[Bldg-sim] Four orientations for new construction attached to existing buildings?
Nick Caton
ncaton at smithboucher.com
Thu May 30 10:06:56 PDT 2013
Just to toss a slightly different experience into the hat:
I recently had a grouping of 3 LEED projects (new building footprint was minimal) sharing the following identical comment language:
"Note that only projects that are greater than 50% new construction are required to simulate all four rotations. Please revise the energy model as required and report only the zero degree rotation in Table EAp2-4."
I think this is a LEED-specific line in the sand, but my takeaway is that buildings which are largely new construction (by >50%) are expected to be rotated for the baseline.
For these recent models, this direction had negligible effect on the documented performance, but I was able to save some fraction of time/effort for the second round of documentation.
Having experienced this, it was a pretty painless fix - I wish all LEED review commentary were this easy! If I were at all unsure on this issue at the first submittal, prior to review commentary, I might just plan on doing the rotations anyway as it's a pretty easy thing to untick the parametric runs and assemble less documentation if it comes up (under eQuest/DOE2).
If you have some weeks prior to your submission deadline, I've heard that contacting GBCI's technical staff directly by email has worked well for others: http://www.gbci.org/contactcertification.aspx This isn't the same thing as a formal CIR (it's free), and I understand they'll tell you plainly if your clarification needs to be submitted as a formal CIR for the project. If you should pursue this option, let us know how it turns out!
Regards,
~Nick
[cid:489575314 at 22072009-0ABB]
NICK CATON, P.E.
SENIOR ENGINEER
Smith & Boucher Engineers
25501 west valley parkway, suite 200
olathe, ks 66061
direct 913.344.0036
fax 913.345.0617
www.smithboucher.com
From: bldg-sim-bounces at lists.onebuilding.org [mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of Bishop, Bill
Sent: Thursday, May 30, 2013 9:55 AM
To: Stormy L. Shanks; Jim Dirkes; Building SimForum
Subject: Re: [Bldg-sim] Four orientations for new construction attached to existing buildings?
Thanks Jim, Stormy.
The project doesn't seem to meet the definition/intent of "addition". It has independent MEP systems and it doesn't share any structural elements with the two other dorms that it is connected to. It just has doors in the stairwells that allow access to the central corridors of the adjacent two dorms.
Nevertheless, I will skip the baseline rotations and let the LEED Reviewer tell me otherwise.
~Bill
From: Stormy L. Shanks [mailto:shankssl at kjww.com]
Sent: Thursday, May 30, 2013 10:22 AM
To: Bishop, Bill; Building SimForum
Subject: RE: [Bldg-sim] Four orientations for new construction attached to existing buildings?
Hi, Bill - I had this situation once, and I rotated the baseline and submitted it. I got the following comment:
Table 1.8.1 and Table 1.8.1(b) of the template include the simulation results for the 90-degree, 180-degree, and 270-degree Baseline model rotations; however, since this project is an addition to an existing project, the Baseline model must not be simulated for the different rotations. Revise Table 1.8.1 and Table 1.8.1(b) by excluding the results for the 90-degree, 180-degree, and 270-degree Baseline model rotations.
[cid:image001.png at 01CE0924.38506AB0]
Stormy L. Shanks, PE
Mechanical Engineer
2882 106th St, Des Moines, IA 50322
web<http://www.kjww.com/> | Facebook<http://www.facebook.com/kjwwengineering> | Twitter<http://twitter.com/kjww> | LinkedIn<http://www.linkedin.com/company/kjww-engineering-consultants>
From: bldg-sim-bounces at lists.onebuilding.org<mailto:bldg-sim-bounces at lists.onebuilding.org> [mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of Bishop, Bill
Sent: Thursday, May 30, 2013 9:06 AM
To: Building SimForum
Subject: [Bldg-sim] Four orientations for new construction attached to existing buildings?
A new dorm is physically connected to two existing buildings. Do I do four rotations for LEED modeling?
Thanks,
Bill
William Bishop, PE, BEMP, BEAP, LEED AP | Pathfinder Engineers & Architects LLP
Senior Energy Engineer
134 South Fitzhugh Street Rochester, NY 14608
T: (585) 325-6004 Ext. 114 F: (585) 325-6005
bbishop at pathfinder-ea.com<mailto:wbishop at pathfinder-ea.com> www.pathfinder-ea.com<http://www.pathfinder-ea.com/>
P Sustainability - the forest AND the trees. P
P.S. The world's first car accident occurred this day in 1896. Henry Wells hit a bicyclist in NYC.
________________________________
This message and any attachments contain information intended for a specific party and may include sensitive or confidential material. If you are not the intended recipient, please do not read, copy, use, or disclose to others. Please notify the sender of the delivery error by reply and then permanently delete this message and all attachments.
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20130530/6842e525/attachment-0002.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image002.jpg
Type: image/jpeg
Size: 1459 bytes
Desc: image002.jpg
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20130530/6842e525/attachment-0002.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image003.png
Type: image/png
Size: 9229 bytes
Desc: image003.png
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20130530/6842e525/attachment-0002.png>
More information about the Bldg-sim
mailing list