889398766899,  !- Vertex 1 X-coordinate {m}
    64.557952125227,  !- Vertex 1 Y-coordinate {m}
    16.480000000000,  !- Vertex 1 Z-coordinate {m}
    2.889398766899,  !- Vertex 2 X-coordinate {m}
    64.557952125227,  !- Vertex 2 Y-coordinate {m}
    13.380000000000,  !- Vertex 2 Z-coordinate {m}
    2.693298345717,  !- Vertex 3 X-coordinate {m}
    66.799390195934,  !- Vertex 3 Y-coordinate {m}
    13.380000000000,  !- Vertex 3 Z-coordinate {m}
    2.693298345717,  !- Vertex 4 X-coordinate {m}
    66.799390195934,  !- Vertex 4 Y-coordinate {m}
    16.480000000000;  !- Vertex 4 Z-coordinate {m}

  FenestrationSurface:Detailed,
    3C3F43,  !- Name
    Window,  !- Surface Type
    EXT_WINDOW_SG,  !- Construction Name
    1FC3FA,  !- Building Surface Name
    ,  !- Outside Boundary Condition Object
    ,  !- TRNSYS 17 - additional surface data
    ,  !- Shading Control Name
    ,  !- Frame and Divider Name
    ,  !- Multiplier
    4,  !- Number of Vertices
    2.889398766899,  !- Vertex 1 X-coordinate {m}
    64.557952125227,  !- Vertex 1 Y-coordinate {m}
    11.890000000000,  !- Vertex 1 Z-coordinate {m}
    2.889398766899,  !- Vertex 2 X-coordinate {m}
    64.557952125227,  !- Vertex 2 Y-coordinate {m}
    8.790000000000,  !- Vertex 2 Z-coordinate {m}
    2.693298345717,  !- Vertex 3 X-coordinate {m}
    66.799390195934,  !- Vertex 3 Y-coordinate {m}
    8.790000000000,  !- Vertex 3 Z-coordinate {m}
    2.693298345717,  !- Vertex 4 X-coordinate {m}
    66.799390195934,  !- Vertex 4 Y-coordinate {m}
    11.890000000000;  !- Vertex 4 Z-coordinate {m}

  FenestrationSurface:Detailed,
    FC0007,  !- Name
    Window,  !- Surface Type
    EXT_WINDOW_SG,  !- Construction Name
    82AE15,  !- Building Surface Name
    ,  !- Outside Boundary Condition Object
    ,  !- TRNSYS 17 - additional surface data
    ,  !- Shading Control Name
    ,  !- Frame and Divider Name
    ,  !- Multiplier
    4,  !- Number of Vertices
    53.607376941602,  !- Vertex 1 X-coordinate {m}
    9.624520586489,  !- Vertex 1 Y-coordinate {m}
    25.650000000000,  !- Vertex 1 Z-coordinate {m}
    53.607376941602,  !- Vertex 2 X-coordinate {m}
    9.624520586489,  !- Vertex 2 Y-coordinate {m}
    22.560000000000,  !- Vertex 2 Z-coordinate {m}
    69.164734971444,  !- Vertex 3 X-coordinate {m}
    41.322544359767,  !- Vertex 3 Y-coordinate {m}
    22.560000000000,  !- Vertex 3 Z-coordinate {m}
    69.164734971444,  !- Vertex 4 X-coordinate {m}
    41.322544359767,  !- Vertex 4 Y-coordinate {m}
    25.650000000000;  !- Vertex 4 Z-coordinate {m}

  FenestrationSurface:Detailed,
    C5F9C6,  !- Name
    Window,  !- Surface Type
    EXT_WINDOW_SG,  !- Construction Name
    82AE15,  !- Building Surface Name
    ,  !- Outside Boundary Condition Object
    ,  !- TRNSYS 17 - additional surface data
    ,  !- Shading Control Name
    ,  !- Frame and Divider Name
    ,  !- Multiplier
    4,  !- Number of Vertices
    70.300924683753,  !- Vertex 1 X-coordinate {m}
    43.637524091072,  !- Vertex 1 Y-coordinate {m}
    25.650000000000,  !- Vertex 1 Z-coordinate {m}
    70.300924683753,  !- Vertex 2 X-coordinate {m}
    43.637524091072,  !- Vertex 2 Y-coordinate {m}
    24.150000000000,  !- Vertex 2 Z-coordinate {m}
    72.415773693757,  !- Vertex 3 X-coordinate {m}
    47.946516277754,  !- Vertex 3 Y-coordinate {m}
    24.150000000000,  !- Vertex 3 Z-coordinate {m}
    72.415773693757,  !- Vertex 4 X-coordinate {m}
    47.946516277754,  !- Vertex 4 Y-coordinate {m}
    25.650000000000;  !- Vertex 4 Z-coordinate {m}

  FenestrationSurface:Detailed,
    2EDE85,  !- Name
    Window,  !- Surface Type
    EXT_WINDOW_SG,  !- Construction Name
    8E85EC,  !- Building Surface Name
    ,  !- Outside Boundary Condition Object
    ,  !- TRNSYS 17 - additional surface data
    ,  !- Shading Control Name
    ,  !- Frame and Divider Name
    ,  !- Multiplier
    4,  !- Number of Vertices
    53.607376941602,  !- Vertex 1 X-coordinate {m}
    9.624520586489,  !- Vertex 1 Y-coordinate {m}
    21.060000000000,  !- Vertex 1 Z-coordinate {m}
    53.607376941602,  !- Vertex 2 X-coordinate {m}
    9.624520586489,  !- Vertex 2 Y-coordinate {m}
    17.970000000000,  !- Vertex 2 Z-coordinate {m}
    57.793015607234,  !- Vertex 3 X-coordinate {m}
    18.152734289297,  !- Vertex 3 Y-coordinate {m}
    17.970000000000,  !- Vertex 3 Z-coordinate {m}
    57.793015607234,  !- Vertex 4 X-coordinate {m}
    18.152734289297,  !- Vertex 4 Y-coordinate {m}
    21.060000000000;  !- Vertex 4 Z-coordinate {m}

  FenestrationSurface:Detailed,
    E8081B,  !- Name
    Window,  !- Surface Type
    EXT_WINDOW_SG,  !- Construction Name
    545B0F,  !- Building Surface Name
    ,  !- Outside Boundary Condition Object
    ,  !- TRNSYS 17 - additional surface data
    ,  !- Shading Control Name
    ,  !- Frame and Divider Name
    ,  !- Multiplier
    4,  !- Number of Vertices
    57.793015607234,  !- Vertex 1 X-coordinate {m}
    18.152734289297,  !- Vertex 1 Y-coordinate {m}
    21.060000000000,  !- Vertex 1 Z-coordinate {m}
    57.793015607234,  !- Vertex 2 X-coordinate {m}
    18.152734289297,  !- Vertex 2 Y-coordinate {m}
    17.970000000000,  !- Vertex 2 Z-coordinate {m}
    69.164734971444,  !- Vertex 3 X-coordinate {m}
    41.322544359767,  !- Vertex 3 Y-coordinate {m}
    17.970000000000,  !- Vertex 3 Z-coordinate {m}
    69.164734971444,  !- Vertex 4 X-coordinate {m}
    41.322544359767,  !- Vertex 4 Y-coordinate {m}
    21.060000000000;  !- Vertex 4 Z-coordinate {m}

  FenestrationSurface:Detailed,
    2A95FD,  !- Name
    Window,  !- Surface Type
    EXT_WINDOW_SG,  !- Construction Name
    545B0F,  !- Building Surface Name
    ,  !- Outside Boundary Condition Object
    ,  !- TRNSYS 17 - additional surface data
    ,  !- Shading Control Name
    ,  !- Frame and Divider Name
    ,  !- Multiplier
    4,  !- Number of Vertices
    70.300924683753,  !- Vertex 1 X-coordinate {m}
    43.637524091072,  !- Vertex 1 Y-coordinate {m}
    21.060000000000,  !- Vertex 1 Z-coordinate {m}
    70.300924683753,  !- Vertex 2 X-coordinate {m}
    43.637524091072,  !- Vertex 2 Y-coordinate {m}
    19.560000000000,  !- Vertex 2 Z-coordinate {m}
    72.415773693757,  !- Vertex 3 X-coordinate {m}
    47.946516277754,  !- Vertex 3 Y-coordinate {m}
    19.560000000000,  !- Vertex 3 Z-coordinate {m}
    72.415773693757,  !- Vertex 4 X-coordinate {m}
    47.946516277754,  !- Vertex 4 Y-coordinate {m}
    21.060000000000;  !- Vertex 4 Z-coordinate {m}

  FenestrationSurface:Detailed,
    355CE5,  !- Name
    Window,  !- Surface Type
    EXT_WINDOW_SG,  !- Construction Name
    DB206A,  !- Building Surface Name
    ,  !- Outside Boundary Condition Object
    ,  !- TRNSYS 17 - additional surface data
    ,  !- Shading Control Name
    ,  !- Frame and Divider Name
    ,  !- Multiplier
    4,  !- Number of Vertices
    53.607376941602,  !- Vertex 1 X-coordinate {m}
    9.624520586489,  !- Vertex 1 Y-coordinate {m}
    16.470000000000,  !- Vertex 1 Z-coordinate {m}
    53.607376941602,  !- Vertex 2 X-coordinate {m}
    9.624520586489,  !- Vertex 2 Y-coordinate {m}
    13.380000000000,  !- Vertex 2 Z-coordinate {m}
    56.030641432231,  !- Vertex 3 X-coordinate {m}
    14.561907467061,  !- Vertex 3 Y-coordinate {m}
    13.380000000000,  !- Vertex 3 Z-coordinate {m}
    56.030641432231,  !- Vertex 4 X-coordinate {m}
    14.561907467061,  !- Vertex 4 Y-coordinate {m}
    16.470000000000;  !- Vertex 4 Z-coordinate {m}

  FenestrationSurface:Detailed,
    1AE7C4,  !- Name
    Window,  !- Surface Type
    EXT_WINDOW_SG,  !- Construction Name
    E6F13C,  !- Building Surface Name
    ,  !- Outside Boundary Condition Object
    ,  !- TRNSYS 17 - additional surface data
    ,  !- Shading Control Name
    ,  !- Frame and Divider Name
    ,  !- Multiplier
    4,  !- Number of Vertices
    56.030641432231,  !- Vertex 1 X-coordinate {m}
    14.561907467061,  !- Vertex 1 Y-coordinate {m}
    16.470000000000,  !- Vertex 1 Z-coordinate {m}
    56.030641432231,  !- Vertex 2 X-coordinate {m}
    14.561907467061,  !- Vertex 2 Y-coordinate {m}
    13.380000000000,  !- Vertex 2 Z-coordinate {m}
    69.164734971444,  !- Vertex 3 X-coordinate {m}
    41.322544359767,  !- Vertex 3 Y-coordinate {m}
    13.380000000000,  !- Vertex 3 Z-coordinate {m}
    69.164734971444,  !- Vertex 4 X-coordinate {m}
    41.322544359767,  !- Vertex 4 Y-coordinate {m}
    16.470000000000;  !- Vertex 4 Z-coordinate {m}

  FenestrationSurface:Detailed,
    78D8E1,  !- Name
    Window,  !- Surface Type
    EXT_WINDOW_SG,  !- Construction Name
    E6F13C,  !- Building Surface Name
    ,  !- Outside Boundary Condition Object
    ,  !- TRNSYS 17 - additional surface data
    ,  !- Shading Control Name
    ,  !- Frame and Divider Name
    ,  !- Multiplier
    4,  !- Number of Vertices
    70.300924683753,  !- Vertex 1 X-coordinate {m}
    43.637524091072,  !- Vertex 1 Y-coordinate {m}
    16.470000000000,  !- Vertex 1 Z-coordinate {m}
    70.300924683753,  !- Vertex 2 X-coordinate {m}
    43.637524091072,  !- Vertex 2 Y-coordinate {m}
    14.970000000000,  !- Vertex 2 Z-coordinate {m}
    72.415773693757,  !- Vertex 3 X-coordinate {m}
    47.946516277754,  !- Vertex 3 Y-coordinate {m}
    14.970000000000,  !- Vertex 3 Z-coordinate {m}
    72.415773693757,  !- Vertex 4 X-coordinate {m}
    47.946516277754,  !- Vertex 4 Y-coordinate {m}
    16.470000000000;  !- Vertex 4 Z-coordinate {m}

  FenestrationSurface:Detailed,
    C401D2,  !- Name
    Window,  !- Surface Type
    EXT_WINDOW_SG,  !- Construction Name
    9456BF,  !- Building Surface Name
    ,  !- Outside Boundary Condition Object
    ,  !- TRNSYS 17 - additional surface data
    ,  !- Shading Control Name
    ,  !- Frame and Divider Name
    ,  !- Multiplier
    4,  !- Number of Vertices
    53.607376941602,  !- Vertex 1 X-coordinate {m}
    9.624520586489,  !- Vertex 1 Y-coordinate {m}
    11.880000000000,  !- Vertex 1 Z-coordinate {m}
    53.607376941602,  !- Vertex 2 X-coordinate {m}
    9.624520586489,  !- Vertex 2 Y-coordinate {m}
    10.380000000000,  !- Vertex 2 Z-coordinate {m}
    69.164734971444,  !- Vertex 3 X-coordinate {m}
    41.322544359767,  !- Vertex 3 Y-coordinate {m}
    10.380000000000,  !- Vertex 3 Z-coordinate {m}
    69.164734971444,  !- Vertex 4 X-coordinate {m}
    41.322544359767,  !- Vertex 4 Y-coordinate {m}
    11.880000000000;  !- Vertex 4 Z-coordinate {m}

  FenestrationSurface:Detailed,
    A115DC,  !- Name
    Window,  !- Surface Type
    EXT_WINDOW_SG,  !- Construction Name
    9456BF,  !- Building Surface Name
    ,  !- Outside Boundary Condition Object
    ,  !- TRNSYS 17 - additional surface data
    ,  !- Shading Control Name
    ,  !- Frame and Divider Name
    ,  !- Multiplier
    4,  !- Number of Vertices
    70.300924683753,  !- Vertex 1 X-coordinate {m}
    43.637524091072,  !- Vertex 1 Y-coordinate {m}
    11.880000000000,  !- Vertex 1 Z-coordinate {m}
    70.300924683753,  !- Vertex 2 X-coordinate {m}
    43.637524091072,  !- Vertex 2 Y-coordinate {m}
    10.380000000000,  !- Vertex 2 Z-coordinate {m}
    72.415773693757,  !- Vertex 3 X-coordinate {m}
    47.946516277754,  !- Vertex 3 Y-coordinate {m}
    10.380000000000,  !- Vertex 3 Z-coordinate {m}
    72.415773693757,  !- Vertex 4 X-coordinate {m}
    47.946516277754,  !- Vertex 4 Y-coordinate {m}
    11.880000000000;  !- Vertex 4 Z-coordinate {m}

  FenestrationSurface:Detailed,
    B347E1,  !- Name
    Window,  !- Surface Type
    EXT_WINDOW_SG,  !- Construction Name
    EB9389,  !- Building Surface Name
    ,  !- Outside Boundary Condition Object
    ,  !- TRNSYS 17 - additional surface data
    ,  !- Shading Control Name
    ,  !- Frame and Divider Name
    ,  !- Multiplier
    4,  !- Number of Vertices
    53.607376941602,  !- Vertex 1 X-coordinate {m}
    9.624520586489,  !- Vertex 1 Y-coordinate {m}
    7.830000000000,  !- Vertex 1 Z-coordinate {m}
    53.607376941602,  !- Vertex 2 X-coordinate {m}
    9.624520586489,  !- Vertex 2 Y-coordinate {m}
    4.710000000000,  !- Vertex 2 Z-coordinate {m}
    56.911828519733,  !- Vertex 3 X-coordinate {m}
    16.357320878178,  !- Vertex 3 Y-coordinate {m}
    4.710000000000,  !- Vertex 3 Z-coordinate {m}
    56.911828519733,  !- Vertex 4 X-coordinate {m}
    16.357320878178,  !- Vertex 4 Y-coordinate {m}
    7.830000000000;  !- Vertex 4 Z-coordinate {m}

  FenestrationSurface:Detailed,
    8634CE,  !- Name
    Window,  !- Surface Type
    EXT_WINDOW_SG,  !- Construction Name
    7C3219,  !- Building Surface Name
    ,  !- Outside Boundary Condition Object
    ,  !- TRNSYS 17 - additional surface data
    ,  !- Shading Control Name
    ,  !- Frame and Divider Name
    ,  !- Multiplier
    4,  !- Number of Vertices
    56.911828519733,  !- Vertex 1 X-coordinate {m}
    16.357320878178,  !- Vertex 1 Y-coordinate {m}
    7.830000000000,  !- Vertex 1 Z-coordinate {m}
    56.911828519733,  !- Vertex 2 X-coordinate {m}
    16.357320878178,  !- Vertex 2 Y-coordinate {m}
    4.710000000000,  !- Vertex 2 Z-coordinate {m}
    69.164734971444,  !- Vertex 3 X-coordinate {m}
    41.322544359767,  !- Vertex 3 Y-coordinate {m}
    4.710000000000,  !- Vertex 3 Z-coordinate {m}
    69.164734971444,  !- Vertex 4 X-coordinate {m}
    41.322544359767,  !- Vertex 4 Y-coordinate {m}
    7.830000000000;  !- Vertex 4 Z-coordinate {m}

  FenestrationSurface:Detailed,
    A90B7C,  !- Name
    Window,  !- Surface Type
    EXT_WINDOW_SG,  !- Construction Name
    7C3219,  !- Building Surface Name
    ,  !- Outside Boundary Condition Object
    ,  !- TRNSYS 17 - additional surface data
    ,  !- Shading Control Name
    ,  !- Frame and Divider Name
    ,  !- Multiplier
    4,  !- Number of Vertices
    70.300924683753,  !- Vertex 1 X-coordinate {m}
    43.637524091072,  !- Vertex 1 Y-coordinate {m}
    3.890000000000,  !- Vertex 1 Z-coordinate {m}
    70.300924683753,  !- Vertex 2 X-coordinate {m}
    43.637524091072,  !- Vertex 2 Y-coordinate {m}
    2.390000000000,  !- Vertex 2 Z-coordinate {m}
    72.415773693757,  !- Vertex 3 X-coordinate {m}
    47.946516277754,  !- Vertex 3 Y-coordinate {m}
    2.390000000000,  !- Vertex 3 Z-coordinate {m}
    72.415773693757,  !- Vertex 4 X-coordinate {m}
    47.946516277754,  !- Vertex 4 Y-coordinate {m}
    3.890000000000;  !- Vertex 4 Z-coordinate {m}

  FenestrationSurface:Detailed,
    B3489C,  !- Name
    Window,  !- Surface Type
    EXT_WINDOW_SG,  !- Construction Name
    D7C7B0,  !- Building Surface Name
    ,  !- Outside Boundary Condition Object
    ,  !- TRNSYS 17 - additional surface data
    ,  !- Shading Control Name
    ,  !- Frame and Divider Name
    ,  !- Multiplier
    4,  !- Number of Vertices
    53.607376941602,  !- Vertex 1 X-coordinate {m}
    9.624520586489,  !- Vertex 1 Y-coordinate {m}
    3.110000000000,  !- Vertex 1 Z-coordinate {m}
    53.607376941602,  !- Vertex 2 X-coordinate {m}
    9.624520586489,  !- Vertex 2 Y-coordinate {m}
    1.010000000000,  !- Vertex 2 Z-coordinate {m}
    55.021682217042,  !- Vertex 3 X-coordinate {m}
    12.506159111332,  !- Vertex 3 Y-coordinate {m}
    1.010000000000,  !- Vertex 3 Z-coordinate {m}
    55.021682217042,  !- Vertex 4 X-coordinate {m}
    12.506159111332,  !- Vertex 4 Y-coordinate {m}
    3.110000000000;  !- Vertex 4 Z-coordinate {m}

  FenestrationSurface:Detailed,
    A20189,  !- Name
    Window,  !- Surface Type
    EXT_WINDOW_DG,  !- Construction Name
    197952,  !- Building Surface Name
    ,  !- Outside Boundary Condition Object
    ,  !- TRNSYS 17 - additional surface data
    ,  !- Shading Control Name
    ,  !- Frame and Divider Name
    ,  !- Multiplier
    4,  !- Number of Vertices
    7.821733791892,  !- Vertex 1 X-coordinate {m}
    -1.609601328521,  !- Vertex 1 Y-coordinate {m}
    20.810000000000,  !- Vertex 1 Z-coordinate {m}
    7.821733791892,  !- Vertex 2 X-coordinate {m}
    -1.609601328521,  !- Vertex 2 Y-coordinate {m}
    17.960000000000,  !- Vertex 2 Z-coordinate {m}
    11.024619423024,  !- Vertex 3 X-coordinate {m}
    -2.268709539582,  !- Vertex 3 Y-coordinate {m}
    17.960000000000,  !- Vertex 3 Z-coordinate {m}
    11.024619423024,  !- Vertex 4 X-coordinate {m}
    -2.268709539582,  !- Vertex 4 Y-coordinate {m}
    20.810000000000;  !- Vertex 4 Z-coordinate {m}

  FenestrationSurface:Detailed,
    B51A83,  !- Name
    Window,  !- Surface Type
    EXT_WINDOW_DG,  !- Construction Name
    197952,  !- Building Surface Name
    ,  !- Outside Boundary Condition Object
    ,  !- TRNSYS 17 - additional surface data
    ,  !- Shading Control Name
    ,  !- Frame and Divider Name
    ,  !- Multiplier
    4,  !- Number of Vertices
    7.821733791892,  !- Vertex 1 X-coordinate {m}
    -1.609601328521,  !- Vertex 1 Y-coordinate {m}
    16.230000000000,  !- Vertex 1 Z-coordinate {m}
    7.821733791892,  !- Vertex 2 X-coordinate {m}
    -1.609601328521,  !- Vertex 2 Y-coordinate {m}
    13.380000000000,  !- Vertex 2 Z-coordinate {m}
    11.024619423024,  !- Vertex 3 X-coordinate {m}
    -2.268709539582,  !- Vertex 3 Y-coordinate {m}
    13.380000000000,  !- Vertex 3 Z-coordinate {m}
    11.024619423024,  !- Vertex 4 X-coordinate {m}
    -2.268709539582,  !- Vertex 4 Y-coordinate {m}
    16.230000000000;  !- Vertex 4 Z-coordinate {m}

  FenestrationSurface:Detailed,
    CD0A11,  !- Name
    Window,  !- Surface Type
    EXT_WINDOW_DG,  !- Construction Name
    D3D445,  !- Building Surface Name
    ,  !- Outside Boundary Condition Object
    ,  !- TRNSYS 17 - additional surface data
    ,  !- Shading Control Name
    ,  !- Frame and Divider Name
    ,  !- Multiplier
    4,  !- Number of Vertices
    7.821733791892,  !- Vertex 1 X-coordinate {m}
    -1.609601328521,  !- Vertex 1 Y-coordinate {m}
    11.640000000000,  !- Vertex 1 Z-coordinate {m}
    7.821733791892,  !- Vertex 2 X-coordinate {m}
    -1.609601328521,  !- Vertex 2 Y-coordinate {m}
    8.790000000000,  !- Vertex 2 Z-coordinate {m}
    11.024619423024,  !- Vertex 3 X-coordinate {m}
    -2.268709539582,  !- Vertex 3 Y-coordinate {m}
    8.790000000000,  !- Vertex 3 Z-coordinate {m}
    11.024619423024,  !- Vertex 4 X-coordinate {m}
    -2.268709539582,  !- Vertex 4 Y-coordinate {m}
    11.640000000000;  !- Vertex 4 Z-coordinate {m}

  FenestrationSurface:Detailed,
    35A126,  !- Name
    Window,  !- Surface Type
    EXT_WINDOW_DG,  !- Construction Name
    809397,  !- Building Surface Name
    ,  !- Outside Boundary Condition Object
    ,  !- TRNSYS 17 - additional surface data
    ,  !- Shading Control Name
    ,  !- Frame and Divider Name
    ,  !- Multiplier
    4,  !- Number of Vertices
    7.821733791892,  !- Vertex 1 X-coordinate {m}
    -1.609601328521,  !- Vertex 1 Y-coordinate {m}
    25.410000000000,  !- Vertex 1 Z-coordinate {m}
    7.821733791892,  !- Vertex 2 X-coordinate {m}
    -1.609601328521,  !- Vertex 2 Y-coordinate {m}
    22.560000000000,  !- Vertex 2 Z-coordinate {m}
    11.024619423024,  !- Vertex 3 X-coordinate {m}
    -2.268709539582,  !- Vertex 3 Y-coordinate {m}
    22.560000000000,  !- Vertex 3 Z-coordinate {m}
    11.024619423024,  !- Vertex 4 X-coordinate {m}
    -2.268709539582,  !- Vertex 4 Y-coordinate {m}
    25.410000000000;  !- Vertex 4 Z-coordinate {m}

  FenestrationSurface:Detailed,
    EA07A0,  !- Name
    Window,  !- Surface Type
    EXT_WINDOW_SG,  !- Construction Name
    3BA882,  !- Building Surface Name
    ,  !- Outside Boundary Condition Object
    ,  !- TRNSYS 17 - additional surface data
    ,  !- Shading Control Name
    ,  !- Frame and Divider Name
    ,  !- Multiplier
    4,  !- Number of Vertices
    7.821733791892,  !- Vertex 1 X-coordinate {m}
    -1.609601328521,  !- Vertex 1 Y-coordinate {m}
    29.240000000000,  !- Vertex 1 Z-coordinate {m}
    7.821733791892,  !- Vertex 2 X-coordinate {m}
    -1.609601328521,  !- Vertex 2 Y-coordinate {m}
    27.150000000000,  !- Vertex 2 Z-coordinate {m}
    10.613239617191,  !- Vertex 3 X-coordinate {m}
    -2.184053439079,  !- Vertex 3 Y-coordinate {m}
    27.150000000000,  !- Vertex 3 Z-coordinate {m}
    10.613239617191,  !- Vertex 4 X-coordinate {m}
    -2.184053439079,  !- Vertex 4 Y-coordinate {m}
    29.240000000000;  !- Vertex 4 Z-coordinate {m}

  FenestrationSurface:Detailed,
    40CDBB,  !- Name
    Window,  !- Surface Type
    EXT_WINDOW_SG,  !- Construction Name
    CE3450,  !- Building Surface Name
    ,  !- Outside Boundary Condition Object
    ,  !- TRNSYS 17 - additional surface data
    ,  !- Shading Control Name
    ,  !- Frame and Divider Name
    ,  !- Multiplier
    4,  !- Number of Vertices
    7.694401947230,  !- Vertex 1 X-coordinate {m}
    -1.583398249794,  !- Vertex 1 Y-coordinate {m}
    3.000000000000,  !- Vertex 1 Z-coordinate {m}
    7.694401947230,  !- Vertex 2 X-coordinate {m}
    -1.583398249794,  !- Vertex 2 Y-coordinate {m}
    2.000000000000,  !- Vertex 2 Z-coordinate {m}
    10.485907772528,  !- Vertex 3 X-coordinate {m}
    -2.157850360352,  !- Vertex 3 Y-coordinate {m}
    2.000000000000,  !- Vertex 3 Z-coordinate {m}
    10.485907772528,  !- Vertex 4 X-coordinate {m}
    -2.157850360352,  !- Vertex 4 Y-coordinate {m}
    3.000000000000;  !- Vertex 4 Z-coordinate {m}

  BuildingSurface:Detailed,
    E12B4A,  !- Name
    Wall,  !- Surface Type
    EXT_WALL_SW_EF_RL,  !- Construction Name
    B2_F5_OF,  !- Zone Name
    Outdoors,  !- Outside Boundary Condition
    ,  !- Outside Boundary Condition Object
    SunExposed,  !- Sun Exposure
    WindExposed,  !- Wind Exposure
    ,  !- TRNSYS 17 - additional surface data
    4,  !- Number of Vertices
    -6.830235356449,  !- Vertex 1 X-coordinate {m}
    67.112551214762,  !- Vertex 1 Y-coordinate {m}
    30.940000000000,  !- Vertex 1 Z-coordinate {m}
    -6.830235356449,  !- Vertex 2 X-coordinate {m}
    67.112551214762,  !- Vertex 2 Y-coordinate {m}
    26.350000000000,  !- Vertex 2 Z-coordinate {m}
    -6.660281627363,  !- Vertex 3 X-coordinate {m}
    65.169971202261,  !- Vertex 3 Y-coordinate {m}
    26.350000000000,  !- Vertex 3 Z-coordinate {m}
    -6.660281627363,  !- Vertex 4 X-coordinate {m}
    65.169971202261,  !- Vertex 4 Y-coordinate {m}
    30.940000000000;  !- Vertex 4 Z-coordinate {m}

  BuildingSurface:Detailed,
    ED4000,  !- Name
    Wall,  !- Surface Type
    EXT_WALL_SW_EF_GL,  !- Construction Name
    B2_F5_OF,  !- Zone Name
    Outdoors,  !- Outside Boundary Condition
    ,  !- Outside Boundary Condition Object
    SunExposed,  !- Sun Exposure
    WindExposed,  !- Wind Exposure
    ,  !- TRNSYS 17 - additional surface data
    4,  !- Number of Vertices
    -6.660281627363,  !- Vertex 1 X-coordinate {m}
    65.169971202261,  !- Vertex 1 Y-coordinate {m}
    30.940000000000,  !- Vertex 1 Z-coordinate {m}
    -6.660281627363,  !- Vertex 2 X-coordinate {m}
    65.169971202261,  !- Vertex 2 Y-coordinate {m}
    26.350000000000,  !- Vertex 2 Z-coordinate {m}
    -5.523860194453,  !- Vertex 3 X-coordinate {m}
    52.180614786127,  !- Vertex 3 Y-coordinate {m}
    26.350000000000,  !- Vertex 3 Z-coordinate {m}
    -5.523860194453,  !- Vertex 4 X-coordinate {m}
    52.180614786127,  !- Vertex 4 Y-coordinate {m}
    30.940000000000;  !- Vertex 4 Z-coordinate {m}

  BuildingSurface:Detailed,
    FC7733,  !- Name
    Wall,  !- Surface Type
    EXT_WALL_SW_EF_GL,  !- Construction Name
    B2_F4_CL,  !- Zone Name
    Outdoors,  !- Outside Boundary Condition
    ,  !- Outside Boundary Condition Object
    SunExposed,  !- Sun Exposure
    WindExposed,  !- Wind Exposure
    ,  !- TRNSYS 17 - additional surface data
    4,  !- Number of Vertices
    -6.660281627363,  !- Vertex 1 X-coordinate {m}
    65.169971202261,  !- Vertex 1 Y-coordinate {m}
    26.350000000000,  !- Vertex 1 Z-coordinate {m}
    -6.660281627363,  !- Vertex 2 X-coordinate {m}
    65.169971202261,  !- Vertex 2 Y-coordinate {m}
    21.760000000000,  !- Vertex 2 Z-coordinate {m}
    -5.523860194453,  !- Vertex 3 X-coordinate {m}
    52.180614786127,  !- Vertex 3 Y-coordinate {m}
    21.760000000000,  !- Vertex 3 Z-coordinate {m}
    -5.523860194453,  !- Vertex 4 X-coordinate {m}
    52.180614786127,  !- Vertex 4 Y-coordinate {m}
    26.350000000000;  !- Vertex 4 Z-coordinate {m}

  BuildingSurface:Detailed,
    46B811,  !- Name
    Wall,  !- Surface Type
    EXT_WALL_SW_EF_RL,  !- Construction Name
    B2_F4_CL,  !- Zone Name
    Outdoors,  !- Outside Boundary Condition
    ,  !- Outside Boundary Condition Object
    SunExposed,  !- Sun Exposure
    WindExposed,  !- Wind Exposure
    ,  !- TRNSYS 17 - additional surface data
    4,  !- Number of Vertices
    -5.523860194453,  !- Vertex 1 X-coordinate {m}
    52.180614786127,  !- Vertex 1 Y-coordinate {m}
    26.350000000000,  !- Vertex 1 Z-coordinate {m}
    -5.523860194453,  !- Vertex 2 X-coordinate {m}
    52.180614786127,  !- Vertex 2 Y-coordinate {m}
    21.760000000000,  !- Vertex 2 Z-coordinate {m}
    -5.353906496095,  !- Vertex 3 X-coordinate {m}
    50.238035124848,  !- Vertex 3 Y-coordinate {m}
    21.760000000000,  !- Vertex 3 Z-coordinate {m}
    -5.353906496095,  !- Vertex 4 X-coordinate {m}
    50.238035124848,  !- Vertex 4 Y-coordinate {m}
    26.350000000000;  !- Vertex 4 Z-coordinate {m}

  BuildingSurface:Detailed,
    ADCA2B,  !- Name
    Wall,  !- Surface Type
    EXT_WALL_SW_EF_GL,  !- Construction Name
    B2_F3_LB,  !- Zone Name
    Outdoors,  !- Outside Boundary Condition
    ,  !- Outside Boundary Condition Object
    SunExposed,  !- Sun Exposure
    WindExposed,  !- Wind Exposure
    ,  !- TRNSYS 17 - additional surface data
    4,  !- Number of Vertices
    -6.660281627363,  !- Vertex 1 X-coordinate {m}
    65.169971202261,  !- Vertex 1 Y-coordinate {m}
    21.760000000000,  !- Vertex 1 Z-coordinate {m}
    -6.660281627363,  !- Vertex 2 X-coordinate {m}
    65.169971202261,  !- Vertex 2 Y-coordinate {m}
    17.170000000000,  !- Vertex 2 Z-coordinate {m}
    -5.523860194453,  !- Vertex 3 X-coordinate {m}
    52.180614786127,  !- Vertex 3 Y-coordinate {m}
    17.170000000000,  !- Vertex 3 Z-coordinate {m}
    -5.523860194453,  !- Vertex 4 X-coordinate {m}
    52.180614786127,  !- Vertex 4 Y-coordinate {m}
    21.760000000000;  !- Vertex 4 Z-coordinate {m}

  BuildingSurface:Detailed,
    E3B25B,  !- Name
    Wall,  !- Surface Type
    EXT_WALL_SW_EF_RL,  !- Construction Name
    B2_F3_LB,  !- Zone Name
    Outdoors,  !- Outside Boundary Condition
    ,  !- Outside Boundary Condition Object
    SunExposed,  !- Sun Exposure
    WindExposed,  !- Wind Exposure
    ,  !- TRNSYS 17 - additional surface data
    4,  !- Number of Vertices
    -5.523860194453,  !- Vertex 1 X-coordinate {m}
    52.180614786127,  !- Vertex 1 Y-coordinate {m}
    21.760000000000,  !- Vertex 1 Z-coordinate {m}
    -5.523860194453,  !- Vertex 2 X-coordinate {m}
    52.180614786127,  !- Vertex 2 Y-coordinate {m}
    17.170000000000,  !- Vertex 2 Z-coordinate {m}
    -5.353906496095,  !- Vertex 3 X-coordinate {m}
    50.238035124848,  !- Vertex 3 Y-coordinate {m}
    17.170000000000,  !- Vertex 3 Z-coordinate {m}
    -5.353906496095,  !- Vertex 4 X-coordinate {m}
    50.238035124848,  !- Vertex 4 Y-coordinate {m}
    21.760000000000;  !- Vertex 4 Z-coordinate {m}

  BuildingSurface:Detailed,
    26574F,  !- Name
    Wall,  !- Surface Type
    EXT_WALL_SW_EF_GL,  !- Construction Name
    B2_F2_CL,  !- Zone Name
    Outdoors,  !- Outside Boundary Condition
    ,  !- Outside Boundary Condition Object
    SunExposed,  !- Sun Exposure
    WindExposed,  !- Wind Exposure
    ,  !- TRNSYS 17 - additional surface data
    4,  !- Number of Vertices
    -6.660281627363,  !- Vertex 1 X-coordinate {m}
    65.169971202261,  !- Vertex 1 Y-coordinate {m}
    17.170000000000,  !- Vertex 1 Z-coordinate {m}
    -6.660281627363,  !- Vertex 2 X-coordinate {m}
    65.169971202261,  !- Vertex 2 Y-coordinate {m}
    12.580000000000,  !- Vertex 2 Z-coordinate {m}
    -5.523860194453,  !- Vertex 3 X-coordinate {m}
    52.180614786127,  !- Vertex 3 Y-coordinate {m}
    12.580000000000,  !- Vertex 3 Z-coordinate {m}
    -5.523860194453,  !- Vertex 4 X-coordinate {m}
    52.180614786127,  !- Vertex 4 Y-coordinate {m}
    17.170000000000;  !- Vertex 4 Z-coordinate {m}

  BuildingSurface:Detailed,
    E2ED6F,  !- Name
    Wall,  !- Surface Type
    EXT_WALL_SW_EF_RL,  !- Construction Name
    B2_F2_CL,  !- Zone Name
    Outdoors,  !- Outside Boundary Condition
    ,  !- Outside Boundary Condition Object
    SunExposed,  !- Sun Exposure
    WindExposed,  !- Wind Exposure
    ,  !- TRNSYS 17 - additional surface data
    4,  !- Number of Vertices
    -5.523860194453,  !- Vertex 1 X-coordinate {m}
    52.180614786127,  !- Vertex 1 Y-coordinate {m}
    17.170000000000,  !- Vertex 1 Z-coordinate {m}
    -5.523860194453,  !- Vertex 2 X-coordinate {m}
    52.180614786127,  !- Vertex 2 Y-coordinate {m}
    12.580000000000,  !- Vertex 2 Z-coordinate {m}
    -5.353906496095,  !- Vertex 3 X-coordinate {m}
    50.238035124848,  !- Vertex 3 Y-coordinate {m}
    12.580000000000,  !- Vertex 3 Z-coordinate {m}
    -5.353906496095,  !- Vertex 4 X-coordinate {m}
    50.238035124848,  !- Vertex 4 Y-coordinate {m}
    17.170000000000;  !- Vertex 4 Z-coordinate {m}

  BuildingSurface:Detailed,
    EBA029,  !- Name
    Wall,  !- Surface Type
    EXT_WALL_SW_EF_GL,  !- Construction Name
    B2_F1_OF,  !- Zone Name
    Outdoors,  !- Outside Boundary Condition
    ,  !- Outside Boundary Condition Object
    SunExposed,  !- Sun Exposure
    WindExposed,  !- Wind Exposure
    ,  !- TRNSYS 17 - additional surface data
    4,  !- Number of Vertices
    -6.660281627363,  !- Vertex 1 X-coordinate {m}
    65.169971202261,  !- Vertex 1 Y-coordinate {m}
    12.580000000000,  !- Vertex 1 Z-coordinate {m}
    -6.660281627363,  !- Vertex 2 X-coordinate {m}
    65.169971202261,  !- Vertex 2 Y-coordinate {m}
    7.990000000000,  !- Vertex 2 Z-coordinate {m}
    -5.523860194453,  !- Vertex 3 X-coordinate {m}
    52.180614786127,  !- Vertex 3 Y-coordinate {m}
    7.990000000000,  !- Vertex 3 Z-coordinate {m}
    -5.523860194453,  !- Vertex 4 X-coordinate {m}
    52.180614786127,  !- Vertex 4 Y-coordinate {m}
    12.580000000000;  !- Vertex 4 Z-coordinate {m}

  BuildingSurface:Detailed,
    752725,  !- Name
    Wall,  !- Surface Type
    EXT_WALL_SW_EF_RL,  !- Construction Name
    B2_F1_OF,  !- Zone Name
    Outdoors,  !- Outside Boundary Condition
    ,  !- Outside Boundary Condition Object
    SunExposed,  !- Sun Exposure
    WindExposed,  !- Wind Exposure
    ,  !- TRNSYS 17 - additional surface data
    4,  !- Number of Vertices
    -5.523860194453,  !- Vertex 1 X-coordinate {m}
    52.180614786127,  !- Vertex 1 Y-coordinate {m}
    12.580000000000,  !- Vertex 1 Z-coordinate {m}
    -5.523860194453,  !- Vertex 2 X-coordinate {m}
    52.180614786127,  !- Vertex 2 Y-coordinate {m}
    7.990000000000,  !- Vertex 2 Z-coordinate {m}
    -5.353906496095,  !- Vertex 3 X-coordinate {m}
    50.238035124848,  !- Vertex 3 Y-coordinate {m}
    7.990000000000,  !- Vertex 3 Z-coordinate {m}
    -5.353906496095,  !- Vertex 4 X-coordinate {m}
    50.238035124848,  !- Vertex 4 Y-coordinate {m}
    12.580000000000;  !- Vertex 4 Z-coordinate {m}

  BuildingSurface:Detailed,
    200468,  !- Name
    Wall,  !- Surface Type
    EXT_WALL_SW_EF_RL,  !- Construction Name
    B1_F5_CL,  !- Zone Name
    Outdoors,  !- Outside Boundary Condition
    ,  !- Outside Boundary Condition Object
    SunExposed,  !- Sun Exposure
    WindExposed,  !- Wind Exposure
    ,  !- TRNSYS 17 - additional surface data
    4,  !- Number of Vertices
    -4.402540559418,  !- Vertex 1 X-coordinate {m}
    50.321268859172,  !- Vertex 1 Y-coordinate {m}
    30.940000000000,  !- Vertex 1 Z-coordinate {m}
    -4.402540559418,  !- Vertex 2 X-coordinate {m}
    50.321268859172,  !- Vertex 2 Y-coordinate {m}
    26.350000000000,  !- Vertex 2 Z-coordinate {m}
    -3.888321677206,  !- Vertex 3 X-coordinate {m}
    44.443720140431,  !- Vertex 3 Y-coordinate {m}
    26.350000000000,  !- Vertex 3 Z-coordinate {m}
    -3.888321677206,  !- Vertex 4 X-coordinate {m}
    44.443720140431,  !- Vertex 4 Y-coordinate {m}
    30.940000000000;  !- Vertex 4 Z-coordinate {m}

  BuildingSurface:Detailed,
    46D347,  !- Name
    Wall,  !- Surface Type
    EXT_WALL_SW_EF_GL,  !- Construction Name
    B1_F4_CL,  !- Zone Name
    Outdoors,  !- Outside Boundary Condition
    ,  !- Outside Boundary Condition Object
    SunExposed,  !- Sun Exposure
    WindExposed,  !- Wind Exposure
    ,  !- TRNSYS 17 - additional surface data
    4,  !- Number of Vertices
    -3.888321677206,  !- Vertex 1 X-coordinate {m}
    44.443720140431,  !- Vertex 1 Y-coordinate {m}
    26.350000000000,  !- Vertex 1 Z-coordinate {m}
    -3.888321677206,  !- Vertex 2 X-coordinate {m}
    44.443720140431,  !- Vertex 2 Y-coordinate {m}
    21.760000000000,  !- Vertex 2 Z-coordinate {m}
    -0.908031053950,  !- Vertex 3 X-coordinate {m}
    10.378842439183,  !- Vertex 3 Y-coordinate {m}
    21.760000000000,  !- Vertex 3 Z-coordinate {m}
    -0.908031053950,  !- Vertex 4 X-coordinate {m}
    10.378842439183,  !- Vertex 4 Y-coordinate {m}
    26.350000000000;  !- Vertex 4 Z-coordinate {m}

  BuildingSurface:Detailed,
    4BF298,  !- Name
    Wall,  !- Surface Type
    EXT_WALL_SW_EF_GL,  !- Construction Name
    B1_F3_LB,  !- Zone Name
    Outdoors,  !- Outside Boundary Condition
    ,  !- Outside Boundary Condition Object
    SunExposed,  !- Sun Exposure
    WindExposed,  !- Wind Exposure
    ,  !- TRNSYS 17 - additional surface data
    4,  !- Number of Vertices
    -3.888321677206,  !- Vertex 1 X-coordinate {m}
    44.443720140431,  !- Vertex 1 Y-coordinate {m}
    21.760000000000,  !- Vertex 1 Z-coordinate {m}
    -3.888321677206,  !- Vertex 2 X-coordinate {m}
    44.443720140431,  !- Vertex 2 Y-coordinate {m}
    17.170000000000,  !- Vertex 2 Z-coordinate {m}
    -0.908031053950,  !- Vertex 3 X-coordinate {m}
    10.378842439183,  !- Vertex 3 Y-coordinate {m}
    17.170000000000,  !- Vertex 3 Z-coordinate {m}
    -0.908031053950,  !- Vertex 4 X-coordinate {m}
    10.378842439183,  !- Vertex 4 Y-coordinate {m}
    21.760000000000;  !- Vertex 4 Z-coordinate {m}

  BuildingSurface:Detailed,
    645F2E,  !- Name
    Wall,  !- Surface Type
    EXT_WALL_SW_EF_GL,  !- Construction Name
    B1_F2_CL,  !- Zone Name
    Outdoors,  !- Outside Boundary Condition
    ,  !- Outside Boundary Condition Object
    SunExposed,  !- Sun Exposure
    WindExposed,  !- Wind Exposure
    ,  !- TRNSYS 17 - additional surface data
    4,  !- Number of Vertices
    -3.888321677206,  !- Vertex 1 X-coordinate {m}
    44.443720140431,  !- Vertex 1 Y-coordinate {m}
    17.170000000000,  !- Vertex 1 Z-coordinate {m}
    -3.888321677206,  !- Vertex 2 X-coordinate {m}
    44.443720140431,  !- Vertex 2 Y-coordinate {m}
    12.580000000000,  !- Vertex 2 Z-coordinate {m}
    -0.908031053950,  !- Vertex 3 X-coordinate {m}
    10.378842439183,  !- Vertex 3 Y-coordinate {m}
    12.580000000000,  !- Vertex 3 Z-coordinate {m}
    -0.908031053950,  !- Vertex 4 X-coordinate {m}
    10.378842439183,  !- Vertex 4 Y-coordinate {m}
    17.170000000000;  !- Vertex 4 Z-coordinate {m}

  BuildingSurface:Detailed,
    566494,  !- Name
    Wall,  !- Surface Type
    EXT_WALL_SW_EF_GL,  !- Construction Name
    B1_F1_CN,  !- Zone Name
    Outdoors,  !- Outside Boundary Condition
    ,  !- Outside Boundary Condition Object
    SunExposed,  !- Sun Exposure
    WindExposed,  !- Wind Exposure
    ,  !- TRNSYS 17 - additional surface data
    4,  !- Number of Vertices
    -3.888321677206,  !- Vertex 1 X-coordinate {m}
    44.443720140431,  !- Vertex 1 Y-coordinate {m}
    12.580000000000,  !- Vertex 1 Z-coordinate {m}
    -3.888321677206,  !- Vertex 2 X-coordinate {m}
    44.443720140431,  !- Vertex 2 Y-coordinate {m}
    7.990000000000,  !- Vertex 2 Z-coordinate {m}
    -0.908031053950,  !- Vertex 3 X-coordinate {m}
    10.378842439183,  !- Vertex 3 Y-coordinate {m}
    7.990000000000,  !- Vertex 3 Z-coordinate {m}
    -0.908031053950,  !- Vertex 4 X-coordinate {m}
    10.378842439183,  !- Vertex 4 Y-coordinate {m}
    12.580000000000;  !- Vertex 4 Z-coordinate {m}

  BuildingSurface:Detailed,
    E6FDFE,  !- Name
    Wall,  !- Surface Type
    EXT_WALL_SW_EF_GL,  !- Construction Name
    B1_F4_SC,  !- Zone Name
    Outdoors,  !- Outside Boundary Condition
    ,  !- Outside Boundary Condition Object
    SunExposed,  !- Sun Exposure
    WindExposed,  !- Wind Exposure
    ,  !- TRNSYS 17 - additional surface data
    4,  !- Number of Vertices
    -0.908031053950,  !- Vertex 1 X-coordinate {m}
    10.378842439183,  !- Vertex 1 Y-coordinate {m}
    30.940000000000,  !- Vertex 1 Z-coordinate {m}
    -0.908031053950,  !- Vertex 2 X-coordinate {m}
    10.378842439183,  !- Vertex 2 Y-coordinate {m}
    21.760000000000,  !- Vertex 2 Z-coordinate {m}
    -0.592963043918,  !- Vertex 3 X-coordinate {m}
    6.777598605582,  !- Vertex 3 Y-coordinate {m}
    21.760000000000,  !- Vertex 3 Z-coordinate {m}
    -0.592963043918,  !- Vertex 4 X-coordinate {m}
    6.777598605582,  !- Vertex 4 Y-coordinate {m}
    30.940000000000;  !- Vertex 4 Z-coordinate {m}

  BuildingSurface:Detailed,
    3F7AEE,  !- Name
    Wall,  !- Surface Type
    EXT_WALL_SW_EF_RL,  !- Construction Name
    B1_F2_SC,  !- Zone Name
    Outdoors,  !- Outside Boundary Condition
    ,  !- Outside Boundary Condition Object
    SunExposed,  !- Sun Exposure
    WindExposed,  !- Wind Exposure
    ,  !- TRNSYS 17 - additional surface data
    4,  !- Number of Vertices
    -0.592963043918,  !- Vertex 1 X-coordinate {m}
    6.777598605582,  !- Vertex 1 Y-coordinate {m}
    21.760000000000,  !- Vertex 1 Z-coordinate {m}
    -0.592963043918,  !- Vertex 2 X-coordinate {m}
    6.777598605582,  !- Vertex 2 Y-coordinate {m}
    12.580000000000,  !- Vertex 2 Z-coordinate {m}
    0.000000000000,  !- Vertex 3 X-coordinate {m}
    0.000000000000,  !- Vertex 3 Y-coordinate {m}
    12.580000000000,  !- Vertex 3 Z-coordinate {m}
    0.000000000000,  !- Vertex 4 X-coordinate {m}
    0.000000000000,  !- Vertex 4 Y-coordinate {m}
    21.760000000000;  !- Vertex 4 Z-coordinate {m}

  BuildingSurface:Detailed,
    719426,  !- Name
    Wall,  !- Surface Type
    EXT_WALL_SW_EF_L0,  !- Construction Name
    B1_F0_SC,  !- Zone Name
    Outdoors,  !- Outside Boundary Condition
    ,  !- Outside Boundary Condition Object
    SunExposed,  !- Sun Exposure
    WindExposed,  !- Wind Exposure
    ,  !- TRNSYS 17 - additional surface data
    4,  !- Number of Vertices
    -0.592963043918,  !- Vertex 1 X-coordinate {m}
    6.777598605582,  !- Vertex 1 Y-coordinate {m}
    12.580000000000,  !- Vertex 1 Z-coordinate {m}
    -0.592963043918,  !- Vertex 2 X-coordinate {m}
    6.777598605582,  !- Vertex 2 Y-coordinate {m}
    3.910000000000,  !- Vertex 2 Z-coordinate {m}
    0.000000000000,  !- Vertex 3 X-coordinate {m}
    0.000000000000,  !- Vertex 3 Y-coordinate {m}
    3.910000000000,  !- Vertex 3 Z-coordinate {m}
    0.000000000000,  !- Vertex 4 X-coordinate {m}
    0.000000000000,  !- Vertex 4 Y-coordinate {m}
    12.580000000000;  !- Vertex 4 Z-coordinate {m}

  BuildingSurface:Detailed,
    14E777,  !- Name
    Wall,  !- Surface Type
    EXT_WALL_SW_EF_L0,  !- Construction Name
    B1_F0_SC,  !- Zone Name
    Outdoors,  !- Outside Boundary Condition
    ,  !- Outside Boundary Condition Object
    SunExposed,  !- Sun Exposure
    WindExposed,  !- Wind Exposure
    ,  !- TRNSYS 17 - additional surface data
    4,  !- Number of Vertices
    -0.908031053950,  !- Vertex 1 X-coordinate {m}
    10.378842439183,  !- Vertex 1 Y-coordinate {m}
    7.990000000000,  !- Vertex 1 Z-coordinate {m}
    -0.908031053950,  !- Vertex 2 X-coordinate {m}
    10.378842439183,  !- Vertex 2 Y-coordinate {m}
    3.910000000000,  !- Vertex 2 Z-coordinate {m}
    -0.592963043918,  !- Vertex 3 X-coordinate {m}
    6.777598605582,  !- Vertex 3 Y-coordinate {m}
    3.910000000000,  !- Vertex 3 Z-coordinate {m}
    -0.592963043918,  !- Vertex 4 X-coordinate {m}
    6.777598605582,  !- Vertex 4 Y-coordinate {m}
    7.990000000000;  !- Vertex 4 Z-coordinate {m}

  BuildingSurface:Detailed,
    FBAC5D,  !- Name
    Wall,  !- Surface Type
    EXT_WALL_SW_EF_RL,  !- Construction Name
    B1_F4_SC,  !- Zone Name
    Outdoors,  !- Outside Boundary Condition
    ,  !- Outside Boundary Condition Object
    SunExposed,  !- Sun Exposure
    WindExposed,  !- Wind Exposure
    ,  !- TRNSYS 17 - additional surface data
    4,  !- Number of Vertices
    0.000000000000,  !- Vertex 1 X-coordinate {m}
    0.000000000000,  !- Vertex 1 Y-coordinate {m}
    30.940000000000,  !- Vertex 1 Z-coordinate {m}
    0.000000000000,  !- Vertex 2 X-coordinate {m}
    0.000000000000,  !- Vertex 2 Y-coordinate {m}
    21.760000000000,  !- Vertex 2 Z-coordinate {m}
    7.772760005483,  !- Vertex 3 X-coordinate {m}
    -1.599523221318,  !- Vertex 3 Y-coordinate {m}
    21.760000000000,  !- Vertex 3 Z-coordinate {m}
    7.772760005483,  !- Vertex 4 X-coordinate {m}
    -1.599523221318,  !- Vertex 4 Y-coordinate {m}
    30.940000000000;  !- Vertex 4 Z-coordinate {m}

  BuildingSurface:Detailed,
    3BA882,  !- Name
    Wall,  !- Surface Type
    EXT_WALL_SW_EF_RL,  !- Construction Name
    B1_F4_SC,  !- Zone Name
    Outdoors,  !- Outside Boundary Condition
    ,  !- Outside Boundary Condition Object
    SunExposed,  !- Sun Exposure
    WindExposed,  !- Wind Exposure
    ,  !- TRNSYS 17 - additional surface data
    4,  !- Number of Vertices
    7.772760005483,  !- Vertex 1 X-coordinate {m}
    -1.599523221318,  !- Vertex 1 Y-coordinate {m}
    30.940000000000,  !- Vertex 1 Z-coordinate {m}
    7.772760005483,  !- Vertex 2 X-coordinate {m}
    -1.599523221318,  !- Vertex 2 Y-coordinate {m}
    26.350000000000,  !- Vertex 2 Z-coordinate {m}
    11.024619423024,  !- Vertex 3 X-coordinate {m}
    -2.268709539582,  !- Vertex 3 Y-coordinate {m}
    26.350000000000,  !- Vertex 3 Z-coordinate {m}
    11.024619423024,  !- Vertex 4 X-coordinate {m}
    -2.268709539582,  !- Vertex 4 Y-coordinate {m}
    30.940000000000;  !- Vertex 4 Z-coordinate {m}

  BuildingSurface:Detailed,
    197952,  !- Name
    Wall,  !- Surface Type
    EXT_WALL_SW_EF_GL,  !- Construction Name
    B1_F2_SC,  !- Zone Name
    Outdoors,  !- Outside Boundary Condition
    ,  !- Outside Boundary Condition Object
    SunExposed,  !- Sun Exposure
    WindExposed,  !- Wind Exposure
    ,  !- TRNSYS 17 - additional surface data
    4,  !- Number of Vertices
    7.772760005483,  !- Vertex 1 X-coordinate {m}
    -1.599523221318,  !- Vertex 1 Y-coordinate {m}
    21.760000000000,  !- Vertex 1 Z-coordinate {m}
    7.772760005483,  !- Vertex 2 X-coordinate {m}
    -1.599523221318,  !- Vertex 2 Y-coordinate {m}
    12.580000000000,  !- Vertex 2 Z-coordinate {m}
    11.024619423024,  !- Vertex 3 X-coordinate {m}
    -2.268709539582,  !- Vertex 3 Y-coordinate {m}
    12.580000000000,  !- Vertex 3 Z-coordinate {m}
    11.024619423024,  !- Vertex 4 X-coordinate {m}
    -2.268709539582,  !- Vertex 4 Y-coordinate {m}
    21.760000000000;  !- Vertex 4 Z-coordinate {m}

  BuildingSurface:Detailed,
    147F4F,  !- Name
    Wall,  !- Surface Type
    EXT_WALL_SW_EF_L0,  !- Construction Name
    B1_F0_SC,  !- Zone Name
    Outdoors,  !- Outside Boundary Condition
    ,  !- Outside Boundary Condition Object
    SunExposed,  !- Sun Exposure
    WindExposed,  !- Wind Exposure
    ,  !- TRNSYS 17 - additional surface data
    4,  !- Number of Vertices
    7.772760005483,  !- Vertex 1 X-coordinate {m}
    -1.599523221318,  !- Vertex 1 Y-coordinate {m}
    7.990000000000,  !- Vertex 1 Z-coordinate {m}
    7.772760005483,  !- Vertex 2 X-coordinate {m}
    -1.599523221318,  !- Vertex 2 Y-coordinate {m}
    3.910000000000,  !- Vertex 2 Z-coordinate {m}
    11.024619423024,  !- Vertex 3 X-coordinate {m}
    -2.268709539582,  !- Vertex 3 Y-coordinate {m}
    3.910000000000,  !- Vertex 3 Z-coordinate {m}
    11.024619423024,  !- Vertex 4 X-coordinate {m}
    -2.268709539582,  !- Vertex 4 Y-coordinate {m}
    7.990000000000;  !- Vertex 4 Z-coordinate {m}

  BuildingSurface:Detailed,
    D3D445,  !- Name
    Wall,  !- Surface Type
    EXT_WALL_SW_EF_GL,  !- Construction Name
    B1_F0_SC,  !- Zone Name
    Outdoors,  !- Outside Boundary Condition
    ,  !- Outside Boundary Condition Object
    SunExposed,  !- Sun Exposure
    WindExposed,  !- Wind Exposure
    ,  !- TRNSYS 17 - additional surface data
    4,  !- Number of Vertices
    7.772760005483,  !- Vertex 1 X-coordinate {m}
    -1.599523221318,  !- Vertex 1 Y-coordinate {m}
    12.580000000000,  !- Vertex 1 Z-coordinate {m}
    7.772760005483,  !- Vertex 2 X-coordinate {m}
    -1.599523221318,  !- Vertex 2 Y-coordinate {m}
    7.990000000000,  !- Vertex 2 Z-coordinate {m}
    11.024619423024,  !- Vertex 3 X-coordinate {m}
    -2.268709539582,  !- Vertex 3 Y-coordinate {m}
    7.990000000000,  !- Vertex 3 Z-coordinate {m}
    11.024619423024,  !- Vertex 4 X-coordinate {m}
    -2.268709539582,  !- Vertex 4 Y-coordinate {m}
    12.580000000000;  !- Vertex 4 Z-coordinate {m}

  Shading:Building:Detailed,
    4A39A2,  !- Name
    ,  !- Transmittance Schedule Name
    4,  !- Number of Vertices
    41.284559512200,  !- Vertex 1 X-coordinate {m}
    12.887672865633,  !- Vertex 1 Y-coordinate {m}
    30.940000000000,  !- Vertex 1 Z-coordinate {m}
    41.284559512200,  !- Vertex 2 X-coordinate {m}
    12.887672865633,  !- Vertex 2 Y-coordinate {m}
    0.000000000000,  !- Vertex 2 Z-coordinate {m}
    36.921715218697,  !- Vertex 3 X-coordinate {m}
    3.997015756185,  !- Vertex 3 Y-coordinate {m}
    0.000000000000,  !- Vertex 3 Z-coordinate {m}
    36.921715218697,  !- Vertex 4 X-coordinate {m}
    3.997015756185,  !- Vertex 4 Y-coordinate {m}
    30.940000000000;  !- Vertex 4 Z-coordinate {m}

  Shading:Building:Detailed,
    53DFBC,  !- Name
    ,  !- Transmittance Schedule Name
    4,  !- Number of Vertices
    49.664936899525,  !- Vertex 1 X-coordinate {m}
    -10.220336122569,  !- Vertex 1 Y-coordinate {m}
    26.350000000000,  !- Vertex 1 Z-coordinate {m}
    49.664936899525,  !- Vertex 2 X-coordinate {m}
    -10.220336122569,  !- Vertex 2 Y-coordinate {m}
    0.000000000000,  !- Vertex 2 Z-coordinate {m}
    51.954078169563,  !- Vertex 3 X-coordinate {m}
    0.903569722315,  !- Vertex 3 Y-coordinate {m}
    0.000000000000,  !- Vertex 3 Z-coordinate {m}
    51.954078169563,  !- Vertex 4 X-coordinate {m}
    0.903569722315,  !- Vertex 4 Y-coordinate {m}
    26.350000000000;  !- Vertex 4 Z-coordinate {m}

  Shading:Building:Detailed,
    B2512F,  !- Name
    ,  !- Transmittance Schedule Name
    4,  !- Number of Vertices
    51.954078169563,  !- Vertex 1 X-coordinate {m}
    0.903569722315,  !- Vertex 1 Y-coordinate {m}
    26.350000000000,  !- Vertex 1 Z-coordinate {m}
    51.954078169563,  !- Vertex 2 X-coordinate {m}
    0.903569722315,  !- Vertex 2 Y-coordinate {m}
    0.000000000000,  !- Vertex 2 Z-coordinate {m}
    49.568123181230,  !- Vertex 3 X-coordinate {m}
    1.394565251080,  !- Vertex 3 Y-coordinate {m}
    0.000000000000,  !- Vertex 3 Z-coordinate {m}
    49.568123181230,  !- Vertex 4 X-coordinate {m}
    1.394565251080,  !- Vertex 4 Y-coordinate {m}
    26.350000000000;  !- Vertex 4 Z-coordinate {m}

  Shading:Building:Detailed,
    C71486,  !- Name
    ,  !- Transmittance Schedule Name
    6,  !- Number of Vertices
    36.921715218697,  !- Vertex 1 X-coordinate {m}
    3.997015756185,  !- Vertex 1 Y-coordinate {m}
    26.350000000000,  !- Vertex 1 Z-coordinate {m}
    36.921715218697,  !- Vertex 2 X-coordinate {m}
    3.997015756185,  !- Vertex 2 Y-coordinate {m}
    0.000000000000,  !- Vertex 2 Z-coordinate {m}
    13.313760693062,  !- Vertex 3 X-coordinate {m}
    8.855196305301,  !- Vertex 3 Y-coordinate {m}
    0.000000000000,  !- Vertex 3 Z-coordinate {m}
    13.313760665876,  !- Vertex 4 X-coordinate {m}
    8.855196326266,  !- Vertex 4 Y-coordinate {m}
    30.940000000000,  !- Vertex 4 Z-coordinate {m}
    17.231663578072,  !- Vertex 5 X-coordinate {m}
    8.048947747597,  !- Vertex 5 Y-coordinate {m}
    30.940000000000,  !- Vertex 5 Z-coordinate {m}
    17.231663578072,  !- Vertex 6 X-coordinate {m}
    8.048947747597,  !- Vertex 6 Y-coordinate {m}
    26.350000000000;  !- Vertex 6 Z-coordinate {m}

  Shading:Building:Detailed,
    37D0D3,  !- Name
    ,  !- Transmittance Schedule Name
    4,  !- Number of Vertices
    36.921715218697,  !- Vertex 1 X-coordinate {m}
    3.997015756185,  !- Vertex 1 Y-coordinate {m}
    26.350000000000,  !- Vertex 1 Z-coordinate {m}
    36.921715218697,  !- Vertex 2 X-coordinate {m}
    3.997015756185,  !- Vertex 2 Y-coordinate {m}
    21.760000000000,  !- Vertex 2 Z-coordinate {m}
    49.568123181230,  !- Vertex 3 X-coordinate {m}
    1.394565251080,  !- Vertex 3 Y-coordinate {m}
    21.760000000000,  !- Vertex 3 Z-coordinate {m}
    49.568123181230,  !- Vertex 4 X-coordinate {m}
    1.394565251080,  !- Vertex 4 Y-coordinate {m}
    26.350000000000;  !- Vertex 4 Z-coordinate {m}

  Shading:Building:Detailed,
    68F996,  !- Name
    ,  !- Transmittance Schedule Name
    4,  !- Number of Vertices
    49.568123181230,  !- Vertex 1 X-coordinate {m}
    1.394565251080,  !- Vertex 1 Y-coordinate {m}
    30.940000000000,  !- Vertex 1 Z-coordinate {m}
    49.568123181230,  !- Vertex 2 X-coordinate {m}
    1.394565251080,  !- Vertex 2 Y-coordinate {m}
    0.000000000000,  !- Vertex 2 Z-coordinate {m}
    52.505893082225,  !- Vertex 3 X-coordinate {m}
    7.380253822592,  !- Vertex 3 Y-coordinate {m}
    0.000000000000,  !- Vertex 3 Z-coordinate {m}
    52.505893082225,  !- Vertex 4 X-coordinate {m}
    7.380253822592,  !- Vertex 4 Y-coordinate {m}
    30.940000000000;  !- Vertex 4 Z-coordinate {m}

  Shading:Building:Detailed,
    98B147,  !- Name
    ,  !- Transmittance Schedule Name
    4,  !- Number of Vertices
    41.284559512200,  !- Vertex 1 X-coordinate {m}
    12.887672865633,  !- Vertex 1 Y-coordinate {m}
    30.940000000000,  !- Vertex 1 Z-coordinate {m}
    36.921715218697,  !- Vertex 2 X-coordinate {m}
    3.997015756185,  !- Vertex 2 Y-coordinate {m}
    30.940000000000,  !- Vertex 2 Z-coordinate {m}
    49.568123181230,  !- Vertex 3 X-coordinate {m}
    1.394565251080,  !- Vertex 3 Y-coordinate {m}
    30.940000000000,  !- Vertex 3 Z-coordinate {m}
    52.505893082225,  !- Vertex 4 X-coordinate {m}
    7.380253822592,  !- Vertex 4 Y-coordinate {m}
    30.940000000000;  !- Vertex 4 Z-coordinate {m}

  Shading:Building:Detailed,
    39597A,  !- Name
    ,  !- Transmittance Schedule Name
    4,  !- Number of Vertices
    17.231663578072,  !- Vertex 1 X-coordinate {m}
    8.048947747597,  !- Vertex 1 Y-coordinate {m}
    26.350000000000,  !- Vertex 1 Z-coordinate {m}
    14.942522335724,  !- Vertex 2 X-coordinate {m}
    -3.074958115804,  !- Vertex 2 Y-coordinate {m}
    26.350000000000,  !- Vertex 2 Z-coordinate {m}
    49.664936899525,  !- Vertex 3 X-coordinate {m}
    -10.220336122569,  !- Vertex 3 Y-coordinate {m}
    26.350000000000,  !- Vertex 3 Z-coordinate {m}
    51.954078169563,  !- Vertex 4 X-coordinate {m}
    0.903569722315,  !- Vertex 4 Y-coordinate {m}
    26.350000000000;  !- Vertex 4 Z-coordinate {m}

  Shading:Building:Detailed,
    DB8F3C,  !- Name
    ,  !- Transmittance Schedule Name
    4,  !- Number of Vertices
    13.313760665876,  !- Vertex 1 X-coordinate {m}
    8.855196326266,  !- Vertex 1 Y-coordinate {m}
    30.940000000000,  !- Vertex 1 Z-coordinate {m}
    11.024619423024,  !- Vertex 2 X-coordinate {m}
    -2.268709539582,  !- Vertex 2 Y-coordinate {m}
    30.940000000000,  !- Vertex 2 Z-coordinate {m}
    14.942522335724,  !- Vertex 3 X-coordinate {m}
    -3.074958115804,  !- Vertex 3 Y-coordinate {m}
    30.940000000000,  !- Vertex 3 Z-coordinate {m}
    17.231663578072,  !- Vertex 4 X-coordinate {m}
    8.048947747597,  !- Vertex 4 Y-coordinate {m}
    30.940000000000;  !- Vertex 4 Z-coordinate {m}

  Shading:Building:Detailed,
    50D50D,  !- Name
    ,  !- Transmittance Schedule Name
    4,  !- Number of Vertices
    14.942522335724,  !- Vertex 1 X-coordinate {m}
    -3.074958115804,  !- Vertex 1 Y-coordinate {m}
    30.940000000000,  !- Vertex 1 Z-coordinate {m}
    14.942522335724,  !- Vertex 2 X-coordinate {m}
    -3.074958115804,  !- Vertex 2 Y-coordinate {m}
    26.350000000000,  !- Vertex 2 Z-coordinate {m}
    17.231663578072,  !- Vertex 3 X-coordinate {m}
    8.048947747597,  !- Vertex 3 Y-coordinate {m}
    26.350000000000,  !- Vertex 3 Z-coordinate {m}
    17.231663578072,  !- Vertex 4 X-coordinate {m}
    8.048947747597,  !- Vertex 4 Y-coordinate {m}
    30.940000000000;  !- Vertex 4 Z-coordinate {m}


  Shading:Building:Detailed,
    AD6C25,  !- Name
    ,  !- Transmittance Schedule Name
    6,  !- Number of Vertices
    24.536619678792,  !- Vertex 1 X-coordinate {m}
    65.305502396701,  !- Vertex 1 Y-coordinate {m}
    26.350000000000,  !- Vertex 1 Z-coordinate {m}
    25.617786667577,  !- Vertex 2 X-coordinate {m}
    52.947707166873,  !- Vertex 2 Y-coordinate {m}
    26.350000000000,  !- Vertex 2 Z-coordinate {m}
    61.480746077348,  !- Vertex 3 X-coordinate {m}
    56.085309555718,  !- Vertex 3 Y-coordinate {m}
    26.350000000000,  !- Vertex 3 Z-coordinate {m}
    69.879993866232,  !- Vertex 4 X-coordinate {m}
    51.972025662008,  !- Vertex 4 Y-coordinate {m}
    26.350000000000,  !- Vertex 4 Z-coordinate {m}
    75.277154679420,  !- Vertex 5 X-coordinate {m}
    62.968709208516,  !- Vertex 5 Y-coordinate {m}
    26.350000000000,  !- Vertex 5 Z-coordinate {m}
    63.559777555276,  !- Vertex 6 X-coordinate {m}
    68.719586325875,  !- Vertex 6 Y-coordinate {m}
    26.350000000000;  !- Vertex 6 Z-coordinate {m}

  Shading:Building:Detailed,
    6BCD35,  !- Name
    ,  !- Transmittance Schedule Name
    4,  !- Number of Vertices
    25.617786667577,  !- Vertex 1 X-coordinate {m}
    52.947707166873,  !- Vertex 1 Y-coordinate {m}
    30.940000000000,  !- Vertex 1 Z-coordinate {m}
    25.617786667577,  !- Vertex 2 X-coordinate {m}
    52.947707166873,  !- Vertex 2 Y-coordinate {m}
    26.350000000000,  !- Vertex 2 Z-coordinate {m}
    24.536619678792,  !- Vertex 3 X-coordinate {m}
    65.305502396701,  !- Vertex 3 Y-coordinate {m}
    26.350000000000,  !- Vertex 3 Z-coordinate {m}
    24.536619678792,  !- Vertex 4 X-coordinate {m}
    65.305502396701,  !- Vertex 4 Y-coordinate {m}
    30.940000000000;  !- Vertex 4 Z-coordinate {m}

  Shading:Building:Detailed,
    284C5B,  !- Name
    ,  !- Transmittance Schedule Name
    4,  !- Number of Vertices
    12.582233580160,  !- Vertex 1 X-coordinate {m}
    64.259629133658,  !- Vertex 1 Y-coordinate {m}
    30.940000000000,  !- Vertex 1 Z-coordinate {m}
    13.663400568944,  !- Vertex 2 X-coordinate {m}
    51.901833903830,  !- Vertex 2 Y-coordinate {m}
    30.940000000000,  !- Vertex 2 Z-coordinate {m}
    25.617786667577,  !- Vertex 3 X-coordinate {m}
    52.947707166873,  !- Vertex 3 Y-coordinate {m}
    30.940000000000,  !- Vertex 3 Z-coordinate {m}
    24.536619678792,  !- Vertex 4 X-coordinate {m}
    65.305502396701,  !- Vertex 4 Y-coordinate {m}
    30.940000000000;  !- Vertex 4 Z-coordinate {m}

  Shading:Building:Detailed,
    88915C,  !- Name
    ,  !- Transmittance Schedule Name
    4,  !- Number of Vertices
    24.536619678792,  !- Vertex 1 X-coordinate {m}
    65.305502396701,  !- Vertex 1 Y-coordinate {m}
    30.940000000000,  !- Vertex 1 Z-coordinate {m}
    24.536619678792,  !- Vertex 2 X-coordinate {m}
    65.305502396701,  !- Vertex 2 Y-coordinate {m}
    7.990000000000,  !- Vertex 2 Z-coordinate {m}
    12.582233580160,  !- Vertex 3 X-coordinate {m}
    64.259629133658,  !- Vertex 3 Y-coordinate {m}
    7.990000000000,  !- Vertex 3 Z-coordinate {m}
    12.582233580160,  !- Vertex 4 X-coordinate {m}
    64.259629133658,  !- Vertex 4 Y-coordinate {m}
    30.940000000000;  !- Vertex 4 Z-coordinate {m}

  Shading:Building:Detailed,
    301B1E,  !- Name
    ,  !- Transmittance Schedule Name
    4,  !- Number of Vertices
    12.187071739319,  !- Vertex 1 X-coordinate {m}
    68.776349642523,  !- Vertex 1 Y-coordinate {m}
    7.990000000000,  !- Vertex 1 Z-coordinate {m}
    12.582233580160,  !- Vertex 2 X-coordinate {m}
    64.259629133658,  !- Vertex 2 Y-coordinate {m}
    7.990000000000,  !- Vertex 2 Z-coordinate {m}
    24.536619678792,  !- Vertex 3 X-coordinate {m}
    65.305502396701,  !- Vertex 3 Y-coordinate {m}
    7.990000000000,  !- Vertex 3 Z-coordinate {m}
    24.141457837952,  !- Vertex 4 X-coordinate {m}
    69.822222905565,  !- Vertex 4 Y-coordinate {m}
    7.990000000000;  !- Vertex 4 Z-coordinate {m}

  Shading:Building:Detailed,
    D3BB76,  !- Name
    ,  !- Transmittance Schedule Name
    4,  !- Number of Vertices
    28.607569344989,  !- Vertex 1 X-coordinate {m}
    109.689202416929,  !- Vertex 1 Y-coordinate {m}
    17.170000000000,  !- Vertex 1 Z-coordinate {m}
    28.607569344989,  !- Vertex 2 X-coordinate {m}
    109.689202416929,  !- Vertex 2 Y-coordinate {m}
    0.000000000000,  !- Vertex 2 Z-coordinate {m}
    20.713968801880,  !- Vertex 3 X-coordinate {m}
    108.998601855005,  !- Vertex 3 Y-coordinate {m}
    0.000000000000,  !- Vertex 3 Z-coordinate {m}
    20.713968801880,  !- Vertex 4 X-coordinate {m}
    108.998601855005,  !- Vertex 4 Y-coordinate {m}
    17.170000000000;  !- Vertex 4 Z-coordinate {m}

  Shading:Building:Detailed,
    F16885,  !- Name
    ,  !- Transmittance Schedule Name
    5,  !- Number of Vertices
    20.713968801880,  !- Vertex 1 X-coordinate {m}
    108.998601855005,  !- Vertex 1 Y-coordinate {m}
    17.170000000000,  !- Vertex 1 Z-coordinate {m}
    23.851575540796,  !- Vertex 2 X-coordinate {m}
    73.135592723702,  !- Vertex 2 Y-coordinate {m}
    17.170000000000,  !- Vertex 2 Z-coordinate {m}
    40.069625225729,  !- Vertex 3 X-coordinate {m}
    74.554488215634,  !- Vertex 3 Y-coordinate {m}
    17.170000000000,  !- Vertex 3 Z-coordinate {m}
    37.543130493972,  !- Vertex 4 X-coordinate {m}
    103.432455142278,  !- Vertex 4 Y-coordinate {m}
    17.170000000000,  !- Vertex 4 Z-coordinate {m}
    28.607569344989,  !- Vertex 5 X-coordinate {m}
    109.689202416929,  !- Vertex 5 Y-coordinate {m}
    17.170000000000;  !- Vertex 5 Z-coordinate {m}

  Shading:Building:Detailed,
    ACE14B,  !- Name
    ,  !- Transmittance Schedule Name
    4,  !- Number of Vertices
    75.277154679420,  !- Vertex 1 X-coordinate {m}
    62.968709208516,  !- Vertex 1 Y-coordinate {m}
    30.940000000000,  !- Vertex 1 Z-coordinate {m}
    75.277154679420,  !- Vertex 2 X-coordinate {m}
    62.968709208516,  !- Vertex 2 Y-coordinate {m}
    26.350000000000,  !- Vertex 2 Z-coordinate {m}
    69.879993866232,  !- Vertex 3 X-coordinate {m}
    51.972025662008,  !- Vertex 3 Y-coordinate {m}
    26.350000000000,  !- Vertex 3 Z-coordinate {m}
    69.879993866232,  !- Vertex 4 X-coordinate {m}
    51.972025662008,  !- Vertex 4 Y-coordinate {m}
    30.940000000000;  !- Vertex 4 Z-coordinate {m}

  Shading:Building:Detailed,
    C84BDA,  !- Name
    ,  !- Transmittance Schedule Name
    4,  !- Number of Vertices
    75.277154679420,  !- Vertex 1 X-coordinate {m}
    62.968709208516,  !- Vertex 1 Y-coordinate {m}
    30.940000000000,  !- Vertex 1 Z-coordinate {m}
    69.879993866232,  !- Vertex 2 X-coordinate {m}
    51.972025662008,  !- Vertex 2 Y-coordinate {m}
    30.940000000000,  !- Vertex 2 Z-coordinate {m}
    76.894075198257,  !- Vertex 3 X-coordinate {m}
    48.537086189170,  !- Vertex 3 Y-coordinate {m}
    30.940000000000,  !- Vertex 3 Z-coordinate {m}
    82.288244339831,  !- Vertex 4 X-coordinate {m}
    59.527673495750,  !- Vertex 4 Y-coordinate {m}
    30.940000000000;  !- Vertex 4 Z-coordinate {m}

  Shading:Building:Detailed,
    5E3DE4,  !- Name
    ,  !- Transmittance Schedule Name
    4,  !- Number of Vertices
    24.536619678792,  !- Vertex 1 X-coordinate {m}
    65.305502396701,  !- Vertex 1 Y-coordinate {m}
    30.940000000000,  !- Vertex 1 Z-coordinate {m}
    24.536619678792,  !- Vertex 2 X-coordinate {m}
    65.305502396701,  !- Vertex 2 Y-coordinate {m}
    26.350000000000,  !- Vertex 2 Z-coordinate {m}
    40.754669363726,  !- Vertex 3 X-coordinate {m}
    66.724397888632,  !- Vertex 3 Y-coordinate {m}
    26.350000000000,  !- Vertex 3 Z-coordinate {m}
    40.754669363726,  !- Vertex 4 X-coordinate {m}
    66.724397888632,  !- Vertex 4 Y-coordinate {m}
    30.940000000000;  !- Vertex 4 Z-coordinate {m}

  Shading:Building:Detailed,
    61F278,  !- Name
    ,  !- Transmittance Schedule Name
    8,  !- Number of Vertices
    20.713968801880,  !- Vertex 1 X-coordinate {m}
    108.998601855005,  !- Vertex 1 Y-coordinate {m}
    17.170000000000,  !- Vertex 1 Z-coordinate {m}
    20.713968801880,  !- Vertex 2 X-coordinate {m}
    108.998601855005,  !- Vertex 2 Y-coordinate {m}
    0.000000000000,  !- Vertex 2 Z-coordinate {m}
    24.141457837952,  !- Vertex 3 X-coordinate {m}
    69.822222905565,  !- Vertex 3 Y-coordinate {m}
    0.000000000000,  !- Vertex 3 Z-coordinate {m}
    24.141457837952,  !- Vertex 4 X-coordinate {m}
    69.822222905565,  !- Vertex 4 Y-coordinate {m}
    7.990000000000,  !- Vertex 4 Z-coordinate {m}
    24.536619678792,  !- Vertex 5 X-coordinate {m}
    65.305502396701,  !- Vertex 5 Y-coordinate {m}
    7.990000000000,  !- Vertex 5 Z-coordinate {m}
    24.536619678792,  !- Vertex 6 X-coordinate {m}
    65.305502396701,  !- Vertex 6 Y-coordinate {m}
    30.940000000000,  !- Vertex 6 Z-coordinate {m}
    23.851575540796,
    73.135592723702,
    30.940000000000,
    23.851575540796,
    73.135592723702,
    17.170000000000;

  Shading:Building:Detailed,
    7AED95,  !- Name
    ,  !- Transmittance Schedule Name
    4,  !- Number of Vertices
    23.851575540796,  !- Vertex 1 X-coordinate {m}
    73.135592723702,  !- Vertex 1 Y-coordinate {m}
    30.940000000000,  !- Vertex 1 Z-coordinate {m}
    24.536619678792,  !- Vertex 2 X-coordinate {m}
    65.305502396701,  !- Vertex 2 Y-coordinate {m}
    30.940000000000,  !- Vertex 2 Z-coordinate {m}
    40.754669363726,  !- Vertex 3 X-coordinate {m}
    66.724397888632,  !- Vertex 3 Y-coordinate {m}
    30.940000000000,  !- Vertex 3 Z-coordinate {m}
    40.069625225729,  !- Vertex 4 X-coordinate {m}
    74.554488215634,  !- Vertex 4 Y-coordinate {m}
    30.940000000000;  !- Vertex 4 Z-coordinate {m}

  Shading:Building:Detailed,
    3D3D4E,  !- Name
    ,  !- Transmittance Schedule Name
    4,  !- Number of Vertices
    40.069625225729,  !- Vertex 1 X-coordinate {m}
    74.554488215634,  !- Vertex 1 Y-coordinate {m}
    30.940000000000,  !- Vertex 1 Z-coordinate {m}
    40.069625225729,  !- Vertex 2 X-coordinate {m}
    74.554488215634,  !- Vertex 2 Y-coordinate {m}
    17.170000000000,  !- Vertex 2 Z-coordinate {m}
    23.851575540796,  !- Vertex 3 X-coordinate {m}
    73.135592723702,  !- Vertex 3 Y-coordinate {m}
    17.170000000000,  !- Vertex 3 Z-coordinate {m}
    23.851575540796,  !- Vertex 4 X-coordinate {m}
    73.135592723702,  !- Vertex 4 Y-coordinate {m}
    30.940000000000;  !- Vertex 4 Z-coordinate {m}

  Shading:Building:Detailed,
    2EBB04,  !- Name
    ,  !- Transmittance Schedule Name
    4,  !- Number of Vertices
    76.894075198257,  !- Vertex 1 X-coordinate {m}
    48.537086189170,  !- Vertex 1 Y-coordinate {m}
    30.940000000000,  !- Vertex 1 Z-coordinate {m}
    76.894075198257,  !- Vertex 2 X-coordinate {m}
    48.537086189170,  !- Vertex 2 Y-coordinate {m}
    0.000000000000,  !- Vertex 2 Z-coordinate {m}
    82.288244339831,  !- Vertex 3 X-coordinate {m}
    59.527673495750,  !- Vertex 3 Y-coordinate {m}
    0.000000000000,  !- Vertex 3 Z-coordinate {m}
    82.288244339831,  !- Vertex 4 X-coordinate {m}
    59.527673495750,  !- Vertex 4 Y-coordinate {m}
    30.940000000000;  !- Vertex 4 Z-coordinate {m}

  Shading:Building:Detailed,
    761FAC,  !- Name
    ,  !- Transmittance Schedule Name
    6,  !- Number of Vertices
    13.663400568944,  !- Vertex 1 X-coordinate {m}
    51.901833903830,  !- Vertex 1 Y-coordinate {m}
    30.940000000000,  !- Vertex 1 Z-coordinate {m}
    13.663400568944,  !- Vertex 2 X-coordinate {m}
    51.901833903830,  !- Vertex 2 Y-coordinate {m}
    0.000000000000,  !- Vertex 2 Z-coordinate {m}
    61.480746077348,  !- Vertex 3 X-coordinate {m}
    56.085309555718,  !- Vertex 3 Y-coordinate {m}
    0.000000000000,  !- Vertex 3 Z-coordinate {m}
    61.480746077348,  !- Vertex 4 X-coordinate {m}
    56.085309555718,  !- Vertex 4 Y-coordinate {m}
    26.350000000000,  !- Vertex 4 Z-coordinate {m}
    25.617786667577,  !- Vertex 5 X-coordinate {m}
    52.947707166873,  !- Vertex 5 Y-coordinate {m}
    26.350000000000,  !- Vertex 5 Z-coordinate {m}
    25.617786667577,  !- Vertex 6 X-coordinate {m}
    52.947707166873,  !- Vertex 6 Y-coordinate {m}
    30.940000000000;  !- Vertex 6 Z-coordinate {m}
 


  Shading:Building:Detailed,
    9465D0,  !- Name
    ,  !- Transmittance Schedule Name
    4,  !- Number of Vertices
    52.505893082225,  !- Vertex 1 X-coordinate {m}
    7.380253822592,  !- Vertex 1 Y-coordinate {m}
    30.940000000000,  !- Vertex 1 Z-coordinate {m}
    52.505893082225,  !- Vertex 2 X-coordinate {m}
    7.380253822592,  !- Vertex 2 Y-coordinate {m}
    26.350000000000,  !- Vertex 2 Z-coordinate {m}
    41.284559564175,  !- Vertex 3 X-coordinate {m}
    12.887672971532,  !- Vertex 3 Y-coordinate {m}
    26.350000000000,  !- Vertex 3 Z-coordinate {m}
    41.284559512200,  !- Vertex 4 X-coordinate {m}
    12.887672865633,  !- Vertex 4 Y-coordinate {m}
    30.940000000000;  !- Vertex 4 Z-coordinate {m}

  Shading:Building:Detailed,
    845D9E,  !- Name
    ,  !- Transmittance Schedule Name
    6,  !- Number of Vertices
    69.879993866232,  !- Vertex 1 X-coordinate {m}
    51.972025662008,  !- Vertex 1 Y-coordinate {m}
    30.940000000000,  !- Vertex 1 Z-coordinate {m}
    69.879993866232,  !- Vertex 2 X-coordinate {m}
    51.972025662008,  !- Vertex 2 Y-coordinate {m}
    26.350000000000,  !- Vertex 2 Z-coordinate {m}
    73.517257553134,  !- Vertex 3 X-coordinate {m}
    50.190783041650,  !- Vertex 3 Y-coordinate {m}
    26.350000000000,  !- Vertex 3 Z-coordinate {m}
    73.517257553134,  !- Vertex 4 X-coordinate {m}
    50.190783041650,  !- Vertex 4 Y-coordinate {m}
    0.000000000000,  !- Vertex 4 Z-coordinate {m}
    76.894075198257,  !- Vertex 5 X-coordinate {m}
    48.537086189170,  !- Vertex 5 Y-coordinate {m}
    0.000000000000,  !- Vertex 5 Z-coordinate {m}
    76.894075198257,  !- Vertex 6 X-coordinate {m}
    48.537086189170,  !- Vertex 6 Y-coordinate {m}
    30.940000000000;  !- Vertex 6 Z-coordinate {m}

  Shading:Building:Detailed,
    B7E988,  !- Name
    ,  !- Transmittance Schedule Name
    4,  !- Number of Vertices
    62.288489505666,  !- Vertex 1 X-coordinate {m}
    55.689741033696,  !- Vertex 1 Y-coordinate {m}
    26.350000000000,  !- Vertex 1 Z-coordinate {m}
    62.288489505666,  !- Vertex 2 X-coordinate {m}
    55.689741033696,  !- Vertex 2 Y-coordinate {m}
    0.000000000000,  !- Vertex 2 Z-coordinate {m}
    61.480746077348,  !- Vertex 3 X-coordinate {m}
    56.085309555719,  !- Vertex 3 Y-coordinate {m}
    0.000000000000,  !- Vertex 3 Z-coordinate {m}
    61.480746077348,  !- Vertex 4 X-coordinate {m}
    56.085309555718,  !- Vertex 4 Y-coordinate {m}
    26.350000000000;  !- Vertex 4 Z-coordinate {m}

  Shading:Building:Detailed,
    10E4BC,  !- Name
    ,  !- Transmittance Schedule Name
    4,  !- Number of Vertices
    0.909563270293,  !- Vertex 1 X-coordinate {m}
    -10.396718601583,  !- Vertex 1 Y-coordinate {m}
    8.750000000000,  !- Vertex 1 Z-coordinate {m}
    0.896000000000,  !- Vertex 2 X-coordinate {m}
    -10.393927473878,  !- Vertex 2 Y-coordinate {m}
    0.000000000000,  !- Vertex 2 Z-coordinate {m}
    60.382467598013,  !- Vertex 3 X-coordinate {m}
    -22.635394624556,  !- Vertex 3 Y-coordinate {m}
    0.000000000000,  !- Vertex 3 Z-coordinate {m}
    60.382467598013,  !- Vertex 4 X-coordinate {m}
    -22.635394624556,  !- Vertex 4 Y-coordinate {m}
    8.750000000000;  !- Vertex 4 Z-coordinate {m}

  Shading:Building:Detailed,
    43D89B,  !- Name
    ,  !- Transmittance Schedule Name
    4,  !- Number of Vertices
    50.154674763612,  !- Vertex 1 X-coordinate {m}
    -10.321117194597,  !- Vertex 1 Y-coordinate {m}
    6.900000000000,  !- Vertex 1 Z-coordinate {m}
    50.154674763612,  !- Vertex 2 X-coordinate {m}
    -10.321117194597,  !- Vertex 2 Y-coordinate {m}
    0.000000000000,  !- Vertex 2 Z-coordinate {m}
    51.881215596101,  !- Vertex 3 X-coordinate {m}
    -2.354634933056,  !- Vertex 3 Y-coordinate {m}
    0.000000000000,  !- Vertex 3 Z-coordinate {m}
    51.881215596101,  !- Vertex 4 X-coordinate {m}
    -2.354634933056,  !- Vertex 4 Y-coordinate {m}
    6.900000000000;  !- Vertex 4 Z-coordinate {m}

  Shading:Building:Detailed,
    9DCFF7,  !- Name
    ,  !- Transmittance Schedule Name
    4,  !- Number of Vertices
    51.881215596101,  !- Vertex 1 X-coordinate {m}
    -2.354634933056,  !- Vertex 1 Y-coordinate {m}
    6.900000000000,  !- Vertex 1 Z-coordinate {m}
    51.881215596101,  !- Vertex 2 X-coordinate {m}
    -2.354634933056,  !- Vertex 2 Y-coordinate {m}
    0.000000000000,  !- Vertex 2 Z-coordinate {m}
    59.908192476734,  !- Vertex 3 X-coordinate {m}
    -4.094286499565,  !- Vertex 3 Y-coordinate {m}
    0.000000000000,  !- Vertex 3 Z-coordinate {m}
    59.908192476734,  !- Vertex 4 X-coordinate {m}
    -4.094286499565,  !- Vertex 4 Y-coordinate {m}
    6.900000000000;  !- Vertex 4 Z-coordinate {m}

  Shading:Building:Detailed,
    47F8C8,  !- Name
    ,  !- Transmittance Schedule Name
    4,  !- Number of Vertices
    59.908192476734,  !- Vertex 1 X-coordinate {m}
    -4.094286499565,  !- Vertex 1 Y-coordinate {m}
    6.900000000000,  !- Vertex 1 Z-coordinate {m}
    59.908192476734,  !- Vertex 2 X-coordinate {m}
    -4.094286499565,  !- Vertex 2 Y-coordinate {m}
    0.000000000000,  !- Vertex 2 Z-coordinate {m}
    60.407052850131,  !- Vertex 3 X-coordinate {m}
    0.142127044854,  !- Vertex 3 Y-coordinate {m}
    0.000000000000,  !- Vertex 3 Z-coordinate {m}
    60.407052850131,  !- Vertex 4 X-coordinate {m}
    0.142127044854,  !- Vertex 4 Y-coordinate {m}
    6.900000000000;  !- Vertex 4 Z-coordinate {m}

  Shading:Building:Detailed,
    5899D6,  !- Name
    ,  !- Transmittance Schedule Name
    4,  !- Number of Vertices
    60.407052850131,  !- Vertex 1 X-coordinate {m}
    0.142127044854,  !- Vertex 1 Y-coordinate {m}
    6.900000000000,  !- Vertex 1 Z-coordinate {m}
    60.407052850131,  !- Vertex 2 X-coordinate {m}
    0.142127044854,  !- Vertex 2 Y-coordinate {m}
    0.000000000000,  !- Vertex 2 Z-coordinate {m}
    54.527518948911,  !- Vertex 3 X-coordinate {m}
    2.913603385075,  !- Vertex 3 Y-coordinate {m}
    0.000000000000,  !- Vertex 3 Z-coordinate {m}
    54.527518948911,  !- Vertex 4 X-coordinate {m}
    2.913603385075,  !- Vertex 4 Y-coordinate {m}
    6.900000000000;  !- Vertex 4 Z-coordinate {m}

  Shading:Building:Detailed,
    2CF626,  !- Name
    ,  !- Transmittance Schedule Name
    24,  !- Number of Vertices
    54.527518948911,  !- Vertex 1 X-coordinate {m}
    2.913603385074,  !- Vertex 1 Y-coordinate {m}
    7.380000000000,  !- Vertex 1 Z-coordinate {m}
    54.527518948911,  !- Vertex 2 X-coordinate {m}
    2.913603385075,  !- Vertex 2 Y-coordinate {m}
    0.000000000000,  !- Vertex 2 Z-coordinate {m}
    87.587104273672,  !- Vertex 3 X-coordinate {m}
    68.728346054125,  !- Vertex 3 Y-coordinate {m}
    0.000000000000,  !- Vertex 3 Z-coordinate {m}
    87.587104273672,  !- Vertex 4 X-coordinate {m}
    68.728346054126,  !- Vertex 4 Y-coordinate {m}
    7.380000000000,  !- Vertex 4 Z-coordinate {m}
    86.756337806944,  !- Vertex 5 X-coordinate {m}
    67.074463203248,  !- Vertex 5 Y-coordinate {m}
    10.380000000000,  !- Vertex 5 Z-coordinate {m}
    84.749644401923,  !- Vertex 6 X-coordinate {m}
    63.079554955919,  !- Vertex 6 Y-coordinate {m}
    7.380000000000,  !- Vertex 6 Z-coordinate {m}
    83.741006844137,  !- Vertex 7 X-coordinate {m}
    61.071567842351,  !- Vertex 7 Y-coordinate {m}
    10.380000000000,  !- Vertex 7 Z-coordinate {m}
    81.558677421530,  !- Vertex 8 X-coordinate {m}
    56.727004897686,  !- Vertex 8 Y-coordinate {m}
    7.380000000000,  !- Vertex 8 Z-coordinate {m}
    80.720212195173,  !- Vertex 9 X-coordinate {m}
    55.057795421295,  !- Vertex 9 Y-coordinate {m}
    10.380000000000,  !- Vertex 9 Z-coordinate {m}
    78.625812447315,  !- Vertex 10 X-coordinate {m}
    50.888282128938,  !- Vertex 10 Y-coordinate {m}
    7.380000000000,  !- Vertex 10 Z-coordinate {m}
    77.853589947211,  !- Vertex 11 X-coordinate {m}
    49.350948111336,  !- Vertex 11 Y-coordinate {m}
    10.380000000000,  !- Vertex 11 Z-coordinate {m}
    75.638874012860,  !- Vertex 12 X-coordinate {m}
    44.941910373189,  !- Vertex 12 Y-coordinate {m}
    7.380000000000,  !- Vertex 12 Z-coordinate {m}
    74.578055413820,  !- Vertex 13 X-coordinate {m}
    42.830041684320,  !- Vertex 13 Y-coordinate {m}
    10.380000000000,  !- Vertex 13 Z-coordinate {m}
    72.468119647922,  !- Vertex 14 X-coordinate {m}
    38.629599418735,  !- Vertex 14 Y-coordinate {m}
    7.380000000000,  !- Vertex 14 Z-coordinate {m}
    71.384314263671,  !- Vertex 15 X-coordinate {m}
    36.471968832414,  !- Vertex 15 Y-coordinate {m}
    10.380000000000,  !- Vertex 15 Z-coordinate {m}
    68.997392221863,  !- Vertex 16 X-coordinate {m}
    31.720104632985,  !- Vertex 16 Y-coordinate {m}
    7.380000000000,  !- Vertex 16 Z-coordinate {m}
    68.065889592865,  !- Vertex 17 X-coordinate {m}
    29.865677082827,  !- Vertex 17 Y-coordinate {m}
    10.380000000000,  !- Vertex 17 Z-coordinate {m}
    65.253514021708,  !- Vertex 18 X-coordinate {m}
    24.266823597941,  !- Vertex 18 Y-coordinate {m}
    7.380000000000,  !- Vertex 18 Z-coordinate {m}
    64.581963059885,  !- Vertex 19 X-coordinate {m}
    22.929905626727,  !- Vertex 19 Y-coordinate {m}
    10.380000000000,  !- Vertex 19 Z-coordinate {m}
    62.427246049596,  !- Vertex 20 X-coordinate {m}
    18.640313238811,  !- Vertex 20 Y-coordinate {m}
    7.380000000000,  !- Vertex 20 Z-coordinate {m}
    61.700701799743,  !- Vertex 21 X-coordinate {m}
    17.193915095215,  !- Vertex 21 Y-coordinate {m}
    10.380000000000,  !- Vertex 21 Z-coordinate {m}
    58.925623698153,  !- Vertex 22 X-coordinate {m}
    11.669313097081,  !- Vertex 22 Y-coordinate {m}
    7.380000000000,  !- Vertex 22 Z-coordinate {m}
    58.069067331916,  !- Vertex 23 X-coordinate {m}
    9.964087932530,  !- Vertex 23 Y-coordinate {m}
    10.380000000000,  !- Vertex 23 Z-coordinate {m}
    55.488872097899,  !- Vertex 24 X-coordinate {m}
    4.827457097793,  !- Vertex 24 Y-coordinate {m}
    7.380000000000;  !- Vertex 24 Z-coordinate {m}

  Shading:Building:Detailed,
    495DC0,  !- Name
    ,  !- Transmittance Schedule Name
    4,  !- Number of Vertices
    2.100834437921,  !- Vertex 1 X-coordinate {m}
    68.683427371966,  !- Vertex 1 Y-coordinate {m}
    26.000000000000,  !- Vertex 1 Z-coordinate {m}
    2.100834437921,  !- Vertex 2 X-coordinate {m}
    68.683427371966,  !- Vertex 2 Y-coordinate {m}
    0.000000000000,  !- Vertex 2 Z-coordinate {m}
    -6.998533520815,  !- Vertex 3 X-coordinate {m}
    67.888836711362,  !- Vertex 3 Y-coordinate {m}
    0.000000000000,  !- Vertex 3 Z-coordinate {m}
    -6.998533520815,  !- Vertex 4 X-coordinate {m}
    67.888836711362,  !- Vertex 4 Y-coordinate {m}
    26.000000000000;  !- Vertex 4 Z-coordinate {m}

  Shading:Building:Detailed,
    B8E407,  !- Name
    ,  !- Transmittance Schedule Name
    4,  !- Number of Vertices
    2.100834437921,  !- Vertex 1 X-coordinate {m}
    124.833830604480,  !- Vertex 1 Y-coordinate {m}
    26.000000000000,  !- Vertex 1 Z-coordinate {m}
    2.100834437921,  !- Vertex 2 X-coordinate {m}
    124.833830604480,  !- Vertex 2 Y-coordinate {m}
    0.000000000000,  !- Vertex 2 Z-coordinate {m}
    2.100834437921,  !- Vertex 3 X-coordinate {m}
    68.683427371966,  !- Vertex 3 Y-coordinate {m}
    0.000000000000,  !- Vertex 3 Z-coordinate {m}
    2.100834437921,  !- Vertex 4 X-coordinate {m}
    68.683427371966,  !- Vertex 4 Y-coordinate {m}
    26.000000000000;  !- Vertex 4 Z-coordinate {m}

  Shading:Building:Detailed,
    9E5ADC,  !- Name
    ,  !- Transmittance Schedule Name
    4,  !- Number of Vertices
    21.061911082713,  !- Vertex 1 X-coordinate {m}
    133.601365746714,  !- Vertex 1 Y-coordinate {m}
    21.737730223961,  !- Vertex 1 Z-coordinate {m}
    21.061911082713,  !- Vertex 2 X-coordinate {m}
    133.601365746714,  !- Vertex 2 Y-coordinate {m}
    0.000000000000,  !- Vertex 2 Z-coordinate {m}
    2.100834437921,  !- Vertex 3 X-coordinate {m}
    124.833830604480,  !- Vertex 3 Y-coordinate {m}
    0.000000000000,  !- Vertex 3 Z-coordinate {m}
    2.100834437921,  !- Vertex 4 X-coordinate {m}
    124.833830604480,  !- Vertex 4 Y-coordinate {m}
    21.737730223961;  !- Vertex 4 Z-coordinate {m}

  Shading:Building:Detailed,
    C57FAF,  !- Name
    ,  !- Transmittance Schedule Name
    4,  !- Number of Vertices
    31.974078756555,  !- Vertex 1 X-coordinate {m}
    119.368476680245,  !- Vertex 1 Y-coordinate {m}
    18.000000000000,  !- Vertex 1 Z-coordinate {m}
    31.974078756555,  !- Vertex 2 X-coordinate {m}
    119.368476680245,  !- Vertex 2 Y-coordinate {m}
    0.000000000000,  !- Vertex 2 Z-coordinate {m}
    21.061911082713,  !- Vertex 3 X-coordinate {m}
    133.601365746714,  !- Vertex 3 Y-coordinate {m}
    0.000000000000,  !- Vertex 3 Z-coordinate {m}
    21.061911082713,  !- Vertex 4 X-coordinate {m}
    133.601365746714,  !- Vertex 4 Y-coordinate {m}
    18.000000000000;  !- Vertex 4 Z-coordinate {m}
-------------- next part --------------
 
 TRNSHD Version 1.0.182
 
 Integrated 2D clipping routine: GPC general polygon clipper library Version 2.2
 3 from Alan Murta, University of Manchester,UK
 
 
*** Notice at time        :         0.000000
    Generated by Unit     : Not applicable or not available
    Generated by Type     : Not applicable or not available
    TRNSHD Message      2 : Successfully opened shading log file.
    Reported information  : Not available
 
*** Notice at time        :         0.000000
    Generated by Unit     : Not applicable or not available
    Generated by Type     : Not applicable or not available
    TRNSHD Message     18 : Shading mask calculation is switched ON.
    Reported information  : Not available
 
 *** Notice at time        :         0.000000
 Orientation of wall   SURF=  10: azimuth angle= 355.00°, slope=  90.00°
 Orientation of wall   SURF=  15: azimuth angle= 116.14°, slope=  90.00°
 Orientation of window SURF=  22: azimuth angle= 116.14°, slope=  90.00°
 Orientation of wall   SURF=  19: azimuth angle= 296.14°, slope=  90.00°
 Orientation of window SURF=  23: azimuth angle= 296.14°, slope=  90.00°
 Orientation of window SURF=  24: azimuth angle= 296.14°, slope=  90.00°
 Orientation of wall   SURF=  26: azimuth angle= 296.14°, slope=  90.00°
 Orientation of window SURF=  32: azimuth angle= 296.14°, slope=  90.00°
 Orientation of wall   SURF=  29: azimuth angle= 116.14°, slope=  90.00°
 Orientation of window SURF=  33: azimuth angle= 116.14°, slope=  90.00°
 Orientation of wall   SURF=  36: azimuth angle=  85.00°, slope=  90.00°
 Orientation of window SURF=  45: azimuth angle=  85.00°, slope=  90.00°
 Orientation of wall   SURF=  39: azimuth angle= 265.00°, slope=  90.00°
 Orientation of window SURF=  42: azimuth angle= 265.00°, slope=  90.00°
 Orientation of window SURF=  43: azimuth angle= 265.00°, slope=  90.00°
 Orientation of wall   SURF=  40: azimuth angle= 355.00°, slope=  90.00°
 Orientation of wall   SURF=  48: azimuth angle= 175.00°, slope=  90.00°
 Orientation of wall   SURF=  50: azimuth angle= 355.00°, slope=  90.00°
 Orientation of wall   SURF=  52: azimuth angle=  85.00°, slope=  90.00°
 Orientation of window SURF=  53: azimuth angle=  85.00°, slope=  90.00°
 Orientation of window SURF=  54: azimuth angle=  85.00°, slope=  90.00°
 Orientation of wall   SURF=  59: azimuth angle= 355.00°, slope=  90.00°
 Orientation of wall   SURF=  60: azimuth angle= 175.00°, slope=  90.00°
 Orientation of window SURF=  64: azimuth angle= 175.00°, slope=  90.00°
 Orientation of window SURF=  65: azimuth angle= 175.00°, slope=  90.00°
 Orientation of wall   SURF=  62: azimuth angle=   0.00°, slope=   0.00°
 Orientation of wall   SURF=  68: azimuth angle= 296.14°, slope=  90.00°
 Orientation of window SURF=  73: azimuth angle= 296.14°, slope=  90.00°
 Orientation of wall   SURF=  69: azimuth angle= 116.14°, slope=  90.00°
 Orientation of window SURF=  72: azimuth angle= 116.14°, slope=  90.00°
 Orientation of wall   SURF=  75: azimuth angle= 281.63°, slope=  90.00°
 Orientation of wall   SURF=  79: azimuth angle=  11.63°, slope=  90.00°
 Orientation of window SURF=  82: azimuth angle=  11.63°, slope=  90.00°
 Orientation of wall   SURF=  80: azimuth angle=  85.00°, slope=  90.00°
 Orientation of window SURF=  81: azimuth angle=  85.00°, slope=  90.00°
 Orientation of wall   SURF=  84: azimuth angle=  11.63°, slope=  90.00°
 Orientation of window SURF=  98: azimuth angle=  11.63°, slope=  90.00°
 Orientation of wall   SURF=  85: azimuth angle=  85.00°, slope=  90.00°
 Orientation of window SURF=  97: azimuth angle=  85.00°, slope=  90.00°
 Orientation of wall   SURF=  87: azimuth angle=  85.00°, slope=  90.00°
 Orientation of window SURF= 103: azimuth angle=  85.00°, slope=  90.00°
 Orientation of wall   SURF=  89: azimuth angle=  85.00°, slope=  90.00°
 Orientation of window SURF= 102: azimuth angle=  85.00°, slope=  90.00°
 Orientation of wall   SURF=  90: azimuth angle=  11.63°, slope=  90.00°
 Orientation of window SURF= 101: azimuth angle=  11.63°, slope=  90.00°
 Orientation of wall   SURF=  95: azimuth angle= 281.63°, slope=  90.00°
 Orientation of window SURF=  99: azimuth angle= 281.63°, slope=  90.00°
 Orientation of wall   SURF=  96: azimuth angle=  11.63°, slope=  90.00°
 Orientation of window SURF= 100: azimuth angle=  11.63°, slope=  90.00°
 Orientation of wall   SURF= 104: azimuth angle= 265.00°, slope=  90.00°
 Orientation of window SURF= 115: azimuth angle= 265.00°, slope=  90.00°
 Orientation of wall   SURF= 105: azimuth angle= 355.00°, slope=  90.00°
 Orientation of wall   SURF= 109: azimuth angle=  85.00°, slope=  90.00°
 Orientation of window SURF= 114: azimuth angle=  85.00°, slope=  90.00°
 Orientation of wall   SURF= 116: azimuth angle= 265.00°, slope=  90.00°
 Orientation of window SURF= 126: azimuth angle= 265.00°, slope=  90.00°
 Orientation of wall   SURF= 117: azimuth angle= 355.00°, slope=  90.00°
 Orientation of wall   SURF= 119: azimuth angle=  85.00°, slope=  90.00°
 Orientation of window SURF= 129: azimuth angle=  85.00°, slope=  90.00°
 Orientation of wall   SURF= 121: azimuth angle=  85.00°, slope=  90.00°
 Orientation of window SURF= 127: azimuth angle=  85.00°, slope=  90.00°
 Orientation of wall   SURF= 124: azimuth angle=  85.00°, slope=  90.00°
 Orientation of window SURF= 128: azimuth angle=  85.00°, slope=  90.00°
 Orientation of wall   SURF= 125: azimuth angle= 175.00°, slope=  90.00°
 Orientation of wall   SURF= 131: azimuth angle= 355.00°, slope=  90.00°
 Orientation of wall   SURF= 134: azimuth angle= 175.00°, slope=  90.00°
 Orientation of window SURF= 137: azimuth angle= 175.00°, slope=  90.00°
 Orientation of wall   SURF= 143: azimuth angle= 116.14°, slope=  90.00°
 Orientation of window SURF= 146: azimuth angle= 116.14°, slope=  90.00°
 Orientation of wall   SURF= 145: azimuth angle= 296.14°, slope=  90.00°
 Orientation of window SURF= 147: azimuth angle= 296.14°, slope=  90.00°
 Orientation of window SURF= 148: azimuth angle= 296.14°, slope=  90.00°
 Orientation of wall   SURF= 150: azimuth angle= 355.00°, slope=  90.00°
 Orientation of wall   SURF= 153: azimuth angle= 265.00°, slope=  90.00°
 Orientation of window SURF= 156: azimuth angle= 265.00°, slope=  90.00°
 Orientation of wall   SURF= 161: azimuth angle= 265.00°, slope=  90.00°
 Orientation of window SURF= 163: azimuth angle= 265.00°, slope=  90.00°
 Orientation of wall   SURF= 169: azimuth angle=  85.00°, slope=  90.00°
 Orientation of wall   SURF= 170: azimuth angle=  85.00°, slope=  90.00°
 Orientation of window SURF= 172: azimuth angle=  85.00°, slope=  90.00°
 Orientation of wall   SURF= 176: azimuth angle= 175.00°, slope=  90.00°
 Orientation of window SURF= 180: azimuth angle= 175.00°, slope=  90.00°
 Orientation of wall   SURF= 178: azimuth angle= 355.00°, slope=  90.00°
 Orientation of wall   SURF= 181: azimuth angle= 265.00°, slope=  90.00°
 Orientation of window SURF= 191: azimuth angle= 265.00°, slope=  90.00°
 Orientation of wall   SURF= 183: azimuth angle=  85.00°, slope=  90.00°
 Orientation of wall   SURF= 184: azimuth angle=  85.00°, slope=  90.00°
 Orientation of wall   SURF= 186: azimuth angle= 175.00°, slope=  90.00°
 Orientation of wall   SURF= 187: azimuth angle= 355.00°, slope=  90.00°
 Orientation of wall   SURF= 190: azimuth angle=  85.00°, slope=  90.00°
 Orientation of window SURF= 192: azimuth angle=  85.00°, slope=  90.00°
 Orientation of wall   SURF= 193: azimuth angle=  85.00°, slope=  90.00°
 Orientation of window SURF= 204: azimuth angle=  85.00°, slope=  90.00°
 Orientation of wall   SURF= 197: azimuth angle= 265.00°, slope=  90.00°
 Orientation of window SURF= 205: azimuth angle= 265.00°, slope=  90.00°
 Orientation of wall   SURF= 202: azimuth angle= 355.00°, slope=  90.00°
 Orientation of wall   SURF= 203: azimuth angle=  85.00°, slope=  90.00°
 Orientation of wall   SURF= 210: azimuth angle= 281.63°, slope=  90.00°
 Orientation of window SURF= 216: azimuth angle= 281.63°, slope=  90.00°
 Orientation of wall   SURF= 211: azimuth angle=  85.00°, slope=  90.00°
 Orientation of window SURF= 220: azimuth angle=  85.00°, slope=  90.00°
 Orientation of window SURF= 221: azimuth angle=  85.00°, slope=  90.00°
 Orientation of wall   SURF= 213: azimuth angle=  11.63°, slope=  90.00°
 Orientation of window SURF= 217: azimuth angle=  11.63°, slope=  90.00°
 Orientation of wall   SURF= 214: azimuth angle=  11.63°, slope=  90.00°
 Orientation of window SURF= 218: azimuth angle=  11.63°, slope=  90.00°
 Orientation of window SURF= 222: azimuth angle=  11.63°, slope=  90.00°
 Orientation of wall   SURF= 215: azimuth angle=  85.00°, slope=  90.00°
 Orientation of window SURF= 219: azimuth angle=  85.00°, slope=  90.00°
 Orientation of wall   SURF= 224: azimuth angle= 296.14°, slope=  90.00°
 Orientation of window SURF= 230: azimuth angle= 296.14°, slope=  90.00°
 Orientation of window SURF= 232: azimuth angle= 296.14°, slope=  90.00°
 Orientation of wall   SURF= 227: azimuth angle= 116.14°, slope=  90.00°
 Orientation of window SURF= 231: azimuth angle= 116.14°, slope=  90.00°
 Orientation of wall   SURF= 235: azimuth angle= 116.14°, slope=  90.00°
 Orientation of window SURF= 240: azimuth angle= 116.14°, slope=  90.00°
 Orientation of wall   SURF= 237: azimuth angle= 296.14°, slope=  90.00°
 Orientation of window SURF= 239: azimuth angle= 296.14°, slope=  90.00°
 Orientation of wall   SURF= 245: azimuth angle= 175.00°, slope=  90.00°
 Orientation of window SURF= 248: azimuth angle= 175.00°, slope=  90.00°
 Orientation of wall   SURF= 246: azimuth angle= 355.00°, slope=  90.00°
 Orientation of wall   SURF= 250: azimuth angle=  85.00°, slope=  90.00°
 Orientation of wall   SURF= 253: azimuth angle= 175.00°, slope=  90.00°
 Orientation of wall   SURF= 254: azimuth angle= 265.00°, slope=  90.00°
 Orientation of window SURF= 259: azimuth angle= 265.00°, slope=  90.00°
 Orientation of wall   SURF= 255: azimuth angle=  85.00°, slope=  90.00°
 Orientation of window SURF= 260: azimuth angle=  85.00°, slope=  90.00°
 Orientation of wall   SURF= 256: azimuth angle=  85.00°, slope=  90.00°
 Orientation of wall   SURF= 257: azimuth angle= 355.00°, slope=  90.00°
 Orientation of wall   SURF= 262: azimuth angle=  85.00°, slope=  90.00°
 Orientation of window SURF= 271: azimuth angle=  85.00°, slope=  90.00°
 Orientation of wall   SURF= 266: azimuth angle=  85.00°, slope=  90.00°
 Orientation of wall   SURF= 267: azimuth angle= 355.00°, slope=  90.00°
 Orientation of wall   SURF= 268: azimuth angle= 265.00°, slope=  90.00°
 Orientation of window SURF= 270: azimuth angle= 265.00°, slope=  90.00°
 Orientation of wall   SURF= 272: azimuth angle= 296.14°, slope=  90.00°
 Orientation of window SURF= 278: azimuth angle= 296.14°, slope=  90.00°
 Orientation of window SURF= 280: azimuth angle= 296.14°, slope=  90.00°
 Orientation of wall   SURF= 273: azimuth angle= 116.14°, slope=  90.00°
 Orientation of window SURF= 279: azimuth angle= 116.14°, slope=  90.00°
 Orientation of wall   SURF= 281: azimuth angle= 296.14°, slope=  90.00°
 Orientation of window SURF= 289: azimuth angle= 296.14°, slope=  90.00°
 Orientation of wall   SURF= 286: azimuth angle= 116.14°, slope=  90.00°
 Orientation of window SURF= 288: azimuth angle= 116.14°, slope=  90.00°
 Orientation of wall   SURF= 291: azimuth angle= 355.00°, slope=  90.00°
 Orientation of wall   SURF= 294: azimuth angle= 175.00°, slope=  90.00°
 Orientation of window SURF= 297: azimuth angle= 175.00°, slope=  90.00°
 Orientation of wall   SURF= 298: azimuth angle= 175.00°, slope=  90.00°
 Orientation of wall   SURF= 299: azimuth angle= 355.00°, slope=  90.00°
 Orientation of wall   SURF= 300: azimuth angle=  85.00°, slope=  90.00°
 Orientation of window SURF= 308: azimuth angle=  85.00°, slope=  90.00°
 Orientation of wall   SURF= 301: azimuth angle= 265.00°, slope=  90.00°
 Orientation of window SURF= 309: azimuth angle= 265.00°, slope=  90.00°
 Orientation of wall   SURF= 302: azimuth angle=  85.00°, slope=  90.00°
 Orientation of wall   SURF= 304: azimuth angle=  85.00°, slope=  90.00°
 Orientation of wall   SURF= 310: azimuth angle= 355.00°, slope=  90.00°
 Orientation of wall   SURF= 311: azimuth angle=  85.00°, slope=  90.00°
 Orientation of wall   SURF= 314: azimuth angle= 265.00°, slope=  90.00°
 Orientation of window SURF= 319: azimuth angle= 265.00°, slope=  90.00°
 Orientation of wall   SURF= 318: azimuth angle=  85.00°, slope=  90.00°
 Orientation of window SURF= 320: azimuth angle=  85.00°, slope=  90.00°
 Orientation of wall   SURF= 322: azimuth angle=   0.00°, slope=   0.00°
 Orientation of wall   SURF= 323: azimuth angle=  11.63°, slope=  90.00°
 Orientation of window SURF= 335: azimuth angle=  11.63°, slope=  90.00°
 Orientation of wall   SURF= 324: azimuth angle=  11.63°, slope=  90.00°
 Orientation of window SURF= 337: azimuth angle=  11.63°, slope=  90.00°
 Orientation of wall   SURF= 326: azimuth angle=  85.00°, slope=  90.00°
 Orientation of window SURF= 333: azimuth angle=  85.00°, slope=  90.00°
 Orientation of window SURF= 336: azimuth angle=  85.00°, slope=  90.00°
 Orientation of wall   SURF= 327: azimuth angle=  11.63°, slope=  90.00°
 Orientation of window SURF= 338: azimuth angle=  11.63°, slope=  90.00°
 Orientation of wall   SURF= 328: azimuth angle=  85.00°, slope=  90.00°
 Orientation of window SURF= 334: azimuth angle=  85.00°, slope=  90.00°
 Orientation of wall   SURF= 329: azimuth angle= 281.63°, slope=  90.00°
 Orientation of window SURF= 332: azimuth angle= 281.63°, slope=  90.00°
 Orientation of wall   SURF= 341: azimuth angle= 296.14°, slope=  90.00°
 Orientation of window SURF= 346: azimuth angle= 296.14°, slope=  90.00°
 Orientation of window SURF= 347: azimuth angle= 296.14°, slope=  90.00°
 Orientation of wall   SURF= 343: azimuth angle=   0.00°, slope=   0.00°
 Orientation of wall   SURF= 345: azimuth angle= 116.14°, slope=  90.00°
 Orientation of window SURF= 348: azimuth angle= 116.14°, slope=  90.00°
 Orientation of wall   SURF= 350: azimuth angle= 355.00°, slope=  90.00°
 Orientation of wall   SURF= 353: azimuth angle=   0.00°, slope=   0.00°
 Orientation of wall   SURF= 355: azimuth angle= 175.00°, slope=  90.00°
 Orientation of window SURF= 356: azimuth angle= 175.00°, slope=  90.00°
 Orientation of wall   SURF= 358: azimuth angle=  85.00°, slope=  90.00°
 Orientation of window SURF= 367: azimuth angle=  85.00°, slope=  90.00°
 Orientation of wall   SURF= 359: azimuth angle= 355.00°, slope=  90.00°
 Orientation of wall   SURF= 360: azimuth angle=   0.00°, slope=   0.00°
 Orientation of wall   SURF= 361: azimuth angle=  85.00°, slope=  90.00°
 Orientation of wall   SURF= 363: azimuth angle= 175.00°, slope=  90.00°
 Orientation of wall   SURF= 364: azimuth angle=  85.00°, slope=  90.00°
 Orientation of wall   SURF= 366: azimuth angle= 265.00°, slope=  90.00°
 Orientation of window SURF= 368: azimuth angle= 265.00°, slope=  90.00°
 Orientation of wall   SURF= 369: azimuth angle=   0.00°, slope=   0.00°
 Orientation of wall   SURF= 371: azimuth angle= 265.00°, slope=  90.00°
 Orientation of window SURF= 378: azimuth angle= 265.00°, slope=  90.00°
 Orientation of wall   SURF= 372: azimuth angle= 355.00°, slope=  90.00°
 Orientation of wall   SURF= 374: azimuth angle=  85.00°, slope=  90.00°
 Orientation of window SURF= 379: azimuth angle=  85.00°, slope=  90.00°
 Orientation of wall   SURF= 375: azimuth angle=  85.00°, slope=  90.00°
 Orientation of wall   SURF=   1: azimuth angle=   0.00°, slope=   0.00°
 Orientation of wall   SURF=   2: azimuth angle=  85.00°, slope=  90.00°
 Orientation of wall   SURF=   3: azimuth angle= 355.00°, slope=  90.00°
 Orientation of wall   SURF=   4: azimuth angle= 355.00°, slope=  90.00°
 Orientation of wall   SURF=   5: azimuth angle= 265.00°, slope=  90.00°
 Orientation of wall   SURF=   6: azimuth angle= 175.00°, slope=  90.00°
 Orientation of wall   SURF=   7: azimuth angle=   0.00°, slope= 180.00°
 Orientation of wall   SURF=   8: azimuth angle=   0.00°, slope=   0.00°
 Orientation of wall   SURF=   9: azimuth angle= 175.00°, slope=  90.00°
 Orientation of wall   SURF=  11: azimuth angle=  85.00°, slope=  90.00°
 Orientation of wall   SURF=  12: azimuth angle=   0.00°, slope= 180.00°
 Orientation of wall   SURF=  13: azimuth angle= 355.00°, slope=  90.00°
 Orientation of wall   SURF=  14: azimuth angle= 265.00°, slope=  90.00°
 Orientation of wall   SURF=  16: azimuth angle=  26.14°, slope=  90.00°
 Orientation of wall   SURF=  17: azimuth angle=  26.14°, slope=  90.00°
 Orientation of wall   SURF=  18: azimuth angle=   0.00°, slope=   0.00°
 Orientation of wall   SURF=  20: azimuth angle= 206.09°, slope=  90.00°
 Orientation of wall   SURF=  21: azimuth angle=   0.00°, slope= 180.00°
 Orientation of wall   SURF=  27: azimuth angle= 206.14°, slope=  90.00°
 Orientation of wall   SURF=  28: azimuth angle=   0.00°, slope= 180.00°
 Orientation of wall   SURF=  30: azimuth angle=   0.00°, slope=   0.00°
 Orientation of wall   SURF=  31: azimuth angle=  26.14°, slope=  90.00°
 Orientation of wall   SURF=  34: azimuth angle= 175.00°, slope=  90.00°
 Orientation of wall   SURF=  35: azimuth angle=   0.00°, slope=   0.00°
 Orientation of wall   SURF=  37: azimuth angle= 175.00°, slope=  90.00°
 Orientation of wall   SURF=  38: azimuth angle= 355.00°, slope=  90.00°
 Orientation of wall   SURF=  41: azimuth angle=   0.00°, slope= 180.00°
 Orientation of wall   SURF=  46: azimuth angle=   0.00°, slope=   0.00°
 Orientation of wall   SURF=  47: azimuth angle= 355.00°, slope=  90.00°
 Orientation of wall   SURF=  49: azimuth angle=   0.00°, slope= 180.00°
 Orientation of wall   SURF=  51: azimuth angle= 265.00°, slope=  90.00°
 Orientation of wall   SURF=  56: azimuth angle=  85.00°, slope=  90.00°
 Orientation of wall   SURF=  57: azimuth angle= 265.00°, slope=  90.00°
 Orientation of wall   SURF=  58: azimuth angle= 355.00°, slope=  90.00°
 Orientation of wall   SURF=  61: azimuth angle=   0.00°, slope=   0.00°
 Orientation of wall   SURF=  63: azimuth angle=   0.00°, slope= 180.00°
 Orientation of wall   SURF=  66: azimuth angle= 206.14°, slope=  90.00°
 Orientation of wall   SURF=  67: azimuth angle=   0.00°, slope=   0.00°
 Orientation of wall   SURF=  70: azimuth angle=  26.14°, slope=  90.00°
 Orientation of wall   SURF=  71: azimuth angle=   0.00°, slope= 180.00°
 Orientation of wall   SURF=  74: azimuth angle= 281.63°, slope=  90.00°
 Orientation of wall   SURF=  76: azimuth angle=   0.00°, slope= 180.00°
 Orientation of wall   SURF=  77: azimuth angle=   0.00°, slope=   0.00°
 Orientation of wall   SURF=  78: azimuth angle= 175.00°, slope=  90.00°
 Orientation of wall   SURF=  86: azimuth angle= 175.00°, slope=  90.00°
 Orientation of wall   SURF=  88: azimuth angle=   0.00°, slope=   0.00°
 Orientation of wall   SURF=  91: azimuth angle=   0.00°, slope= 180.00°
 Orientation of wall   SURF=  92: azimuth angle= 281.63°, slope=  90.00°
 Orientation of wall   SURF=  93: azimuth angle= 175.00°, slope=  90.00°
 Orientation of wall   SURF=  94: azimuth angle= 175.00°, slope=  90.00°
 Orientation of wall   SURF= 106: azimuth angle= 355.00°, slope=  90.00°
 Orientation of wall   SURF= 107: azimuth angle=   0.00°, slope=   0.00°
 Orientation of wall   SURF= 108: azimuth angle=   0.00°, slope= 180.00°
 Orientation of wall   SURF= 110: azimuth angle=   0.00°, slope=   0.00°
 Orientation of wall   SURF= 111: azimuth angle= 175.00°, slope=  90.00°
 Orientation of wall   SURF= 112: azimuth angle=   0.00°, slope=   0.00°
 Orientation of wall   SURF= 113: azimuth angle= 175.00°, slope=  90.00°
 Orientation of wall   SURF= 118: azimuth angle=   0.00°, slope=   0.00°
 Orientation of wall   SURF= 120: azimuth angle= 265.00°, slope=  90.00°
 Orientation of wall   SURF= 122: azimuth angle= 355.00°, slope=  90.00°
 Orientation of wall   SURF= 123: azimuth angle=   0.00°, slope= 180.00°
 Orientation of wall   SURF= 130: azimuth angle=   0.00°, slope=   0.00°
 Orientation of wall   SURF= 132: azimuth angle=  85.00°, slope=  90.00°
 Orientation of wall   SURF= 133: azimuth angle=   0.00°, slope= 180.00°
 Orientation of wall   SURF= 135: azimuth angle= 355.00°, slope=  90.00°
 Orientation of wall   SURF= 136: azimuth angle= 265.00°, slope=  90.00°
 Orientation of wall   SURF= 138: azimuth angle=  26.14°, slope=  90.00°
 Orientation of wall   SURF= 139: azimuth angle=   0.00°, slope= 180.00°
 Orientation of wall   SURF= 140: azimuth angle=   0.00°, slope= 180.00°
 Orientation of wall   SURF= 141: azimuth angle=   0.00°, slope=   0.00°
 Orientation of wall   SURF= 142: azimuth angle= 206.09°, slope=  90.00°
 Orientation of wall   SURF= 144: azimuth angle=   0.00°, slope=   0.00°
 Orientation of wall   SURF= 149: azimuth angle=   0.00°, slope=   0.00°
 Orientation of wall   SURF= 151: azimuth angle=  85.00°, slope=  90.00°
 Orientation of wall   SURF= 152: azimuth angle=   0.00°, slope= 180.00°
 Orientation of wall   SURF= 154: azimuth angle= 175.00°, slope=  90.00°
 Orientation of wall   SURF= 155: azimuth angle= 355.00°, slope=  90.00°
 Orientation of wall   SURF= 157: azimuth angle= 355.00°, slope=  90.00°
 Orientation of wall   SURF= 158: azimuth angle=   0.00°, slope= 180.00°
 Orientation of wall   SURF= 159: azimuth angle=  85.00°, slope=  90.00°
 Orientation of wall   SURF= 160: azimuth angle= 175.00°, slope=  90.00°
 Orientation of wall   SURF= 162: azimuth angle=   0.00°, slope=   0.00°
 Orientation of wall   SURF= 164: azimuth angle= 265.00°, slope=  90.00°
 Orientation of wall   SURF= 165: azimuth angle=   0.00°, slope=   0.00°
 Orientation of wall   SURF= 166: azimuth angle=   0.00°, slope= 180.00°
 Orientation of wall   SURF= 167: azimuth angle= 355.00°, slope=  90.00°
 Orientation of wall   SURF= 168: azimuth angle= 265.00°, slope=  90.00°
 Orientation of wall   SURF= 171: azimuth angle= 175.00°, slope=  90.00°
 Orientation of wall   SURF= 173: azimuth angle=   0.00°, slope= 180.00°
 Orientation of wall   SURF= 174: azimuth angle= 355.00°, slope=  90.00°
 Orientation of wall   SURF= 175: azimuth angle=   0.00°, slope=   0.00°
 Orientation of wall   SURF= 177: azimuth angle=  85.00°, slope=  90.00°
 Orientation of wall   SURF= 179: azimuth angle= 265.00°, slope=  90.00°
 Orientation of wall   SURF= 182: azimuth angle= 355.00°, slope=  90.00°
 Orientation of wall   SURF= 185: azimuth angle= 265.00°, slope=  90.00°
 Orientation of wall   SURF= 188: azimuth angle=   0.00°, slope=   0.00°
 Orientation of wall   SURF= 189: azimuth angle=   0.00°, slope= 180.00°
 Orientation of wall   SURF= 194: azimuth angle=   0.00°, slope= 180.00°
 Orientation of wall   SURF= 195: azimuth angle= 175.00°, slope=  90.00°
 Orientation of wall   SURF= 196: azimuth angle=   0.00°, slope=   0.00°
 Orientation of wall   SURF= 198: azimuth angle= 355.00°, slope=  90.00°
 Orientation of wall   SURF= 199: azimuth angle=   0.00°, slope= 180.00°
 Orientation of wall   SURF= 200: azimuth angle=   0.00°, slope= 180.00°
 Orientation of wall   SURF= 201: azimuth angle= 175.00°, slope=  90.00°
 Orientation of wall   SURF= 206: azimuth angle=   0.00°, slope= 180.00°
 Orientation of wall   SURF= 207: azimuth angle= 175.00°, slope=  90.00°
 Orientation of wall   SURF= 208: azimuth angle=   0.00°, slope=   0.00°
 Orientation of wall   SURF= 209: azimuth angle= 281.63°, slope=  90.00°
 Orientation of wall   SURF= 212: azimuth angle= 175.00°, slope=  90.00°
 Orientation of wall   SURF= 223: azimuth angle= 206.09°, slope=  90.00°
 Orientation of wall   SURF= 225: azimuth angle=   0.00°, slope=   0.00°
 Orientation of wall   SURF= 226: azimuth angle=   0.00°, slope= 180.00°
 Orientation of wall   SURF= 228: azimuth angle=   0.00°, slope=   0.00°
 Orientation of wall   SURF= 229: azimuth angle=  26.14°, slope=  90.00°
 Orientation of wall   SURF= 233: azimuth angle=  26.14°, slope=  90.00°
 Orientation of wall   SURF= 234: azimuth angle=   0.00°, slope=   0.00°
 Orientation of wall   SURF= 236: azimuth angle=   0.00°, slope= 180.00°
 Orientation of wall   SURF= 238: azimuth angle= 206.14°, slope=  90.00°
 Orientation of wall   SURF= 241: azimuth angle= 265.00°, slope=  90.00°
 Orientation of wall   SURF= 242: azimuth angle=   0.00°, slope=   0.00°
 Orientation of wall   SURF= 243: azimuth angle=  85.00°, slope=  90.00°
 Orientation of wall   SURF= 244: azimuth angle= 355.00°, slope=  90.00°
 Orientation of wall   SURF= 247: azimuth angle=   0.00°, slope= 180.00°
 Orientation of wall   SURF= 249: azimuth angle= 265.00°, slope=  90.00°
 Orientation of wall   SURF= 251: azimuth angle= 355.00°, slope=  90.00°
 Orientation of wall   SURF= 252: azimuth angle=   0.00°, slope= 180.00°
 Orientation of wall   SURF= 258: azimuth angle=   0.00°, slope=   0.00°
 Orientation of wall   SURF= 261: azimuth angle=   0.00°, slope= 180.00°
 Orientation of wall   SURF= 263: azimuth angle= 175.00°, slope=  90.00°
 Orientation of wall   SURF= 264: azimuth angle= 355.00°, slope=  90.00°
 Orientation of wall   SURF= 265: azimuth angle= 175.00°, slope=  90.00°
 Orientation of wall   SURF= 269: azimuth angle=   0.00°, slope=   0.00°
 Orientation of wall   SURF= 274: azimuth angle=   0.00°, slope=   0.00°
 Orientation of wall   SURF= 275: azimuth angle=   0.00°, slope= 180.00°
 Orientation of wall   SURF= 276: azimuth angle=  26.14°, slope=  90.00°
 Orientation of wall   SURF= 277: azimuth angle= 206.09°, slope=  90.00°
 Orientation of wall   SURF= 282: azimuth angle=   0.00°, slope= 180.00°
 Orientation of wall   SURF= 283: azimuth angle= 206.14°, slope=  90.00°
 Orientation of wall   SURF= 284: azimuth angle=  26.14°, slope=  90.00°
 Orientation of wall   SURF= 285: azimuth angle=   0.00°, slope=   0.00°
 Orientation of wall   SURF= 287: azimuth angle=   0.00°, slope= 180.00°
 Orientation of wall   SURF= 290: azimuth angle= 355.00°, slope=  90.00°
 Orientation of wall   SURF= 292: azimuth angle=   0.00°, slope=   0.00°
 Orientation of wall   SURF= 293: azimuth angle=  85.00°, slope=  90.00°
 Orientation of wall   SURF= 295: azimuth angle= 265.00°, slope=  90.00°
 Orientation of wall   SURF= 296: azimuth angle=   0.00°, slope= 180.00°
 Orientation of wall   SURF= 303: azimuth angle= 355.00°, slope=  90.00°
 Orientation of wall   SURF= 305: azimuth angle=   0.00°, slope= 180.00°
 Orientation of wall   SURF= 306: azimuth angle=   0.00°, slope=   0.00°
 Orientation of wall   SURF= 307: azimuth angle= 265.00°, slope=  90.00°
 Orientation of wall   SURF= 312: azimuth angle= 175.00°, slope=  90.00°
 Orientation of wall   SURF= 313: azimuth angle= 175.00°, slope=  90.00°
 Orientation of wall   SURF= 315: azimuth angle= 355.00°, slope=  90.00°
 Orientation of wall   SURF= 316: azimuth angle=   0.00°, slope= 180.00°
 Orientation of wall   SURF= 317: azimuth angle=   0.00°, slope=   0.00°
 Orientation of wall   SURF= 321: azimuth angle= 281.63°, slope=  90.00°
 Orientation of wall   SURF= 325: azimuth angle= 175.00°, slope=  90.00°
 Orientation of wall   SURF= 330: azimuth angle= 175.00°, slope=  90.00°
 Orientation of wall   SURF= 331: azimuth angle=   0.00°, slope= 180.00°
 Orientation of wall   SURF= 339: azimuth angle=   0.00°, slope= 180.00°
 Orientation of wall   SURF= 340: azimuth angle= 206.09°, slope=  90.00°
 Orientation of wall   SURF= 342: azimuth angle=  26.14°, slope=  90.00°
 Orientation of wall   SURF= 344: azimuth angle=   0.00°, slope= 180.00°
 Orientation of wall   SURF= 349: azimuth angle= 355.00°, slope=  90.00°
 Orientation of wall   SURF= 351: azimuth angle=  85.00°, slope=  90.00°
 Orientation of wall   SURF= 352: azimuth angle= 265.00°, slope=  90.00°
 Orientation of wall   SURF= 354: azimuth angle=   0.00°, slope= 180.00°
 Orientation of wall   SURF= 357: azimuth angle= 355.00°, slope=  90.00°
 Orientation of wall   SURF= 362: azimuth angle= 265.00°, slope=  90.00°
 Orientation of wall   SURF= 365: azimuth angle=   0.00°, slope= 180.00°
 Orientation of wall   SURF= 370: azimuth angle= 355.00°, slope=  90.00°
 Orientation of wall   SURF= 373: azimuth angle= 175.00°, slope=  90.00°
 Orientation of wall   SURF= 376: azimuth angle= 175.00°, slope=  90.00°
 Orientation of wall   SURF= 377: azimuth angle=   0.00°, slope= 180.00°
 
 Processing external WALL SURF=  15 at time   1
 Processing external WALL SURF=  19 at time   1
 Processing external WALL SURF=  26 at time   1
 Processing external WALL SURF=  29 at time   1
 Processing external WALL SURF=  36 at time   1
 Processing external WALL SURF=  39 at time   1
 Processing external WALL SURF=  52 at time   1
 Processing external WALL SURF=  60 at time   1
 Processing external WALL SURF=  68 at time   1
 Processing external WALL SURF=  69 at time   1
 Processing external WALL SURF=  79 at time   1
 Processing external WALL SURF=  80 at time   1
 Processing external WALL SURF=  84 at time   1
 Processing external WALL SURF=  85 at time   1
 Processing external WALL SURF=  87 at time   1
 Processing external WALL SURF=  89 at time   1
 Processing external WALL SURF=  90 at time   1
 Processing external WALL SURF=  95 at time   1
 Processing external WALL SURF=  96 at time   1
 Processing external WALL SURF= 104 at time   1
 Processing external WALL SURF= 109 at time   1
 Processing external WALL SURF= 116 at time   1
 Processing external WALL SURF= 119 at time   1
 Processing external WALL SURF= 121 at time   1
 Processing external WALL SURF= 124 at time   1
 Processing external WALL SURF= 134 at time   1
 Processing external WALL SURF= 143 at time   1
 Processing external WALL SURF= 145 at time   1
 Processing external WALL SURF= 153 at time   1
 Processing external WALL SURF= 161 at time   1
 Processing external WALL SURF= 170 at time   1
 Processing external WALL SURF= 176 at time   1
 Processing external WALL SURF= 181 at time   1
 Processing external WALL SURF= 190 at time   1
 Processing external WALL SURF= 193 at time   1
 Processing external WALL SURF= 197 at time   1
 Processing external WALL SURF= 210 at time   1
 Processing external WALL SURF= 211 at time   1
 Processing external WALL SURF= 213 at time   1
 Processing external WALL SURF= 214 at time   1
 Processing external WALL SURF= 215 at time   1
 Processing external WALL SURF= 224 at time   1
 Processing external WALL SURF= 227 at time   1
 Processing external WALL SURF= 235 at time   1
 Processing external WALL SURF= 237 at time   1
 
*** Fatal Error at time   :         0.000000
    Generated by Unit     : Not applicable or not available
    Generated by Type     : Not applicable or not available
    TRNSHD Message     14 : The internal solar distribution did not sum up 1. Make sure that the zones with detailed beam radiation mode are CONVEX and CLOSED!!
    Reported information  : Not available


More information about the TRNSYS-users mailing list