[bldg-sim] Modeling UFAD
Peter Simmonds
peter.simmonds at ibece.net
Sun Dec 10 08:26:27 PST 2006
Varkie, what we typically do is calculate the projected temperature
profiles using the ESHG method, then insert the return temperature from
the ESHG calc as the space operating temperature. This way the
underfloor supply CFM is only for the load it 'sees'. Look at the system
pressure drops carefully and amend the fan pressure accordingly. Make
sure the systems have perimeter heating. Depending upon your location
you are right in checking the AHU to see if it dehumidifies the supply
and doesn't simply provide air at 63F. Another way we check this is to
run the same model but this time with 55F and the same delta T as the
underfloor model, checking the latent loads between these models will
give an indication of the dehumidification been carried in the model.
Good luck.
Peter Simmonds Ph.D.
Associate
IBE Consulting Engineers
14130 Riverside Drive Suite 201
Sherman Oaks, CA 91423
p: (818) 377-8220
f: (818) 377-8230
m: (818) 219-1284
IDEAS FOR THE BUILT ENVIRONMENT <BLOCKED::http://www.ibece.com/>
This e-mail message, including any attachments, is for the sole use of
the intended recipient(s) and may contain confidential and privileged
information. Any unauthorized review, use, disclosure, or distribution
is prohibited. If you are not the intended recipient, please contact the
sender by reply e-mail and destroy all copies of the original message.
________________________________
From: bldg-sim at gard.com [mailto:bldg-sim at gard.com] On Behalf Of Varkie
Thomas
Sent: Saturday, December 09, 2006 12:23 PM
To: bldg-sim at gard.com
Subject: [bldg-sim] Modeling UFAD
Are there any examples of modeling UFAD with DOE2.1E (or EQUEST).
This is a commercial project with electric heating in climate zone 3A.
The baseline System No. is 8 - VAV w/PFP Boxes). The proposed is also
PIU (DOE2). The perimeter zones up to 3 ft are served from the ceiling.
The remaining interior zones have UFAD. The CHW coil leaving temp of
the primary air is 48F. The UFAD supply temp is 65 F. The ceiling
return air temp is 78. The System MIN-SUPPLY-T = 65 and COOL-SET-T =
48. ZONE-FAN-RATIO = 1.74 ?? 80% glass.
The Baseline primary air is 53F and ceiling supply is 55F. The ceiling
return air temp is 76. System MIN-SUPPLY-T = 55 and COOL-SET-T = 53.
ZONE-FAN-RATIO = 1.1. 40% glass.
Is all this correct? Increasing the ZFR increases the Fan energy.
Increasing the MIN-SUPPLY-T from 55F to 65F increased the System Supply
Air and Fan energy considerably.
For UFAD is it acceptable to assume the following space volume temps?
$ Baseline Summer & Winter Space Volume Temp = 75 $
$ UFAD: 75F from 0' to 7' 85F from 7.1' to 10' Avg Summer Space Temp =
78F $
$ UFAD: 75F from 0' to 7' 65F from 7.1' to 10' Avg Winter Space Temp =
72F $
STD62.1-2004 Table 6-2 'Zone Air Distribution Effectiveness (Ez)' shows
Ez = 1.0 for Ceiling Supply of Cool Air
Ez = 1.2 for Floor Supply of Cool Air and Ceiling Return.
How would you apply this in DOE2.1E for Under-floor Air Distribution?
How is occupancy based lighting modeled? Based on 10CFR435 Table
401.3.3. Lighting Schedule = Max Design Lighting * Base Lighting
Schedule * 0.7 ?
How is occupancy based ventilation modeled? Percent Outdoor Air for Hour
= Maximum Design Percent Outdoor Air * Occupancy Schedule Fraction.
Apply this schedule in MIN-AIR-SCH ?
V.C. Thomas
==================
You received this e-mail because you are subscribed
to the BLDG-SIM at GARD.COM mailing list. To unsubscribe
from this mailing list send a blank message to
BLDG-SIM-UNSUBSCRIBE at GARD.COM
===========================
You received this e-mail because you are subscribed
to the BLDG-SIM at GARD.COM mailing list. To unsubscribe
from this mailing list send a blank message to
BLDG-SIM-UNSUBSCRIBE at GARD.COM
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20061210/d434a65a/attachment-0002.htm>
More information about the Bldg-sim
mailing list