Re: [EnergyPlus_Support] PurchAir 210 MJ/m2/year, RadLoTempHydrTermReheat 314 MJ/m2/year




RadLoTempHydrTermReheat.idf include a constant voume terminal reheat system for 
cooling, so I would expect the total heating load to be higher.  
RadLoHydrHeatCoolAuto.idf would give a better comparison (with Milano design 
days instead of Chicago design days).

Mike


On 11 Feb 2005, at 8:02, ingdallolio wrote:

> 
> 
> Using the Milano (Italy) weather file,  I'm running the example file 
> PurchAir.idf and I get a PurchasedHeating:facility of 210 MJ/m2/year 
> ( its 130 m2 building), when I run, with the same weather file, the 
> same building, with RadLoTempHydrTermReheat.idf I get a 
> PurchasedHeating:facility of 314 MJ/m2/year. It looks like a big 
> difference. I'd appreciate any help to understand this.
> Thanks, Andrea.
> 
> 
> 
> 
> 
> 
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
> 
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
> 
> Attachments are not allowed -- please post any files to the appropriate folder
> in the Files area of the Support Web Site.
> 
> Yahoo! Groups Links
> 
> 
> 
> 
> 
> 
> 
> 
> 



========================================================
Michael J. Witte, GARD Analytics, Inc.
EnergyPlus Testing and Support      
EnergyPlus-Support@xxxxxxxx




The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
 
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/