[Bldg-sim] 90.1 VAV Baseline
    Demba Ndiaye 
    demba.ndiaye at setty.com
       
    Thu Jul 31 12:48:31 PDT 2008
    
    
  
Mike, 
Section G3.1.3.13 calls for a minimum of 0.4 cfm/ft2 of floor area
served. Use this number as your minimum flow.
______________
Demba Ndiaye
> -----Original Message-----
> From: bldg-sim-bounces at lists.onebuilding.org [mailto:bldg-sim-
> bounces at lists.onebuilding.org] On Behalf Of Tobias, Mike
> Sent: Thursday, July 31, 2008 3:42 PM
> To: bldg-sim at lists.onebuilding.org
> Subject: [Bldg-sim] 90.1 VAV Baseline
> 
> My baseline system is System 5: Packaged VAV w/ reheat, but 90.1
doesn't
> specify the minimum airflow percentage and I'm not sure what to use.
> Equest defaults the min VAV airflow at 40% in core zones and 30% in
> perimeter zones.  Increasing this number to 100% (cv) nearly doubles
the
> heating energy.  Since this is such a sensitive number, it's accuracy
is
> critical, what do you think I should use?
> 
> -Mike
> _______________________________________________
> Bldg-sim mailing list
> http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
> To unsubscribe from this mailing list send  a blank message to
BLDG-SIM-
> UNSUBSCRIBE at ONEBUILDING.ORG
    
    
More information about the Bldg-sim
mailing list