[Equest-users] LEED results way out of bounds
Sami, Vikram
Vikram.Sami at perkinswill.com
Thu Jul 12 11:07:03 PDT 2012
Andy,
Here's my 2 cents:
1. - You might want to specify some outdoor air - for ventilation. If it's a new building - use ASHRAE 62 levels at a minimum - if the design team is not supplying this - encourage them very strongly to do so.
2. Hours out of bounds could be for a number of reasons. The most common three are:
a. Cycling of fans - make sure your fans are allowed to cycle off hour (specified under night cycle control).
b. Fans aren't scheduled when cooling/heating is scheduled
c. System capacity is inadequate.
What type of system are you using?
Vikram Sami, LEED AP BD+C
Sustainable Design Analyst
1315 Peachtree St. NE, Atlanta, GA 30309
t: 404-443-7462 f: 404.892.5823 e: vikram.sami at perkinswill.com www.perkinswill.com<http://www.perkinswill.com/>
Perkins+Will. Ideas + buildings that honor the broader goals of society
From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Andy Higgins
Sent: Wednesday, July 11, 2012 5:26 PM
To: equest-users at lists.onebuilding.org
Cc: Maggie Straebel; Shapour Arami
Subject: [Equest-users] LEED results way out of bounds
All:
What might be the cause for the following?:
1. Warning "System has no outdoor air for calculation"
2. Exported LEED results show between 1187 and 5277 hours (depending on the orientation and whether the run is baseline or proposed) of loads not met.
A little help, please?
Andrew C. Higgins, P.E.
Senior Mechanical Engineer
ProLink Engineering, LLC
600 Enterprise Dr. Suite 220
Oak Brook, IL. 60523
P:(630) 573-8020
F:(630) 573-8021
andy at hinkle-engineering.com<mailto:andy at hinkle-engineering.com>
www.hinkle-engineering.com<http://www.hinkle-engineering.com>