Matthew -
Here is an approach I am taking on a current project:
The project is an existing building with CMU walls, single pane glass
and no insulation. We are adding an open air atrium to the middle (for
daylight) and modifying two entrances.
The proposed building is full of energy efficient features (good
windows, daylighting, light shelves, geothermal heat pump, good
insulation, solar water heating, etc).
The baseline building model is exactly the same shape as the proposed
(Table G3.1, item 1) and includes the atrium and entrance modifications.
The existing building envelope characteristics such as single clear
glass, no insulation, roof, and walls, etc. are depicted in the baseline
model (per Table G3.1, item 5 (f)).
However, the components of the existing building that are being
modified, i.e. the atrium, and entrances (and in your case the
clerestory), are to be modeled in the baseline with ASHRAE 90.1-2004
minimum performance as these are new additions and alterations to the
existing building. 
The occupancy schedules, use, program, spaces, etc, are the same for the
baseline and proposed.
I would welcome any comment on this approach.
Regards,
Jeffrey G. Ross-Bain, PE, LEED 
Smith Dalia Architects 
621 North Ave NE 
Suite C-140 
Atlanta, GA, 30308 
404-892-2443 
www.smithdalia.com 
P Consider the environment. Please don't print this e-mail unless you
really need to.
-----Original Message-----
From: BLDG-SIM at gard.com [mailto:BLDG-SIM at gard.com] On Behalf Of Matthew
Higgins
Sent: Thursday, November 01, 2007 11:46 AM
To: BLDG-SIM at gard.com
Subject: [BLDG-SIM] Existing Buildings 90.1
When modeling the baseline building for ASHRAE 90.1 Appendix G should 
one assume that the following passage means to delete all new elements 
from the proposed model to create the baseline. I am specifically 
wondering about a section of roof that was raised to accommodate 
clerestories.
Section 5. Building Envelope - Sub-section (f):
"Existing Buildings. For existing building envelopes, the baseline 
building design shall reflect existing conditions prior to any revisions
that are part of the scope of work being evaluated."
Any help is appreciated.
-- 
Matthew Higgins, LEED AP
Green Building Program Technical Specialist
Environmental Dynamics, Inc.
Architecture and Sustainability Consulting Services
505.242.2851
======================================================
You received this e-mail because you are subscribed 
to the BLDG-SIM at GARD.COM mailing list.  To unsubscribe 
from this mailing list send a blank message to 
BLDG-SIM-UNSUBSCRIBE at GARD.COM
===========================
You received this e-mail because you are subscribed 
to the BLDG-SIM at GARD.COM mailing list.  To unsubscribe 
from this mailing list send a blank message to 
BLDG-SIM-UNSUBSCRIBE at GARD.COM
    
    
More information about the Bldg-sim
mailing list