[Date Prev][Date Next][Thread Prev][Thread Next][Date Index][Thread Index]

Re: [EnergyPlus_Support] Mass Flow Rate Error Message



There is a known problem in version 1.2.3.023 which can cause such warnings to 
occur during the intial iterations for an HVAC timestep.  If these warnings are 
due to that problem, the solution continues to iterate to a final answer and 
this condition no longer exists for that time step.  So, if the final results 
look correct, then these warnings can be ignored.

Mike


On 22 Nov 2005, at 8:58, serrangeli wrote:

> Error -- Mass Flow Rate Calculation in Plant Loop=92 HOT WATER LOOP,
> Outlet and Inlet differ by more than tolerance.
>    **   ~~~   ** Loop inlet node=92 HW SUPPLY INLET,
> flowrate=4.650098100473592E-002
>    **   ~~~   ** Loop outlet node=92 HW SUPPLY OUTLET,
> flowrate=0.000000000000000E+000
> 
> 
> Hello, How Can I receive this error message if the room's heat gain is
> ok? Why Does the room temperature increase if flowrate = 0? 
> 
> Thanks
> 
> 
> 
> 
> 
> 
> 
> 
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
> 
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
> 
> Attachments are not allowed -- please post any files to the appropriate folder
> in the Files area of the Support Web Site.
> 
> EnergyPlus Documentation is searchable.  Open EPlusMainMenu.idf and press the
> "search" button.
> 
> Yahoo! Groups Links
> 
> 
> 
> 
> 
> 
> 
> 
> 



========================================================
Michael J. Witte, GARD Analytics, Inc.
EnergyPlus Testing and Support      
EnergyPlus-Support@xxxxxxxx




------------------------ Yahoo! Groups Sponsor --------------------~--> 
1.2 million kids a year are victims of human trafficking. Stop slavery.
http://us.click.yahoo.com/WpTY2A/izNLAA/yQLSAA/dkFolB/TM
--------------------------------------------------------------------~-> 

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.idf and press the "search" button.
 
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/