[Date Prev][Date Next][Thread Prev][Thread Next][Date Index][Thread Index]

Re: [EnergyPlus_Support] a doubt for air loop!




There can be multiple AIR PRIMARY LOOPs in a simulation.  Or some zones may be 
served by zone equipment only, or by zone equipment and an AIR PRIMARY LOOP.  
The only restriction is that a given zone may not be served by more than one 
air loop.  Some examples with multiple air loops are IndEvapCoolerRTUoffice and 
SmOffPSZ.

Mike


On 14 Mar 2005, at 2:14, hbn_pch wrote:

> 
> 
> Dear,
>    I've a doubt for air loop.
> 
>    I found that all the zones are served by the same air supply loop 
> in the E+'s examples.But not all the zones have the centralized air 
> supply for an actual building.
> 
>   For example,some zones have their own outside air supply and their 
> own cooling&heating coils;but others perhaps have another outside air 
> supply and different cooling&heating coils.
> 
>   How to simulate for the above instance?
>   thanks!
> 
>   pch
> 
> 
> 
> 
> 
> 
> 
> 
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
> 
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
> 
> Attachments are not allowed -- please post any files to the appropriate folder
> in the Files area of the Support Web Site.
> 
> Yahoo! Groups Links
> 
> 
> 
> 
> 
> 
> 
> 
> 



========================================================
Michael J. Witte, GARD Analytics, Inc.
EnergyPlus Testing and Support      
EnergyPlus-Support@xxxxxxxx




The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
 
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/