[Bldg-sim] Claiming refrigerated casework savings for a LEED project
Julien Marrec
julien.marrec at gmail.com
Wed Jan 22 15:10:36 PST 2014
Hi Jim,
Just to clarify, are those open or closed refrigerated units? (Is there a
door?)
How many are we talking about? (kW or tons)
Are the compressors integrated within the unit (heat rejection within the
conditioned area) or do you have condensers outside? If you do, are you
also reusing waste heat to produce either hot water or heating?
When you say you have data from other stores but they are not identical,
what do you mean? Isn't there a unit that is similar (or exactly the same)
to those previously installed (reading your email I believe the
replacements have already been made in your studied building) where you
could strap a pulse meter for example for at least a couple of weeks?
Best,
--
Julien Marrec, EBCP, BPI MFBA
Ingénieur en efficacité énergétique du bâtiment
T: +33 6 95 14 42 13
www.julienmarrec.com
DoYouBuzz : www.doyoubuzz.com/julien-marrec_1
LinkedIn (fr) : www.linkedin.com/in/julienmarrec/fr
LinkedIn (en) : www.linkedin.com/in/julienmarrec
2014/1/22 Jim Dirkes <jim at buildingperformanceteam.com>
> Dear Forum,
>
> I am modeling a supermarket which has made effort to install refrigerated
> casework that is more efficient than “normal” in three ways:
>
> • Casework lighting is LED instead of fluorescent
>
> • Evaporator fans use ECM motors and are demonstrably more
> efficient
>
> • The compressors have higher COP
>
> I did not realize that claiming savings from a “process” load also
> requires substantiation of the Baseline energy for the process load via
> comparison to several similar facilities or a published paper. I wish I
> knew that months ago!
>
> We have data from three other supermarkets owned by the same company, but
> these other examples are not identical. So far, all I can say is that:
>
> a) Manufacturer literature claims that LEDs used in their
> casework use ~ 65% less energy than fluorescent lights
>
> b) ECM fans use about 35% less energy in a manufacturer power
> comparison table
>
> c) The COP is better (I do not have detailed data yet)
>
>
>
> *This strikes me as a fairly weak argument, so I am asking you for
> suggestions or published data to strengthen the argument.*
>
>
>
> p.s., My last alternative is to ignore the process energy savings and make
> it the same for both models. I think the savings are substantial, however,
> and would rather find a way to claim them!
>
>
>
> [image: BPT-e-mail-signature-template_readable-text]
>
>
>
> "Attack me … rather than the path I follow and which I point to anyone who
> asks me where I think it lies. If I know the way home and am walking along
> it drunkenly, is it any less the right way because I am staggering side to
> side?" Leo Tolstoy
>
>
>
> _______________________________________________
> Bldg-sim mailing list
> http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
> To unsubscribe from this mailing list send a blank message to
> BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20140123/d9302309/attachment-0002.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/png
Size: 23722 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20140123/d9302309/attachment-0002.png>
More information about the Bldg-sim
mailing list