RE: [EnergyPlus_Support] Water-to-Air Heatpump and Humidity Control



EnergyPlus can model GSHP plus boiler plus solar serving the same hot water 
loop.  There are some limitations on the ground heat exchanger types that can 
be modeled.  In the EnergyPlus Input Output reference, please see GROUND HEAT 
EXCHANGER:VERTICAL.  For solar hot water, there is an extensive dataset of 
predefined performance parameters for 170 specific models of flat plate 
collector.

Mike


On 20 Apr 2007 at 11:22, Kevin J. Kyte wrote:

> I am modeling a GSHP that complements a boiler in which the hot water loop
> goes to heating coils in a make-up air unit.
> I have been trying to model this in equest/doe 2.2 and I understand several
> complications result from this scenario.
> 
> Can energyplus simulate such a situation?  Also, I will need to include
> solar water heating into the system.  I know doe 2.2
> does not compute solar water heating, can energyplus simulate solar heating
> water into the loop too?
> 
> I am thankful for any assistance.
> 
> Kevin J. Kyte
> Junior Mechanical Engineer
> T.  717.636.1800
> F.  716.636.1856
> 
> 
> 
> 
> [Non-text portions of this message have been removed]
> 
> 
> 
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
> 
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
> 
> Attachments are not allowed -- please post any files to the appropriate folder
> in the Files area of the Support Web Site.
> 
> EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the
> Documentation link and press the "search" button.
> 
> Yahoo! Groups Links
> 
> 
> 
> 
> 


========================================================
Michael J. Witte, GARD Analytics, Inc.
EnergyPlus Testing and Support      
EnergyPlus-Support@xxxxxxxx





The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
 
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/