[BLDG-SIM] Major disagreement on Chiller Performance Curves in DOE-2.1E and DOE-2.2
Mike Roberts
mroberts20 at kc.rr.com
Wed Oct 15 12:38:43 PDT 2003
Major disagreement on Chiller Performance Curves in DOE-2.1E and DOE-2.2The
easy way to settle that is to create a spreadsheet that uses the
coefficients. You can get them from the .bdl file if you enter DIAGNOSTIC
COMMENTS .. right before your chiller instructions. Interestingly enough,
that's what I was doing this morning. I have attached my spreadsheet.
Please excuse that it is not ready for distribution. Just something I was
playing with.
The coefficients are for DOE-2.2 and do include upgrades since the mid '70s
that DOE-2.1E uses. The VFD coefficients are new.
As you can see, kW/ton does change with temperatures.
If you want FIXED condenser water temperature and chilled water temperature
(the default), do not turn on the resets. Condenser water (and maybe
chilled water) will still drift with what the equipment can do.
Mike
-----Original Message-----
From: postman at gard.com [mailto:postman at gard.com]On Behalf Of Aulbach, John
Sent: Wednesday, October 15, 2003 1:23 PM
To: BLDG-SIM at gard.com
Subject: [BLDG-SIM] Major disagreement on Chiller Performance Curves in
DOE-2.1E and DOE-2.2
I am having a "friendly" disagreement with a colleague on what chiller
curves to ask for from a manufacturer to input into DOE-2 (could be either
2.1E or 2.2). We both agree that the infamous ARI point for a 100% load
should be input. But the curves are where we disagree.
Is the Default DOE-2 curve for % Power versus % Tons the ARI curve with
the allowable reduction in condenser water temperature, or is it based on
the FIXED 85°F entering condenser water and FIXED 44°F leaving chilled water
ALL the way down the curve?
Therefore, when I am given a chiller with a variable speed drive
installed, what parameters should I ask for in such a Power/Tons to be FIXED
???
John R. Aulbach, PE, CEM
Project Engineer
Sempra Energy Solutions
555 West Fifth Street
Mail Location 27F3
Los Angeles, CA 90013
Tel: (213) 244-8551 Cell (213) 219-4875
"Sempra Energy Solutions is not the same company as SDG&E/ SoCalGas, the
Utilities. Sempra Energy Solutions is not regulated by the California
Public Utilities Commission, and you do not have to buy Sempra Energy
Solutions products or services to continue to receive quality regulated
service from the Utilities."
==================
You received this e-mail because you are subscribed
to the BLDG-SIM at GARD.COM mailing list. To unsubscribe
from this mailing list send a blank message to
BLDG-SIM-UNSUBSCRIBE at GARD.COM
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20031015/fd982f12/attachment-0002.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: DOE Chiller Coefficients.xls
Type: application/vnd.ms-excel
Size: 20992 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20031015/fd982f12/attachment-0002.xls>
More information about the Bldg-sim
mailing list