[Bldg-sim] Spam:Re: LEED	modelingrequirements	forexistingbuildings
    Mark Sorensen 
    DEnergyServices at comcast.net
       
    Thu Aug 21 08:56:36 PDT 2008
    
    
  
Table G3.1 item 5(f) indicates that you would use the U-factors and SHGC
from the existing building envelope prior to any revisions that are part
of the scope of work being evaluated. Someone please straighten me out
on this because I'm having a hard time understanding how it could be
interpreted that you need to use the minimum U-factors and SHGC from the
tables in Section 5 for the baseline building regardless of whether
those envelope components are being altered or not.
Regards,
Mark Sorensen CEM
Diversified Energy Services
5890 E. Pontaluna Rd.
Fruitport, MI 49415
-----Original Message-----
From: bldg-sim-bounces at lists.onebuilding.org
[mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of Carol
Gardner
Sent: Thursday, August 21, 2008 11:33 AM
To: Jeff Ross-Bain
Cc: Eric O'Neill; bldg-sim at lists.onebuilding.org
Subject: Re: [Bldg-sim] Spam:Re: LEED modelingrequirements
forexistingbuildings
I thought that the rotation requirement was gone in any case.
Carol
Jeff Ross-Bain wrote:
>
> I asked the USGBC for an interpretation (not an official CIR) on the 
> need for rotating an existing building for modeling purposes and the 
> response was that the existing building does in fact need to be
rotated.
>
> This is their response (the "specified analysis" refers to building 
> rotation of an existing building):
>
> If the existing building being renovated is pursuing LEED-NC rather 
> than LEED-EB, then it would indeed be required to undergo the 
> specified analysis. This analysis is used to establish the baseline 
> for energy performance using the ASHRAE standard. LEED doesn't have 
> any specific exemptions for existing buildings in this requirement, 
> but if ASHRAE has some kind of exemption, we will honor that.
>
> Regards,
>
> */Jeffrey G. Ross-Bain, PE, LEED/*
> Smith Dalia Architects
> 621 North Ave NE
> Suite C-140
> Atlanta, GA, 30308
> 404-892-2443
> www.smithdalia.com <http://www.smithdalia.com>
>
> P Build Green...Save Time
>
>
------------------------------------------------------------------------
>
> *From:* bldg-sim-bounces at lists.onebuilding.org 
> [mailto:bldg-sim-bounces at lists.onebuilding.org] *On Behalf Of *Michael
> Tillou
> *Sent:* Thursday, August 21, 2008 9:15 AM
> *To:* 'Jay Keazer'
> *Cc:* 'Eric O'Neill'; bldg-sim at lists.onebuilding.org
> *Subject:* Re: [Bldg-sim] Spam:Re: LEED modeling requirements 
> forexistingbuildings
>
> Jay,
>
> It is my understanding that that is the correct interpretation.
>
> However, I don't think Eric's interpretation that the baseline 
> rotation requirement does not apply to existing buildings is correct. 
> Let me explain why I disagree.
>
> Requirement f in Part 5 of Table 3.1 refers specifically to the 
> //baseline building design// (note the italics which signify that a 
> phrase or word is defined in Section 3 of the Standard) while 
> Requirement a in Part 5 of Table 3.1 refers specifically to the 
> //baseline building performance// (again in italics). The //baseline 
> building design// is not the same as the //baseline building 
> performance// and therefore Requirement f. cannot supercede 
> Requirement a in any case.
>
> One last comment about the equal window distribution. ASHRAE 90.1-2004
> Addendum a removes the equal distribution requirement for windows in 
> the baseline. If you're working on a LEED project I suggest you 
> consider adopting Addendum a to avoid this requirement. USGBC has 
> allowed the use of ASHRAE 90.1-2004 addenda. If you do decide to adopt
> Addendum a remember that USGBC requires that you incorporate all the 
> changes included in the Addenddum. Addendum a has a total of eight 
> changes to Appendix G, most important of which are the changes to the 
> calculation of the baseline HVAC system types.
>
> regards,
>
> Mike
>
> Michael Tillou, PE, LEED
>
> Tillou Engineering, LLC
>
> Williamstown, MA 01267
>
> P: 413-458-9870 C: 413-652-1087
>
>
------------------------------------------------------------------------
>
> *From:* bldg-sim-bounces at lists.onebuilding.org 
> [mailto:bldg-sim-bounces at lists.onebuilding.org] *On Behalf Of *Jay
Keazer
> *Sent:* Tuesday, August 19, 2008 10:42 AM
> *To:* Eric O'Neill; Mark Sorensen; bldg-sim at lists.onebuilding.org
> *Subject:* Re: [Bldg-sim] Spam:Re: LEED modeling requirements for 
> existingbuildings
>
> What about the baseline envelope assemblies? As an example I have an 
> existing building where the windows are being replaced and insulation 
> is being sprayed on the outside of a built up roof.
>
> In the same column of Table G3.1, requirement (b) states that "Opaque 
> assemblies used for /alterations/ shall conform with 5.1.3" and 
> requirement (c) states that "The fenestration areas for envelope 
> /alterations/ shall reflect the limitations on area, U-factor, and 
> SHGC as described in 5.1.3."
>
> 5.1.3 states that "Alterations to the building envelope shall comply 
> with the requirements of Section 5 for insulation, air leakage, and 
> fenestration *applicable to those specific portions of the building 
> that are being altered*."
>
> My interpretation is: because the windows and roof are being altered, 
> I have to use the appropriate U-factors and SHGC from the tables for 
> the baseline windows and roof. However, the walls are not being 
> altered, so I can use the existing construction for the baseline
walls.
>
> Does anybody have a different interpretation?
>
> Thanks!
>
> */Jay Keazer, EI/*
>
> Energy Engineer
>
> TME, Inc.
>
> 2039 N Green Acres Road
>
> Fayetteville, AR 72703
>
> ph 479.521.8634
>
> fax 479.521.1014
>
> _jkeazer at tmecorp.com <mailto:email at tmecorp.com>___
>
> _www.tmecorp.com <http://www.tmecorp.com/>_
>
> *From:* bldg-sim-bounces at lists.onebuilding.org 
> [mailto:bldg-sim-bounces at lists.onebuilding.org] *On Behalf Of *Eric 
> O'Neill
> *Sent:* Thursday, August 14, 2008 3:16 PM
> *To:* Mark Sorensen; bldg-sim at lists.onebuilding.org
> *Subject:* Spam:Re: [Bldg-sim] LEED modeling requirements for existing
> buildings
>
> Mark,
> Under ASHRAE 90.1 Appendix G, Table G3.1, Section 5, "Baseline 
> Building Performance" column, requirement (f) (take a breath.) it 
> states that "For existing building envelopes, the baseline building 
> design shall reflect existing conditions prior to any revisions that 
> are part of the scope of work being evaluated". So the rotation 
> doesn't apply to you. Also, I interpret that to mean the windows don't
> need to be redistributed either. Hope that helps!
>
> */Eric O'Neill/*
> Mechanical Engineer
> Energy Division - Michaels Engineering
>
> 811 Monitor St. Ste 100
> La Crosse, WI 54603
> v: 608-785-1900 x521
> f: 608-784-2270
> elo at michaelsengineering.com
> http://www.michaelsengineering.com
>
> *From:* Mark Sorensen [mailto:DEnergyServices at comcast.net]
> *Sent:* Thursday, August 14, 2008 10:40 AM
> *To:* bldg-sim at lists.onebuilding.org
> *Subject:* [Bldg-sim] LEED modeling requirements for existing
buildings
>
> When modeling an existing building, is required to calculate the 
> proposed building window to wall ratio and equally redistribute the 
> glass area to the baseline building and prepare models for the four 
> rotation exposures? My take is that for a proposed existing building, 
> there is not an opportunity to position the building to the most 
> advantageous exposure and you could end up being penalized if the 
> baseline energy use is averaged for all rotations but I have not been 
> able to find any reference in LEED or ASHRAE to support this. I'm not 
> sure what to think about equal redistribution of the glass areas.
>
> Mark Sorensen
> Diversified Energy Services
> 5890 E. Pontaluna Rd.
> Fruitport, MI 49415
>
>
------------------------------------------------------------------------
>
> _______________________________________________
> Bldg-sim mailing list
> http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
> To unsubscribe from this mailing list send  a blank message to
BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG
>   
_______________________________________________
Bldg-sim mailing list
http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
To unsubscribe from this mailing list send  a blank message to
BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG
    
    
More information about the Bldg-sim
mailing list