[Bldg-sim] natural ventilation for LEED
David Bradley
bradley at tess-inc.com
Thu Mar 20 07:57:21 PDT 2008
Karen,
Yes, we have. We used CONTAM, which is a bulk air flow modeling tool
available from NIST (www.nist.gov) coupled with TRNSYS . TRNSYS did the
thermal model and CONTAM did the interzonal air flows. If your building
model is a single zone, however, I don't think CONTAM or other bulk air
flow models (such as COMIS) will be appropriate, however. Bulk air flow
models define pressure nodes (much like the thermal zones of a building)
and predict air flow between those nodes based on the resistance offered
by gaps around doors, the porosity of building materials, joints between
walls, window frames, operable windows, etc.). If you are just dealing
with one large space then the internal resistance to air flow is quite
low and you would probably need to use a CFD tool such as Fluent to get
at it.
Kind regards,
David
Karen Walkerman wrote:
> Hi All,
>
> has anyone completed a "macroscopic multi-zone, analytic model that
> predicts room-b-room outdoor air flow rates" for LEED NC 2.2 EQ credit
> 2? What software did you use? I'm actually evaluating just one large
> space for my current project.
>
> Any help is appreciated.
>
> Thanks,
>
>
> ~Karen~
> ------------------------------------------------------------------------
>
> _______________________________________________
> Bldg-sim mailing list
> http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
> To unsubscribe from this mailing list send a blank message to BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG
>
--
***********************************************************************
Thermal Energy System Specialists (TESS), LLC
David BRADLEY 2916 Marketplace Drive - Suite 104
Partner Madison, WI 53719
USA
P: +1.608.274.2577
F: +1.608.278.1475
E-mail: bradley at tess-inc.com
Web Pages: http://www.tess-inc.com and http://www.trnsys.com
***********************************************************************
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20080320/85835dd4/attachment-0002.htm>
More information about the Bldg-sim
mailing list