[BLDG-SIM] eQUEST HVAC sizing runs
gail
gail22 at gmail.com
Thu Feb 15 13:31:05 PST 2007
Hi Andy,
Auto-sizing is a good way to go. That makes the schedule inputs for CDD and
HDD very important. Also, make sure the Zone Sizing option is "Adjust
loads" and the System Sizing Option is "Coincident". When using the
Auto-size, set the System Heat Sizing Ratio to 1.25 and the System Cool
Sizing Ratio to 1.15. Similarly for any central plant equipment, set the
capacity ratio to 1.15 for cooling equipment and 1.25 for heating equipment.
You can find out what the auto-sized capacities are in the SV-A output
reports for systems, and the PV-A output reports for plant equipment.
Gail Stranske
CTG Energetics
On 2/15/07, Andy McNamara <andyjmc at gmail.com> wrote:
>
> Hello,
>
> As I mentioned previously, I am creating an energy model for a LEED
> project. In "baselining" the building, one of the stipulations of ASHRAE
> 90.1 2004 is:
> "G3.1.2.2 Equipment Capacities. The equipment capacities for the baseline
> building design shall be based on sizing runs for each orientation and shall
> be oversized by 15% for cooling and 25% for heating"
>
> I think that means I use "auto-size", but then how do I capture what that
> size is and oversize it accordingly? I am guessing that the results may be
> in the SIM file. Can anyone provide tips for executing this? Is there a
> better way to do that auto-sizing for each orientation?
>
> Thanks,
> Andrew McNamara
>
======================================================
You received this e-mail because you are subscribed
to the BLDG-SIM at GARD.COM mailing list. To unsubscribe
from this mailing list send a blank message to
BLDG-SIM-UNSUBSCRIBE at GARD.COM
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20070215/fd5e1bb6/attachment-0002.htm>
More information about the Bldg-sim
mailing list