[Equest-users] oa from system

Verena Kindl kindl at scholze.de
Tue Sep 1 07:30:32 PDT 2009


Thanks for the great help. But how do I specify the constant cool and heat control to 68 F? I can not find where I can specify the temperature for the system unit only the zone entering supply temp (see figure) but this is the temperature after the Fan coils ?

 

Thanks Verena

 

 

 

________________________________

Von: Bishop, Bill [mailto:wbishop at pathfinder-ea.com] 
Gesendet: Dienstag, 1. September 2009 14:49
An: Verena Kindl; equest-users at lists.onebuilding.org
Betreff: RE: [Equest-users] oa from system

 

Verena,

You should be able to assign different loops to the system-level and zone-level coils:

 

 

 

Regards,

 

William Bishop, EIT, LEED® AP | Pathfinder Engineers & Architects LLP

Mechanical Engineer

 

134 South Fitzhugh Street
Rochester, NY 14608
T: (585) 325-6004 Ext. 114
F: (585) 325-6005

wbishop at pathfinder-ea.com

www.pathfinder-ea.com

P Please strive to live sustainably.

________________________________

From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Verena Kindl
Sent: Tuesday, September 01, 2009 8:14 AM
To: equest-users at lists.onebuilding.org
Subject: Re: [Equest-users] oa from system

 

Thanks Josh, but I already tried to model a IU unit but i have a different temperature range of the coils for the main AHU (90/50°C) and the coils of the FC (45/36°C) and I can not assign to different loops to the IU. So I am still trying.

 

________________________________

Von: Joshua Wolfe [mailto:jwolfe at geo-marine.com] 
Gesendet: Dienstag, 1. September 2009 14:11
An: Verena Kindl; equest-users at lists.onebuilding.org
Betreff: RE: oa from system

 

Try a system type of IU, with the induction ratio matching that of the FCs. The main system then needs to be set to 100% OA with constant cool and heat control set to 68F. You will have to fake in extra fan power to match that of the FCs. Hope this helps.

 

Josh

From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Verena Kindl
Sent: Tuesday, September 01, 2009 3:15 AM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] oa from system

 

Hello,

 

I have a SZRH system which should provide outside air to the FC system. The air it provides should always be 68 F. What temperatures shall I put for cooling design and heating design / thermostat setpoint T. I put min supply temp and max supply temp to 68 F and the other design temperatures to 53/90F cause I do not have a thermostat there ( the air is always provided with 68 F). Then I specified the OA constant to 4000 cfm and determined the min outside air ratio =1. Is there sth wrong with my temperature settings as I do not get any coil loads for the system (SS-J report)? When I set all temperatures to 68 F the ventilation air I require is too huge. Do I have to put the min OA ratio to 1, 0 or shall I leave it blank for the FC system? I mean is it enough to put OA from system SZRH? Cause someone told me I have to put it to 0 as I do not have any outside air put I do it is from the system. I am confused. 

Thanks for your help.

Verena

 

-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20090901/09ef3ae2/attachment-0002.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 33705 bytes
Desc: image001.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20090901/09ef3ae2/attachment-0004.jpeg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 59977 bytes
Desc: image002.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20090901/09ef3ae2/attachment-0005.jpeg>


More information about the Equest-users mailing list