[Date Prev][Date Next][Thread Prev][Thread Next][Date Index][Thread Index]

Re: [EnergyPlus_Support] Humidity



 I suspect that the window AC is running with cycling fan while the other 
systems are continuous fan.  Make the the window ac objects (AIR 
CONDITIONER:WINDOW:CYCLING and COIL:DX:CoolingBypassFactorEmpirical) are set to 
continuous fan (ContFanCycComp).

Mike


On 30 Nov 2005, at 14:49, eric_zhou1223 wrote:

>  Hi,
> 
>     With  thermostats control in some zones, I noticed a windowAC 
> system can achieve a notablly lower relative humidity than a fancoil 
> system or the whole-air system in summer days. Given that all other 
> conditions are kept the same, i,e.,cooling capacity, building 
> discriptions, supply air design condition,and so forth.  Is this result 
> reliable? If yes , what would be the reason?
> 
> Thank you .
> 
> Eric
> 
> 
> 
> 
> 
> 
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
> 
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
> 
> Attachments are not allowed -- please post any files to the appropriate folder
> in the Files area of the Support Web Site.
> 
> EnergyPlus Documentation is searchable.  Open EPlusMainMenu.idf and press the
> "search" button.
> 
> Yahoo! Groups Links
> 
> 
> 
> 
> 
> 
> 



========================================================
Michael J. Witte, GARD Analytics, Inc.
EnergyPlus Testing and Support      
EnergyPlus-Support@xxxxxxxx




------------------------ Yahoo! Groups Sponsor --------------------~--> 
Get Bzzzy! (real tools to help you find a job). Welcome to the Sweet Life.
http://us.click.yahoo.com/KIlPFB/vlQLAA/TtwFAA/dkFolB/TM
--------------------------------------------------------------------~-> 

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.idf and press the "search" button.
 
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/