Bill,
Lighting can be all over for existing buildings since so
many improvements have been made in the last ten years.
One point of reference is the latest draft of ASHRAE
Standard 90.1 that allows 1.6 W/sqft overall for the entire
hospital building and specific spaces being 1.0 W/sqft in
the nursery, 1.2 in the patient rooms, 2.8 in the emergency
room and 7.6 in the operating room. Altogether they have
over twenty different spaces identified for a hospital.
These are supposed to represent efficient lighting options
that are cost effective - I believe it is appropriate to
consider them less than the state of the art.
Jason
On 10 Mar 99, at 18:43, BKoran at aol.com wrote:
> I'm looking for some rules-of thumb for energy use by end-use for hospitals.
> I'm particularly interested in the electricity use for lighting at the present
> time. Percentages of the total electricity use would be fine.
>
> I'm seeking this information just to use for reasonableness checks. I have a
> copy of a completed lighting audit that has numbers I don't think are
> reasonable. The hospital whose use I'm investigating is located in San
> Francisco.
>
> I would be interested in a good source for this type of information as well as
> the information itself.
>
> Thanks, Bill
>
>
> ======================================================
> You received this e-mail because you are subscribed
> to the BLDG-SIM at GARD.COM mailing list. To unsubscribe
> from this mailing list send a blank message to
> BLDG-SIM-UNSUBSCRIBE at GARD.COM
>
=========================================================
Jason Glazer, P.E. mailto:jglazer at gard.com 847 698 5686
GARD Analytics - http://www.gard.com/
Building Energy Simulation and Analysis
List Administrator & 90.1 Consultant
======================================================
You received this e-mail because you are subscribed
to the BLDG-SIM at GARD.COM mailing list. To unsubscribe
from this mailing list send a blank message to
BLDG-SIM-UNSUBSCRIBE at GARD.COM
More information about the Bldg-sim
mailing list