[TRNSYS-users] Problem of Type 917 and water temperature simulation

David BRADLEY d.bradley at tess-inc.com
Fri Jul 12 08:40:04 PDT 2013


Jing,

> I am modeling a building using water to air heat pump. I am using type 
> 917 and I have several questions:
> 1. When I use buried horizontal pipes and ground Vertical U-tube in 
> GHP library, how could I simulate the ground variables? Like the local 
> water flow temperature, soil temperature. etc. TMY2 doesn't provide 
> with such data.
the soil properties usually come from having done a test bore (unless of 
course the project is theoretical in which case you will have to use 
ground properties that you find in reference materials. You can get 
estimates of the average ground temperature, the amplitude of the 
ambient temperature swing, and the day of the minimum ambient 
temperature by plotting results from the TMY file. The ground water flow 
is very difficult to estimate. I suppose that what I would recommend is 
to run your simulation with a few different values of ground water flow 
rate to see how much the simulation results are impacted by your 
assumption.
> 2. Could buried horizontal pipes and vertical U tube be used together? 
> Just simply connect their inlet and outlet flow rates will be correct?
there should be no problem doing this.
> 3.If I connect vertical U tube with horizontal pipes, should I have 
> different size horizontal piples to cater the flowrate accumulation of 
> the U tube in series? For example, the horizontal pipe with one U-tube 
> is 1/4 and the pipe with two U-tube will be 1/2 . But if I put some 
> many type 952, I guess my model will be messed up. Is there any 
> solution for that?
I am not entirely sure that I understand your concern. The models are 
only looking at the thermal aspect of the problem. The tube diameters 
are used in calculating the pipe surface area, not for any pressure loss 
calculations. I also don't know what configuration you are looking at 
but you may be able to use a single instance of Type997 instead of many 
instances of Type952.
> 4. What's the major difference between type 917 and 919  ?
Type917 models an air-to-water heat pump where the air is the source 
side. Type919 models a water-to-air heat pump where water is on the 
source side.

Kind regards,
  David

-- 
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI  53703 USA

P:+1.608.274.2577
F:+1.608.278.1475
d.bradley at tess-inc.com

http://www.tess-inc.com
http://www.trnsys.com




More information about the TRNSYS-users mailing list