[BLDG-SIM] Error in eQUEST example file LP2LPHP.inp
    Routh Consulting Engineers 
    routhconsultingengineers at charter.net
       
    Wed Nov 21 17:06:36 PST 2007
    
    
  
Mr. Tian:
I believe you need to change the heating water supply temperature in the heating loop attached to the heat pump chiller system to 130F or lower. This is pretty much a limitation of an actual chiller used in a heat pump configuration that this model simulates. The refrigerant temperature in a typical chiller condenser isn't hot enough to raise the condenser water temperature to any warmer than this. In my experience, even 130F is pushing it.
Rick Routh
Routh Consulting Engineers, Inc.
P.O. Box 3187
Pasco, WA  99302
509-547-8262
509-542-0650 FAX
routhconsultingengineers at charter.net
  ----- Original Message ----- 
  From: Zhen Tian 
  To: BLDG-SIM at gard.com 
  Sent: Wednesday, November 21, 2007 4:03 PM
  Subject: [BLDG-SIM] Error in eQUEST example file LP2LPHP.inp
  Dear all,
  I tried to setup a loop-to-loop heat-pump system. I used the example file LP2LPHP.inp from doe2.com. However, when I run the example file, I got the following error report: "HW design temperature too hight for loop-to-loop heat-pump. Errors during HVAC simulation setup-abortion."
  In the detailed simulation file, I got the error: "chiller 1 has a design HW temperature too high for a loop-to-loop heat-pump (max 130F)."
  Does someone have an idea what is the problem with the loop-to-loop heat-pump example file and how can I solve this problem?
  Thanks a lot in advance.
  Regards,
  David
------------------------------------------------------------------------------
  Be a better sports nut! Let your teams follow you with Yahoo Mobile. Try it now.
===========================
You received this e-mail because you are subscribed 
to the BLDG-SIM at GARD.COM mailing list.  To unsubscribe 
from this mailing list send a blank message to 
BLDG-SIM-UNSUBSCRIBE at GARD.COM
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20071121/12561710/attachment-0002.htm>
    
    
More information about the Bldg-sim
mailing list