[Date Prev][Date Next][Thread Prev][Thread Next][Date Index][Thread Index]

Re: [EnergyPlus_Support] I add a window, but the temperature inside the building doen't change



The shoebox is unconditioned, but the ground temperatures under the slab are 17-
21C which is representative of a conditioned space.  So, the ground 
temperatures are driving the entire simulation for this model.  The window is 
small and it has similar thermal properties to the exterior walls (window u-
value=6, wall u-value=4).  To see the impact you expect, either change the 
ground temperatures, or decouple the floor from the ground.

Mike


On 2 Oct 2007 at 19:45, Daniel Solís wrote:

> I'm newbie in e+, so I started simulating a shoebox-shaped room. Then, 
> I added a window (single 6mm clear glass, 1m2) facing to the south. 
> When I compare the temperature in the inside with and w/o the window, 
> it's almost the same (few hundreths of difference), which doesn't make 
> sense.
> 
> I uploaded the file, it's Odon3.idf
> 
> 
> Thanks
> 
> Daniel Solís
> 
> 
> 
> 
> 
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
> 
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
> 
> Attachments are not allowed -- please post any files to the appropriate folder
> in the Files area of the Support Web Site.
> 
> EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the
> Documentation link and press the "search" button.
> 
> Yahoo! Groups Links
> 
> 
> 
> 
> 


========================================================
Michael J. Witte, GARD Analytics, Inc.
EnergyPlus Testing and Support      
EnergyPlus-Support@xxxxxxxx





The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
 
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/