[Date Prev][Date Next][Thread Prev][Thread Next][Date Index][Thread Index]

[EnergyPlus_Support] cfm/ton limits file



I examined the issues in Fred's post responding to my question about 
cfm/ton (message and response below) and still cannot figure out why 
my PTACs are sizing the way that they are.  I posted the file for 
more help (D1+_401.idf).  A note about the file - the HVAC systems 
are a bit complicated as I am modeling a DOAS system - so I have one 
system supplying ventilation air to the zones and then PTACs in each 
zone providing secondary heating/cooling.

Thanks,

Andrew







>The air flow is calculated first and is fundamental - it is not 
>altered.
The cooling capacity
is then calculated and is limited by 450 cfm/ton.

The cooling flow rate is basically established by the zone design
sensible cooling load - which is set
by your design day weather, internal loads, outside air requirements,
window & wall heat gains etc.

So, if you are seeing an error by a factor of 6, the questions would 
be:

1) are your design calc inputs correct (does the design flow rate 
seem
reasonable).

2) do you have a huge latent load (from internal sources or outside 
air)?

Upload your file if things continue to ne baffling.

Fred Buhl

asheaffe wrote:
> I am having a problem getting PTAC cooling coils to size correctly.
> The coil cooling capacities are sizing smaller than they should
> (considerably smaller - by a factor of almost 6). The eio file
> reports that the coils are sizing right up at the limit of 450 
cfm/ton
> (6.04E-05 m3/W). Sooo - I am taking this to mean that the low 
tonnage
> is correspondingly limiting the air flow. However, I need more
> tonnage to supply zone temps - so why is the sizing routing 
limiting
> my tonnage?
>
> How do I move them off of this limit? The PTAC air flows are all
> autosized. My zone sizing design cooling temp is 14C - which I 
think
> is fairly resonable.
>
> Thanks for the help,
>
> Andrew
>
>
>
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
>
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
>
> Attachments are not allowed -- please post any files to the 
appropriate folder
in the Files area of the Support Web Site.
>
> EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf 
under the
Documentation link and press the "search" button.
>
> Yahoo! Groups Links
>
>
>
>




The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
 
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/