[BLDG-SIM] energy consumption of low-E glazing , why the cooling energy increases
Llona, Joseph
Joseph.Llona at tetratech.com
Mon Jul 30 08:42:35 PDT 2007
I ran into this once on lab project in the northwest (mild climate). Turned out the higher performance glazing was trapping the high internal heat gains. Higher cooling energy and lower heating energy.
Joe Llona, P.E. LEED® AP, CSBA | Senior Mechanical Engineer
Direct: 206.883.9318 | Main: 206.883.9300 | Fax: 206.883.9301
joseph.llona at tetratech.com
Tetra Tech | Infrastructure Group
1420 Fifth Avenue, Suite 600 | Seattle, Washington 98101 | www.tetratech.com
PLEASE NOTE: This message, including any attachments, may include privileged, confidential and/or inside information. Any distribution or use of this communication by anyone other than the intended recipient is strictly prohibited and may be unlawful. If you are not the intended recipient, please notify the sender by replying to this message and then delete it from your system.
________________________________
From: BLDG-SIM at gard.com on behalf of nicole chen
Sent: Mon 7/30/2007 1:03 AM
To: BLDG-SIM at gard.com
Cc: bldg-sim at gard.com
Subject: [BLDG-SIM] energy consumption of low-E glazing , why the cooling energy increases
What I did is define a new glass type with simplied method in detailed model. Then replace the old glass with the new defined one. Can this do? How to avoid the defauls percolate through the program? I check again and find that there was no wrong with the conduction heat and solar radiation through window .But the load due to occupancy /lighting/euqipment of Glass Type II is higher than Glass Type I . And the cooling energy of Glass type II is a little highter. It make me confused. Why the load due to due to occupancy /lighting/euqipment was different when Glass type changed.
And I doubt if the problem has something to do with OA load .
On 7/29/07, Karen Walkerman <kwalkerman at gmail.com> wrote:
Hi nicole,
I can't tell you why the heating energy of glass type II may be lower
because of the better U-value. With Shading Coefficients almost the
same, there should be little change in heat gain from solar radiation
between the two types.
What method did you use to enter your data? You should be careful of
defaults that can percolate through the program. For example, the
window frame U-value may not be consistent, or the glass spacer-type
may be different.
Another good place to look for some feedback is the building and space
peak loads summary. Here, the solar gain (heat energy gained through
radiation) and simple conditioning (energy transfered through the
glass-same as walls), are broken out. The heating design case will
not take solar radiation into account.
Hope this helps.
~karen~
On 7/29/07, nicole chen <cloris.chen at gmail.com> wrote:
> Dear all
>
> I have tried to compare the energy consumption between two different glass
> types and got a curious result. The parameters of these two glasses are
> listed below:
>
> 1) Coated U=2.5 SC=0.45
> 2) low-e U=1.76 SC=0.44
>
> I thought the energy consumption of Glass Type II would be lower than that
> of Glass Type I . But the result is the cooling energy of Glass Type II is
> higher than that of Glass Type I , and the heating energy lower than that
> of Glass Type I.
>
> I have no idea of this. And I checked LS-F/ SS-D / BEPS and found some
> points listed below
>
> 1) in LS-F annual sensible cooling load of Glass Type II is lower than that
> of Glass Type I , latent cooling load of Glass Type II is higher. The total
> annual cooling load of Glass Type II is a little higher
>
> 2) in SS-D monthly cooling energy of Glass Type II is higher
>
> 3) dencity and schedule of occupancy /lighting /euqipment are the same in
> the two models , but cooling load and heating load due to these indoor
> factors are different , why?
>
> 4) monthly schedule of occupancy /lighting /euqipment is all the same
> during the year, but cooling load and heating load due to these indoor
> factors are different every month, why?
>
>
>
> --
> Yours
> Nicole Chen
--
Karen Walkerman
Second Law Consulting
802-238-0980
kwalkerman at gmail.com
--
Yours
Nicole Chen
===========================
You received this e-mail because you are subscribed
to the BLDG-SIM at GARD.COM mailing list. To unsubscribe
from this mailing list send a blank message to
BLDG-SIM-UNSUBSCRIBE at GARD.COM
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20070730/54beea3a/attachment-0008.htm>
More information about the Bldg-sim
mailing list