[BLDG-SIM] Equest unmet load report
Sean Henry
SeanH at ieice.com
Fri Mar 16 11:10:08 PDT 2007
Nicole:
The building % hours out of range can be found in the DOE2.2 BEPS and
BEPU reports. The BEPU outputs are frequently used to show compliance
with A90.1-2004-App G and the LEED NC2.2-EAc1 letter template.
However, the SS reports have a lot of good zone specific information. I
believe you can look at individual zone unmet load hours (i.e. hours out
of range) in the SS-F report.
Incidentally, eQuest also provides a summary report (under Airside HVAC)
that shows individual; hours out of range for each thermal zone.
I hope this helps.
Sean
S.P. Henry, LEED(r) AP | Mechanical Design Engineer / Lead Energy
Analyst
INTERFACE ENGINEERING
708 SW Third Avenue | Suite 400 | Portland, OR 97204
direct: 503.382.2695
office: 503.382.2266
fax: 503.382.2262
email: seanh at ieice.com
web: www.ieice.com
Consultants of Choice to the Built Environment for over 35 years
Kirkland, WA | Portland, OR | Sacramento, CA | Salem, OR | San
Francisco, CA |
________________________________
From: BLDG-SIM at gard.com [mailto:] On Behalf Of nicole chen
Sent: Friday, March 16, 2007 4:54 AM
To: BLDG-SIM at gard.com
Subject: [BLDG-SIM] Equest unmet load report
Dear folks:
Would anyone help me gotta know where to find the report of unment lolad
hours in Equest Sim files that is required in ASHRAE APPG?
According to ASHRAE 90.1 APPG , dose the "unment load hours" mean the
sum of all unmet load hors of each zone, Please advise if I mis
understood this important term.
--
Yours
Nicole Chen
===========================
You received this e-mail because you are subscribed
to the BLDG-SIM at GARD.COM mailing list. To unsubscribe
from this mailing list send a blank message to
BLDG-SIM-UNSUBSCRIBE at GARD.COM
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20070316/2798ef2c/attachment-0002.htm>
More information about the Bldg-sim
mailing list