[bldg-sim] OA loads
Chris Jones
cj at cr-jay.ca
Mon Mar 15 14:40:05 PST 2004
You won't find a report that tells you the actual OA heating and cooling
loads - sensible and latent. You need to calculate that yourself based on
the outdoor air ratio at the peak heating/cooling times.
You can use hourly reports to help with this task.
>Hi:
>Outside ventilation air loads are excluded from the LS-C report in DOE 2.
>Is it reported in any other report - as it is usually a major % of the
>total loads. Is it in any of the system reports? Latent / sensible
>separated, etc
?
>How does one read it in DOE 2?
>Thank you.
>~m
>
>
>
>
>
>