[Date Prev][Date Next][Thread Prev][Thread Next][Date Index][Thread Index]

Re: [EnergyPlus_Support] Electric Equipment per sq.mt.



Theoretically there is no upper limit on the level of internal gains 
in a zone.  If the system is not cooling properly, then there is 
something wrong with the sizing inputs, the system connections, or 
the thermostat controls.

Mike



On 13 May 2003, at 16:46, Ruchi Choudhary wrote:

> 
> 
> Hi,
> 
> I am simulating a 500 sq.mt. laboratory with a dual duct VAV system
> set to autosize with control type 4. I am wondering if there is an
> upper limit to how much electric equipment per sq.mt. can be input for
> maintaining the zone air temperature within a reasonable range? The
> three zone in the example files uses approx 60-80W/sq.mt. Even with 47
> w/sq.mt., the zone temperatures I get are way off the specified
> setpoint.
> 
> I have checked all schedules and both heating and cooling are
> available all through the year.
> 
> thanks
> 
> 
> 
> 
> 
> ------------------------ Yahoo! Groups Sponsor
> ---------------------~--> Rent DVDs Online - Over 14,500 titles. No
> Late Fees & Free Shipping. Try Netflix for FREE!
> http://us.click.yahoo.com/YoVfrB/XP.FAA/uetFAA/dkFolB/TM
> ---------------------------------------------------------------------~
> ->
> 
> To unsubscribe from this group, send an email to:
> EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
> 
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
> 
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
> 
> Attachments are not allowed -- please post any files to the
> appropriate folder in the Files are of the Support Web Site.
> 
> 
> 
> 
> 
> 
> Your use of Yahoo! Groups is subject to
> http://docs.yahoo.com/info/terms/ 
> 



========================================================
EnergyPlus Testing and Support      
EnergyPlus-Support@xxxxxxxx


------------------------ Yahoo! Groups Sponsor ---------------------~-->
Rent DVDs from home.
Over 14,500 titles. Free Shipping
& No Late Fees. Try Netflix for FREE!
http://us.click.yahoo.com/BVVfoB/hP.FAA/uetFAA/dkFolB/TM
---------------------------------------------------------------------~->

To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files are of the Support Web Site.




 

Your use of Yahoo! Groups is subject to http://docs.yahoo.com/info/terms/