[Bldg-sim] cooling energy / solar loads
Daniel Tuhus-Dubrow
daniel.tuhus.dubrow at gmail.com
Wed Jun 18 19:36:49 PDT 2008
I'm looking at two south-facing multifamily residential buildings in
eQuest that are identical except for the wall construction. The base
case walls are uninsulated 18" brick, while the proposed case walls
have an R-11 resistance layer of insulation in addition to the brick.
Windows are double low-e with around a 40% window-wall ratio. The
building is located in Boston.
Cooling energy is higher for the proposed case (insulated walls), and
while investigating I found a strange result in the hourly reports.
The glass transmitted solar load in the insulated case consistently
peaks higher (and troughs lower) than in the uninsulated case. I had
expected the solar loads to be the same in both cases (the solar gains
are indeed the same) since window properties are the same.
How come adding a resistance layer to the walls causes solar loads in
the space to change?
Okay, I just checked the number of response factors for the walls in
both cases. The uninsulated case has 30, and the insulated case has
38. I guess that's the difference, but I still don't feel like I have
a good understanding of it. Thanks for any insights or explanations.
-Dan
More information about the Bldg-sim
mailing list