Where can the LP2LPHP.INP file be found?  Can it be downloaded directly
from DOE2.com?  I could not find it there.
 
Thanks,
Doug Maddox
The Weidt Group
 
________________________________
From: BLDG-SIM at gard.com [mailto:BLDG-SIM at gard.com] On Behalf Of Routh
Consulting Engineers
Sent: Wednesday, November 21, 2007 8:07 PM
To: BLDG-SIM at gard.com
Subject: [BLDG-SIM] Error in eQUEST example file LP2LPHP.inp
 
Mr. Tian:
 
I believe you need to change the heating water supply temperature in the
heating loop attached to the heat pump chiller system to 130F or lower.
This is pretty much a limitation of an actual chiller used in a heat
pump configuration that this model simulates. The refrigerant
temperature in a typical chiller condenser isn't hot enough to raise the
condenser water temperature to any warmer than this. In my experience,
even 130F is pushing it.
 
Rick Routh
Routh Consulting Engineers, Inc.
P.O. Box 3187
Pasco, WA  99302
509-547-8262
509-542-0650 FAX
routhconsultingengineers at charter.net
 
	----- Original Message ----- 
	From: Zhen Tian <mailto:tianzhen9 at yahoo.com>  
	To: BLDG-SIM at gard.com 
	Sent: Wednesday, November 21, 2007 4:03 PM
	Subject: [BLDG-SIM] Error in eQUEST example file LP2LPHP.inp
	 
	Dear all,
	
	I tried to setup a loop-to-loop heat-pump system. I used the
example file LP2LPHP.inp from doe2.com. However, when I run the example
file, I got the following error report: "HW design temperature too hight
for loop-to-loop heat-pump. Errors during HVAC simulation
setup-abortion."
	
	In the detailed simulation file, I got the error: "chiller 1 has
a design HW temperature too high for a loop-to-loop heat-pump (max
130F)."
	
	Does someone have an idea what is the problem with the
loop-to-loop heat-pump example file and how can I solve this problem?
	
	Thanks a lot in advance.
	
	Regards,
	
	David
	
________________________________
	Be a better sports nut! Let your teams follow you with Yahoo
Mobile. Try it now.
<http://us.rd.yahoo.com/evt=51731/*http:/mobile.yahoo.com/sports;_ylt=At
9_qDKvtAbMuh1G1SQtBI7ntAcJ> 
 
 
==================
You received this e-mail because you are subscribed 
to the BLDG-SIM at GARD.COM mailing list.  To unsubscribe 
from this mailing list send a blank message to 
BLDG-SIM-UNSUBSCRIBE at GARD.COM
===========================
You received this e-mail because you are subscribed 
to the BLDG-SIM at GARD.COM mailing list.  To unsubscribe 
from this mailing list send a blank message to 
BLDG-SIM-UNSUBSCRIBE at GARD.COM
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20071125/423138de/attachment-0002.htm>
    
    
More information about the Bldg-sim
mailing list