[BLDG-SIM] Indirect Evap Cooling Not Appearing in BEPS Report
Mike Tillou
miket at etcgrp.com
Wed Apr 26 13:47:33 PDT 2006
Kendra,
Without seeing your model I can only guess at what is going on. I am
assuming you are using the add-on preconditioner and not the system type
EVAP-COOL.
Most likely you have not properly defined keywords EVAP-CL-AIR and
EVAP-CL-LIMIT-T. The default for EVAP-CL-AIR is the minimum OA ratio
(low airflow may explain the poor indirect cooling results). You must
also be careful because the air-side economizer will also effect how the
indirect/direct add-on will operate.
I suggest you review the eQuest documentation which should help explain
how the system is intended to work. You can find the Direct/Indirect
keyword explanations in the "Vol 2.-Dictionary" documentation file.
Check under HVAC System - Ventilation after the keywords for ERV heat
recovery
Good luck
Mike
Michael Tillou, PE
etc Group, Inc.
PO Box 7, Williamstown, MA 01267
ph. (413) 458-9870 fx. (413) 458-9875
-----Original Message-----
From: BLDG-SIM at gard.com [mailto:BLDG-SIM at gard.com] On Behalf Of
Tupper, Kendra
Sent: Wednesday, April 26, 2006 12:55 PM
To: BLDG-SIM at gard.com
Subject: [BLDG-SIM] Indirect Evap Cooling Not Appearing in BEPS
Report
I am trying to model an indirect evaporative cooler in eQuest,
and am encountering a the following problem.
No space cooling energy is being shown in the BEPS report for my
indirect evap coolers - in fact, there is no change in any of my end use
categories! If I change the type to Direct, then the report shows space
cooling savings, and increased fan energy (from added pressure drop) as
expected.
I looked in the supplemental Evap. Cooling report that DOE-2
provides, and this report shows a total cooling energy of about 1,000
MBtu for the indirect case. A very small amount of electric energy is
being consumed by the pump, but not nearly enough to offset the cooling
savings. This report also shows that the indirect evap. cooler is
operating for about 6000 hrs/yr (location is Las Vegas) - with this
runtime, it seems impossible that the there is no change in any end use
categories in the BEPS report!
I also printed hourly reports for the electric power and total
cooling of the indirect evaporative cooler, and these reports indicate
that the evap. cooler is running and performing cooling.
Does anyone know why this cooling is not appearing in the main
DOE-2 reports, such as BEPS (or the reports that come up in eQuest)? I
don't understand why the reports account for direct evaporative cooling,
but not indirect.
Thank you in advance!
Kendra
Kendra Tupper
FLACK + KURTZ
405 Howard Street 415.398.3833 Main
Suite 500 415.402.5840 Direct
San Francisco, CA 94105 415.433.5311 Fax
http://www.flackandkurtz.com kendra.tupper at sf.fk.com
<mailto:kendra.tupper at sf.fk.com>
This e-mail may contain confidential and/or privileged
information.
If you are not the intended recipient (or have received this
e-mail in error)
please notify the sender immediately and destroy this e-mail.
Any unauthorized copying, disclosure or distribution of the
material
in this e-mail is strictly forbidden.
==================
You received this e-mail because you are subscribed
to the BLDG-SIM at GARD.COM mailing list. To unsubscribe
from this mailing list send a blank message to
BLDG-SIM-UNSUBSCRIBE at GARD.COM
===========================
You received this e-mail because you are subscribed
to the BLDG-SIM at GARD.COM mailing list. To unsubscribe
from this mailing list send a blank message to
BLDG-SIM-UNSUBSCRIBE at GARD.COM
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20060426/f7870d06/attachment-0002.htm>
More information about the Bldg-sim
mailing list