[BLDG-SIM] Cold Storage Facility / LEED
Zoeteman, Mark R.
mrzoeteman at FTCH.com
Wed Dec 5 06:14:59 PST 2007
Alec:
In 3/6/07 email from Gail Stranske, she reinforces what Marcus Sheffer
indicated in a prior email that exceptional calculation method is to be
used to show process energy savings:
The modeling approach you suggest for process loads would not comply
with the current requirements for LEED. The 25% process load
requirement is set up as a minimum process load requirement to avoid
underreporting of process load energy usage ( i.e. an office building
reporting 0.25 W/sf of miscellaneous equipment). However, all projects
are still expected to follow the Appendix G, Table G.3.1.12 requirements
for receptacles and process loads, stating that "these loads shall be
included when calculating the baseline building performance and proposed
building performance"). Unless LEED requirements change, If your
building is expected to consume 60% process energy, it should be modeled
with 60% process energy, and the Percentage Improvement should be
calculated with your projected actual process energy consumption
included in the energy results. I would echo Marcus' recommendation
unless & until the EA TAG comes up with an alternate solution:
"In the mean time I would suggest that project teams strive to make all
building energy systems as energy efficient as possible and follow the
exceptional calculation method to show savings for process loads in the
LEED certification review process."
Best Regards,
Gail Stranske
Mark Zoeteman
-----Original Message-----
From: BLDG-SIM at gard.com [mailto:BLDG-SIM at gard.com] On Behalf Of Alec
Stevens
Sent: Wednesday, December 05, 2007 8:07 AM
To: BLDG-SIM at gard.com
Subject: [BLDG-SIM] Cold Storage Facility / LEED
Hi,
I've been asked to provide LEED energy modeling services for a
refrigerated warehouse. 90% of the space in the building will be a -15F
freezer space, with the remainder a small office area.
Under Appendix G, am I correct in interpreting that the unregulated
process loads (i.e. refrigeration equipment) would need to be the same
in the base case and proposed case models? If so, how would you account
for any improvements to the performance of the refrigeration system
under EACR1?
If we cannot take credit for process performance improvements, I am not
sure how we would manage to capture the pre-requisite 2 points under
EACR1.
Also, would we be required to model the building using eQuest-R instead
of the temperature bin spreadsheet models we usually use for
refrigeration systems? I've never found the eQuest-R package to be that
adept at modeling refrigeration systems, although I haven't looked at it
in a while. Have there been any recent improvements to its
capabilities?
Thanks for any sage advice as to how this type of project has been
successfully handled in the past.
Sincerely,
Alec Stevens, PE, LEED AP
DMI
35 Walnut Street, Wellesley, MA 02481
p: 781-431-1100 x11 f: 781-431-1109
e: astevens at dmiinc.com
======================================================
You received this e-mail because you are subscribed to the
BLDG-SIM at GARD.COM mailing list. To unsubscribe from this mailing list
send a blank message to BLDG-SIM-UNSUBSCRIBE at GARD.COM
===========================
You received this e-mail because you are subscribed
to the BLDG-SIM at GARD.COM mailing list. To unsubscribe
from this mailing list send a blank message to
BLDG-SIM-UNSUBSCRIBE at GARD.COM
More information about the Bldg-sim
mailing list