[BLDG-SIM] eQUEST/economizer
Pat Bailey
pbailey at geopraxis.com
Wed Apr 28 14:21:21 PDT 2004
David,
We've run into this as well. One issue that is relatively common with
simulated VAV systems is that the economizer operation and the VAV box
operation can be completely independent of each other, even if you don't
want them to be. This may or might not be an issue in an actual system
depending on how the controls are configured. Even if the design flow of
outside air is sufficient to cool a zone, the reduced flow at some level of
VAV turndown may not be sufficient. For this reason, there are hours of the
year (typically cooler periods) when a constant volume unit may show less
simulated cooling energy.
One solution to this is to schedule increased levels of outside air during
cooler months, perhaps in the morning. The solution depends on when the
cooling load is not being met by outside air alone.
You can also set the priorities of air flow and temperature reset. Varying
these will impact the trade off between fan energy and cooling energy.
Good luck.
_______________________
Pat Bailey, P.E.
Principal
GeoPraxis, Inc
205 Keller Street
Petaluma, CA 94952
www.geopraxis.com
707.766.7010 (v)
707.766.7014 (f)
-----Original Message-----
From: postman at gard.com [mailto:]On Behalf Of David Lanceta
Sent: Wednesday, April 28, 2004 11:35 AM
To: BLDG-SIM at GARD.COM
Subject: [BLDG-SIM] eQUEST/economizer
Hi everybody!
First of all, I would like to say thank you to everybody that have helped
me in the past, I used to send emails to everyone but I´m sure I´ve
forgotten some of them.
I´m simulating an office building with eQUEST, and I´m trying to know how
much energy can be saved up.
The HVAC system type is "Standard VAV with HW Reheat" for all the zones,
the cold deck reset is 55ºF. I´ve also set up a drybulb temperature
economizer, high limit 65ºF.
I think that when the drybulb exterior temperature is below 55ºF there
should be free-cooling, but checking the temperature values this only
happens when it´s under 49ºF
does anybody know why it could be?
thanks
=================================
David Lanceta
Área de Mecánica de Fluidos
Centro Politécnico Superior
Universidad de Zaragoza
María de Luna 3, tel (0034)9761000 ext 5044
50015 ZARAGOZA
ESPAÑA
==================
You received this e-mail because you are subscribed
to the BLDG-SIM at GARD.COM mailing list. To unsubscribe
from this mailing list send a blank message to
BLDG-SIM-UNSUBSCRIBE at GARD.COM
======================================================
You received this e-mail because you are subscribed
to the BLDG-SIM at GARD.COM mailing list. To unsubscribe
from this mailing list send a blank message to
BLDG-SIM-UNSUBSCRIBE at GARD.COM
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20040428/e63c4247/attachment-0002.htm>
More information about the Bldg-sim
mailing list