John Ross wrote;
Remember the climate is usually dryer in Winter reducing the ground
thermal coupling for most
climates. This would probably be reversed for California and South
Texas / Houston areas.
David Bradley wrote:
> Keith,
> If you have a cooling dominated application and a relatively cool
> average annual ground temperature, insulating underneath the slab is
> going to disrupt some amount of free cooling that you are getting.
> Adding insulation would drive cooling energy up a bit and heating
> energy down. Depending on the magnitude of the heating and cooling
> changes, you could see a net increase in HVAC energy over the year. An
> increase in heating energy and no change in cooling energy is a bit
> suspicious. You might look into how the software you are using models
> the ground heat transfer. There has been a good bit of work done and
> recently wrapped up under IEA Task 34/45 on evaluating the ground
> coupling models used by various simulation tools.
> Kind regards,
> David
>
>
> Keith Swartz wrote:
>>
>> Do any of you know the reasoning behind why the 2006 edition of the
>> International Energy Conservation Code (IECC) removed the requirement
>> for insulation for unheated slabs for some climate zones? I have done
>> a few energy models recently with slab insulation as a potential
>> energy saving measure. The numbers were very small, which was
>> expected, but what surprised me was that the savings were negative.
>> Adding insulation to the slab actually _increased_ annual energy
>> usage (very slightly). Cooling was unaffected, but fan energy was
>> slightly higher during the heating season. My quick search for
>> research reports or other insights to explain this came up empty. Do
>> any of you have any thoughts? Are the results so insignificant that
>> the differences I am seeing in the calculations could just be
>> considered "noise"?
>>
>>
>>
>> _____________________
>>
>> Keith Swartz, P.E., LEED AP
>> Energy Engineer / Senior Project Manager
>> Energy Center of Wisconsin
>> 455 Science Drive, Suite 200
>> Madison, WI 53711
>> Phone: 608.238.8276 x123
>> Fax: 608.238.0523
>> Email: kswartz at ecw.org <mailto:kswartz at ecw.org>
>> Web: www.ecw.org <http://www.ecw.org>
>>
>> *Energy Center University
>> */Your gateway to sustainable design training and online education
>> programs.
>> /www.ecw.org/university/ <http://www.ecw.org/university/>
>>
>>
>>
>> ------------------------------------------------------------------------
>>
>> _______________________________________________
>> Bldg-sim mailing list
>> http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
>> To unsubscribe from this mailing list send a blank message to BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG
>>
>
> --
> ***********************************************************************
> Thermal Energy System Specialists (TESS), LLC
> David BRADLEY 22 N. Carroll Street - Suite 370
> Partner Madison, WI 53703
> USA
> P: +1.608.274.2577
> F: +1.608.278.1475
> E-mail: bradley at tess-inc.com
> Web Pages: http://www.tess-inc.com and http://www.trnsys.com
>
> ***********************************************************************
> ------------------------------------------------------------------------
>
> _______________________________________________
> Bldg-sim mailing list
> http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
> To unsubscribe from this mailing list send a blank message to BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20090122/74c43f33/attachment-0002.htm>
More information about the Bldg-sim
mailing list