[BLDG-SIM]
Aulbach, John
jaulbach at nexant.com
Thu Sep 7 13:51:49 PDT 2006
Hi, Holly:
I am assuming you are using eQUEST. This web site is for ALL energy
simulation programs, not just certain ones, please remember.
There are two obvious things i would check:
1) Are you getting ELECTRIC how water heating? If so, change your source
to GAS.
2: In eQUEST, you must be connected to a LOOP if you want a chilled,
hot, or domestic water load to be satisfied by equipment. Change over to
the Detailed Edit mode, go to the Water Side Icon on the menus, and see
if your DHW equipment is attached to a circulation loop. If not, you
will need to do this.
3) Do you have a reasonable SCHEDULE for your hot water load? Or ANT
schedule operating to give the hot water "life"?
Hope this helps.
John R. Aulbach, PE, CEM
Project Manager
Nexant, Inc.
100 North Barranca, Suite 820
West Covina, CA 91791 USA
Phone: 626-430-9054
Fax: 626-430-9060
email: jaulbach at nexant.com
________________________________
From: BLDG-SIM at GARD.COM [mailto:BLDG-SIM at GARD.COM] On Behalf Of Holly
Richardson
Sent: Thursday, September 07, 2006 1:11 PM
To: BLDG-SIM at GARD.COM
Subject: [BLDG-SIM]
Hello all,
I sorry that I have too ask this question...but more then once I have
had this issue. After setting up my DWH system for my building, and
having all my rate schedules set up correctly, I then do a run. On the
BEUP, and other reports it does not show that the model is accounting
for the Natural Gas DWH for the building. Can anyone give me an idea of
what I am doing wrong?
Thanks for the help!
Holly Richardson
LONG Energy Solutions
Technology for Better Buildings
303.975.2147 303.328.0002 fax
hrichardson at long.com
http://www.long.com <http://www.long.com/>
==================
You received this e-mail because you are subscribed
to the BLDG-SIM at GARD.COM mailing list. To unsubscribe
from this mailing list send a blank message to
BLDG-SIM-UNSUBSCRIBE at GARD.COM
===========================
You received this e-mail because you are subscribed
to the BLDG-SIM at GARD.COM mailing list. To unsubscribe
from this mailing list send a blank message to
BLDG-SIM-UNSUBSCRIBE at GARD.COM
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20060907/7819c2e8/attachment-0002.htm>
More information about the Bldg-sim
mailing list