[Date Prev][Date Next][Thread Prev][Thread Next][Date Index][Thread Index]

Re: [EnergyPlus_Support] clarification



The restriction is probably better stated "Only one air loop terminal unit is 
allowed per zone."  Air terminal units are objects such as SINGLE 
DUCT:VAV:REHEAT and DIRECT AIR.  Some air terminal units connect directly to 
the zone splitter or supply plenum outlet, but some require an extra object 
called AIR DISTRIBUTION UNIT to complete the connection.  All of these types of 
objects apply to AIR PRIMARY LOOPs serving a zone.

Mike


On 15 Jan 2006 at 6:02, kir kumar wrote:

> Dear Micheal witte,
>   As i mentioned in one of my previousd emails, that i came across  the
> following statement. " Only one ADU(Air Distribution Unit) is allowed per
> zone". The source of this statement is  'University Teaching material online"
> which i downloaded from the main E+ website--Building technologies program.
>    
>    Actually i nedd one clarification. What is the difference between "Air
> distribution unit" and "Air terminal unit".
>    As far as i understand, ADU is not VAV box alone. It involves splitter, Vav
> box, mixer etc. ATU is a terminal unit which is virtually a VAV BOX.(MAY
> INCLUDE REHEAT COILS).
>    Please correct me if i am wrong.
>   kiran
>    
>     u
> 
> 
> 
> Send instant messages to your online friends http://in.messenger.yahoo.com 
> 
> [Non-text portions of this message have been removed]
> 
> 
> 
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
> 
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
> 
> Attachments are not allowed -- please post any files to the appropriate folder
> in the Files area of the Support Web Site.
> 
> EnergyPlus Documentation is searchable.  Open EPlusMainMenu.idf and press the
> "search" button.
>  
> Yahoo! Groups Links
> 
> 
> 
>  
> 
> 
> 
> 


========================================================
Michael J. Witte, GARD Analytics, Inc.
EnergyPlus Testing and Support      
EnergyPlus-Support@xxxxxxxx





The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.idf and press the "search" button.
 
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/