[BLDG-SIM] eQUEST/free-cooling
    Stirling Walkes 
    Swalkes at smseng.com
       
    Tue Feb 10 07:04:52 PST 2004
    
    
  
David,
In eQuest, assign a schedule for the chilled water loop operation such that it is not available during the winter.  That may clear up the problem.  The chilled water loop may be providing a fixed quantity of chilled water demand just because it is on.
Regards,
V. Stirling Walkes, P.Eng., LEED AP
SMS Engineering Ltd.
770 Bradford Street 
Winnipeg MB R3H 0N3 Canada
phone: 204.775.0291
fax: 204.772.2153
Swalkes at smseng.com
>>> "David Lanceta" <dlanceta at mafalda.cps.unizar.es> 02/10/04 07:52AM >>>
Hi everybody
I m trying to simulate a kind of Mall with eQUEST. I have 4 perimeter zones and a core. The HVAC system chosen is standard VAV reheat with baseboards in the perimeter zones (I m not very sure if it s suitable for the kind of building). I ve also set up an economizer. 
My question is this: I don t understand why in the output file I have a fixed quantity of chilled water demand in winter, when it s sure that the outdoor temperature is good enough to satisfy the core refrigeration load.
Can anybody explain me this?
thanks
=================================
David Lanceta 
Área de Mecánica de Fluidos
Centro Politécnico Superior
Universidad de Zaragoza
María de Luna 3, tel (0034)9761000 ext 5044
50015 ZARAGOZA
ESPAÑA
=====================================================You received this e-mail because you are subscribed
to the BLDG-SIM at GARD.COM mailing list.  To unsubscribe
from this mailing list send a blank message to
BLDG-SIM-UNSUBSCRIBE at GARD.COM
===========================
You received this e-mail because you are subscribed 
to the BLDG-SIM at GARD.COM mailing list.  To unsubscribe 
from this mailing list send a blank message to 
BLDG-SIM-UNSUBSCRIBE at GARD.COM
    
    
More information about the Bldg-sim
mailing list