[bldg-sim] Radiant Heating/Cooling
Harvey Bryan
Harvey.Bryan at asu.edu
Wed Apr 14 11:08:52 PDT 2004
-----Original Message-----
From: Harvey Bryan
Sent: Tuesday, April 13, 2004 11:18 AM
To: 'stvgates at pacbell.net'
Subject: RE: [bldg-sim] Radiant Heating/Cooling
It seems that radiant systems are attracting a lot good discussion; I
just wanted to let you all know that ASU recently completed testing a
Radiant Cooled house for an ASHRAE project. A description of that house,
data gathered as well as a good presentation (with several animations)
on radiant systems is available at http://support.caed.asu.edu/radiant
We are now working on a K-6 School using a similar cooling system.
Harvey Bryan, Ph.D.
School of Architecture
Arizona State University
Tempe, AZ 85287-1605
Tel: 480-965-6094
Fax: 480-965-0968
Email: harvey.bryan at asu.edu
-----Original Message-----
From: postman at gard.com [mailto:postman at gard.com] On Behalf Of
stvgates at pacbell.net
Sent: Tuesday, April 13, 2004 8:49 AM
To: bldg-sim at gard.com
Subject: [bldg-sim] Radiant Heating/Cooling
I also have some questions on radiant heating that I hope someone can
answer:
1. It is well understood that, for a given comfort level, a higher mean
radiant temperature allows for a lower ambient temperature. This
suggests
that one can lower the thermostat setpoint. But, if the thermostat is
lowered to 65F, and the ambient temperature is 66F, then the radiant
heat is
off, and the mean radiant temperature drops. So are the people
comfortable
when the space is 66F, or do they raise the thermostat?
2. Granted, infiltration heat losses can be lowered by reducing the air
temperature. But the radiant heat source is also warming the room
surfaces,
including the exterior wall surfaces and window surfaces. If those
surface
temperatures are then higher than they would be with a convective
heating
system, their conduction losses are now greater, even though the air
temperature is lower. Also, infiltration/exfiltration losses are
typically
through cracks. If the cracks in the interior surfaces are warmer from
radiant heating, then the crack warms the exfiltrating air, and space
temperature is not a valid criterion for calculating exfiltration loss.
So
does a radiant heating system REALLY save any energy?
3. If the radiant elements are imbedded in the ceiling, which is
common,
the interior ceiling temperature can now be in excess of 90F, which
increases the conduction losses to the attic. So if this loss is
counted as
a delivery loss, the efficiency of the system drops compared to the
theoretical. The same argument applies to radiant elements in floors.
So
is a radiant system REALLY any more efficient than a convective system
in
terms of delivered energy?
4. With a setback thermostat and a convective heating system, I can
turn
off the heat at night, but my home will be comfortable in less than a
1/2
hour the next morning. But most radiant heating systems have a slow
response time. Do people turn them off/down at night, or do they run
them
continuously?
----- Original Message -----
From: "Jon Maxwell" <jmaxwell at aspensys.com>
To: <bldg-sim at gard.com>
Sent: Monday, April 12, 2004 8:46 PM
Subject: [bldg-sim] Radiant Heating/Cooling
> I have modeled the savings for radiant systems for unvented low
intensity
> gas fired radiant tube heating systems in high bay warehouses and
> manufacturing facilities in particular by:
>
> 1. Reducing the setpoint dry bulb temperature a few degrees
because
> human comfort with radiant heating is reached at a lower ambient than
with
> convection heating systems. I am certain that comfort research
supports
> this.
> 2. Reducing the setpoint temperature a few more degrees because
there
is
> less floor-to-ceiling temperature stratification. With the desired
> temperature at belly button level, radiant systems will have a lower
average
> temperature floor-to-ceiling than unit heaters overall.
> 3. Reducing the amount of infiltration, due to reduced stack
effect,
due
> to reduced temperature stratification
> 4. Increasing the heating system combustion efficiency slightly
due to
> having no intermediate media such as air or water between the
combustion
air
> and the space to be heated and lack of venting.
>
> While I cannot cite studies to validate the adjustments or quantify
them
> generally (though I have rules of thumb based on ceiling height), such
an
> approach has predicted savings roughly in the right ballpark, close
enough
> to make a do/don't do decision at least.
>
> Would love to be able to cite rigorous research that proves or
disproves
my
> approach.
>
> Jonathan B. Maxwell, PE
> Senior Engineer
> Aspen Systems Corporation
> 710 Park Place
> College Station, TX 77840
> (979) 764-6779 wk
> (979) 764-7810 fax
> (979) 575-1281 mobile
> jmaxwell at aspensys.com
> www.OPUSPOWER.com
> www.aspensys.com
>
> ----- Original Message -----
> From: "Chris Jones" <cj at cr-jay.ca>
> To: <BLDG-SIM at gard.com>
> Sent: Monday, April 12, 2004 6:25 AM
> Subject: [BLDG-SIM] Radiant Heating/Cooling
>
>
> In your research with radiant heating cooling savings, have you found
any
> energy "savings" that can be attributed directly to the use of the
radiant
> system vs other systems (air supply in particular). For example, I
have
> seen some papers that note that the heating setpoint can be relaxed
while
> still maintaining thermal comfort with a radiant system.
>
>
> At 10:47 07/04/2004, you wrote:
> >Dear All,
> >
> >For those interested in the simulation of radiant heating/cooling
systems,
> >IRC has developed a semi-analytical model for integration in energy
> >simulation software that use the one-dimensional numerical modeling
to
> >calculate the heat transfer within the building construction
assemblies.
> >
> >The model combines the one-dimensional model of the energy simulation
> >software with a two-dimensional analytical model. The advantage of
this
> >model over the one-dimensional one is that it accurately predict the
> contact
> >surface temperature of the circuit-tubing and the adjacent medium,
required
> >to compute the boiler/chiller power, and the minimum and maximum
> >ceiling/floor temperatures, required for local moisture condensation
> >(ceiling cooling systems), thermal discomfort (heating floor systems)
and
> >controls. The model predictions for slab-on-grade heating systems
compared
> >very well with the results from a full two-dimensional numerical
model.
> >
> >The model was implemented in the Canadian software HOT3000 and the UK
> >software ESP-r as a plant component. The implementation of this model
in
> the
> >ESP-r program offers additional flexibilities to the radiant system
> designer
> >community, mainly:
> >* Designers can use any control algorithm possible in ESP-r
with
the
> >new plant component (e.g.., use the flux or temperature control, and
> compare
> >their performance).
> >* Designers can specify any number of radiant surfaces of the
> building
> >fed by the same or different heat source.
> >* Designers can size realistic radiant systems, and get
realistic
> >energy consumption (from the source side) and cost.
> >
> >
> >A copy may be downloaded from:
> >Laouadi, A. "Development of a radiant heating and cooling model for
> building
> >energy simulation software," Building and Environment, 39, (4),
April,
pp.
> >421-431, Apr, 2004
> >(NRCC-46099)
> ><http://irc.nrc-cnrc.gc.ca/fulltext/nrcc46099/>
> >
> >
> >Thanks
> >
> >Dr. Abdelaziz (Aziz) Laouadi
> >Research Officer
> >Indoor Environment Research Program
> >Institute for Research in Construction
> >National Research Council of Canada
> >1200 Montreal Road, Building M-24
> >Ottawa, Ontario, Canada, K1A 0R6
> >Tel.: (613) 990 6868; Fax: (613) 954 3733
> >Email: Aziz.Laouadi at nrc-cnrc.gc.ca
> >Web: http://irc.nrc-cnrc.gc.ca/ie/light/skyvision/
> >
> >
> >You received this e-mail because you are subscribed
> >to the BLDG-SIM at GARD.COM mailing list. To unsubscribe
> >from this mailing list send a blank message to
> >BLDG-SIM-UNSUBSCRIBE at GARD.COM
>
>
> Chris Jones, P.Eng.
> 14 Oneida Avenue
> Toronto, ON M5J2E3
> Tel. 416 203-7465
> Fax. 416 946-1005
>
> =====================================================You received this
> e-mail because you are subscribed
> to the BLDG-SIM at GARD.COM mailing list. To unsubscribe
> from this mailing list send a blank message to
> BLDG-SIM-UNSUBSCRIBE at GARD.COM
>
>
> ======================================================
> You received this e-mail because you are subscribed
> to the BLDG-SIM at GARD.COM mailing list. To unsubscribe
> from this mailing list send a blank message to
> BLDG-SIM-UNSUBSCRIBE at GARD.COM
>
======================================================
You received this e-mail because you are subscribed
to the BLDG-SIM at GARD.COM mailing list. To unsubscribe
from this mailing list send a blank message to
BLDG-SIM-UNSUBSCRIBE at GARD.COM
===========================
You received this e-mail because you are subscribed
to the BLDG-SIM at GARD.COM mailing list. To unsubscribe
from this mailing list send a blank message to
BLDG-SIM-UNSUBSCRIBE at GARD.COM
More information about the Bldg-sim
mailing list