Vikram,
If you look at LEED NC CIR ruling date 2/20/2009 you'll find a similar
situation in a hospital, that was told to use PTACs. This is a situation I
looked up a while ago. I modeled my special pressurization requirement
rooms with PTACs quickly and saw the baseline used less energy than my
proposed design with the chiller / boiler. I didn't go back to look into it
in much, I've got that on my list to do. I can only think it was because
the PTACs fan and coils cycle as needed and don't need to keep running like
the chiller and boiler in the hospital. Anyone have any other insight into
this?
Good luck Vikram.
This e-mail and any attachments contain URS Corporation confidential
information that may be proprietary or privileged. If you receive this
message in error or are not the intended recipient, you should not retain,
distribute, disclose or use any of this information and you should destroy
the e-mail and any attachments or copies.
bldg-sim-request at lists.
onebuilding.org
Sent by: To
bldg-sim-bounces at lists. bldg-sim at lists.onebuilding.or
onebuilding.org g
cc
06/18/2009 03:00 PM Subject
Bldg-sim Digest, Vol 19,
Issue 15
Please respond to
bldg-sim at lists.onebuild
ing.org
Send Bldg-sim mailing list submissions to
bldg-sim at lists.onebuilding.org
To subscribe or unsubscribe via the World Wide Web, visit
http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
or, via email, send a message with subject or body 'help' to
bldg-sim-request at lists.onebuilding.org
You can reach the person managing the list at
bldg-sim-owner at lists.onebuilding.org
When replying, please edit your Subject line so it is more specific
than "Re: Contents of Bldg-sim digest..."
Today's Topics:
1. Appendix G Zoning (Vikram Sami)
2. Re: Appendix G Zoning (David S Eldridge)
3. Re: Appendix G Zoning (David Reddy)
4. BESTTEST Certification (Harding, Ross)
5. Re: BESTTEST Certification (Linda Lawrie)
6. Re: BESTTEST Certification (Michael Donn)
7. conversion factors electricity primary energy (leen peeters)
8. VRV / VRF systems (Allison Coley)
9. Re: VRV / VRF systems (Marcus Sheffer)
10. Re: VRV / VRF systems (Julia Beabout)
11. Re: conversion factors electricity primary energy
(Cramer Silkworth)
12. Chilled Water Meter and Utility Rate (eric wang)
----- Message from Vikram Sami <VSami at lasarchitect.com> on Wed, 17 Jun 2009
17:22:42 -0400 -----
To: "Bldg-Sim" <bldg-sim at lists.onebuilding.org>
Subject: [Bldg-sim] Appendix G Zoning
Exceptions to G3.1.1:
(c) If the baseline HVAC system type is 5, 6, 7, or 8, use separate
single-zone systems conforming with the requirements
of System 3 or System 4 (depending on building
heat source) for any zones having special pressurization
relationships, cross-contamination requirements, or code required
minimum circulation rates.
I’m modeling a building that has baseline system 7. If I read this
correctly then all lab spaces will have their own system and that system
will conform to system 3 from table g3.1.1A. Is that correct? If so – are
all of my lab spaces going to be packaged single zone units? That doesn’t
seem right – especially since lab spaces are more than 50% of the building
area in this case.
I’d appreciate anyone’s help with this.
Thanks
Vikram Sami, LEED AP
Direct Phone 404-253-1466 | Direct Fax 404-253-1366
LORD, AECK & SARGENT ARCHITECTURE
1201 Peachtree Street NE, Suite 300, Atlanta, GA 30361
Responsive Design · Technological Expertise · Exceptional Service
Please visit our new website | www.lordaecksargent.com
P Think GREEN before you print.
----- Message from David S Eldridge <DSE at grummanbutkus.com> on Wed, 17 Jun
2009 17:33:09 -0500 -----
To: Bldg-Sim <bldg-sim at lists.onebuilding.org>
Subject: Re: [Bldg-sim] Appendix G Zoning
Vikram, you should follow the exception (c) if you have a few zones in a
larger building that have special requirements, different from the bulk of
the System 7. This I think would be intended for cold rooms, server rooms,
etc.
For your case with roughly 50% labs and 50% other, you may instead want to
use the exception (a) to add a second system type in order to account for
differences in space requirements between labs and other spaces.
The design building is probably a good guide – if you are accomplishing
your proposed design with one system, then you might find some way to use
one system 7. If you have separate lab/office AHUs in the proposed design,
then two systems under exception (a) may be called for.
Depending on the size of the lab, you may end up with several System type 3
or 4 in the baseline, but for larger labs I think the intention would be to
make two System 7’s.
You may also want to look for the Labs21 guide to Appendix G which includes
some other unrelated suggestions.
David
____________________________________________________________________________________________________________________
David Eldridge, PE
LEED® AP, HBDP
Grumman/Butkus Associates | 820 Davis Street, STE 300 | Evanston, IL 60201
| Ph: (847) 328-3555, ext 224 | Fax: (847) 328-4550
Energy Consultants and Design Engineers
____________________________________________________________________________________________________________________
From: bldg-sim-bounces at lists.onebuilding.org
[mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of Vikram Sami
Sent: Wednesday, June 17, 2009 4:23 PM
To: Bldg-Sim
Subject: [Bldg-sim] Appendix G Zoning
Exceptions to G3.1.1:
(c) If the baseline HVAC system type is 5, 6, 7, or 8, use separate
single-zone systems conforming with the requirements
of System 3 or System 4 (depending on building
heat source) for any zones having special pressurization
relationships, cross-contamination requirements, or code required
minimum circulation rates.
I’m modeling a building that has baseline system 7. If I read this
correctly then all lab spaces will have their own system and that system
will conform to system 3 from table g3.1.1A. Is that correct? If so – are
all of my lab spaces going to be packaged single zone units? That doesn’t
seem right – especially since lab spaces are more than 50% of the building
area in this case.
I’d appreciate anyone’s help with this.
(See attached file: Labs21 - Appendix G for Laboratories.pdf)
----- Message from "David Reddy" <davidr at madisonengineeringps.com> on Wed,
17 Jun 2009 18:27:10 -0700 -----
To: "'Vikram Sami'" <VSami at lasarchitect.com>, "'Bldg-Sim'"
<bldg-sim at lists.onebuilding.org>
Subjec Re: [Bldg-sim] Appendix G Zoning
t:
USGBC also has provided some guidance on the appropriate baseline system
for large laboratories via a few CIRs. Specifically LEED-NC CIR rulings
dated on:
2/27/2007
&
8/13/2007
David Reddy
Madison Engineering, PS
444 NE Ravenna Blvd, Suite 406
Seattle, WA 98115
office: 206-834-0002
direct: 206-829-8622
From: bldg-sim-bounces at lists.onebuilding.org
[mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of Vikram Sami
Sent: Wednesday, June 17, 2009 2:23 PM
To: Bldg-Sim
Subject: [Bldg-sim] Appendix G Zoning
Exceptions to G3.1.1:
(c) If the baseline HVAC system type is 5, 6, 7, or 8, use separate
single-zone systems conforming with the requirements
of System 3 or System 4 (depending on building
heat source) for any zones having special pressurization
relationships, cross-contamination requirements, or code required
minimum circulation rates.
I’m modeling a building that has baseline system 7. If I read this
correctly then all lab spaces will have their own system and that system
will conform to system 3 from table g3.1.1A. Is that correct? If so – are
all of my lab spaces going to be packaged single zone units? That doesn’t
seem right – especially since lab spaces are more than 50% of the building
area in this case.
I’d appreciate anyone’s help with this.
Thanks
Vikram Sami, LEED AP
Direct Phone 404-253-1466 | Direct Fax 404-253-1366
LORD, AECK & SARGENT ARCHITECTURE
1201 Peachtree Street NE, Suite 300, Atlanta, GA 30361
Responsive Design · Technological Expertise · Exceptional Service
Please visit our new website | www.lordaecksargent.com
P Think GREEN before you print.
----- Message from "Harding, Ross" <ross.harding at lincolnescott.com> on Thu,
18 Jun 2009 12:09:33 +1000 -----
To: <bldg-sim at lists.onebuilding.org>
Subject: [Bldg-sim] BESTTEST Certification
Hi All,
Does anyone know where I can find a list of BESTTEST certified Building
Energy Simulation software?
I can only find that Energy Plus has done the test, but not that it is
BESTTest certified?
What about TAS 8.5, does anyone know where the BESTTest certification is?
Regards
Ross Harding
Environmental Design Consultant
Phone +61 2 8907 0900
Direct +61 2 8907 0953
ross.harding at lincolnescott.com
Please consider the environment before printing this email.
This email message is intended only for the addressee(s) and contains
information which may be confidential. If you are not the intended
recipient please do not read, save, forward, disclose, or copy the contents
of this email. If this email has been sent to you in error, please delete
this email and any copies or links to this email completely and immediately
from your system. Views expressed in this message are those of the
individual sender and are not necessarily the views of Lincolne Scott.
http://www.lincolnescott.com/email Advanced Environmental Pty http://ww
s/AElogo1.gif Ltd w.lincoln
is a specialist service of escott.co
Lincolne Scott Pty Ltd m/emails/
a climate neutral company cnlogob.g
lincolnescott.com if
----- Message from Linda Lawrie <linda at fortlawrie.com> on Wed, 17 Jun 2009
20:19:39 -0600 -----
To: "Harding, Ross" <ross.harding at lincolnescott.com>
cc: bldg-sim at lists.onebuilding.org
Subject: Re: [Bldg-sim] BESTTEST Certification
All the EnergyPlus testing reports are posted on the EnergyPlus web site:
http://energyplus.gov/testing.cfm
ASHRAE Standard 140-2007 incorporates many of the IEA BESTest methods. IEA
does not certify software--just provides tests.
Linda
EnergyPlus Development Team
----- Message from Michael Donn <Michael.Donn at vuw.ac.nz> on Thu, 18 Jun
2009 14:26:20 +1200 -----
To: "Harding, Ross" <ross.harding at lincolnescott.com>
cc: "bldg-sim at lists.onebuilding.org"
<bldg-sim at lists.onebuilding.org>
Subject: Re: [Bldg-sim] BESTTEST Certification
Hi Ross
Typically the vendors publish their BESTEST data online. The BESTEST system
is one of self-certification, not a central authorising body….. (see
http://www.iea-shc.org/task34/index.html )
ASHRAE Standard 140 incorporates some of the IEA BESTEST suite and I
understand over time will incorporate more. (
http://www.nrel.gov/docs/fy06osti/40360.pdf )
I am not aware that ASHRAE ‘certify’ software in the way you seek.
m
Michael Donn
Director Centre for Building Performance Research
School of Architecture
Victoria University +64 4 463 6221 work
PO Box 600 +64 21 611 280 mobile
Wellington +64 4 463 6204 work fax
New Zealand +64 21 611 594 mobilefax
http://www.vuw.ac.nz/architecture/staff/academics/michael-donn.aspx
------------------------------------------------------------------------------------
From: bldg-sim-bounces at lists.onebuilding.org
[mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of Harding, Ross
Sent: Thursday, 18 June 2009 2:10 p.m.
To: bldg-sim at lists.onebuilding.org
Subject: [Bldg-sim] BESTTEST Certification
Hi All,
Does anyone know where I can find a list of BESTTEST certified Building
Energy Simulation software?
I can only find that Energy Plus has done the test, but not that it is
BESTTest certified?
What about TAS 8.5, does anyone know where the BESTTest certification is?
Regards
Ross Harding
Environmental Design Consultant
Phone +61 2 8907 0900
Direct +61 2 8907 0953
ross.harding at lincolnescott.com
Please consider the environment before printing this email.
This email message is intended only for the addressee(s) and contains
information which may be confidential. If you are not the intended
recipient please do not read, save, forward, disclose, or copy the contents
of this email. If this email has been sent to you in error, please delete
this email and any copies or links to this email completely and immediately
from your system. Views expressed in this message are those of the
individual sender and are not necessarily the views of Lincolne Scott.
http://www.lincolnescott.com/email Advanced Environmental Pty http://ww
s/AElogo1.gif Ltd w.lincoln
is a specialist service of escott.co
Lincolne Scott Pty Ltd m/emails/
a climate neutral company cnlogob.g
lincolnescott.com if
----- Message from leen peeters <l.f.r.peeters at gmail.com> on Thu, 18 Jun
2009 12:51:02 +0200 -----
To: "bldg-sim at lists.onebuilding.org"
<bldg-sim at lists.onebuilding.org>
Subject: [Bldg-sim] conversion factors electricity primary energy
Dear,
could anyone help me out with conversion factors primary energy to
electricity for Canada and Italy?
Thanks!
Leen
----- Message from "Allison Coley" <Allison.Coley at cjmw.com> on Thu, 18 Jun
2009 09:10:03 -0400 -----
To: <bldg-sim at lists.onebuilding.org>
Subject: [Bldg-sim] VRV / VRF systems
Hello,
We are in the very early stages of a project and are weighing the pros/cons
of a VRV/VRF system vs. geothermal. Any general lessons learned with using
VRV/VRF systems, or pros/cons of certain software packages in modeling them
for demonstrated energy savings?
Thanks,
Allison
----- Message from "Marcus Sheffer" <sheffer at energyopportunities.com> on
Thu, 18 Jun 2009 09:46:20 -0400 -----
To: "'Allison Coley'" <Allison.Coley at cjmw.com>,
<bldg-sim at lists.onebuilding.org>
Subject Re: [Bldg-sim] VRV / VRF systems
:
I believe EnergyPro can model these systems.
Marcus Sheffer
7group
From: bldg-sim-bounces at lists.onebuilding.org
[mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of Allison Coley
Sent: Thursday, June 18, 2009 9:10 AM
To: bldg-sim at lists.onebuilding.org
Subject: [Bldg-sim] VRV / VRF systems
Hello,
We are in the very early stages of a project and are weighing the pros/cons
of a VRV/VRF system vs. geothermal. Any general lessons learned with using
VRV/VRF systems, or pros/cons of certain software packages in modeling them
for demonstrated energy savings?
Thanks,
Allison
----- Message from Julia Beabout <juliabeabout at yahoo.com> on Thu, 18 Jun
2009 07:41:12 -0700 (PDT) -----
To: Allison Coley <Allison.Coley at cjmw.com>,
bldg-sim at lists.onebuilding.org
Subject: Re: [Bldg-sim] VRV / VRF systems
Hi Allison
Trace 700 can model VRV/VRF systems.
I haven't tried in Trace before, but, looks pretty easy.
Julia
From: Allison Coley <Allison.Coley at cjmw.com>
To: bldg-sim at lists.onebuilding.org
Sent: Thursday, June 18, 2009 9:10:03 AM
Subject: [Bldg-sim] VRV / VRF systems
Hello,
We are in the very early stages of a project and are weighing the pros/cons
of a VRV/VRF system vs. geothermal. Any general lessons learned with using
VRV/VRF systems, or pros/cons of certain software packages in modeling them
for demonstrated energy savings?
Thanks,
Allison
----- Message from "Cramer Silkworth" <silkworth at transsolar.com> on Thu, 18
Jun 2009 17:07:20 +0200 -----
To: bldg-sim at lists.onebuilding.org, l.f.r.peeters at gmail.com
Subject: Re: [Bldg-sim] conversion factors electricity primary energy
Awhile ago I found a lot of this type info on Natural Resources Canada's
energy webpage:
http://nrcan.gc.ca/eneene/statstat/index-eng.php
it's huge, but maybe some strategic searching will get you to PE factors
-Cramer
J. Cramer Silkworth
Transsolar Inc.
Technical consulting for energy efficiency and user comfort in buildings.
Stuttgart - Munich - New York
134 Spring Street Suite 601
New York, NY 10012
212-219-2255
silkworth at transsolar.com
From: leen peeters [mailto:l.f.r.peeters at gmail.com]
Sent: Thursday, June 18, 2009 6:51 AM
To: bldg-sim at lists.onebuilding.org
Subject: [Bldg-sim] conversion factors electricity primary energy
Dear,
could anyone help me out with conversion factors primary energy to
electricity for Canada and Italy?
Thanks!
Leen
----- Message from eric wang <shaojieworld2006 at yahoo.com> on Thu, 18 Jun
2009 08:53:40 -0700 (PDT) -----
To: "bldg-sim at lists.onebuilding.org bldg-sim at lists.onebuilding.org"
<bldg-sim at lists.onebuilding.org>
Subjec [Bldg-sim] Chilled Water Meter and Utility Rate
t:
Hi,
I created a chilled water meter and its utility rate. For the utility
rate, all parameters are either left blank or undefined except taxes are
set to base. After exporting the DOE2 sim report, I found there is still a
charge for chiller water meter. Does anyone know why the charge is not
zero for the chilled water meter?
Thanks,
Shaojie
_______________________________________________
Bldg-sim mailing list
Bldg-sim at lists.onebuilding.org
http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20090618/7a56da62/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: C2336189.jpg
Type: image/jpeg
Size: 59935 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20090618/7a56da62/attachment.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: graycol.gif
Type: image/gif
Size: 105 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20090618/7a56da62/attachment.gif>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: pic18875.gif
Type: image/gif
Size: 1255 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20090618/7a56da62/attachment-0001.gif>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: ecblank.gif
Type: image/gif
Size: 45 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20090618/7a56da62/attachment-0002.gif>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: C9974237.gif
Type: image/gif
Size: 1327 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20090618/7a56da62/attachment-0003.gif>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: C8272987.gif
Type: image/gif
Size: 928 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20090618/7a56da62/attachment-0004.gif>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: C7269931.gif
Type: image/gif
Size: 1327 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20090618/7a56da62/attachment-0005.gif>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: C0899992.gif
Type: image/gif
Size: 928 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20090618/7a56da62/attachment-0006.gif>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: Labs21 - Appendix G for Laboratories.pdf
Type: application/pdf
Size: 144347 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20090618/7a56da62/attachment.pdf>
More information about the Bldg-sim
mailing list