[bldg-sim] eQUEST-cooling coil leaving temp troubles
Mike Roberts
Mike at roberts-engineering.com
Mon Feb 6 22:17:25 PST 2006
This is telling you that your entering chilled water temperature must be at
least 6 degrees below your coil leaving temperature. Since your cooling
supply temp is 52 degrees, your chilled water temperature would have to be
46 degrees or less. If it is less than that, check for CHW temperature
reset. You could also have some heat gain in the SA duct, requiring an even
lower coil leaving temperature and CHW temperature.
Incidentally, I believe this was added with DOE-2.2. Prior to that DOE-2.1E
and most other simulation programs didn't care if your coil expectations
were possible or not. They just did a BTU transfer, so you could have a
supply air temperature lower than your entering CHW temperature.
Mike
-----Original Message-----
From: bldg-sim at gard.com [mailto:bldg-sim at gard.com]On Behalf Of Scott
Runyon
Sent: Monday, February 06, 2006 10:45 PM
To: bldg-sim at gard.com
Subject: [bldg-sim] eQUEST-cooling coil leaving temp troubles
In EL1 Sys1 (VAVS) (B) , cooling coil leaving temperature must
be at least 6F higher than entering water temp.
I have this exact error multiple times.
I know this is like asking for a needle in a hay stack, but can anyone
give me some areas to check.
I have a standard VAV system(with hw reheat) and chilled and hot water
coils.
Thermostat setpoints:
Occupied (Cooling/Heating):72/68
UnOccupied (Cooling/Heating):75/64
Design Temps:
Cooling (Indoor/Supply): 72/52
Heating (Indoor/Supply): 68/55
Baseboards:none
Heat/reheat: 20deg (this was untouched)
Economizer:
Dry Bulb Temp 65deg
Any help would be extremely appreciated.
Thanks in advance.
-Scott
==================
You received this e-mail because you are subscribed
to the BLDG-SIM at GARD.COM mailing list. To unsubscribe
from this mailing list send a blank message to
BLDG-SIM-UNSUBSCRIBE at GARD.COM
======================================================
You received this e-mail because you are subscribed
to the BLDG-SIM at GARD.COM mailing list. To unsubscribe
from this mailing list send a blank message to
BLDG-SIM-UNSUBSCRIBE at GARD.COM
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20060207/e18dec97/attachment-0002.htm>
More information about the Bldg-sim
mailing list