[bldg-sim] Humidity control in eQUEST
Peter Alspach
peter.alspach at arup.com
Mon Jan 23 16:08:02 PST 2006
Vikram,
If your base system already is dehumidifying enough to bring the space
down to 50% RH under normal operation then you would not expect to see
any additional energy requirement. Depending on your OA fraction in
Atlanta you may not need any additional dehumidification than what you
get with your base DX system. Have you checked the RH reports from your
base model to determine if the base design is floating up over 50% RH?
Peter Alspach, P.E.
Senior Mechanical Engineer
Arup
901 Market Street, Suite 260
San Francisco, CA 94103
T: 415.957.9445
D: 415.946.0607
F: 415.957.9096
E: peter.alspach at arup.com
________________________________
From: bldg-sim at gard.com [mailto:bldg-sim at gard.com] On Behalf Of Vikram
Sami
Sent: Monday, January 23, 2006 3:11 PM
To: bldg-sim at gard.com
Subject: [bldg-sim] Humidity control in eQUEST
I am trying to model a humidistat in eQUEST using a packaged single zone
system (for a project in Atlanta), and for some reason, it doesn't seem
to be adding energy for reducing max humidity from 100% to 50%. The
result is that there is a cooling penalty for using a liquid desiccant
dehumidifier. My question is:
A) Is it possible to have humidity controls for a PSZ system type? If so
- how do I do it?
B) If not - what system type should I use, and how do I get it to
dehumidify?
Thanks in advance.
Vikram Sami, LEED AP
Direct Phone 404-253-1466 | Direct Fax 404-253-1366
LORD, AECK & SARGENT ARCHITECTURE
Responsive Design * Technological Expertise * Exceptional Service
www.lordaecksargent.com <file://www.lordaecksargent.com>
==================
You received this e-mail because you are subscribed
to the BLDG-SIM at GARD.COM mailing list. To unsubscribe
from this mailing list send a blank message to
BLDG-SIM-UNSUBSCRIBE at GARD.COM
____________________________________________________________
Electronic mail messages entering and leaving Arup business
systems are scanned for acceptability of content and viruses
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20060123/d6054c54/attachment-0002.htm>
More information about the Bldg-sim
mailing list