[Bldg-sim] Performance Rating Method of of Ashrae 90.1 (2004) Baseline Chiller COP
Ho Tinkit
ho.tinkit at scottwilson.com.hk
Mon Dec 1 04:43:37 PST 2008
Regarding to the Performance Rating Method of of Ashrae 90.1 (2004), there
is an issue of determining baseline Chiller COP need to be clarified.
Regarding to the baseline HVAC system, the parameters need to be set
according to Appendix G of Ashrae 90.1 Standard.
According to table G3.1.1A and table G3.1.1B of App. G3.1.1, the baseline
HVAC system for a building with area larger than 150,000 sqft is specified
as variable air volume with reheat with centrifugal chiller >300tons,
whereas the equipment efficiencies should be modeled at the minimum
efficiency levels in accordance with section 6.4 of Ashrae 90.1 Standard.
Then referring to table 6.8.1 J of section 6.4 of Ashrae 90.1 Standard,
minimum efficiencies for centrifugal chiller COP(standard) should be 6.1.
However, What is the minimum efficiencies for the baseline design COP under
the following condition,
1) If the proposed HVAC design is design to work with leaving chilled water
at 42.8F and entering condenser water temperature of 85F,
2) If the proposed HVAC design is design to work with leaving chilled water
at 42.8F and entering condenser water temperature of 89.6F, and this chiller
is designed to be a ice storage system.
Should the baseline design be modeled at COP 6.1 or should the baseline COP
be estimated by the equations listed below the table 6.8.1 J?
Please advise.
Thanks you for any kindly helps.
Regards,
TK HO
Senior Assistant Engineer
Scott Wilson Ltd
Tel. no. (852) 2410 3847
^^^^^^^^^^^^^^^^^^^^^^^^^^^^^^^^^^^^^^^^^^^^^^^^^^^^^^^^^^^^^^
Scott Wilson supports the UN Global Compact and Caring for the Climate initiatives.
Please consider the environment and only print this email if necessary.
^^^^^^^^^^^^^^^^^^^^^^^^^^^^^^^^^^^^^^^^^^^^^^^^^^^^^^^^^^^^^^
This email and any attachments to it are intended only for the party to
whom they are addressed. They may contain privileged and / or
confidential information. If you have received this transmission in error
please notify the sender immediately and delete any digital copies and
destroy any paper copies. Thank you. Scott Wilson accepts no
contractual liabilities or commitments arising from this email unless
subsequently confirmed by fax or letter or as an email attachment
giving company name, address, registration number and authorized
signatory.
More information about the Bldg-sim
mailing list