[BLDG-SIM] Heat recovery not functioning in EE4
Calla, Robert
RCalla at NRCan.gc.ca
Tue Jul 5 08:48:43 PDT 2005
Alex,
Further to Stephen's response, the usual cause of the error is that no
return fan is specified - EE4 and hence DOE-2 assumes that heat recovery is
on the return air for non-distributed systems. For distributed systems, heat
recovery is taken into account by adjusting the amount of outdoor air.
Regards,
-------------------------------------------------
Robert Calla, B.Eng, PMP
Project Leader / EE4 Project Manager
Sustainable Buildings & Communities
CANMET Energy Technology Centre - Ottawa
Natural Resources Canada
580 Booth Street, 13th Floor, Ottawa, ON K1A 0E4
Tel: 613-947-6601 Fax: 613-996-9909
email: rcalla at nrcan.gc.ca <mailto:rcalla at nrcan.gc.ca>
website: www.sbc-bcd.nrcan.gc.ca <http://www.sbc-bcd.nrcan.gc.ca/>
Government of Canada
Chef de projets / Gestionnaire logiciel EE4
Groupe des bâtiments et des collectivités durables
Centre de la technologie de l'énergie de CANMET - Ottawa
Ressources naturelles Canada
580 rue Booth, 13e étage, Ottawa (Ontario) K1A 0E4
Tel: 613-947-6601 Fax: 613-996-9909
courriel: rcalla at nrcan.gc.ca <mailto:rcalla at nrcan.gc.ca>
site web: www.sbc-bcd.nrcan.gc.ca <http://www.sbc-bcd.nrcan.gc.ca/>
Gouvernement du Canada
<http://www.sbc-bcd.nrcan.gc.ca>
-----Original Message-----
From: Pope, Stephen
Sent: July 4, 2005 9:58 AM
To: 'alex555 at fastmail.fm'
Cc: Tardif, Michel; Lubun, Mike; Girgis, Elisabeth; Newman, Mark
Subject: RE: [BLDG-SIM] Heat recovery not functioning in EE4
Hi Alex
There are a number of things that could go wrong with heat recovery, all
having roots in DOE-2.1e. If you are using a central air-side system that
relies on reheat to keep zones at temperature (affecting 6 of the 15 systems
in EE4), the zone reheat (especially baseboards) will serve the load before
there is a call for heat recovery. Zonal systems escape this problem.
On way around the hang-up is to add the zone heat capacity to the central
system and zero out the zone capacity, but that will produce underheated
hours when the fans are off. For CBIP purposes it may be worth submitting a
file that shows the impact of heat recovery, plus the working file that
shows all loads are satisfied, and a spreadsheet that reconciles the two to
give the proper design performance.
Happy 4th of July.
Regards,
SFP
Stephen Pope, OAA, MRAIC
for
Natural Resources Canada / CANMET Energy Technology Centre
Sustainable Buildings & Communities / Commercial Buildings Section
580 Booth St., 13th Flr, D5, Ottawa ON K1A 0E4
tel. (613) 947-9823 cel. (613) 324-1642, fax (613) 996-9909
email spope at nrcan.gc.ca, web http://buildingsgroup.nrcan.gc.ca
-----Original Message-----
From: postman at gard.com [mailto:postman at gard.com]On Behalf Of
alex555 at fastmail.fm
Sent: Friday, July 01, 2005 4:57 PM
To: BLDG-SIM at gard.com
Subject: [BLDG-SIM] Heat recovery not functioning in EE4
has anyone had a problem with heat recovery in EE4? If i add heat
recovery to my sytems there is NO impact on energy consumption! i think
EE4 is only used by folks in canada for CBIP so unfortunately that
probably narrows down who can help me.
thanks
alex
On Fri, 1 Jul 2005 14:35:47 -0600, "Mike Tillou" <miket at etcgrp.com>
said:
> I do what Vikram does.
>
> Another choice for advanced users is to make the changes directly in the
> BDLlib.dat file that eQuest uses. Unfortunetly this file sometimes
> changes with updates so all your work to create a custom library would
> have to be re-created with each new update.
>
> Mike
>
> Michael Tillou, PE
> etc Group, Inc.
> PO Box 7, Williamstown, MA 01267
> ph. (413) 458-9870 fx. (413) 458-9875
>
> -----Original Message-----
> From: postman at gard.com [mailto:postman at gard.com] On Behalf Of Vikram
> Sami
> Sent: Friday, July 01, 2005 3:00 PM
> To: BLDG-SIM at gard.com
> Subject: [BLDG-SIM] Saving components to the user library in Equest
>
>
> Personally, I save the comonents as text files out of the inp file. You
> can then paste them into your inp file whenver you need them in a new
> project.
>
> Vikram Sami, LEED AP
> Direct Phone 404-253-1466 | Direct Fax 404-253-1366
>
> LORD, AECK & SARGENT ARCHITECTURE
> Responsive Design * Technological Expertise * Exceptional Service
> www.lordaecksargent.com
>
> -----Original Message-----
> From: postman at gard.com [mailto:postman at gard.com]On Behalf Of Scott
> Criswell
> Sent: Friday, July 01, 2005 12:37 PM
> To: BLDG-SIM at gard.com
> Cc: BLDG-SIM at gard.com
> Subject: [BLDG-SIM] Saving components to the user library in Equest
>
>
> I apologize for the confusion - the documentation instructing users
> about saving components to a user library was supposed to be stricken
> from the eQUEST online help system. eQUEST does not currently support
> the saving of building components to user libraries.
>
>
> Dustin Schafer wrote:
>
>
> Good morning,
> I'm having an issue with trying to save a component to the user library
> in Equest. The help files make it sound pretty straight forward,
>
> "After you have created or edited a building component, the Edit, Save
> Component to Library command allows you to save it to your User Library.
> The default User Library is USRLIB.DAT."
>
> The problem that I'm running into is that the "save component to
> library" command is not a selectable option on my edit menu. When I
> right click on a component to bring up the edit menu, the library
> command is "grayed out". Is there some sort of set up that needs to be
> done so that I am able to save the user library?
>
> Thanks,
> Dustin
>
> Dustin Schafer, PE + LEED(tm) Accredited Professional
>
> ELEMENTS | a division of berkebile nelson immenschuh mcdowell architects
> 106 W. 14th Street Suite 200
> Kansas City, Missouri 64105
>
> p 816.783.1683 f 816.783.1501
> elements.bnim.com | <http://www.bnim.com> www.bnim.com
>
> ======================================================
>
> You received this e-mail because you are subscribed
>
> to the BLDG-SIM at GARD.COM mailing list. To unsubscribe
>
> from this mailing list send a blank message to
>
> BLDG-SIM-UNSUBSCRIBE at GARD.COM
>
>
>
> ======================================================
>
> You received this e-mail because you are subscribed
>
> to the BLDG-SIM at GARD.COM mailing list. To unsubscribe
>
> from this mailing list send a blank message to
>
> BLDG-SIM-UNSUBSCRIBE at GARD.COM
>
>
>
> ==================
>
> You received this e-mail because you are subscribed
>
> to the BLDG-SIM at GARD.COM mailing list. To unsubscribe
>
> from this mailing list send a blank message to
>
> BLDG-SIM-UNSUBSCRIBE at GARD.COM
>
>
> =====================================================You received this
> e-mail because you are subscribed
> to the BLDG-SIM at GARD.COM mailing list. To unsubscribe
> from this mailing list send a blank message to
> BLDG-SIM-UNSUBSCRIBE at GARD.COM
======================================================
You received this e-mail because you are subscribed
to the BLDG-SIM at GARD.COM mailing list. To unsubscribe
from this mailing list send a blank message to
BLDG-SIM-UNSUBSCRIBE at GARD.COM
===========================
You received this e-mail because you are subscribed
to the BLDG-SIM at GARD.COM mailing list. To unsubscribe
from this mailing list send a blank message to
BLDG-SIM-UNSUBSCRIBE at GARD.COM
More information about the Bldg-sim
mailing list