[Equest-users] BEPU space heating calculation
Carol Gardner
cmg750 at gmail.com
Thu Aug 26 09:22:37 PDT 2010
I agree it's good to know the calcs behind the eQUEST inputs but since it is
an hourly energy model drawing on 8760 hours of weather data and dealing
with all the interactions between systems you will never be able to had calc
a result that will be anywhere near the eQ output. So, I still say either do
a hand calc or forget about it and use eQUEST, check your inputs, output
reports, etc., and if you don't find any glaring errors, call it good.
Carol
On Thu, Aug 26, 2010 at 7:12 AM, Grammy <grammy.hkust at gmail.com> wrote:
> Yes, sometimes there will be one guy, who takes the calcs to ask you prove
> your model result, like a challenge. It's not a happy thing and you must
> know a lot of details in your model and the energy distribution in annual
> energy consumption, to answer such questions.
>
> At the beginning I am angry with these kind of actions, but soon
> I realize that these actions can push me to become a better energy modeler.
> When you can answer these questions, and point out the mistake in their hand
> calcs, you prove yourself and grow up to a better modeler~
>
>
> On Thu, Aug 26, 2010 at 9:00 PM, Chris Jones <cj at enersave.ca> wrote:
>
>> Re equest and hand calcs. I know a few people that actually use hand
>> calcs to demonstrate where equest, ecotect and other simulation programs are
>> coming up with incorrect answers. Graham, care to illustrate?
>>
>>
>>
>> At 08:38 AM 26/08/2010, Carol Gardner wrote:
>>
>> Let me take a crack at this. What John is saying is that eQUEST takes into
>> consideration all building components and their interactions. You can't just
>> pull out one and ask hey why doesn't this match my hand calc? In fact, if
>> you want eQUEST to match a hand calc, you shouldn't be using it: use the
>> hand calc.
>>
>> Carol
>>
>> On Wed, Aug 25, 2010 at 2:04 PM, Paul Riemer < Paul.Riemer at dunhameng.com>
>> wrote:
>>
>> John,
>>
>> Internal gains figure into Ben 's approach by choosing a HDD number based
>> on a balance point temperature that is below the actual space set point.
>>
>> The balance point temperature is a theoretical temperature at which the
>> building does not require heating because the internal gains offset the
>> envelope loads.
>>
>> To say it accounts for solar gain is a stretch but hey it is just a hand
>> calc.
>>
>> Ben does not state which HDD base he chose, but there are published values
>> for temps like 55F, 60F, 65F etc.
>>
>>
>>
>> Ben,
>>
>> It is good you are checking your results but I would ask do you believe
>> your baseline model? Try your HDD calc on the your building U rather than
>> the differential. How does that gas consumption compare to your baseline
>> model heating gas consumption?
>>
>> Does a different HDD base fit your model better?
>>
>>
>>
>> If you think your baseline model is okay, when you changed the U did you
>> also change your shading coefficient? A lower SC would eliminate some
>> passive solar heating.
>>
>> A daylighting interaction could be another possibility.
>>
>>
>>
>> You'll figure it out.
>>
>> Paul Riemer
>>
>> Dunham
>>
>>
>>
>>
>>
>>
>>
>> From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org<equest-users-bounces at lists.onebuilding.org>]
>> On Behalf Of John Aulbach
>> Sent: Wednesday, August 25, 2010 3:38 PM
>> To: Ben Pressman; equest-users at lists.onebuilding.org
>> Subject: Re: [Equest-users] BEPU space heating calculation
>>
>>
>>
>> Ben - dumb question.
>>
>>
>>
>> How is internal load figuring into this equation? And solar gain from the
>> sun?
>>
>>
>>
>> I NEVER get an exact U x A x dT savings, as eQuest takes ALL factors into
>> consideration.
>>
>>
>>
>> John R. Aulbach, PE, CEM
>>
>> Senior Energy Engineer
>>
>> Partner Energy
>>
>> 1990 E. Grand Avenue, El Segundo, CA 90245
>> W: 888-826-1216, X254| D: 310-765-7295 | F: 310-817-2745
>>
>> www.ptrenergy.com | jaulbach at ptrenergy.com <%7C%20jaulbach at ptrenergy.com>
>>
>>
>>
>>
>>
>> From: Ben Pressman < bpressman at practicalenergy.net>
>> To: equest-users at lists.onebuilding.org
>> Sent: Wed, August 25, 2010 1:32:04 PM
>> Subject: [Equest-users] BEPU space heating calculation
>>
>> I have a Window Glass EEM run that upgrades the windows in a 1970s school
>> building from single-paned to double-paned, tinted, and argon-filled; a
>> decrease in U-factor from 1.04 to 0.35. The LV-D report shows a decrease in
>> building U-factor from 0.176 to 0.142 which, based on an HDD calculation:
>>
>> (0.176-0.142)*24hrs*(estimated HDD for my area)*A/eff = 1217 therms
>>
>> of savings, or 24.7% of the overall energy usage of my baseline model. The
>> BEPU report, however, shows almost no energy savings. How can this be? Is
>> there some way to see what schedule, or number of degree days the
>> calculation in the BEPU is using? Has anyone had this sort of problem?
>>
>> Thanks,
>> Ben
>>
>> -- Ben Pressman
>> Project Engineer
>> Practical Energy Solutions
>> 770 E. Market Street, Suite 250
>> West Chester, PA 19382
>> ph 610.430.1382
>> cell 610.733.9518
>> web www.practicalenergy.net
>>
>>
>> _______________________________________________
>> Equest-users mailing list
>> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
>> To unsubscribe from this mailing list send a blank message to
>> EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
>>
>>
>>
>> _______________________________________________
>> Equest-users mailing list
>> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
>> To unsubscribe from this mailing list send a blank message to
>> EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
>>
>>
>>
>>
>> --
>> Carol Gardner PE
>> _______________________________________________
>> Equest-users mailing list
>> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
>> To unsubscribe from this mailing list send a blank message to
>> EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
>>
>>
>> Chris Jones
>> 14 Oneida Avenue
>> Toronto, ON M5J 2E3.
>> Tel. 416-203-7465
>> Fax. 416-946-1005
>>
>>
>> _______________________________________________
>> Equest-users mailing list
>> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
>> To unsubscribe from this mailing list send a blank message to
>> EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
>>
>>
>
--
Carol Gardner PE
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20100826/41b99bec/attachment-0014.htm>
More information about the Equest-users
mailing list