[Bldg-sim] Equest and gbXML import
Talbert, Joshua
jtalbert at hallam-ics.com
Fri Jan 4 10:37:53 PST 2008
Hello Again,
Thank you all for your responses! Per all of your instructions I registered with www.greenbuildingstudio.com<http://www.greenbuildingstudio.com/> and attempted to use their services to create an Equest type *.BDL or *.INP file from the gbXML file I was emailed.
When I attempted to upload the *.XML file using the Green Building Studio Client I was given an error that said:
"File does not have a valid five digit zip code."
So I opened the *.XML file with an editor and added the project zip code and saved it with a new name. Then I tried uploading it again via the Green Building Studio Client and I was presented with this next error:
"File received does not have any building area defined. This is an essential requirement."
Similarly, as I am also an experienced HAP V4.31 user I tried importing the *.XML file into HAP which gave me the following error:
"Data from the specified gbXML file could not be imported. Usually this is due to one of the following problems: (1) the file does not contain XML, (2) the file is not formatted according to the gbXML schema, or (3) the file cannot be found."
Of those three options I am assuming the problem is the wrong schema (2), as I know the file contains *.XML of some sort, and I do know where it is.
The architect with whom I am in collaboration used the File Menu pulldown option in Revit to "Export to gbXML" and then they emailed me the *.XML file that export command generated. Is there something that can be down to verify the file is: (1) in the right schema, (2) has been exported properly, (3) contains the information appropriate for Equest and/or HAP imports?
When I view the *.XML file I was emailed in my text editor it has only a bunch of 'surfaces' defined, 1,025 to be exact, it seems to me like there needs to be more in a gbXML file to perform and energy model than just 'surface' polygon definitions. Is this Architect providing me with an appropriate file, are there other ways to achieve better interoperability between his architectural needs and my energy analysis needs?
Thank you for all of your continued assistance.
Sincerely,
Josh
________________________________
From: Brandon Nichols [mailto:BrandonN at Hargis.biz]
Sent: Thursday, January 03, 2008 4:26 PM
To: Talbert, Joshua; bldg-sim at lists.onebuilding.org
Subject: RE: [Bldg-sim] Equest and gbXML import
For gbXML to eQuest, check out www.greenbuildingstudio.com<http://www.greenbuildingstudio.com> ...
You can import the gbXML into GBS, then save as DOE-2 file. However, this DOE-2 file cannot be edited with eQuest wizards. You'll need to do all editing going forward in the detailed interface. If you've not done any projects yet with eQuest, there IS a learning curve that seems to vary inversely with the cube of your overall level of computing expertise ;-)
So if the project is coming from Revit, be sure to check out IES<http://www.iesve.com/content/default.asp?page=s97_1>. Despite the relatively spendy price tag, you may be time and money ahead in the race to obtain meaningful results.
Regards,
Brandon Nichols, PE, LEED(r) AP
Mechanical
HARGIS ENGINEERS
600 Stewart Street
Suite 1000
Seattle, WA 98101
www.hargis.biz
d | 206.436.0400 c | 206.228.8707
o | 206.448.3376 f | 206.448.4450
________________________________
From: bldg-sim-bounces at lists.onebuilding.org [mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of Talbert, Joshua
Sent: Thursday, January 03, 2008 12:51 PM
To: bldg-sim at lists.onebuilding.org
Cc: Josh Talbert (E-mail)
Subject: [Bldg-sim] Equest and gbXML import
Hello All,
I am a moderately experienced Equest user and a first time inquirer to the Bldg Sim forum, and I have just been posed with a question from my boss to which I don't know the answer. Is it possible to import a gbXML file into Equest? We are trying to collaborate our design efforts with our client, an architect working in Revit, who has send us a gbXML file to use for our energy modeling purposes. Are their other software suites that will convert gbXML to a regular Equest *.inp file?
I look forward to working with and contributing further with you all at the Bldg Sim forum.
Happy New Year,
Sincerely,
Josh Talbert
Joshua W. Talbert
Mechanical Engineer
LEED-AP
Hallam///ICS
38 Eastwood Dr. Suite 200
S. Burlington, VT 05403
P: (802) 658-4891
F: (802) 658-1457
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20080104/12eb9a7a/attachment-0001.htm>
More information about the Bldg-sim
mailing list