You can define more than one VENTILATION type for your zone. In many
HVAC systems (especially in humid climates) it is typical for the
outdoor air to mix with return air before passing across the cooling
coil in which case you would only define a single VENTILATION type in
TRNBuild. When you define the VENTILATION type make the air temperature,
RH, and flow rate into INPUTS (as opposed to scheduled values) and then
those inputs will show up in the Simulation Studio along with all the
other Type56 inputs.
regards,
David
On 5/14/2015 2:57 PM, Anton Åhlund wrote:
> Hi!
>
> I want to have a scheduled ventilation of a type 56 zone with outside
> air, while at the same time have inputs(Temp, Rel.hum. and air flow)
> for a cooling coil in the same zone.
>
> Is this possible? If it is, how can I do it?
>
>
> Best regards,
> Anton Åhlund
>
>