[Date Prev][Date Next][Thread Prev][Thread Next][Date Index][Thread Index]

Re: [EnergyPlus_Support] revisiting design day info



The design data in the weather files is from 2001 ASHRAE data.  The  
datasets use pre-1997 data.  The ASHRAE data was completely redone in 
the 1997 Handbook of Fundamental.  The percentage basis was seasonal 
in pre-1997, now it is annual.  This, along with some other changes 
in method resulted in slightly different values. 

"MWS .40%" and PWD .40% are the cooling wind conditions. 3.  Almost, 
use "Range of DB" data for cooling day, use zero range (constant 
temperature) for heating day; clearness, must select, conservative is 
zero for heating day, 1.0 for cooling day, clearness ranges from 0.9 
at sea level in humid region to 1.1 at high altitude.  



On 9 Nov 2002, at 22:08, no_rb wrote:

> If i look at the 5zoneaircooled.idf example - the design day 
> information does not completely match the info in the USA_IL_Chicago-
> Ohare_TMY2.epw/rpt file (and it did not match the blastdesign file).
> Also i cannot seem to find wind direction slot for the cooling design
> day in the weather file
> 
> am i missing something or does the ashrae design day not provide
> complete information for the eplus design input?
> 
> thanks in advance for any pointers.
> 
> rohini
> 
> 
> To unsubscribe from this group, send an email to:
> EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
> 
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
> 
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
> 
> 
> 
> 
> 
> 
> Your use of Yahoo! Groups is subject to
> http://docs.yahoo.com/info/terms/ 
> 


------------------------ Yahoo! Groups Sponsor ---------------------~-->
Get 128 Bit SSL Encryption!
http://us.click.yahoo.com/JjlUgA/vN2EAA/kG8FAA/dkFolB/TM
---------------------------------------------------------------------~->

To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/




 

Your use of Yahoo! Groups is subject to http://docs.yahoo.com/info/terms/