[BLDG-SIM] Closed circuit cooling tower in DOE2.1E
Konstantin Babets
babetsk at jbb.com
Wed Mar 24 06:13:04 PST 2004
Thanks to everybody for helping with my river water cooling problem. I found that using hourly output and programming excell spreadsheet was the way to go.
Here is another problem. How can I approach modeling a closed circuit cooling tower in DOE2.1E?
Konstantin Babets
Jaros Baum and Bolles
Consulting Engineers
212 530 9455
----- Original Message -----
From: mbusman at noresco.com
To: babetsk at jbb.com ; BLDG-SIM at gard.com
Sent: Thursday, March 18, 2004 12:20 PM
Subject: RE: [BLDG-SIM] River water cooling
Konstantin,
I have become a big fan of the hourly output report capabilities of DOE-2 for presentation purposes, troubleshooting, and to handle situations such as yours where I'm not aware of how to approach the solution within DOE-2.
You could probably run an hourly report to export systems tons load, CHW supply temperature, and any other variables you might need (CHW pump kW, condenser pump kW, lighting kW, etc.) and dump the 8760 hours of data into an Excel file. Based on your CHW pump kW, you might want to add a column to account for pump heat to give you total cooling load seen by the chiller.
Then you need to add 3 columns to calculate from the DOE chiller curve coefficients the multiplier for capacity based on CHW and CW temp. (I assume you have a good idea of the variation in river water temp. by season), multiplier for EIR based on the water temperatures, and EIR-FPLR. The product of these three values should give you the hourly EIR. Add another column so that based on the total tons cooling load, you can then calculate chiller kW from the hourly EIR.
It might end up being a big spreadsheet, but it's really simple in concept to set up and should give you the results you desire. If you'd like to discuss further, feel free to call me.
Mike Busman
NORESCO, LLC
949-253-3533, ext. 303
-----Original Message-----
From: Konstantin Babets [mailto:babetsk at jbb.com]
Sent: Thursday, March 18, 2004 7:52 AM
To: BLDG-SIM at gard.com
Subject: [BLDG-SIM] River water cooling
Alec, thank you.
Unfortunately I am using Doe2.1E, where I cannot schedule loop temperatures. BTW, is it possible to write a custom function to access the PLANT? It does look like I can only use custom functions to modify computations in Loads and Systems.
Any ideas?
Konstantin Babets
Jaros Baum and Bolles
Consulting Engineers
212 530 9455
----- Original Message -----
From: Alec Stevens
To: babetsk at jbb.com
Sent: Wednesday, March 17, 2004 6:02 PM
Subject: Re: [BLDG-SIM] River water cooling
Konstantin,
Not 100% sure, but I think you should be able to schedule the loop temperature. Create day/week/year schedules and input the appropriate variation in river water temp, use that for loop temp.
I know you can do this for ground source loop temperature for a WLHP system, so it should be applicable to CW loop.
just for fun:
http://www.utilities.cornell.edu/LSC/default.htm
good luck
Alec
----- Original Message -----
From: Konstantin Babets
To: BLDG-SIM at gard.com
Sent: Wednesday, March 17, 2004 4:53 PM
Subject: [BLDG-SIM] River water cooling
Hello,
I am working on a project that considers utilizing river water instead of a conventional cooling tower condenser water. Does anyone have an idea how could this be simulated in DOE2.1? (Basically, somehow I need to reset entering condenser water temperature to that of a river water).
Thank you,
Konstantin Babets
Jaros Baum and Bolles
Consulting Engineers
212 530 9455
==================
You received this e-mail because you are subscribed
to the BLDG-SIM at GARD.COM mailing list. To unsubscribe
from this mailing list send a blank message to
BLDG-SIM-UNSUBSCRIBE at GARD.COM
=====================================================You received this e-mail because you are subscribed
to the BLDG-SIM at GARD.COM mailing list. To unsubscribe
from this mailing list send a blank message to
BLDG-SIM-UNSUBSCRIBE at GARD.COM
===========================
You received this e-mail because you are subscribed
to the BLDG-SIM at GARD.COM mailing list. To unsubscribe
from this mailing list send a blank message to
BLDG-SIM-UNSUBSCRIBE at GARD.COM
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20040324/628cffb4/attachment.htm>
More information about the Bldg-sim
mailing list