[BLDG-SIM] HVAC efficiencies in DOE2
Steven Gates
steve.gates at doe2.com
Tue Jun 20 11:43:54 PDT 2006
Efficiency numbers such as SEER and AFUE are useful for enforcement purposes
in energy standards, and for selecting equipment when no energy analysis is
to be performed (which of course applies to the majority of purchases).
Unfortunately, such numbers do not convert readily to the data needed by an
hourly building simulation program. Moreover, they can lead to the wrong
result in some applications. A few examples:
1. Packaged air conditioners with the highest SEERs are typically two-speed
units. The high SEER is achieved by the contribution of low-speed
compressor operation at 82F outdoor temperature. A two-speed high-SEER unit
may actually have a lower EER (measured at peak output at 95F) than a "less
efficient" single-speed unit having a lower SEER but a higher EER. Where I
live (hot, dry summer with a large daily temperature swing), many people
don't even run their air conditioners if the outdoor temperature peaks in
the mid-80s. Instead, we need maximum efficiency when the outdoor
temperature is in the mid-90s to low 100s. SEER misses this effect, and the
promotion of SEER over EER in this climate may cause the peak electrical
demand on power plants to increase.
2. Water-cooled chiller part-load performance data (IPLV) assumes condenser
relief; that is, the cooling tower temperature is assumed to drop as the
chiller load drops (85F at full load, 65F at 25% load). But what if the
cooling tower is controlled to a fixed setpoint of 85F? Or, what if the
building is in a low-wetbulb climate, and the maximum tower temperature will
never exceed 76F? Or, what if the building has two chillers, and when the
building is at 40% load, one of the chillers is running at 80% load?
3. The issues described in #2 above are doubly important for centrifugal
chillers with variable-speed drives; the reported savings are highly
dependent on condenser relief. Without condenser relief at reduced loads,
the impeller cannot slow down appreciably. This is because the impeller
must spin fast enough to overcome the pressure differential between the
evaporator and condenser; this pressure differential is primarily governed
by the temperature differential, not the load.
4. For boilers, part-load and temperature-dependent performance data is
rarely published.
Building simulation programs can be highly useful for studying these types
of interactions, but their usefullness is limited if manufacturers do not
publish data in a form that can be readily converted to program input. To
resolve these issues, Standards such as ARI 210, 550, etc. would need to be
expanded to report data in a format useful for hourly simulation. And of
course, simulation programs may need to be modified to accept data in some
future "standard format".
Steve Gates
-----Original Message-----
From: BLDG-SIM at GARD.COM [mailto:BLDG-SIM at GARD.COM] On Behalf Of Michael
Brandemuehl
Sent: Tuesday, June 20, 2006 7:47 AM
To: BLDG-SIM at GARD.COM
Subject: [BLDG-SIM] HVAC efficiencies in DOE2
Andy,
You might also look at the following paper that came from ASHRAE Research
Project 1197-RP Updated Energy Calculation Models for Residential HVAC
Equipment:
Wassmer, M., and M. J. Brandemuehl. 2006. Effect of Data Availability on
Modeling of Residential Air Conditioners and Heat Pumps for Energy
Calculations. ASHRAE Transactions 111(1).
The paper includes another couple relationships of EER=f(SEER) and
COP47=f(HSPF). In our case, we used a set of 25 air conditioners and heat
pumps to develop the correlations.
Also, Jeff Hirsh and his colleagues (Marlin Addison, John Hill, Paul Reeves,
and Steve Gates) did some work for Southern California Edison a few years
ago that involved examining EER and SEER as predictors of actual seasonal
energy efficiency. As I recall, it also included comparisons of EER=f(SEER)
using a larger set of units. I don't think the work has been published, but
may be available through the authors.
And yes, you also need to remove the fan power from the power data. The
performance data reported under the various ARI standards are typically
"net" values of capacity and power - i.e., net capacity delivered by the
HVAC unit and total power consumed by the unit. Most simulation program
treat the indoor fan separately and expect input data based on "gross"
performance of the coil and the power used by everything except the indoor
fan.
Mike
___________________________________________________
Michael J. Brandemuehl, Ph.D., P.E.
Civil, Environmental, and Architectural Engineering
University of Colorado
428 UCB, ECOT 441
Boulder, CO 80309-0428
303 492 8594
303 492 7317 fax
michael.brandemuehl at colorado.edu
-----Original Message-----
From: BLDG-SIM at gard.com [mailto:BLDG-SIM at gard.com] On Behalf Of Andy Lau
Sent: Tuesday, June 20, 2006 6:33 AM
To: BLDG-SIM at gard.com
Subject: [BLDG-SIM] HVAC efficiencies in DOE2
I'm working on putting together a document to guide students in defining
the heating and cooling equipment efficiencies that are input to DOE2.2,
specifically eQuest v.3.55. In the process, I've realized that I'm not
that confident on some of these issues and seek the knowledge of this
BLDG-SIM group.
First, HIR for furnaces and boilers, derived from AFUE and Et. Because
eQuest has built-in HIR=f(PLR) curves, the program accounts for
part-load effects like cycling and flue losses. Therefore, I would
expect that it is Et, thermal efficiency, that should be used to
determine HIR=1/Et. The question then is whether there is a documented
relationship for determining Et from AFUE. All I have found thus far is
the California Energy Commission's 2005 "Nonresidential Alternative
Calculation Method (ACM) Approval Manual" wherein there are
relationships for HIR for packed and split systems as well as boilers
(the relationships are in the attached spreadsheet). Not sure where
these relations have come from plus I would expect AFUE to be lower than
Et which is not always the case in these correlations.
Second, EIR for heat pumps in heating mode. My understanding is that
the eQuest input should reflect the COP at 47F outdoor temperature, not
including the supply fan energy use which is modeled separately in
eQuest. If a heat pump is rated in terms of HSPF, then this seasonal
average value must be converted to COP47. I've found an FSEC/ASHRAE
publication, "Climate Impacts on Heating Seasonal Performance Factor
(HSPF) and Seasonal Energy Efficiency Ratio (SEER) for Air Source Heat
Pumps," that provides a simple correlation, COP47 = 1.718*HSPF/3.413.
In this correlation, supply fan power is removed from the HSPF using the
ARI standard blower value of 0.365 W/cfm.
Third, EIR for packaged cooling equipment in cooling mode. Here the EIR
should be based on the COP at 95F outdoor, 80F indoor, which is related
to the EER, COP95 = EER/3.413. For smaller units, SEER is often the
reported measure, which accounts for seasonal variation. In the same
FSEC/ASHRAE study, they found this correlation, COP95 =
1.063*SEER/3.413. Again, fan power is backed out of the SEER values
using the ARI standard blower.
On the issue of removing supply fan power when it is included in HSPF,
SEER, or EER, there is the question of whether it should just be removed
from the electrical input, or also as a heat gain.
I would appreciate your comments on these relationships and references
to any other publications that address these issues.
Andy Lau
Associate Professor of Engineering
(814) 863-9075, andylau at psu.edu
www.cede.psu.edu/~andylau
======================================================
You received this e-mail because you are subscribed
to the BLDG-SIM at GARD.COM mailing list. To unsubscribe
from this mailing list send a blank message to
BLDG-SIM-UNSUBSCRIBE at GARD.COM
==================
You received this e-mail because you are subscribed
to the BLDG-SIM at GARD.COM mailing list. To unsubscribe
from this mailing list send a blank message to
BLDG-SIM-UNSUBSCRIBE at GARD.COM
======================================================
You received this e-mail because you are subscribed
to the BLDG-SIM at GARD.COM mailing list. To unsubscribe
from this mailing list send a blank message to
BLDG-SIM-UNSUBSCRIBE at GARD.COM
More information about the Bldg-sim
mailing list